Default Mobile home wiring

Hi Folks,
When doing a home inspection on a double wide trailer with an addition and attached garage, the pole main disconnect had been eliminated and the panel in the garage appeared to be wired as the main panel,[bonded neutral and ground], but the power to the trailer sub-panel did not appear to come from this box. The grounding could not be determined due to the 4' of snow and the access to the crawl space was blocked. I will be returning when the snow is manageable for a dye test, roof and exterior evaluation and crawl space inspection. Is there any way that this would be an acceptable electrical installation? If all power goes through the garage main panel and it is properly grounded, that is acceptable, right?
Thanks, Ralph
Reply With Quote
  #2  
Old 3/10/07, 9:19 AM
Gerry Beaumont's Avatar
Gerry Beaumont Gerry Beaumont is offline
InterNACHI Member
 
Join Date: Jan 2003
Location: Clearwater, FL
Posts: 5,747
Send a message via AIM to gbeaumont Send a message via MSN to gbeaumont Send a message via Yahoo to gbeaumont
Default Re: Mobile home wiring

Quote:
Originally Posted by rsmith5
Hi Folks,
When doing a home inspection on a double wide trailer with an addition and attached garage, the pole main disconnect had been eliminated and the panel in the garage appeared to be wired as the main panel,[bonded neutral and ground], but the power to the trailer sub-panel did not appear to come from this box. The grounding could not be determined due to the 4' of snow and the access to the crawl space was blocked. I will be returning when the snow is manageable for a dye test, roof and exterior evaluation and crawl space inspection. Is there any way that this would be an acceptable electrical installation? If all power goes through the garage main panel and it is properly grounded, that is acceptable, right?
Thanks, Ralph
Hi Ralph,

I cannot see anything wrong in principle with moving the main from the pole to a panel in the garage, however if that has been done you should be able to see a feeder in the garage panel supplying the remote panel in the unit. The fact that you can't bothers me, I see very many problems with manufactured housing wiring caused by unlicensed electrical work.

Do you have any pictures of the panels that show the breakers and connections? if not maybe you can take some when you go back later, that would help determine the issues.

Regards

Gerry



Virtue is more to be feared than vice, because its excesses are not subject to the regulation of conscience.
Adam Smith (1723-1790)

Commercial property Inspection Tampa, Orlando, Sarasota, Jacksonville, Ft Launderdale, Miami, Florida.
NACHI cell 484-429-5466
NACHI02121106
Reply With Quote
  #3  
Old 3/10/07, 10:11 AM
Tab M. Wilcox Tab M. Wilcox is offline
Active Poster
 
Join Date: Feb 2006
Location: Yuma, AZ
Posts: 165
Please Note: Tab M. Wilcox is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Mobile home wiring

I recently did a manufactured home that had some conditions that would be easy to fix like wire without proper box coneectors, missing junction box covers, etc... The one big condition was where a subpanel was installed in an addition using aluminum feeder with only 3 conductors, and the subpanel was not rated for aluminum feeder on its lugs. The potential buyer took a copy of my report to a licensed electrician and the electrician told him that his company does not touch manufactured homes because all that is remebered is the last electrican that worked on the home. The buyer did not buy the home (I inspected a regular house for him) but I think what that contractor did is wrong. To me that would be a simple thing to correct. The home did not have aluminum 120 volt wiring and otherwise looked okay. Thoughts?
Reply With Quote
  #4  
Old 3/10/07, 12:00 PM
Scott F. Coslett Scott F. Coslett is offline
InterNACHI Member
 
Join Date: Mar 2005
Location: Berwick, PA
Posts: 146
Default Re: Mobile home wiring

Ralph -

Here are a couple of thoughts:

With a mobile home the service equipment is not to be mounted to the home itself. It (service equipment) should be 20'-30' ft away from the home and needs to be visible. If the service is in the garage, and the garage is attached to the mobile home, it would appear as if this is incorrect. Any pic's?

The feeder going to the panel in the home needs to be a 4-wire conductor: 3 insulated conductors (2 ungnded, 1 gnded) and a gnd. Was this visible?

Grounding should be at the service equipment (pole) in a proper installation. I've seen some homes that run a 2nd grounding electrode off of the gnded bus bar in the distribution panel (home). Also, the chassis should be bonded to the gnded bus.

Hope this helps



Scott Coslett
National Property Inspections
Berwick, PA
PennInspector.com
scoslett@pa.metrocast.net

Last edited by scoslett; 3/10/07 at 12:04 PM..
Reply With Quote
  #5  
Old 3/10/07, 4:56 PM
Greg Fretwell Greg Fretwell is offline
Active Poster
 
Join Date: Jul 2004
Location: Estero Florida
Posts: 1,798
Please Note: Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Mobile home wiring

Bear in mind a manufactured home, a mobile home and an RV are 3 different animals. Make sure which one this is.
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
PIC of State Rep and sponsor of new NACHI H.I. Bill in NH. gromicko Misc. Discussion 53 8/30/06 6:58 PM
Hot market hurting home inspections rwand1 Canadian Inspectors 2 5/25/06 8:35 AM
No Ashi / Nachi Conflict!! fcarrio Legislation, Licensing & Legal Issues 5 2/11/06 2:32 PM


All times are GMT -4. The time now is 9:38 AM.


Copyright © International Association of Certified Home Inspectors, Inc. 1 2 3 4 5 6 7 8 9 10 11 12 13 14 15 16 17 18 19 20 21 22 23 24 25 26 27 28 29 30 31 32 33 34 35 36 37 38 39 40 41 42 43 44 45 46 47 48 49 50 51 52 53 54 55 56 57 58 59 60 61 62 63 64 65 66 67 68 69 70 71 72 73 74 75 76 77 78 79 80 81 82 83 84 85 86 87 88 89 90 91 92 93 94 95 96 97 98 99 100 101 102 103 104 105 106 107 108 109 110 111 112 113 114 115 116 117 118 119 120 121 122 123 124 125 126 127 128 129 130 131 132 133 134 135 136 137 138 139 140 141 142 143 144 145 146 147

Popular Sections

:

All Sections

Popular

Membership

Inspection Standards

Education

Chapters & Members

Articles & Links

Other Organizations

 

 

 

NACHI.ORG Statistics

 

 

no new posts