ound this yesterday. I know this issue is frequently discussed but haven't seen this particular situation on the board recently. I'm tossing it out here for comment and discussion. Share your thoughts. The panel installation sure looked pretty.
![]()
You can argue with intelligent people but to argue with a mush head is like trying to grab fog-Thomas Sowell Last edited by mlarson; 6/28/06 at 5:46 PM.. |
|
#2
|
||||
|
||||
|
Connection of the neutral and grounding conductors under the same lug/terminal has never been allowed.
I wouldn't call this a "double tap," I would just call it "wrong." IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ® Jeff PopeJPI Home Inspection Service Santa Clarita CA (661) 212-0738 Santa Clarita Home Inspection http://www.MyInspector.net |
|
#3
|
|||
|
|||
|
Agreed...from Mike Holt's site:
|
|
#4
|
|||
|
|||
|
Please Note:
Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
This has never been legal but it is very common. When these are both on the same circuit it is not a particular hazard but it is still wrong.
The real "douple lug neutral" thing addresses having to disturb one circuit to work on another. It is similar to the requirement about pigtailing multiwire neutrals. |
|
#5
|
|||
|
|||
|
Quote:
Such as: Each grounded conductor shall terminate within the panelboard in an individual terminal that is not also used for another conductor. |
|
#6
|
||||
|
||||
|
Quote:
![]() Read the line that begins "When used as service equipment...." What have you done when you have seen this wiring method? You can argue with intelligent people but to argue with a mush head is like trying to grab fog-Thomas Sowell |
|
#7
|
||||
|
||||
|
Quote:
|
|
#8
|
|||
|
|||
|
Please Note:
Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
Yes that is what it says. Note it doesn't say you can stick neutrals in spare ground bus holes.
extra credit for the first person who knows why (code wise) Last edited by Greg Fretwell; 6/28/06 at 9:20 PM.. |
|
#9
|
||||
|
||||
|
Quote:
|
|
#10
|
|||
|
|||
|
Quote:
Is that what you mean? |
|
#11
|
||||
|
||||
|
Quote:
Otherwise the left bar is ground and the right bar is Neutral if the jumper is not in place in this panel. You can argue with intelligent people but to argue with a mush head is like trying to grab fog-Thomas Sowell |
|
#12
|
||||
|
||||
|
Quote:
You can argue with intelligent people but to argue with a mush head is like trying to grab fog-Thomas Sowell |
|
#13
|
||||
|
||||
|
I think a neutral and ground wire on a single lug is just as much of an issue/defect as double lug neutrals or hot wires. Part of the problem with conductors that regularly carry significant current is wire to wire contact that causes an inferior electrical connection (as opposed to one wire per terminal with good contact against the set screw and lug where the wire is compressed). While the ground wire doesn't regularly carry current, the neutral wire most likely does since it's for a house.
I would write it up the same way, and call it a day JMO & 2-nickels ... Robert O'Connor, PE Consulting Engineer & Inspector LIU CW Post Adjunct Professor NACHI Education Committee www.reporthost.com/-rjo I am absolutely amazed sometimes by how much thought goes into doing things wrong ... |
|
#14
|
||||
|
||||
|
Quote:
Quote:
Also, if ya have a neutral on the grounding buss and there is a problem with the buss strap or bonding lugs, there may be a hot circuit that appears to be dead, which could be a hazard (similar to the reason fused neutrals are not allowed any more). It's always good to understand the reason behind code/labeling provisions ... [P.S. How many times have ya seen neutrals on the ground buss in a service panel, or the service entrance feeder neutral wire connected to the ground buss lug ... Robert O'Connor, PE Consulting Engineer & Inspector LIU CW Post Adjunct Professor NACHI Education Committee www.reporthost.com/-rjo I am absolutely amazed sometimes by how much thought goes into doing things wrong ... Last edited by roconnor; 7/5/06 at 11:28 PM.. |
|
#15
|
|||
|
|||
|
Please Note:
Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
Yup that's it. If you attach a neutral to the grounding bus you get neutral current through the main bonding jumper and that is "objectionable current over the grounding conductors" 250.6(A)
|
![]() |
| Thread Tools | |
|
|
Similar Threads
|
||||
| Thread | Thread Starter | Forum | Replies | Last Post |
| Double Tap Question | ekartal6 | Electrical Inspections | 6 | 10/22/07 7:30 AM |
| Double tapping question | mroe | Electrical Inspections | 17 | 8/30/07 8:32 AM |
| Double Tap Questions | jkogel | Electrical Inspections | 6 | 6/28/07 9:46 PM |
| Double Taps | rwand1 | Canadian Inspectors | 39 | 3/29/06 7:16 PM |