Default More Double Tap Fun.....

ound this yesterday. I know this issue is frequently discussed but haven't seen this particular situation on the board recently. I'm tossing it out here for comment and discussion. Share your thoughts. The panel installation sure looked pretty.

more-double-tap-fun-100_0631-medium-.jpg.JPG
Views:	174
Size:	54.7 KB
ID:	4323more-double-tap-fun-100_0633-medium-.jpg.JPG
Views:	144
Size:	40.8 KB
ID:	4324



You can argue with intelligent people but to argue with a mush head is like trying to grab fog-Thomas Sowell

Never underestimate the difficulty of changing false beliefs by facts. - Henry Rosovsky-Harvard

Michael Larson
Hudson, WI

Services provided in East MN and West WI

[/I]

Last edited by mlarson; 6/28/06 at 5:46 PM..
Reply With Quote
  #2  
Old 6/28/06, 3:08 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,047
Default Re: More Double Tap Fun.....

Connection of the neutral and grounding conductors under the same lug/terminal has never been allowed.

I wouldn't call this a "double tap," I would just call it "wrong."



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #3  
Old 6/28/06, 3:46 PM
Larry D. Kage Larry D. Kage is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Lake Ann (Traverse City), MI
Posts: 8,847
Default Re: More Double Tap Fun.....

Agreed...from Mike Holt's site:
Attached Files
File Type: doc Double lugged neutrals 2.doc (44.0 KB, 246 views)
Reply With Quote
  #4  
Old 6/28/06, 3:59 PM
Greg Fretwell Greg Fretwell is offline
Active Poster
 
Join Date: Jul 2004
Location: Estero Florida
Posts: 1,798
Please Note: Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: More Double Tap Fun.....

This has never been legal but it is very common. When these are both on the same circuit it is not a particular hazard but it is still wrong.
The real "douple lug neutral" thing addresses having to disturb one circuit to work on another. It is similar to the requirement about pigtailing multiwire neutrals.
Reply With Quote
  #5  
Old 6/28/06, 4:38 PM
Larry D. Kage Larry D. Kage is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Lake Ann (Traverse City), MI
Posts: 8,847
Default Re: More Double Tap Fun.....

Quote:
Originally Posted by Greg Fretwell
This has never been legal but it is very common. When these are both on the same circuit it is not a particular hazard but it is still wrong.
The real "douple lug neutral" thing addresses having to disturb one circuit to work on another. It is similar to the requirement about pigtailing multiwire neutrals.
Good info Greg. That's why I underlined some text in the attachment.

Such as:
Each grounded conductor shall terminate within the panelboard in an individual terminal that is not also used for another conductor.
Reply With Quote
  #6  
Old 6/28/06, 5:45 PM
Michael Larson's Avatar
Michael Larson Michael Larson is offline
InterNACHI Member
 
Join Date: May 2006
Location: Hudson, WI including the Twin Cities of MN
Posts: 32,049
Default Re: More Double Tap Fun.....

Quote:
Originally Posted by Greg Fretwell
This has never been legal but it is very common. When these are both on the same circuit it is not a particular hazard but it is still wrong.
The real "douple lug neutral" thing addresses having to disturb one circuit to work on another. It is similar to the requirement about pigtailing multiwire neutrals.
I agree. It presents no real "hazard" but it does not agree with the code in section 408.21. Its frustrating when the manufacturer seems to indicate its permissible by the following text on the panel door.
more-double-tap-fun-100_0634-small-.jpg.JPG
Views:	145
Size:	49.2 KB
ID:	4330

Read the line that begins "When used as service equipment...."

What have you done when you have seen this wiring method?



You can argue with intelligent people but to argue with a mush head is like trying to grab fog-Thomas Sowell

Never underestimate the difficulty of changing false beliefs by facts. - Henry Rosovsky-Harvard

Michael Larson
Hudson, WI

Services provided in East MN and West WI

[/I]
Reply With Quote
  #7  
Old 6/28/06, 8:45 PM
Brian E. Kelly's Avatar
Brian E. Kelly Brian E. Kelly is offline
InterNACHI Member
 
Join Date: Oct 2004
Location: Phoenix, AZ
Posts: 15,973
Default Re: More Double Tap Fun.....

Quote:
Originally Posted by mlarson
I agree. It presents no real "hazard" but it does not agree with the code in section 408.21. Its frustrating when the manufacturer seems to indicate its permissible by the following text on the panel door.
Attachment 4330

Read the line that begins "When used as service equipment...."

What have you done when you have seen this wiring method?
Did I read that wrong, does it say "Any unused nuetral holes may be used for equipment grounds"?
Reply With Quote
  #8  
Old 6/28/06, 9:03 PM
Greg Fretwell Greg Fretwell is offline
Active Poster
 
Join Date: Jul 2004
Location: Estero Florida
Posts: 1,798
Please Note: Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: More Double Tap Fun.....

Yes that is what it says. Note it doesn't say you can stick neutrals in spare ground bus holes.

extra credit for the first person who knows why (code wise)

Last edited by Greg Fretwell; 6/28/06 at 9:20 PM..
Reply With Quote
  #9  
Old 6/28/06, 9:05 PM
Brian E. Kelly's Avatar
Brian E. Kelly Brian E. Kelly is offline
InterNACHI Member
 
Join Date: Oct 2004
Location: Phoenix, AZ
Posts: 15,973
Default Re: More Double Tap Fun.....

Quote:
Originally Posted by Greg Fretwell
Yes that is what it says. Note it doesn't say you can stick neutrals in spare ground bus holes.
That's funny.
Reply With Quote
  #10  
Old 6/28/06, 9:06 PM
Larry D. Kage Larry D. Kage is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Lake Ann (Traverse City), MI
Posts: 8,847
Default Re: More Double Tap Fun.....

Quote:
Originally Posted by mlarson
I agree. It presents no real "hazard" but it does not agree with the code in section 408.21. Its frustrating when the manufacturer seems to indicate its permissible by the following text on the panel door.
Attachment 4330

Read the line that begins "When used as service equipment...."

What have you done when you have seen this wiring method?
Michael, I'm not following you. Grounding conductors can have more than one conductor under a lug screw, as/when stated on the panel board label, but grounded wires cannot.

Is that what you mean?
Reply With Quote
  #11  
Old 6/28/06, 11:12 PM
Michael Larson's Avatar
Michael Larson Michael Larson is offline
InterNACHI Member
 
Join Date: May 2006
Location: Hudson, WI including the Twin Cities of MN
Posts: 32,049
Default Re: More Double Tap Fun.....

Quote:
Originally Posted by bkelly2
Did I read that wrong, does it say "Any unused nuetral holes may be used for equipment grounds"?
That's what it says, Though that's only for 'Service Equipment" use

Otherwise the left bar is ground and the right bar is Neutral if the jumper is not in place in this panel.



You can argue with intelligent people but to argue with a mush head is like trying to grab fog-Thomas Sowell

Never underestimate the difficulty of changing false beliefs by facts. - Henry Rosovsky-Harvard

Michael Larson
Hudson, WI

Services provided in East MN and West WI

[/I]
Reply With Quote
  #12  
Old 6/28/06, 11:20 PM
Michael Larson's Avatar
Michael Larson Michael Larson is offline
InterNACHI Member
 
Join Date: May 2006
Location: Hudson, WI including the Twin Cities of MN
Posts: 32,049
Default Re: More Double Tap Fun.....

Quote:
Originally Posted by lkage
Michael, I'm not following you. Grounding conductors can have more than one conductor under a lug screw, as/when stated on the panel board label, but grounded wires cannot.

Is that what you mean?
Open the attachment in Larry's post #3. That graphic makes it very clear. Sorry for any confustion. Grounded conductor is the term for "Neutral".



You can argue with intelligent people but to argue with a mush head is like trying to grab fog-Thomas Sowell

Never underestimate the difficulty of changing false beliefs by facts. - Henry Rosovsky-Harvard

Michael Larson
Hudson, WI

Services provided in East MN and West WI

[/I]
Reply With Quote
  #13  
Old 6/29/06, 8:59 PM
Robert J. OConnor's Avatar
Robert J. OConnor Robert J. OConnor is offline
InterNACHI Member
 
Join Date: Jul 2003
Location: Long Island, NY
Posts: 1,288
Default Re: More Double Tap Fun.....

I think a neutral and ground wire on a single lug is just as much of an issue/defect as double lug neutrals or hot wires. Part of the problem with conductors that regularly carry significant current is wire to wire contact that causes an inferior electrical connection (as opposed to one wire per terminal with good contact against the set screw and lug where the wire is compressed). While the ground wire doesn't regularly carry current, the neutral wire most likely does since it's for a house.

I would write it up the same way, and call it a day

JMO & 2-nickels ...



Robert O'Connor, PE
Consulting Engineer & Inspector
LIU CW Post Adjunct Professor
NACHI Education Committee
www.reporthost.com/-rjo

I am absolutely amazed sometimes by how much thought goes into doing things wrong ...
Reply With Quote
  #14  
Old 7/5/06, 9:17 PM
Robert J. OConnor's Avatar
Robert J. OConnor Robert J. OConnor is offline
InterNACHI Member
 
Join Date: Jul 2003
Location: Long Island, NY
Posts: 1,288
Default Re: More Double Tap Fun.....

Quote:
Originally Posted by bkelly2
Did I read that wrong, does it say "Any unused neutral holes may be used for equipment grounds"?
So the opposite of unused equipment ground holes being used for neutral wires isn't specifically allowed ... so it should't be done (often is though).

Quote:
Originally Posted by Greg Fretwell
Note it doesn't say you can stick neutrals in spare ground bus holes ... extra credit for the first person who knows why (code wise)
I'm assuming thats because neutral wires in a house normally carry current, where you want a more direct connection between the circuit neutral wire and the service entrance neutral wire (which should be directly connected to the neutral buss).

Also, if ya have a neutral on the grounding buss and there is a problem with the buss strap or bonding lugs, there may be a hot circuit that appears to be dead, which could be a hazard (similar to the reason fused neutrals are not allowed any more).

It's always good to understand the reason behind code/labeling provisions ...

[P.S. How many times have ya seen neutrals on the ground buss in a service panel, or the service entrance feeder neutral wire connected to the ground buss lug ... ]



Robert O'Connor, PE
Consulting Engineer & Inspector
LIU CW Post Adjunct Professor
NACHI Education Committee
www.reporthost.com/-rjo

I am absolutely amazed sometimes by how much thought goes into doing things wrong ...

Last edited by roconnor; 7/5/06 at 11:28 PM..
Reply With Quote
  #15  
Old 7/5/06, 10:53 PM
Greg Fretwell Greg Fretwell is offline
Active Poster
 
Join Date: Jul 2004
Location: Estero Florida
Posts: 1,798
Please Note: Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: More Double Tap Fun.....

Yup that's it. If you attach a neutral to the grounding bus you get neutral current through the main bonding jumper and that is "objectionable current over the grounding conductors" 250.6(A)
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Double Tap Question ekartal6 Electrical Inspections 6 10/22/07 7:30 AM
Double tapping question mroe Electrical Inspections 17 8/30/07 8:32 AM
Double Tap Questions jkogel Electrical Inspections 6 6/28/07 9:46 PM
Double Taps rwand1 Canadian Inspectors 39 3/29/06 7:16 PM


All times are GMT -4. The time now is 3:42 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts