Default Multi-unit condo question

I inspected two apartment style condo units in the same new building (350+ units, downtown) yesterday. The 3 bedroom unit was equipped with AFCI protection and all was fine. The smaller, studio unit, did not have a bedroom and had no AFCI protection. I guess it is assumed that the living room (hallway, closets, kitchen, bedroom and living room were the only rooms) would be used for sleeping, is this a problem?

Comments? How would you write it?

Thanks;



Will Decker, CMI
ILL License # 450.0002240
Board Certified Master Inspector
Decker Home Services, LLC
Chicago and Northern Suburban Home Inspections
Office: (847) 676-8393
Cell: (847) 609-2345
Home: (847) 673-2702

wjd@DeckerHomeServices.com
www.DeckerHomeServices.com

Learn, Educate, Serve and have fun doing it!
Reply With Quote
  #2  
Old 11/7/06, 3:50 PM
wsiegel wsiegel is online now
Active Poster
 
Join Date: Oct 2006
Location: Hialeah, Fl
Posts: 2,542
Please Note: wsiegel is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Multi-unit condo question

That is a good question. Cant wait for the gurus to answer.
In 2008 you wont have to worry about it. All circuits will be AFCI protected.
Reply With Quote
  #3  
Old 11/7/06, 4:36 PM
Speedy Petey Speedy Petey is offline
Unmoderated Guest
 
Join Date: Jul 2006
Posts: 1,297
Please Note: Speedy Petey is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Multi-unit condo question

Quote:
Originally Posted by wsiegel
In 2008 you wont have to worry about it. All circuits will be AFCI protected.
This is for 120v-15 & 20 amp circuits. It is still only a proposal and not likely to pass. ( I hope)
Reply With Quote
  #4  
Old 11/7/06, 4:38 PM
gbeaumont's Avatar
gbeaumont gbeaumont is offline
InterNACHI Member
 
Join Date: Jan 2003
Location: Clearwater, FL
Posts: 6,261
Send a message via AIM to gbeaumont Send a message via MSN to gbeaumont Send a message via Yahoo to gbeaumont
Default Re: Multi-unit condo question

Wil,

It sounds very much like someone is playing the stupid side of a very pedantic arguement there. If your area requires AFCI's in sleeping spaces on new contruction then I would write it up as being defficient in not having one installed.

Regards

Gerry



"To realize our true destiny, we must be guided not by a myth from our past, but by a vision of our future."
(Mark B Adams)

Commercial property Inspection Tampa, Orlando, Sarasota, Jacksonville, Ft Launderdale, Miami, Florida.
NACHI cell 484-429-5466
NACHI02121106

Reply With Quote
  #5  
Old 11/7/06, 10:13 PM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,047
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Multi-unit condo question

basically...is it classified as a bedroom...does it have a cloth closet within the room in question......if it is a living room or similar that is converted....it would be a good argument for AFCI..but as the NEC stands now...if it is not a bedroom as classified....It would not require AFCI....

Important to note that the AFCI requirements are changing and many areas still do not understand them...

I have one AHj that says Lights within a bedroom are not OUTLETS and do not require them to be protected by AFCI.....

But the NEC says OUTLETS...then outlets define and I am briefing it....Utilization equipment....which is equipment that utilizes electric energy for electronic ( smoke detectors ) and lighting....( sure I left out a few....)

Then look up Equipment in the definition and it explains Luminaries are considered equipment....if the electrical energy powers these "equipment" for needs to utilize lighting...then it is required to be protected by AFCI...

Man....did I digress or what....anyway had to teach a local AHJ that the other day....was fun.....anyway......it really depends on it's classification as a bedroom......if it has a closet and is combined....then chances are in the layout and specs of the design it is also a bedroom and then AFCI is required...

In the end...make a call to the local AHJ and ask them HOW they view it..chances are they have no idea....



Paul W. Abernathy,CMI,CPI,CME
National Electrical Code Expert
Electrical & Fire Protection Systems Code Supervisor- Alexandria,VA
Weekly Live Radio Show :http://en.1000mikes.com/show/the_electrical_guru
Weekly Chat on Wednesdays -7:30 PM E.S.T
* Get my 13 hour commentary audio CD for the book "How to Perform Electrical Inspections"

2007 InterNACHI Member of the Year
Reply With Quote
  #6  
Old 11/7/06, 11:31 PM
gbeaumont's Avatar
gbeaumont gbeaumont is offline
InterNACHI Member
 
Join Date: Jan 2003
Location: Clearwater, FL
Posts: 6,261
Send a message via AIM to gbeaumont Send a message via MSN to gbeaumont Send a message via Yahoo to gbeaumont
Default Re: Multi-unit condo question

Hi to all,

Lets try on this senario.

You cannot have a residence without a bedroom.

You can skip, lounges, studys,dining rooms, family rooms, yada, yada, yada, etc.

If there is only one room in a residence apart from Kitchens, bathrooms, closets, and hallways then that space has to be the sleeping or bedroom space. if Chicago code madates that sleeping spaces are protected by AFCI's then that room has to be AFCI protected.

QED.

Regards

Gerry



"To realize our true destiny, we must be guided not by a myth from our past, but by a vision of our future."
(Mark B Adams)

Commercial property Inspection Tampa, Orlando, Sarasota, Jacksonville, Ft Launderdale, Miami, Florida.
NACHI cell 484-429-5466
NACHI02121106

Reply With Quote
  #7  
Old 11/7/06, 11:37 PM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,047
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Multi-unit condo question

You can't speak for the local AHJ....they may in fact determine in their own mind it is not considered a bedroom and if that is the case the NEC refers to the location for AFCI's to be in bedrooms...

Again......READ my post......it explains the potential of both sides....but personally i would install a AFCI



Paul W. Abernathy,CMI,CPI,CME
National Electrical Code Expert
Electrical & Fire Protection Systems Code Supervisor- Alexandria,VA
Weekly Live Radio Show :http://en.1000mikes.com/show/the_electrical_guru
Weekly Chat on Wednesdays -7:30 PM E.S.T
* Get my 13 hour commentary audio CD for the book "How to Perform Electrical Inspections"

2007 InterNACHI Member of the Year
Reply With Quote
  #8  
Old 11/7/06, 11:47 PM
William J. Decker's Avatar
William J. Decker William J. Decker is offline
InterNACHI Member
 
Join Date: Nov 2004
Location: Skokie, IL
Posts: 7,717
Default Re: Multi-unit condo question

Gerry;

As usual, a voice of rationality calling out in the wilderness of local governmental cluelessness.

But, isn't this the lot of home inspectors.

Thanks;



Will Decker, CMI
ILL License # 450.0002240
Board Certified Master Inspector
Decker Home Services, LLC
Chicago and Northern Suburban Home Inspections
Office: (847) 676-8393
Cell: (847) 609-2345
Home: (847) 673-2702

wjd@DeckerHomeServices.com
www.DeckerHomeServices.com

Learn, Educate, Serve and have fun doing it!
Reply With Quote
  #9  
Old 11/7/06, 11:54 PM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,047
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Multi-unit condo question

lol...gotta fight the fight Sir William.....



Paul W. Abernathy,CMI,CPI,CME
National Electrical Code Expert
Electrical & Fire Protection Systems Code Supervisor- Alexandria,VA
Weekly Live Radio Show :http://en.1000mikes.com/show/the_electrical_guru
Weekly Chat on Wednesdays -7:30 PM E.S.T
* Get my 13 hour commentary audio CD for the book "How to Perform Electrical Inspections"

2007 InterNACHI Member of the Year
Reply With Quote
  #10  
Old 11/8/06, 3:15 PM
tdietrich1's Avatar
tdietrich1 tdietrich1 is offline
InterNACHI Member
 
Join Date: Oct 2006
Location: Northampton County - Pa
Posts: 1,954
Send a message via Yahoo to tdietrich1
Default Re: Multi-unit condo question

Quote:
Originally Posted by wsiegel
That is a good question. Cant wait for the gurus to answer.
In 2008 you wont have to worry about it. All circuits will be AFCI protected.
That will be the day.

J/K. I've been told that AFCI aren't even required in NJ because the builder's lobbyists are very powerful. I've upgraded my house's bedroom circuits, and getting money together to get the other circuits upgraded. Plus, I do suggest it as an FYI to home owners.

later,

tom
Reply With Quote
  #11  
Old 11/8/06, 6:50 PM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,047
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Multi-unit condo question

Quote:
Originally Posted by tdietrich1
That will be the day.

J/K. I've been told that AFCI aren't even required in NJ because the builder's lobbyists are very powerful. I've upgraded my house's bedroom circuits, and getting money together to get the other circuits upgraded. Plus, I do suggest it as an FYI to home owners.

later,

tom
lol...go figure...since NJ was the state that won against FPE in the class action lawsuit...lol.......can you say BACKWARDS...I knew that you could...lol



Paul W. Abernathy,CMI,CPI,CME
National Electrical Code Expert
Electrical & Fire Protection Systems Code Supervisor- Alexandria,VA
Weekly Live Radio Show :http://en.1000mikes.com/show/the_electrical_guru
Weekly Chat on Wednesdays -7:30 PM E.S.T
* Get my 13 hour commentary audio CD for the book "How to Perform Electrical Inspections"

2007 InterNACHI Member of the Year
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Important Question for tenant in Georgia (posted by LaWanda Hugley) AskNACHI.org AskNACHI.org Inspection Questions Forum 4 7/30/07 9:36 AM
Question for AC guys gwilcox Inspecting HVAC Systems 7 7/7/07 10:28 PM
Answer to a common question about GFCI's jtedesco1 Electrical Inspections 4 1/12/06 10:29 PM


All times are GMT -4. The time now is 8:23 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts