Default Multi-wire Circuits

Quote:
NEC 210.4 (B) Devices or Equipment. Where a multiwire branch circuit supplies more than one device or equipment on the same yoke, a means shall be provided to disconnect simultaneously all ungrounded conductors supplying those devices or equipment at the point where the branch circuit originates.

A multi-wire circuit is serving a living area of a home. One branch serves the receptacle outlets, while the other serves the lighting outlets.

Question - Are the breakers required to be tied together for simultaneous shutoff?

Please qualify your answer.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
Need a home inspection in Massachusetts? Check out InterNACHI's listing of Massachusetts certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #2  
Old 7/16/10, 2:20 PM
Bruce A. King's Avatar
Bruce A. King Bruce A. King is offline
InterNACHI Member
 
Join Date: Jan 2005
Location: York, SC
Posts: 3,207
Default Re: Multi-wire Circuits

I read a discussion on Mike Holt's forum once where someone said the 2002 code actually required the handle tie when outlets were on the multi wire branch circuits. The 2008 code then included devices and equipment as part of the handle tie requirement.



B.A. King Home Inspections, LLC
www.BAKingHomeInspections.com
Serving Charlotte NC area and Rock Hill SC areas.
CMI Certified Master Inspector and Independent
License NC2449 and SC1597
704 301-3207



"Discovery consists in seeing what everyone else has seen and thinking what no one else has thought."
- Albert Szent-Gyvrgyi, Nobel Prize for Medicine 1937
Reply With Quote
  #3  
Old 7/16/10, 3:56 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,057
Default Re: Multi-wire Circuits

The question is, what is your definition of "equipment on the same yoke?" I generally define "yoke" as a device or piece of equipment contained in a single "space" or enclosure - such as a multi-wire circuit powering a single duplex receptacle.

My interpretation is that there is no need for a handle tie in the instance I described, as these are not "on the same yoke."



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #4  
Old 7/16/10, 4:15 PM
Jeffrey R. Wicklander's Avatar
Jeffrey R. Wicklander Jeffrey R. Wicklander is offline
InterNACHI Member
 
Join Date: Mar 2008
Location: Lake Forest, Il
Posts: 1,223
Default Re: Multi-wire Circuits

No requirement for a handle-tie, until a house is built under the 2008 NEC adoption that requires a MWC to include a handle-tie.

Jeff



Jeff Wicklander
Corwick Home Services

Join my business on Facebook
Reply With Quote
  #5  
Old 7/16/10, 4:17 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,057
Default Re: Multi-wire Circuits

CA is currently using the 2005 NEC. Can you post the 2008 section?



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #6  
Old 7/16/10, 4:20 PM
Bruce A. King's Avatar
Bruce A. King Bruce A. King is offline
InterNACHI Member
 
Join Date: Jan 2005
Location: York, SC
Posts: 3,207
Default Re: Multi-wire Circuits

I did see that mentioned in lots of discussions, a yoke is simply the strap on an outlet or switch body used to mount it.

Some "experts" are posting on the web that ALL multiwire circuits must have handle ties or be a dedicated double pole breaker based on the 2008 code.

Here is a good article.....

http://www.ecmag.com/?fa=article&articleID=8741



B.A. King Home Inspections, LLC
www.BAKingHomeInspections.com
Serving Charlotte NC area and Rock Hill SC areas.
CMI Certified Master Inspector and Independent
License NC2449 and SC1597
704 301-3207



"Discovery consists in seeing what everyone else has seen and thinking what no one else has thought."
- Albert Szent-Gyvrgyi, Nobel Prize for Medicine 1937
Reply With Quote
  #7  
Old 7/16/10, 4:25 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,057
Default Re: Multi-wire Circuits

Good article - thanks Bruce.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #8  
Old 7/16/10, 6:37 PM
Chuck Evans's Avatar
Chuck Evans Chuck Evans is offline
InterNACHI Member
 
Join Date: Sep 2006
Location: Stagecoach, TX
Posts: 2,037
Default Re: Multi-wire Circuits

Quote:
Originally Posted by jpope View Post
The question is, what is your definition of "equipment on the same yoke?" I generally define "yoke" as a device or piece of equipment contained in a single "space" or enclosure - such as a multi-wire circuit powering a single duplex receptacle.

My interpretation is that there is no need for a handle tie in the instance I described, as these are not "on the same yoke."
That is consistent with the way that I have always treated it. If they are connected separately to a single duplex receptacle or stacked switches on the same yoke - yes; separate outlets and switches - no. I consider whether someone can safely work on one circuit and not be endangered by the other. Though the shared grounded conductor may present a potential issue.



Chuck Evans (TREC #7657)
Level III Infraspection Institute Certified Infrared Thermographer (#8402)
HomeCert Houston Home Inspections & Thermal Inspections Find us on Facebook
Houston Thermal Inspections & Infrared Imaging Find us on Facebook
Houston Home Inspector

Houston, TX
Reply With Quote
  #9  
Old 7/16/10, 6:40 PM
Jim Port Jim Port is offline
Unmoderated Guest
 
Join Date: Jul 2007
Location: Maryland
Posts: 805
Please Note: Jim Port is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Multi-wire Circuits

Quote:
Originally Posted by cevans View Post
I consider whether someone can safely work on one circuit and not be endangered by the other. Though the shared grounded conductor may present a potential issue.
This is the reason the the 08 NEC now requires a 2 pole breaker for MWBCs.
Reply With Quote
  #10  
Old 7/16/10, 9:45 PM
Robert Meier's Avatar
Robert Meier Robert Meier is online now
Active Poster
 
Join Date: Feb 2010
Location: New Jersey
Posts: 1,250
Please Note: Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Multi-wire Circuits

All multi-wire branch circuits require simultaneous disconnect (multi-pole CB or handle tie) under the 2008 NEC. This requirement was actually in the 2005 NEC {605.7} but only applied to freestanding type furniture partitions, and as mentioned MWBC's on the same yoke.

Here's the 2008:

Quote:
210.4 Multiwire Branch Circuits.
(A) General. Branch circuits recognized by this article shall be permitted as multiwire circuits. A multiwire circuit shall be permitted to be considered as multiple circuits. All conductors of a multiwire branch circuit shall originate from the same panelboard or similar distribution equipment.
FPN: A 3-phase, 4-wire, wye-connected power system used to supply power to nonlinear loads may necessitate that the power system design allow for the possibility of high harmonic currents on the neutral conductor.
(B) Disconnecting Means. Each multiwire branch circuit shall be provided with a means that will simultaneously disconnect all ungrounded conductors at the point where the branch circuit originates.
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
"UFER" Ground? see last paragraph. jtedesco1 Electrical Inspections 19 8/23/11 3:56 PM
Evaluating your home's wiring system mcyr Electrical Inspections 0 12/30/09 1:31 PM
Multi Wire Circuits jallingham Electrical Inspections 7 10/15/08 2:18 PM
What's this video worth? jtedesco1 Inspection Education & Training 5 4/18/08 9:24 AM
Nice Report on AL Wire Terminations - Enjoy pabernathy Electrical Inspections 0 7/2/07 12:35 PM