Do you write that up as a defect? Example: dishwasher and garbage disposal share the same grounded (neutral) conductor. This is a common wiring practice

If you don't, I'd recommend it. Here's the hazard: you need to change the garbage disposal. You flip its breaker off. You're working on the neutral conductor and someone turns on the dishwasher. The neutral is now a current carrying conductor. Ouch! Begin to curse wife!

Photo below: 2 lower breakers serve 2 kitchen appliances. One neutral.

multi-wire-circuits-no-handle-ties-082609-073.jpg



“The things that will destroy America are peace at any price,
prosperity at any cost, safety first instead of duty first,
the love of soft living, and the get-rich-quick theory of life.”
Theodore Roosevelt


Joe Funderburk, CMI
Alpha & Omega Home Inspections, LLC
Inspecting Upstate SC & Charlotte Metro, NC
NACHI ID: NACHI05120170
www.aohomeinspection.com


Reply With Quote
Find an InterNACHI certified Connecticut Home Inspector (and anywhere else in North America)
  #2  
Old 8/27/09, 2:27 PM
Jim Port Jim Port is offline
Unmoderated Guest
 
Join Date: Jul 2007
Location: Maryland
Posts: 805
Please Note: Jim Port is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Multi-wire circuits: no handle ties

Prior to the 08 NEC there was no requirement for a handle tie on MWBCs unless in commercial settings or on the same yoke. This is now required whenever MWBCs are used along with the conductors of the MWBC to be grouped together in the panel.
Reply With Quote
  #3  
Old 8/27/09, 2:55 PM
Jim Port Jim Port is offline
Unmoderated Guest
 
Join Date: Jul 2007
Location: Maryland
Posts: 805
Please Note: Jim Port is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Multi-wire circuits: no handle ties

I forgot to add in my other post that the neutral was required to be pigtailed. You could not use the device to splice the neutral in the MWBC.
Reply With Quote
  #4  
Old 8/27/09, 10:15 PM
Jeffrey R. Wicklander's Avatar
Jeffrey R. Wicklander Jeffrey R. Wicklander is offline
InterNACHI Member
 
Join Date: Mar 2008
Location: Lake Forest, Il
Posts: 1,223
Default Re: Multi-wire circuits: no handle ties

Won't mention anything about it unless the house was built while the jurisdiction was under 2008 code.

Jeff



Jeff Wicklander
Corwick Home Services

Join my business on Facebook
Reply With Quote
  #5  
Old 8/27/09, 10:33 PM
Mark E. Northrup's Avatar
Mark E. Northrup Mark E. Northrup is offline
InterNACHI Member
 
Join Date: Dec 2008
Location: Oregon
Posts: 473
Default Re: Multi-wire circuits: no handle ties

Joe I was wondering how you know that they are sharing a neutral. From the pic i see a red wire and a black wire. but cannot see how they share a neutral. Thanks
Mark





House 2 Home LLC
503-602-1420
HomePros@House2HomeLLC.ORG
Protecting Peace of Mind One House at a Time
IAC2 Certified
IR Certified
A favorite place on Google Maps
Reply With Quote
  #6  
Old 8/27/09, 10:48 PM
Jeffrey R. Wicklander's Avatar
Jeffrey R. Wicklander Jeffrey R. Wicklander is offline
InterNACHI Member
 
Join Date: Mar 2008
Location: Lake Forest, Il
Posts: 1,223
Default Re: Multi-wire circuits: no handle ties

If romex was run, it would be pretty simple to tell. Two hots in the jacket along with a single neutral coming out of the panel. If it was run in pipe, they may be the only three wires running in the pipe.

Jeff



Jeff Wicklander
Corwick Home Services

Join my business on Facebook
Reply With Quote
  #7  
Old 8/27/09, 10:48 PM
Joe Funderburk, CMI's Avatar
Joe Funderburk, CMI Joe Funderburk, CMI is offline
InterNACHI Member
 
Join Date: Dec 2005
Location: Hickory Grove, SC
Posts: 8,343
Send a message via Yahoo to jfunderburk
Default Re: Multi-wire circuits: no handle ties

Quote:
Originally Posted by mnorthrup View Post
Joe I was wondering how you know that they are sharing a neutral. From the pic i see a red wire and a black wire. but cannot see how they share a neutral. Thanks
Mark
Count the 15/20 amp breakers and count the neutrals. They should be equal in number. In this case, there was one more breaker than there were neutrals. A scan of the incoming wires revealed that this one was a 3 conductor + ground.



“The things that will destroy America are peace at any price,
prosperity at any cost, safety first instead of duty first,
the love of soft living, and the get-rich-quick theory of life.”
Theodore Roosevelt


Joe Funderburk, CMI
Alpha & Omega Home Inspections, LLC
Inspecting Upstate SC & Charlotte Metro, NC
NACHI ID: NACHI05120170
www.aohomeinspection.com


Reply With Quote
  #8  
Old 8/27/09, 10:50 PM
Joe Funderburk, CMI's Avatar
Joe Funderburk, CMI Joe Funderburk, CMI is offline
InterNACHI Member
 
Join Date: Dec 2005
Location: Hickory Grove, SC
Posts: 8,343
Send a message via Yahoo to jfunderburk
Default Re: Multi-wire circuits: no handle ties

Quote:
Originally Posted by jwicklander View Post
Won't mention anything about it unless the house was built while the jurisdiction was under 2008 code.

Jeff
I wrote it up as a recommended upgrade. It's a safety hazard, same as the lack of a GFCI, no matter the age of the home.



“The things that will destroy America are peace at any price,
prosperity at any cost, safety first instead of duty first,
the love of soft living, and the get-rich-quick theory of life.”
Theodore Roosevelt


Joe Funderburk, CMI
Alpha & Omega Home Inspections, LLC
Inspecting Upstate SC & Charlotte Metro, NC
NACHI ID: NACHI05120170
www.aohomeinspection.com


Reply With Quote
  #9  
Old 8/27/09, 10:52 PM
Jeffrey R. Wicklander's Avatar
Jeffrey R. Wicklander Jeffrey R. Wicklander is offline
InterNACHI Member
 
Join Date: Mar 2008
Location: Lake Forest, Il
Posts: 1,223
Default Re: Multi-wire circuits: no handle ties

I don't consider it a safety hazard. It's a very commonly applied and accepted work practice.

Jeff



Jeff Wicklander
Corwick Home Services

Join my business on Facebook
Reply With Quote
  #10  
Old 8/27/09, 11:34 PM
Joe Funderburk, CMI's Avatar
Joe Funderburk, CMI Joe Funderburk, CMI is offline
InterNACHI Member
 
Join Date: Dec 2005
Location: Hickory Grove, SC
Posts: 8,343
Send a message via Yahoo to jfunderburk
Default Re: Multi-wire circuits: no handle ties

Quote:
Originally Posted by jwicklander View Post
I don't consider it a safety hazard.

Jeff
So, then, what is the purpose of the handle tie in today's code?



“The things that will destroy America are peace at any price,
prosperity at any cost, safety first instead of duty first,
the love of soft living, and the get-rich-quick theory of life.”
Theodore Roosevelt


Joe Funderburk, CMI
Alpha & Omega Home Inspections, LLC
Inspecting Upstate SC & Charlotte Metro, NC
NACHI ID: NACHI05120170
www.aohomeinspection.com


Reply With Quote
  #11  
Old 8/27/09, 11:39 PM
Jeffrey R. Wicklander's Avatar
Jeffrey R. Wicklander Jeffrey R. Wicklander is offline
InterNACHI Member
 
Join Date: Mar 2008
Location: Lake Forest, Il
Posts: 1,223
Default Re: Multi-wire circuits: no handle ties

The NEC is starting to become a babysitting service because of the unqualified personnel that think they know how to work on electrical. Do you recommend every client to upgrade all their receptacles to be tamper proof as required?

Jeff



Jeff Wicklander
Corwick Home Services

Join my business on Facebook
Reply With Quote
  #12  
Old 8/28/09, 12:08 AM
Bruce A. King's Avatar
Bruce A. King Bruce A. King is offline
InterNACHI Member
 
Join Date: Jan 2005
Location: York, SC
Posts: 3,207
Default Re: Multi-wire circuits: no handle ties

Quote:
Originally Posted by jfunderburk View Post
So, then, what is the purpose of the handle tie in today's code?
The handle ties are needed on 240V loads so that both breaker sections trip if the load is excessive on just one leg.

The disposal and d/w are just 120V loads so there is no reason to trip both breakers if one draws too much.


As far as I know, the situation in the original post is considered acceptable since "only electricians should be working with the wiring".

I was installing a ceiling fan once and the power company guy came to turn off the power to the house so I was just working away and got fried because of two reasons. He turned it back on within 10 minutes without coming back to the door to warn me even after I told him what I was doing and voltage was still at the fixture with the switch off to a crappy wiring technique called "switched neutrals".

Maybe someone has the code history on switched neutrals (thread drift here), I don't think they are allowed anymore but once were allowed.



B.A. King Home Inspections, LLC
www.BAKingHomeInspections.com
Serving Charlotte NC area and Rock Hill SC areas.
CMI Certified Master Inspector and Independent
License NC2449 and SC1597
704 301-3207



"Discovery consists in seeing what everyone else has seen and thinking what no one else has thought."
- Albert Szent-Gyvrgyi, Nobel Prize for Medicine 1937
Reply With Quote
  #13  
Old 8/28/09, 12:09 AM
Joe Funderburk, CMI's Avatar
Joe Funderburk, CMI Joe Funderburk, CMI is offline
InterNACHI Member
 
Join Date: Dec 2005
Location: Hickory Grove, SC
Posts: 8,343
Send a message via Yahoo to jfunderburk
Default Re: Multi-wire circuits: no handle ties

Only electricians install garbage disposals?



“The things that will destroy America are peace at any price,
prosperity at any cost, safety first instead of duty first,
the love of soft living, and the get-rich-quick theory of life.”
Theodore Roosevelt


Joe Funderburk, CMI
Alpha & Omega Home Inspections, LLC
Inspecting Upstate SC & Charlotte Metro, NC
NACHI ID: NACHI05120170
www.aohomeinspection.com


Reply With Quote
Find an InterNACHI certified Connecticut Home Inspector (and anywhere else in North America)
  #14  
Old 8/28/09, 12:24 AM
Mark E. Northrup's Avatar
Mark E. Northrup Mark E. Northrup is offline
InterNACHI Member
 
Join Date: Dec 2008
Location: Oregon
Posts: 473
Default Re: Multi-wire circuits: no handle ties

Quote:
Originally Posted by jfunderburk View Post
Only electricians install garbage disposals?
If that was the case i would be out of work. And home depot would not sell disposals.
I agree with you on the neutral though. It would be a safety concern.





House 2 Home LLC
503-602-1420
HomePros@House2HomeLLC.ORG
Protecting Peace of Mind One House at a Time
IAC2 Certified
IR Certified
A favorite place on Google Maps
Reply With Quote
  #15  
Old 8/28/09, 12:28 AM
Bruce A. King's Avatar
Bruce A. King Bruce A. King is offline
InterNACHI Member
 
Join Date: Jan 2005
Location: York, SC
Posts: 3,207
Default Re: Multi-wire circuits: no handle ties

Anyone can install one, just some get shocked in the process.

I have to admit, I never thought of that scenario.

I did a reinspect once where they still had not tightened a panel lug, the builder called the electrician and the owner of this fairly large company was in the area so he came right over to fix it. I watched this guy, he probably had 30 years experience, he turned off the main breaker and pulled out a big allen wrench (non insulated type) and started to tighten the lug and stopped. He put the tool in his pocket and walked about 60 feet to the truck and came back with a voltmeter and made sure the power was off and then proceeded. I was thinking, yep, he has seen some weird wiring problems and was not ready to take a chance that day.



B.A. King Home Inspections, LLC
www.BAKingHomeInspections.com
Serving Charlotte NC area and Rock Hill SC areas.
CMI Certified Master Inspector and Independent
License NC2449 and SC1597
704 301-3207



"Discovery consists in seeing what everyone else has seen and thinking what no one else has thought."
- Albert Szent-Gyvrgyi, Nobel Prize for Medicine 1937
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
"UFER" Ground? see last paragraph. jtedesco1 Electrical Inspections 19 8/23/11 3:56 PM
GFCIs on 2 wire circuits dscott2 Electrical Inspections 10 4/4/09 2:41 PM
Multi Wire Circuits jallingham Electrical Inspections 7 10/15/08 2:18 PM
What's this video worth? jtedesco1 Inspection Education & Training 5 4/18/08 9:24 AM
Nice Report on AL Wire Terminations - Enjoy pabernathy Electrical Inspections 0 7/2/07 12:35 PM


All times are GMT -4. The time now is 7:46 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts