A recent client called in an electrician to address some of the issues that I called out. After he (the electrician)minimized my comments on multiple neutrals on one terminal, he told me that since the panel was 200amps, it needed two grounding electrodes. One for each 100amps of service. Has anyone else heard of this? I have not found any reference to this. Thanks.
|
|
#2
|
|||
|
|||
|
Please Note:
Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
Try another electrician. This guy is clueless
|
|
#3
|
||||
|
||||
|
Please Note:
Mike Whitt is a non-member guest and is in no way affiliated with InterNACHI or its members.
Quote:
I agree If he means two rods it would be due to the wording in 250.56 or if it is water pipe then 250.53. The size of the service plays no role in the number or type of electrodes that are installed. I would also be concerned with the things that he minimized. |
|
#4
|
|||
|
|||
|
Please Note:
Speedy Petey is a non-member guest and is in no way affiliated with InterNACHI or its members.
Quote:
I SINCERELY hope this guy was joking! |
|
#5
|
||||
|
||||
|
Quote:
IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ® Jeff PopeJPI Home Inspection Service Santa Clarita CA (661) 212-0738 Santa Clarita Home Inspection http://www.MyInspector.net |
|
#6
|
||||
|
||||
|
Ah you guys seem to be missing the point. When someone tells me something has to be one way, or another, I usually follow up with..... why?
This electrician might now that the AHJ will not approve installations with less than 2 ground rods over 100 amp services. Back to the OP's questions, not that specifically, but weirdness of AHJ's in Pa? Oh yes. I have one, very respectable (might be a pain to some) but I respect his knowledge, option, and position, that refuses to allow GFCI's on non-grounded circuits. Although allowed by by the NEC, he wasn't a separate ground run, and if you run a 'separate' ground, then you are in violation another article(he'll inform you of that before you run it), and the only option is to re-run the circuit. tom |
|
#7
|
||||
|
||||
|
Is he willing to pay for the upgrade cost of rewiring? $$$.
|
|
#8
|
|||
|
|||
|
Please Note:
Brian A. MacNeish is a non-member guest and is in no way affiliated with InterNACHI or its members.
but weirdness of AHJ's in Pa? Oh yes. I have one, very respectable (might be a pain to some) but I respect his knowledge, option, and position, that refuses to allow GFCI's on non-grounded circuits.
A GFCI trips at 5-10 milliamps leakage to ground (possibly through you!!!). A 15 amp fuse or breaker trips a two conductor circuit with ground at 15 amps leakage to ground wire does 100% ensure that no current will go through you. If something is leaking 10 amps somewhere and is not causing a "dead short" that opens the circuit.......what may happen??? I would rather have a GFCI protecting that circuit!!! |
|
#9
|
||||
|
||||
|
Quote:
tom P.S. For the OP, give the AHJ a call, he/she has the final call. I know of places where they don't even check for grounding rods. |
|
#10
|
|||
|
|||
|
Please Note:
Brian A. MacNeish is a non-member guest and is in no way affiliated with InterNACHI or its members.
Thomas:
I was implying that an ungrounded circuit protected by a GFI is safer than a two conductor with ground when small amp shorts/leakage are not tripping a 15 amp overcurrent device. Sure it's fine to put the GFI in after a new circuit wire is run but as someone else said "who's going to pay for the extra wiring costs?" The reason we have uniform codes is so all work done is safely and all are treated equally. Sounds like if you step outside the town or county you're in, safe, code approved wiring may be cheaper The fact that a code official is overstepping their authority without having the law to back them is atrocious. If an electrician wanted to wire beyond code minimums that is their decision and it benefits his/her customers. But for the inspector to decide that a code drawn up by some of the most experienced in the electrical industry by concensus is not adequate..............what if every type of inspector did this?? Someone should be challenging him. |
|
#11
|
||||
|
||||
|
Please Note:
Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Quote:
|
|
#12
|
|||
|
|||
|
Please Note:
jbreazeale is a non-member guest and is in no way affiliated with InterNACHI or its members.
The AHJ can pretty much do what it wants to, outside of uniform state codes....IF the state has one.
|
![]() |
| Thread Tools | |
|
|
Similar Threads
|
||||
| Thread | Thread Starter | Forum | Replies | Last Post |
| Double tapped grounds. | gheller | Electrical Inspections | 10 | 4/17/07 8:14 PM |
| multiple apt units | mbonvissuto | Miscellaneous Discussion for Inspectors | 2 | 3/10/07 6:41 PM |
| multiple apt units | mbonvissuto | Miscellaneous Discussion for Inspectors | 3 | 3/10/07 1:06 PM |