Default Murray fuse panel

I ran into this on my last “mock” inspection.(yes I'm a newbe" )

Murray fuse panel. House was built in early 60's.

  • Meter is 200 AMP
  • 4/0 Alum SEC (200 AMP)
  • 200 AMP rated panel
This is fine and would have said “200 AMP service” The question is the “Plugin Fusible Components” are - 100 AMP (top) and 60 AMP (middle).

There is a 100 AMP “sub-panel” located in another area and there is an add-on breaker for the A/C mounted on top of the main service panel.

All fuses are either 15 or 20 AMP.

My questions – Is this really a 200 AMP service? And should this be updated to a new breaker panel?
Attached Thumbnails
murray-fuse-panel-panel.jpg   murray-fuse-panel-top.jpg   murray-fuse-panel-middle.jpg  
Reply With Quote
Need a home inspection in Connecticut? Check out InterNACHI's listing of Connecticut certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #2  
Old 3/26/10, 9:20 AM
Michael Roberson's Avatar
Michael Roberson Michael Roberson is offline
InterNACHI Member
 
Join Date: May 2008
Location: West Michigan, Lower Penninsula
Posts: 1,732
Default Re: Murray fuse panel

Wow What a beauty. Never seen one like this. For you to run into this on your first few mock inspections is a great learning experience.

My thoughts: (Im sure Paul Abernathy will spank me with his vastly superior knowledge)
You go by the lowest rated point, if it is a 200 A panel, but 100 A feed wire, it is 100 A. If there are 2 100 A main fuses (one per lag) I would call this a 200 A panel.

As for replacing, I would recommend updating based on age and useful life. If it was put in in the early 60's, it is 50 years old. My issue with Fuse panels is the Human element: I always find 20-30 amp fuses where a 15 amp belongs, circumventing the safety measures.

**Post script** Please put your location in your profile, thanks.
Reply With Quote
  #3  
Old 3/26/10, 10:14 AM
Jim Port Jim Port is offline
Unmoderated Guest
 
Join Date: Jul 2007
Location: Maryland
Posts: 805
Please Note: Jim Port is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Murray fuse panel

Quote:
Originally Posted by mroberson View Post
If there are 2 100 A main fuses (one per lag) I would call this a 200 A panel.
This would still be a 100 amp rated service. You do not add the ratings of the legs together.
Reply With Quote
  #4  
Old 3/26/10, 1:45 PM
Michael Roberson's Avatar
Michael Roberson Michael Roberson is offline
InterNACHI Member
 
Join Date: May 2008
Location: West Michigan, Lower Penninsula
Posts: 1,732
Default Re: Murray fuse panel

Jim is correct. ( I looked it up) You cannot add the lags together, therefore it is only a 100 A panel.
Reply With Quote
  #5  
Old 3/26/10, 2:50 PM
Mark Thorman Mark Thorman is offline
Unmoderated Guest
 
Join Date: Mar 2008
Posts: 392
Please Note: Mark Thorman is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Murray fuse panel

Quote:
Originally Posted by Jim Port View Post
This would still be a 100 amp rated service. You do not add the ratings of the legs together.
But if the meter, service wires and main panel are rated for 200 amps, is not the "service" rated at 200 amps?

www.MauiHomeInspections.com
Reply With Quote
  #6  
Old 3/26/10, 3:11 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,057
Default Re: Murray fuse panel

It's better described as service capacity, rather than service rating. The service capacity is 100 amps.

If all components are rated for 200 amps except for one, the capacity is limited by that one component. So there's no real point in reporting component ratings.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net



Last edited by jpope; 3/26/10 at 3:20 PM..
Reply With Quote
  #7  
Old 3/26/10, 3:12 PM
Jim Port Jim Port is offline
Unmoderated Guest
 
Join Date: Jul 2007
Location: Maryland
Posts: 805
Please Note: Jim Port is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Murray fuse panel

While the service entrance conductors may be 200 amp rated, the smallest part of the service is only rated for 100 amps.
Reply With Quote
  #8  
Old 3/26/10, 4:28 PM
Robert Meier's Avatar
Robert Meier Robert Meier is online now
Active Poster
 
Join Date: Feb 2010
Location: New Jersey
Posts: 1,250
Please Note: Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Murray fuse panel

Quote:
Originally Posted by Jim Port View Post
While the service entrance conductors may be 200 amp rated, the smallest part of the service is only rated for 100 amps.
Jim,
How do we know that from the information that Donald provided? He said that he has a 100 amp and a 60 amp plug-in fuse component. Do we know that the 100 amp is feeding the 60 amp? To me it sounds like he has a 100 amp and a 60 amp.
Reply With Quote
  #9  
Old 3/26/10, 5:02 PM
David Hays David Hays is offline
InterNACHI Member
 
Join Date: Feb 2010
Location: Denver, CO
Posts: 353
Default Re: Murray fuse panel

Is this panel a split bus panel?

It apears to me that it is. To me it would be rated at 200 amps which is the capacity of the panel, feeders and meter housing.

If you have a split bus pane & feeders that is rated for 125 amps and it has two 50 amp and one 30 amp breakers (within the 6 handle rule) you wouldn't say it is a 30 amp. It would still be a 125 amp.

Just my opinion.



David Hays
All Points Home Inspections LLC
Denver, CO
720-670-0366
allpointshomeinspect@yahoo.com
www.allpointshomeinspections.org
Reply With Quote
  #10  
Old 3/26/10, 5:28 PM
dtowers dtowers is offline
InterNACHI Member
 
Join Date: Nov 2009
Location: Levittown (Phila) PA
Posts: 4
Default Re: Murray fuse panel

Here are some additional pics of the interior of the panel. It does appear that the top is feeding the bottom.

I hope these will explain this in a little more detail.
Attached Thumbnails
murray-fuse-panel-panel-top.jpg   murray-fuse-panel-panel-mid-1.jpg   murray-fuse-panel-panel-mid-2.jpg   murray-fuse-panel-panel-bottom.jpg  
Reply With Quote
  #11  
Old 3/26/10, 8:35 PM
Robert Meier's Avatar
Robert Meier Robert Meier is online now
Active Poster
 
Join Date: Feb 2010
Location: New Jersey
Posts: 1,250
Please Note: Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Murray fuse panel

From the additional photo's it looks to me like the panel has no main and 6 pull out overcurrent protection devices. Five on the top for various loads and the sixth one feeding the fuse portion on the bottom.
Reply With Quote
  #12  
Old 3/26/10, 11:49 PM
Chuck Evans's Avatar
Chuck Evans Chuck Evans is offline
InterNACHI Member
 
Join Date: Sep 2006
Location: Stagecoach, TX
Posts: 2,037
Default Re: Murray fuse panel

Very interesting older panel. Lucky to encounter one like that on one of your first inspections (even if it didn't seem like it at the time). This is worth like 20 plain old mundane service panels as far as what you can learn from it.

Michael - You're under arrest for breaking Watts Law
Quote:
If there are 2 100 A main fuses (one per lag) I would call this a 200 A panel.
Just teasing



Chuck Evans (TREC #7657)
Level III Infraspection Institute Certified Infrared Thermographer (#8402)
HomeCert Houston Home Inspections & Thermal Inspections Find us on Facebook
Houston Thermal Inspections & Infrared Imaging Find us on Facebook
Houston Home Inspector

Houston, TX
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
National Electrical Code Information and Discussion jtedesco1 Electrical Inspections 50 6/15/10 7:28 PM
Electrical for Dummies mcyr Electrical Inspections 16 6/9/08 9:59 PM
Fuse panel Michael Martin Electrical Inspections 7 11/1/07 2:18 PM
Bad electrical problem Pest Guy Electrical Inspections 4 1/20/06 9:26 PM


All times are GMT -4. The time now is 7:47 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts