Default Murray Split Main Panel

Murray Split Main Panel



Joseph P. Hagarty
joseph.hagarty@comcast.net
Main Line Inspections, Inc.
Phone: 610-399-3675
Email: MainLineHI@comcast.net

http://pa.nachi.org/mainlinepa/about.html
http://www.householdinspector.com

National President / NACHI (2003-2004)
NACHI Education Committee Member

Last edited by jhagarty; 2/18/08 at 4:34 PM..
Reply With Quote
  #2  
Old 2/17/07, 4:18 PM
Marc D. Shunk's Avatar
Marc D. Shunk Marc D. Shunk is offline
Banned
 
Join Date: Dec 2006
Location: Central PA
Posts: 1,980
Please Note: Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Murray Split Main Panel

Looks like some handle ties not originally designed for use as handle ties. About 9,000 NM cables going through one Tomic connector. Grounds made up outside the enclosure. Missing GEC(s). The conductors on the 30 amp "tied" breakers may or may not be of an appropriate gauge for that size OCPD device. Hard to tell. That's some stuff I notice right off the bat.

If those grounds outside of the box were done before 1967 (going off memory, but close), they might have been done legally.

Last edited by Marc D. Shunk; 2/17/07 at 4:23 PM..
Reply With Quote
  #3  
Old 2/17/07, 4:55 PM
Joseph Hagarty,  CMI's Avatar
Joseph Hagarty, CMI Joseph Hagarty,  CMI is offline
InterNACHI Member
 
Join Date: Jan 2003
Location: Parkesburg, PA
Posts: 5,636
Default Re: Murray Split Main Panel

Home was built in 1966. Original Panel...

I noted the improper grounding anyway........

The Roofing Nails as breaker ties were interesting...



Joseph P. Hagarty
joseph.hagarty@comcast.net
Main Line Inspections, Inc.
Phone: 610-399-3675
Email: MainLineHI@comcast.net

http://pa.nachi.org/mainlinepa/about.html
http://www.householdinspector.com

National President / NACHI (2003-2004)
NACHI Education Committee Member
Reply With Quote
  #4  
Old 2/17/07, 5:11 PM
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,072
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Murray Split Main Panel

Legally or not......recommend those EGC's be bought into the box properly as if the entire house has this then it can go from a ungrounded system to a grounded system and be a MORE appealing sale.....people seem to want it.

Bet their are 3 prong plugs in the house.....done without that nice EGC being done..........

The 1965 NEC I have talks about grounding the receptacles IF they have a grounding terminal....starts to get BLURRY after that unless it is to equipment and then they require it.



Paul W. Abernathy
Reply With Quote
  #5  
Old 2/17/07, 7:27 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,047
Default Re: Murray Split Main Panel

Technically, the breakers feeding the lower bus should also be tied together. . .



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #6  
Old 2/17/07, 7:29 PM
Marc D. Shunk's Avatar
Marc D. Shunk Marc D. Shunk is offline
Banned
 
Join Date: Dec 2006
Location: Central PA
Posts: 1,980
Please Note: Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Murray Split Main Panel

Quote:
Originally Posted by jpope
Technically, the breakers feeding the lower bus should also be tied together. . .
My gut sorta tells me the same thing, but darned if I can come up with anything specific that would require that. You got something? I can find stuff about branch circuits, but not for services or feeders.

Last edited by Marc D. Shunk; 2/17/07 at 7:32 PM..
Reply With Quote
  #7  
Old 2/17/07, 7:32 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,047
Default Re: Murray Split Main Panel

The fact that the lower bus would be considered a "240 volt circuit" or a 240 volt feed, is enough for me. There is at least one two-pole breaker fed from the lower bus, so there is the potential for only one leg to be energized.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #8  
Old 2/17/07, 7:36 PM
Marc D. Shunk's Avatar
Marc D. Shunk Marc D. Shunk is offline
Banned
 
Join Date: Dec 2006
Location: Central PA
Posts: 1,980
Please Note: Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Murray Split Main Panel

Quote:
Originally Posted by jpope
The fact that the lower bus would be considered a "240 volt circuit" or a 240 volt feed, is enough for me. There is at least one two-pole breaker fed from the lower bus, so there is the potential for only one leg to be energized.
Yeah, that's why my gut is telling me the same thing you're thinking, but there is nothing that I can find that requires simultaneous opeing of both poles of the overcurrent device in a service. For some branch circuits, yes. After all, you protect 240 volt circuits with 2 fuses, and there's no "handle tie" for a fuse that blows. There is no hazard created when 240 volt single phase circuit is "half hot" or has a "dead leg".
Reply With Quote
  #9  
Old 2/17/07, 8:02 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,047
Default Re: Murray Split Main Panel

Several arguments could be made for either case, but for the record, that would be my recommendation.

215.2(B)(2) addresses feeders supplying a combination of transformers and utilization equipment. I think the lower bus qualifies as utilization equipment, although there is no transformer.

225.38(B), 225.53 and 230.74 address building or structure service disconnects. Obviously, this is not the service disconnect.

As there is no "danger" of an over-loaded neutral, this wouldn't qualify as in multi-wire circuits. . .

So. . .

I can't find a "requirement" either, but I would still make the recommendation. We'll see what others have to say. . .



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #10  
Old 2/17/07, 8:24 PM
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,072
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Murray Split Main Panel

Utilization Equipment. Equipment that utilizes electric energy for electronic,
electromechanical, chemical, heating, lighting, or similar purposes.

Not sure I would use that one...lol


But I love where ya are going....



Paul W. Abernathy
Reply With Quote
  #11  
Old 2/17/07, 8:29 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,047
Default Re: Murray Split Main Panel

Just shootin' from the hip - to see what sticks



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #12  
Old 2/18/07, 3:04 PM
Pierre Belarge Pierre Belarge is offline
Active Poster
 
Join Date: Apr 2006
Posts: 202
Please Note: Pierre Belarge is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Murray Split Main Panel

External splicing of the EGCs as seen in this photo has never been permitted, as they would still be required to be bonded to the enclosure.

Who says this is the service panel? Where is the service disconnect?
Reply With Quote
  #13  
Old 2/18/07, 3:10 PM
Pierre Belarge Pierre Belarge is offline
Active Poster
 
Join Date: Apr 2006
Posts: 202
Please Note: Pierre Belarge is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Murray Split Main Panel

Taking a closer look at this picture... I blew it up as much as the picture would allow before it became blurry...

If this is a service panel, I cannot see an GEC going towards a Grounding Electrode.

If this is a secondary panel (subpanel), there is no neutral conductor, or... the neutral conductor is bare(taped at the entry) and there is no equipment grounding conductor.

This panel needs someone to take a closer look at it.
Reply With Quote
  #14  
Old 2/18/07, 3:16 PM
Marc D. Shunk's Avatar
Marc D. Shunk Marc D. Shunk is offline
Banned
 
Join Date: Dec 2006
Location: Central PA
Posts: 1,980
Please Note: Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Murray Split Main Panel

Quote:
Originally Posted by Pierre Belarge
External splicing of the EGCs as seen in this photo has never been permitted, ...
Prior to about 1967, the code was mute on the matter.
Reply With Quote
  #15  
Old 2/18/07, 3:19 PM
Joseph Hagarty,  CMI's Avatar
Joseph Hagarty, CMI Joseph Hagarty,  CMI is offline
InterNACHI Member
 
Join Date: Jan 2003
Location: Parkesburg, PA
Posts: 5,636
Default Re: Murray Split Main Panel

This is the only Panel in the Home.

It is located within the Garage (Exterior Wall) directly opposite the overhead service drop and Meter.



Joseph P. Hagarty
joseph.hagarty@comcast.net
Main Line Inspections, Inc.
Phone: 610-399-3675
Email: MainLineHI@comcast.net

http://pa.nachi.org/mainlinepa/about.html
http://www.householdinspector.com

National President / NACHI (2003-2004)
NACHI Education Committee Member
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
National Electrical Code Information and Discussion jtedesco1 Electrical Inspections 50 6/15/10 7:28 PM
Subpanel wired as main panel. jlybolt Electrical Inspections 15 5/23/07 4:10 PM
Main disconnect at meter instead of main panel. OK? kshepard Electrical Inspections 14 11/8/06 6:24 PM
Panel main rating sfalvey Electrical Inspections 7 9/24/06 8:46 PM
Bad electrical problem Pest Guy Electrical Inspections 4 1/20/06 9:26 PM