Default For My Buddy Duffy

Nothing really "wrong" here, but you were asking for it. . .

The top bus bar is a bit warmer than the lower, but nothing I considered abnormal.
Attached Thumbnails
my-buddy-duffy-p7290009.jpg   my-buddy-duffy-ir_0114.jpg  



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #2  
Old 7/30/07, 2:24 AM
Dale Duffy's Avatar
Dale Duffy Dale Duffy is offline
InterNACHI Member
 
Join Date: Oct 2005
Location: Scottsdale, AZ
Posts: 8,261
Default Re: For My Buddy Duffy

Quote:
Originally Posted by jpope
Nothing really "wrong" here, but you were asking for it. . .

The top bus bar is a bit warmer than the lower, but nothing I considered abnormal.
Oh Lord..............

121?...no of course she's fine.... ........I bet it won't be very long before we see temps in the 160-200 Range................ ....From Santa Zinsco Clarita........

I think the hottest breaker I scanned (found) with the IR Therm. was 190......
Reply With Quote
  #3  
Old 7/30/07, 1:05 PM
George P. Wells, CMI's Avatar
George P. Wells, CMI George P. Wells, CMI is offline
InterNACHI Member
 
Join Date: Oct 2004
Location: Michigan
Posts: 554
Send a message via Skype™ to gwells
Default Re: For My Buddy Duffy

It looks like the insulated conductors are touching the live bus. That's not good.



BestInspectors.Net
& Real Estate Training Academy

Inspection Report Software for
Windows - iOS - Mac - Android

Continuing Education
Home and Commercial Building Inspection - Skilled Trades – Real Estate – Appraisal – NFPA 921

http://www.bestinspectors.net

est. 1992
Reply With Quote
  #4  
Old 7/30/07, 1:10 PM
mnahrgang's Avatar
mnahrgang mnahrgang is offline
InterNACHI Member
 
Join Date: Apr 2007
Location: Springfield, OH
Posts: 5,799
Default Re: For My Buddy Duffy

What's considered a "normal", and what's considered "excessive" for the temerature range?



Mark Nahrgang
www.DaytonSpringfieldHomeInspector.com
www.HeyMark.info

Home Inspections for Springfield, Dayton, and surrounding OH areas.
Reply With Quote
  #5  
Old 7/30/07, 4:24 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,057
Default Re: For My Buddy Duffy

That's a difficult question to answer Mark.

Temperatures of 150 and below don't usually get my attention, but it really depends on other factors as well. When there is discoloration to the breaker, wire, terminal or bus bar, regardless of the temps, there is something "not right."

A high temp reading (IMHO) should generally be considered as a means to "confirm" a problem, rather than to "diagnose" a problem.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #6  
Old 7/30/07, 4:25 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,057
Default Re: For My Buddy Duffy

Quote:
Originally Posted by gwells
It looks like the insulated conductors are touching the live bus. That's not good.
They were close (very common with Zinsco), but not touching. . .



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #7  
Old 7/30/07, 7:19 PM
Marcel R. Cyr's Avatar
Marcel R. Cyr Marcel R. Cyr is online now
InterNACHI Member
 
Join Date: Jul 2004
Location: Winslow, ME
Posts: 19,795
Default Re: For My Buddy Duffy

Jeff;

Pardon my French, but would not a 40 amp breaker drawing 30 to 35 amps at the time you took the camera shot explain why the temp. reading is such as it was?

Marcel
Reply With Quote
  #8  
Old 7/30/07, 7:33 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,057
Default Re: For My Buddy Duffy

That was the circuit for the condensing unit of the A/C after about 15 minutes of operation. The house was vacant, so no other circuits were in operation at that time (except the FAU).



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #9  
Old 7/30/07, 8:17 PM
Peter C. Russell's Avatar
Peter C. Russell Peter C. Russell is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Alton Bay NH
Posts: 3,998
Default Re: For My Buddy Duffy

Jeff, Did you move your position with the camera to determine whether it was a heat related problem or a reflection?
Reply With Quote
  #10  
Old 7/30/07, 8:37 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,057
Default Re: For My Buddy Duffy

Yep. I always look from several different angles.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #11  
Old 7/30/07, 9:52 PM
David A. Andersen's Avatar
David A. Andersen David A. Andersen is offline
InterNACHI Member
 
Join Date: Jun 2005
Location: Woodlawn, TN
Posts: 5,925
Default Re: For My Buddy Duffy

I don't know about this one you guys!

I think you should change the emissivity setting in your software and see what that low emissive bar is actually kicking out there!

I understand that this is a hot panel, but the temps your camera is showing is for 97% emissivity? What happens at 23%? Aluminum is from .10 -.40 depending how corroded it is. That bar could be from 250-300 degrees F.
Reply With Quote
  #12  
Old 7/30/07, 9:55 PM
Dale Duffy's Avatar
Dale Duffy Dale Duffy is offline
InterNACHI Member
 
Join Date: Oct 2005
Location: Scottsdale, AZ
Posts: 8,261
Default Re: For My Buddy Duffy

Quote:
Originally Posted by dandersen
That bar could be from 250-300 degrees F.
I'd bet my left arm Jeff checked the bar temp with his IR Therm also...........
Reply With Quote
  #13  
Old 7/30/07, 10:21 PM
Barry Adair's Avatar
Barry Adair Barry Adair is offline
InterNACHI Member
 
Join Date: Aug 2004
Location: TEXAS
Posts: 3,932
Default Re: For My Buddy Duffy

Quote:
Originally Posted by dduffy
I'd bet my left arm Jeff checked the bar temp with his IR Therm also...........
What a guy!
Sacraficing "unused" body parts.
You are a righty, right?



ADAIR INSPECTION
972-487-5634

Commercial-Residential-Construction-EIFS-Infrared Thermography
TREC # 4563
EDI: EIFS-MA TX # 39

2008 US Member of the Year

life is the random lottery of events followed by numerous narrow escapes accept the good
Reply With Quote
  #14  
Old 7/30/07, 11:07 PM
Dale Duffy's Avatar
Dale Duffy Dale Duffy is offline
InterNACHI Member
 
Join Date: Oct 2005
Location: Scottsdale, AZ
Posts: 8,261
Default Re: For My Buddy Duffy

Quote:
Quote:
Originally Posted by dduffy
I'd bet my left arm Jeff checked the bar temp with his IR Therm also...........
Quote:
What a guy!
Sacraficing "unused" body parts.
You are a righty, right?

Big B...... .......

Hey...I bet Nick a years salary he didn't land a couple hundred thousand foreclosure inspections, so I'm down to body parts until Nick PAYS up..!!!..................


http://www.nachi.org/forum/showthrea...nd+foreclosure

...................................... .......................................
Reply With Quote
  #15  
Old 7/30/07, 11:12 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,057
Default Re: For My Buddy Duffy

My digital thermometer read 120 degrees, which is awful close to what the BCAM shows. I don't consider this to be abnormal by any means.

I'm still a beginner with my BCAM, but I have a little experience with the rest of my tool box, and I'm certainly no stranger to likes of Zinsco. . .



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
sewer smell only in the AM (posted by Buddy Moore) AskNACHI.org AskNACHI.org Inspection Questions Forum 7 9/26/07 6:20 PM
Exclusively for Dale Duffy jpope Electrical Inspections 11 11/30/06 9:01 PM
Hey Buddy, Nice Flat Roof psmothers Exterior Inspections 3 4/29/06 12:10 AM


All times are GMT -4. The time now is 7:47 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts