  #1  
Old 3/20/07, 9:53 PM
Speedy Petey Speedy Petey is offline
Unmoderated Guest
 
Join Date: Jul 2006
Posts: 1,294
Please Note: Speedy Petey is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Myth No. 1 – Grounding and Ideal (Makers of Suretest)

Ideal wrote a newsletter about grounding that was so off base and misleading it is not funny. Mike Holt picks it apart paragraph by paragraph.
This is a shame as Ideal makes some high quality tools, testers & equipment.

Have a read:
http://www.mikeholt.com/newsletters....y&letterID=339
Reply With Quote
  #2  
Old 3/20/07, 10:21 PM
rromoser's Avatar
rromoser rromoser is offline
InterNACHI Member
 
Join Date: Oct 2006
Location: Fishers, IN
Posts: 187
Default Re: Myth No. 1 – Grounding and Ideal (Makers of Suretest)

Does this need to be grounded too?
Attached Thumbnails
myth-no-1-grounding-and-ideal-makers-suretest-lightning-strike-1.jpg  
Reply With Quote
  #3  
Old 3/20/07, 10:35 PM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Harrisonburg, VA
Posts: 7,697
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Myth No. 1 – Grounding and Ideal (Makers of Suretest)

Quote:
Originally Posted by Speedy Petey
Ideal wrote a newsletter about grounding that was so off base and misleading it is not funny. Mike Holt picks it apart paragraph by paragraph.
This is a shame as Ideal makes some high quality tools, testers & equipment.

Have a read:
http://www.mikeholt.com/newsletters....y&letterID=339
Yeah...I was the one that sent it to Mike....I sent alot of stuff I find to Mike. He asked me to do the newsletters for things like this but I am just so poor at doing the newsletters....Mike is awesome at it.

I found that thing from ideal a few weeks ago....and broke it up and sent it to mike...and he jumped all over it because he actually consults to ideal....

Sad to say Mike is taking ALOT of heat over the newsletter...I am not sure why as he did not personally attack IDEAL....just clearing up the facts on the myths.....he asked me to do this article for the onging myth thing but I am just so poor at writting things.......if I was not so poor I would have a book out or something else other than the CD I am still working on......just better at saying it than putting it to paper.........it's a curse...I need a ghost writer...

I think what Mike does is SO valuable to the learning of this industry.....sometimes those who make change also make waves..both good and bad.



Paul W. Abernathy,CMI,CEI,CEPE
National Electrical Code Expert-ONLY
Weekly Live Chat :http://www.theelectricalguru.com/chat.html
Weekly Chat on Mondays & Wednesdays -8PM E.S.T
* Notice- I will not be conducting any future seminars for the HI Industry. I am a CODE GUY so I will be focusing efforts on the NEC Code. If you have CODE question visit my website...if you have Electrical HI questions ask Nick or Ben Gromicko.

Last edited by pabernathy; 3/22/07 at 11:32 AM..
Reply With Quote
  #4  
Old 3/23/07, 9:22 PM
Larry D. Kage Larry D. Kage is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Lake Ann (Traverse City), MI
Posts: 6,350
Default Re: Myth No. 1 – Grounding and Ideal (Makers of Suretest)

Mike Holt Fails in His Myth Busting Efforts

By Mike Holt

Dear Newsletter readers,
Last Tuesday I sent out a newsletter with the intent of busting electrical myths. The subheading of the newsletter stated “This is the first installment of a new series we’re developing to uncover industry myths. But the manner in which I handled the entire topic was totally inappropriate. The tone of the newsletter was such that some, if not many of my readers interpreted it as ‘me against IDEAL’ when in fact IDEAL and Mike Holt have a close working relationship.

The intent of my Mythbuster newsletter was to highlight the fact that numerous articles and training books use old terminology and phrasing that does not reflect the current Code language and purpose of Grounding versus Bonding of premises wiring, which has seen a radical change the past two Code cycles.

To illustrate my point, I happened to highlight an article in electronic circulation by IDEAL. But, some readers extrapolated from my comments that IDEAL does not have an understanding of the current Code language and theories of Grounding versus Bonding.

The undated article happened to be several years old and more representative of older Code language. I can assure you that this loose inference is not accurate of them as IDEAL has an active training initiative and new product program that stays current with customers’ needs to comply with the latest Code revisions. IDEAL has and still does actively support my grounding seminars, maintains close relationships with the apprenticeship programs, and frequently conducts up-to-date hands-on training in the field.

I owe IDEAL, its employees, distributors, as well as their customers an apology for how I handled this feeble attempt of Mythbusting. This newsletter developed into a misperception that IDEAL and I had polarizing views on the topic and resulted in many viewers taking sides. I was 100% wrong and if I had to do this again, I would have done it differently.

Lessons I’ve learned:
  • Do a better job of introducing the issue and goal of the newsletter.
  • Do not highlight a myth based on an individual article from an individual company, unless I’ve contacted the company in advance and have given them the opportunity to make the necessary correction to the offending web page.

IDEAL has communicated to me that they are using this as an opportunity to diligently review and date all of their literature and to distinguish short articles designed for marketing brevity from white papers designed to explore technical avenues and application development. As a highly customer-focused company, their mission continues to be to provide their customers, you, with the products and support that you need from a leading manufacturer of test equipment.

If you have been a reader of my newsletter for a few years, you have seen me fail in my efforts to make things better (http://www.mikeholt.com/mojonewsarchive/AFCI-HTML/HTML/AFCI_-_Update~20021209.htm). All I can say is that when I do fail, it hurts me that I’ve hurt others and I can only do the responsible thing and that is to ‘man up’ and make things right.

To my buddies at IDEAL, I’m sorry for my actions and any hurt it has caused you.

Mike Holt

P.S. I want to encourage all manufacturers of grounding devices, fitting, tools, meters, as well as those who write magazine articles, books, etc. to follow IDEAL’s lead to review and date all of your literature and distinguish short articles designed for marketing brevity from white papers designed to explore technical avenues and application development.




____________________________________________
"An Education, not just an Inspection"

Larry Kage, CMI
Lake Ann (Traverse City), Michigan 49650
231 929 3525


Professional Inspector and Infrared Thermographer serving the Traverse City, Michigan area and beyond.


ITC/FLIR CERTIFIED BUILDING SCIENCES THERMOGRAPHER

ITC/FLIR CERTIFIED LEVEL 1 THERMOGRAPHER
Reply With Quote
  #5  
Old 3/23/07, 9:38 PM
Speedy Petey Speedy Petey is offline
Unmoderated Guest
 
Join Date: Jul 2006
Posts: 1,294
Please Note: Speedy Petey is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Myth No. 1 – Grounding and Ideal (Makers of Suretest)

This does not change the fact that that article was mostly bogus, old or not.

Like he said, there is too much of this erroneous material floating around. This is only perpetuating falsehoods and flat out wrong information.

At least this is a wake up call to Ideal, and hopefully other companies as well, to update and substantiate the inforamtion they are providing.
Reply With Quote
  #6  
Old 3/23/07, 9:42 PM
Larry D. Kage Larry D. Kage is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Lake Ann (Traverse City), MI
Posts: 6,350
Default Re: Myth No. 1 – Grounding and Ideal (Makers of Suretest)

Yes,

Quote:
Originally Posted by lkage

IDEAL has communicated to me that they are using this as an opportunity to diligently review and date all of their literature and to distinguish short articles designed for marketing brevity from white papers designed to explore technical avenues and application development.



____________________________________________
"An Education, not just an Inspection"

Larry Kage, CMI
Lake Ann (Traverse City), Michigan 49650
231 929 3525


Professional Inspector and Infrared Thermographer serving the Traverse City, Michigan area and beyond.


ITC/FLIR CERTIFIED BUILDING SCIENCES THERMOGRAPHER

ITC/FLIR CERTIFIED LEVEL 1 THERMOGRAPHER
Reply With Quote
  #7  
Old 3/24/07, 12:29 PM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Harrisonburg, VA
Posts: 7,697
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Myth No. 1 – Grounding and Ideal (Makers of Suretest)

I agree.......but I don't think mike needed to appologize to anyone as personally he did not KNIFE at Ideal...just the myths being propogated by the many articles that spread the falseness of grounding and bonding which is kinda his mission.



Paul W. Abernathy,CMI,CEI,CEPE
National Electrical Code Expert-ONLY
Weekly Live Chat :http://www.theelectricalguru.com/chat.html
Weekly Chat on Mondays & Wednesdays -8PM E.S.T
* Notice- I will not be conducting any future seminars for the HI Industry. I am a CODE GUY so I will be focusing efforts on the NEC Code. If you have CODE question visit my website...if you have Electrical HI questions ask Nick or Ben Gromicko.
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On



All times are GMT -4. The time now is 2:57 AM.


Popular Sections

:

All Sections

Popular

Membership

Inspection Standards

Education

Chapters & Members

Articles & Links

Other Organizations

 

 

 

NACHI.ORG Statistics

 

 

no new posts