Default Name that defect? Care to play?

I will send an $25.00 check to the first person who can identify this electrical panel defect.

1931 apartment conversion condo building. Milbank multiple unit panes in the basement commojn area (Picture 1).

Now, here is the question:
Look at picture 2. Inside of the subject unit's panel. What is the major defect.

Hint 1: In Illinois, inspectors, are required to call out, as "significantly deficient" items that are unsafe. From the state SOP administratibe rules:

"Unsafe: A condition in a system or component that is a significant risk of personal injury or property damage during normal, day-to-day use. The risk may be due to damage, deterioration, improper installation or a change in accepted residential construction standards."

Hint 2: NEC 2008 is the current accepted residential construction standards.

Hint 3: Yeah, I know that the panel was not properly labeled as to branch circuits. That is not the defect I mean.

To gain the prize, name the defect AND site the NEC 2008 code section.

Good Luck. I will contact the winner and send him (or her) the check. I will not, right away, post who that winner is in the interest my messing with meany other people's minds and promoting discussion, argument and the good old give and take excahnge that this board is noted for.

You may begin.
Attached Thumbnails
name-defect-care-play-dscf7386.jpg   name-defect-care-play-dscf7387.jpg  



Will Decker, CMI
ILL License # 450.0002240
Board Certified Master Inspector
Decker Home Services, LLC
Chicago and Northern Suburban Home Inspections
Office: (847) 676-8393
Cell: (847) 609-2345
Home: (847) 673-2702

wjd@DeckerHomeServices.com
www.DeckerHomeServices.com

Learn, Educate, Serve and have fun doing it!
Reply With Quote
Find an InterNACHI certified Utah Home Inspector (and anywhere else in North America)
  #2  
Old 9/9/09, 8:39 PM
Bruce M. Graham, III's Avatar
Bruce M. Graham, III Bruce M. Graham, III is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Gainesville, FL
Posts: 2,025
Default Re: Name that defect? Care to play?

panel could have more than 6 throws.



Bungalows to Mansions
Professional Inspection Services, LLC dba
1st Inspection Services
Bruce M. Graham III
Gainesville, FL 32608
352 871 8989
Florida Licensed Home Inspector #HI10
NACHI05091592
ICC 5268478
www.1stinspectionsfl.com
www.bungalowstomansions.com
Reply With Quote
  #3  
Old 9/9/09, 8:45 PM
Mark E. Northrup's Avatar
Mark E. Northrup Mark E. Northrup is offline
InterNACHI Member
 
Join Date: Dec 2008
Location: Oregon
Posts: 473
Default Re: Name that defect? Care to play?

Where's the ground lug?





House 2 Home LLC
503-602-1420
HomePros@House2HomeLLC.ORG
Protecting Peace of Mind One House at a Time
IAC2 Certified
IR Certified
A favorite place on Google Maps
Reply With Quote
  #4  
Old 9/9/09, 8:48 PM
William J. Decker's Avatar
William J. Decker William J. Decker is offline
InterNACHI Member
 
Join Date: Nov 2004
Location: Skokie, IL
Posts: 7,717
Default Re: Name that defect? Care to play?

Distrobution panel. Neutral is floated (around here, everything is required to be in conduit, which carries the ground.

The six throw rule is OK. Six throws means six "hand throws", not six switches. My hands are pretty big.

No joy yet.

Any other players.

Final hint. Look at picture #2. It is right there before you and deals with a change in the 2008 NEC.

Now get to it



Will Decker, CMI
ILL License # 450.0002240
Board Certified Master Inspector
Decker Home Services, LLC
Chicago and Northern Suburban Home Inspections
Office: (847) 676-8393
Cell: (847) 609-2345
Home: (847) 673-2702

wjd@DeckerHomeServices.com
www.DeckerHomeServices.com

Learn, Educate, Serve and have fun doing it!
Reply With Quote
  #5  
Old 9/9/09, 8:52 PM
Bruce M. Graham, III's Avatar
Bruce M. Graham, III Bruce M. Graham, III is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Gainesville, FL
Posts: 2,025
Default Re: Name that defect? Care to play?

Multi wire circuits, the 2 ungrounded conductors should be tied together and on seperate phase. The box should have 3 double pole breakers.



Bungalows to Mansions
Professional Inspection Services, LLC dba
1st Inspection Services
Bruce M. Graham III
Gainesville, FL 32608
352 871 8989
Florida Licensed Home Inspector #HI10
NACHI05091592
ICC 5268478
www.1stinspectionsfl.com
www.bungalowstomansions.com

Last edited by bgraham; 9/9/09 at 9:08 PM..
Reply With Quote
  #6  
Old 9/9/09, 9:07 PM
Bob Elliott's Avatar
Bob Elliott Bob Elliott is offline
InterNACHI Member
 
Join Date: Aug 2009
Location: Chicago
Posts: 11,729
Default Re: Name that defect? Care to play?

Biggest mistake would be applying 2008 NEC code to a grandfathered panel.
Ok looking back you mentioned rehab.
Assuming there is no Remote distribution panel I would if applying Code site lack of AFCI protection.

That would be my first issue if this is a recent rehab and electrical work was done ,as it needs to be brought up to code under those conditions..
Reply With Quote
  #7  
Old 9/9/09, 9:12 PM
Jeffrey R. Wicklander's Avatar
Jeffrey R. Wicklander Jeffrey R. Wicklander is offline
InterNACHI Member
 
Join Date: Mar 2008
Location: Lake Forest, Il
Posts: 1,117
Default Re: Name that defect? Care to play?

The only thing I can think of is...grouping the neutral with the appropriate multi-wire branch circuits (NEC 210.4d) and along with that the MWC branch circuit breakers must have a handle tie to disconnect both ungrounded conductors. (NEC 210.4b)

Jeff



Jeff Wicklander
Corwick Home Services

Join my business on Facebook
Reply With Quote
  #8  
Old 9/9/09, 10:49 PM
William J. Decker's Avatar
William J. Decker William J. Decker is offline
InterNACHI Member
 
Join Date: Nov 2004
Location: Skokie, IL
Posts: 7,717
Default Re: Name that defect? Care to play?

Quote:
Originally Posted by bgraham View Post
Multi wire circuits, the 2 ungrounded conductors should be tied together and on seperate phase. The box should have 3 double pole breakers.
Close.



Will Decker, CMI
ILL License # 450.0002240
Board Certified Master Inspector
Decker Home Services, LLC
Chicago and Northern Suburban Home Inspections
Office: (847) 676-8393
Cell: (847) 609-2345
Home: (847) 673-2702

wjd@DeckerHomeServices.com
www.DeckerHomeServices.com

Learn, Educate, Serve and have fun doing it!
Reply With Quote
  #9  
Old 9/9/09, 10:52 PM
Bob Elliott's Avatar
Bob Elliott Bob Elliott is offline
InterNACHI Member
 
Join Date: Aug 2009
Location: Chicago
Posts: 11,729
Default Re: Name that defect? Care to play?

Picture is to fuzzy to tell much on that left side as far as the breakers are concerned.
Reply With Quote
  #10  
Old 9/9/09, 10:57 PM
Christopher Currins's Avatar
Christopher Currins Christopher Currins is offline
InterNACHI Member
 
Join Date: Feb 2007
Location: Godfrey, IL
Posts: 6,931
Default Re: Name that defect? Care to play?

Each multiwire branch circuit shall have a means to simultaneously disconnect all ungrounded conductors at the point where the branch circuit originates. That's not the case here.



Christopher Currins
Certified, Licensed

Proudly serving the Illinois Metro-East

Illinois Home Inspector

Top 5 Tasks for January
Reply With Quote
  #11  
Old 9/9/09, 11:01 PM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,047
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Name that defect? Care to play?

poor dang breakers look like they have no ratings on them...are they simply disconnects and not the required Overcurrent protection?

I only see (3) grounded conductors.....how about

(D) Grouping.
The ungrounded and grounded conductors
of each multiwire branch circuit shall be grouped by wire
ties or similar means in at least one location within the
panelboard or other point of origination.

Exception: The requirement for grouping shall not apply if
the circuit enters from a cable or raceway unique to the
circuit that makes the grouping obvious.

and
(B) Disconnecting Means.
Each multiwire branch circuit
shall be provided with a means that will simultaneously
disconnect all ungrounded conductors at the point where
the branch circuit originates.




Paul W. Abernathy,CMI,CPI,CME
National Electrical Code Expert
Electrical & Fire Protection Systems Code Supervisor- Alexandria,VA
Weekly Live Radio Show :http://en.1000mikes.com/show/the_electrical_guru
Weekly Chat on Wednesdays -7:30 PM E.S.T
* Get my 13 hour commentary audio CD for the book "How to Perform Electrical Inspections"

2007 InterNACHI Member of the Year
Reply With Quote
  #12  
Old 9/9/09, 11:10 PM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,047
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Name that defect? Care to play?

Now when you say it is a distribution panel...i will assume their is a service disconnect somewhere upstream on all of these...otherwise i would expect a case to neutral connection at these panels also.....but you say it is a distribution panel so I wont venture down that path.



Paul W. Abernathy,CMI,CPI,CME
National Electrical Code Expert
Electrical & Fire Protection Systems Code Supervisor- Alexandria,VA
Weekly Live Radio Show :http://en.1000mikes.com/show/the_electrical_guru
Weekly Chat on Wednesdays -7:30 PM E.S.T
* Get my 13 hour commentary audio CD for the book "How to Perform Electrical Inspections"

2007 InterNACHI Member of the Year
Reply With Quote
  #13  
Old 9/9/09, 11:13 PM
Michael Roberson's Avatar
Michael Roberson Michael Roberson is offline
InterNACHI Member
 
Join Date: May 2008
Location: West Michigan, Lower Penninsula
Posts: 1,650
Default Re: Name that defect? Care to play?

3 Neutrals, and 6 branch circuits. Possibly due to the change in the 2008 code concerning the neutrals making it all the way back to the distribution panel and not just tied together somewhere in the middle?

** Edit* Ah I see Paul said it more eloquently than I.
Reply With Quote
Find an InterNACHI certified Utah Home Inspector (and anywhere else in North America)
  #14  
Old 9/10/09, 12:20 AM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,047
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Name that defect? Care to play?

lol...thats ok...someone was faster than I was at answering it correctly....but I posted the code...so I get extra points from the Deckster....



Paul W. Abernathy,CMI,CPI,CME
National Electrical Code Expert
Electrical & Fire Protection Systems Code Supervisor- Alexandria,VA
Weekly Live Radio Show :http://en.1000mikes.com/show/the_electrical_guru
Weekly Chat on Wednesdays -7:30 PM E.S.T
* Get my 13 hour commentary audio CD for the book "How to Perform Electrical Inspections"

2007 InterNACHI Member of the Year
Reply With Quote
  #15  
Old 9/10/09, 11:45 PM
Christopher Currins's Avatar
Christopher Currins Christopher Currins is offline
InterNACHI Member
 
Join Date: Feb 2007
Location: Godfrey, IL
Posts: 6,931
Default Re: Name that defect? Care to play?

So who's the winner Will?



Christopher Currins
Certified, Licensed

Proudly serving the Illinois Metro-East

Illinois Home Inspector

Top 5 Tasks for January
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Congrat's Obama Jason1 Canadian Inspectors 80 11/13/08 8:49 PM
I Don't Care jstewart1 Miscellaneous Discussion for Inspectors 16 7/4/07 11:46 PM


All times are GMT -4. The time now is 4:57 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts