Default is it nec 2010 for a GFCI to be on a garage door opener

I have a electrician stating that it is a nec code for a garage opener to be on a GFCI outlet. Please state the code if this is true. House was remodled in 2008 and has multiple GFCI's in the garage almost all the outlets have one even if it is in the same run. Double tapping in the main service panel and two of the 15 amp breakers were over loaded with fans and bath ceiling heaters. IE turn them on and the breaker trips.
Thanks for your help
Mark
House 2 Home LLc.





House 2 Home LLC
503-602-1420
HomePros@House2HomeLLC.ORG
Protecting Peace of Mind One House at a Time
IAC2 Certified
IR Certified
A favorite place on Google Maps
Reply With Quote
Need a home inspection in Washington? Check out InterNACHI's listing of Washington certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #2  
Old 8/8/10, 12:49 AM
Bob Elliott's Avatar
Bob Elliott Bob Elliott is offline
InterNACHI Member
 
Join Date: Aug 2006
Location: Chicago
Posts: 21,916
Default Re: is it nec 2010 for a GFCI to be on a garage door opener

I have it as all general purpose receptacles must be GFCI.
Door opener is "dedicated" usually isn't it?
Reply With Quote
  #3  
Old 8/8/10, 1:01 AM
Mark E. Northrup's Avatar
Mark E. Northrup Mark E. Northrup is offline
InterNACHI Member
 
Join Date: Dec 2008
Location: Oregon
Posts: 473
Default Re: is it nec 2010 for a GFCI to be on a garage door opener

That is what i thought and I wrote it up. But the Russian contractor states that it is NEC code. Which I have inspected lots of 2010 houses that have not had the garage door opener on a GFCI. this is a 1980 house that was remodled. And all the outlets in the garage except one had a GFCI on it. Some were in line with the string. So mulitiple GFCI's were used. Gives me the idea that someone didn't know what they were doing.





House 2 Home LLC
503-602-1420
HomePros@House2HomeLLC.ORG
Protecting Peace of Mind One House at a Time
IAC2 Certified
IR Certified
A favorite place on Google Maps
Reply With Quote
  #4  
Old 8/8/10, 1:37 AM
Chuck Evans's Avatar
Chuck Evans Chuck Evans is offline
InterNACHI Member
 
Join Date: Sep 2006
Location: Stagecoach, TX
Posts: 2,037
Default Re: is it nec 2010 for a GFCI to be on a garage door opener

Quote:
Originally Posted by mnorthrup View Post
I have a electrician stating that it is a nec code for a garage opener to be on a GFCI outlet. Please state the code if this is true. House was remodled in 2008 and has multiple GFCI's in the garage almost all the outlets have one even if it is in the same run. Double tapping in the main service panel and two of the 15 amp breakers were over loaded with fans and bath ceiling heaters. IE turn them on and the breaker trips.
Thanks for your help
Mark
House 2 Home LLc.
Yes the sparky is correct. The 2008 NEC revision to article 210.8(A)(2) did away with the exceptions for dedicated outlets (e.g., freezers, irrigation controllers, etc.) and for inaccessible outlets such as those in the ceiling for garage door operators. Basically, if it's in the garage, it must be GFCI protected.



Chuck Evans (TREC #7657)
Level III Infraspection Institute Certified Infrared Thermographer (#8402)
HomeCert Houston Home Inspections & Thermal Inspections Find us on Facebook
Houston Thermal Inspections & Infrared Imaging Find us on Facebook
Houston Home Inspector

Houston, TX

Last edited by cevans; 8/8/10 at 1:41 AM..
Reply With Quote
  #5  
Old 8/8/10, 1:39 AM
Joe Funderburk, CMI's Avatar
Joe Funderburk, CMI Joe Funderburk, CMI is offline
InterNACHI Member
 
Join Date: Dec 2005
Location: Hickory Grove, SC
Posts: 8,343
Send a message via Yahoo to jfunderburk
Default Re: is it nec 2010 for a GFCI to be on a garage door opener

Who puts up a ladder to test an outlet in the ceiling anyway?



“The things that will destroy America are peace at any price,
prosperity at any cost, safety first instead of duty first,
the love of soft living, and the get-rich-quick theory of life.”
Theodore Roosevelt


Joe Funderburk, CMI
Alpha & Omega Home Inspections, LLC
Inspecting Upstate SC & Charlotte Metro, NC
NACHI ID: NACHI05120170
www.aohomeinspection.com


Reply With Quote
  #6  
Old 8/8/10, 2:08 AM
Chuck Evans's Avatar
Chuck Evans Chuck Evans is offline
InterNACHI Member
 
Join Date: Sep 2006
Location: Stagecoach, TX
Posts: 2,037
Default Re: is it nec 2010 for a GFCI to be on a garage door opener

Quote:
Originally Posted by jfunderburk View Post
Who puts up a ladder to test an outlet in the ceiling anyway?
LOL. I disclaim checking GFCI for inaccessible outlets, however most of the newer construction that I do has the openers on the same device as the convenience outlets. When you trip the GFCI device the garage operator stops working, when you reset it, the light will typically come on. So its pretty easy to tell.



Chuck Evans (TREC #7657)
Level III Infraspection Institute Certified Infrared Thermographer (#8402)
HomeCert Houston Home Inspections & Thermal Inspections Find us on Facebook
Houston Thermal Inspections & Infrared Imaging Find us on Facebook
Houston Home Inspector

Houston, TX

Last edited by cevans; 8/8/10 at 2:50 AM..
Reply With Quote
  #7  
Old 8/8/10, 7:14 AM
Robert Meier's Avatar
Robert Meier Robert Meier is online now
Active Poster
 
Join Date: Feb 2010
Location: New Jersey
Posts: 1,250
Please Note: Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: is it nec 2010 for a GFCI to be on a garage door opener

Quote:
Originally Posted by cevans View Post
Yes the sparky is correct. The 2008 NEC revision to article 210.8(A)(2) did away with the exceptions for dedicated outlets (e.g., freezers, irrigation controllers, etc.) and for inaccessible outlets such as those in the ceiling for garage door operators. Basically, if it's in the garage, it must be GFCI protected.
Yes Chuck is correct. This requirement changed in the 2008 NEC. That is unless you're in New Jersey where the State opted to keep the exception which IMO is a good idea. The 2008 would now require a sump pump receptacle to be GFCI protected. Given the possible consequences of a nuisance trip on a sump pump I like leaving the exception in the NEC.

One other point of interest, the new requirement under the 2008 only applies to 120 volt receptacles, a 240 volt receptacle would not require GFCI protection. I'm sure that when Chuck said "Basically, if it's in the garage, it must be GFCI protected" he meant only 120 volt receptacles.

Last edited by Robert Meier; 8/8/10 at 8:02 AM.. Reason: Added comment
Reply With Quote
  #8  
Old 8/8/10, 8:03 PM
Mark E. Northrup's Avatar
Mark E. Northrup Mark E. Northrup is offline
InterNACHI Member
 
Join Date: Dec 2008
Location: Oregon
Posts: 473
Default Re: is it nec 2010 for a GFCI to be on a garage door opener

thanks for the info guys. And yes Joe F I check all outlets that are reachable. The one i don't will be the one that does not work.





House 2 Home LLC
503-602-1420
HomePros@House2HomeLLC.ORG
Protecting Peace of Mind One House at a Time
IAC2 Certified
IR Certified
A favorite place on Google Maps
Reply With Quote
  #9  
Old 8/9/10, 8:42 PM
Brian E. Kelly's Avatar
Brian E. Kelly Brian E. Kelly is offline
InterNACHI Member
 
Join Date: Oct 2004
Location: Phoenix, AZ
Posts: 15,973
Default Re: is it nec 2010 for a GFCI to be on a garage door opener

Quote:
Originally Posted by jfunderburk View Post
Who puts up a ladder to test an outlet in the ceiling anyway?
the same guy who checks those fireplace outlets i suppose Joe.
Reply With Quote
  #10  
Old 8/9/10, 9:43 PM
Bruce A. King's Avatar
Bruce A. King Bruce A. King is offline
InterNACHI Member
 
Join Date: Jan 2005
Location: York, SC
Posts: 3,207
Default Re: is it nec 2010 for a GFCI to be on a garage door opener

So far all of the garage door outlets I have seen with GFI have the test/reset on the ceiling or a dedicated GFI device (no outlets) on the wall. These are independent of the regular garage outlet circuit. The code people should have required the reset to be within reach of a normal height person without standing on anything.



B.A. King Home Inspections, LLC
www.BAKingHomeInspections.com
Serving Charlotte NC area and Rock Hill SC areas.
CMI Certified Master Inspector and Independent
License NC2449 and SC1597
704 301-3207



"Discovery consists in seeing what everyone else has seen and thinking what no one else has thought."
- Albert Szent-Gyvrgyi, Nobel Prize for Medicine 1937
Reply With Quote
  #11  
Old 8/9/10, 10:20 PM
Brian E. Kelly's Avatar
Brian E. Kelly Brian E. Kelly is offline
InterNACHI Member
 
Join Date: Oct 2004
Location: Phoenix, AZ
Posts: 15,973
Default Re: is it nec 2010 for a GFCI to be on a garage door opener

Quote:
Originally Posted by bking View Post
So far all of the garage door outlets I have seen with GFI have the test/reset on the ceiling or a dedicated GFI device (no outlets) on the wall. These are independent of the regular garage outlet circuit. The code people should have required the reset to be within reach of a normal height person without standing on anything.
they make a special tool for those high ones Bruce, out here they call the special tool a "Stick".
Reply With Quote
  #12  
Old 8/11/10, 12:54 AM
Tim Spargo's Avatar
Tim Spargo Tim Spargo is offline
InterNACHI Member
 
Join Date: Jun 2006
Location: Lancaster, CA
Posts: 2,407
Default Re: is it nec 2010 for a GFCI to be on a garage door opener

Good point Bruce... "my outlet is compliant, but I broke my leg resetting it"



Home Inspections in Palmdale Lancaster California

Tim Spargo
Spec Rite Inspections
Commercial and Residential Inspections
Palmdale Lancaster Santa Clarita CA
661-317-5770








Reply With Quote
  #13  
Old 8/11/10, 12:56 AM
Joe Funderburk, CMI's Avatar
Joe Funderburk, CMI Joe Funderburk, CMI is offline
InterNACHI Member
 
Join Date: Dec 2005
Location: Hickory Grove, SC
Posts: 8,343
Send a message via Yahoo to jfunderburk
Default Re: is it nec 2010 for a GFCI to be on a garage door opener

If I see a reset in the ceiling, I write it up as "just plain stupid".



“The things that will destroy America are peace at any price,
prosperity at any cost, safety first instead of duty first,
the love of soft living, and the get-rich-quick theory of life.”
Theodore Roosevelt


Joe Funderburk, CMI
Alpha & Omega Home Inspections, LLC
Inspecting Upstate SC & Charlotte Metro, NC
NACHI ID: NACHI05120170
www.aohomeinspection.com


Reply With Quote
Need a home inspection in Washington? Check out InterNACHI's listing of Washington certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #14  
Old 8/11/10, 12:58 AM
Joe Funderburk, CMI's Avatar
Joe Funderburk, CMI Joe Funderburk, CMI is offline
InterNACHI Member
 
Join Date: Dec 2005
Location: Hickory Grove, SC
Posts: 8,343
Send a message via Yahoo to jfunderburk
Default Re: is it nec 2010 for a GFCI to be on a garage door opener

Quote:
Originally Posted by bkelly2 View Post
they make a special tool for those high ones Bruce, out here they call the special tool a "Stick".
And they come in right hand and left hand versions. I think Professional Equipment sells them.



“The things that will destroy America are peace at any price,
prosperity at any cost, safety first instead of duty first,
the love of soft living, and the get-rich-quick theory of life.”
Theodore Roosevelt


Joe Funderburk, CMI
Alpha & Omega Home Inspections, LLC
Inspecting Upstate SC & Charlotte Metro, NC
NACHI ID: NACHI05120170
www.aohomeinspection.com


Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
attached garage ghelder General Inspection Discussion 5 2/23/10 5:40 PM
Garage door inspection procedure bgromicko General Inspection Discussion 5 8/7/09 12:47 PM
Installing GFCI in garage with no ground cyezza Electrical Inspections 53 11/30/07 5:05 PM
Garage GFCI rdale Electrical Inspections 29 8/8/07 4:06 PM


All times are GMT -4. The time now is 7:48 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts