Default NEC 250.32B1 Isolate neutral from EGC

Electrician says nothing wrong with sub panel. Wants to know from what code I am calling this out. Do I have the correct code? He said it is alright the way it is neutral and grounds using the same lug attached to the box. I said put it in writing and and make sure I get a copy.
Reply With Quote
  #2  
Old 7/12/07, 9:04 PM
Speedy Petey Speedy Petey is offline
Unmoderated Guest
 
Join Date: Jul 2006
Posts: 1,297
Please Note: Speedy Petey is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: NEC 250.32B1 Isolate neutral from EGC

250.32(B)(1) supports you, BUT...250.32(B)(2) supports him. Who is correct, only you can tell.

(2) Grounded Conductor
Where (1) an equipment grounding conductor is not run with the supply to the building or structure, (2) there are no continuous metallic paths bonded to the grounding system in each building or structure involved, and (3) ground-fault protection of equipment has not been installed on the supply side of the feeder(s), the grounded conductor run with the supply to the building or structure shall be connected to the building or structure disconnecting means and to the grounding electrode(s) and shall be used for grounding or bonding of equipment, structures, or frames required to be grounded or bonded.
Reply With Quote
  #3  
Old 7/12/07, 9:15 PM
tdietrich1's Avatar
tdietrich1 tdietrich1 is offline
InterNACHI Member
 
Join Date: Oct 2006
Location: Northampton County - Pa
Posts: 1,954
Send a message via Yahoo to tdietrich1
Default Re: NEC 250.32B1 Isolate neutral from EGC

imho:

Photos, please.

Besides, you recorded a concern, an electrician looked it over, you have filled your obligation.

tom
Reply With Quote
  #4  
Old 7/12/07, 9:19 PM
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,072
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: NEC 250.32B1 Isolate neutral from EGC

ewwww.......now SPEEDY knows that one is a catch 22 type of reply...lol

Let me just say this....lol....I am glad that the 2008 NEC will finally address this issue....thank GAWD...


(B) Grounded Systems.
For a grounded system at the
separate building or structure, the connection to the grounding
electrode, the grounding and bonding of equipment,
structures, or frames required to be grounded and bonded
shall comply with 250.32(B)(1).
[ROP 5–77, 5–119,
5–121a]
(1) Equipment Grounding Conductor.
An equipment
grounding conductor as described in 250.118 shall be run
with the supply conductors and connected to the building or
structure disconnecting means and to the grounding electrode(
s). The equipment grounding conductor shall be used
for grounding or bonding of equipment, structures, or
frames required to be grounded or bonded. The equipment
grounding conductor shall be sized in accordance with
250.122. Any installed grounded conductor shall not be
connected to the equipment grounding conductor or to the
grounding electrode(s).



Exception: For existing premises wiring systems only, the

grounded conductor run with the supply to the building or
structure shall be permitted to be connected to the building
or structure disconnecting means and to the grounding
electrode(s) and shall be used for grounding and bonding
of equipment, structures, or frames required to be grounded
and bonded where all the following requirements of (1), (2),
and (3) are met:
[ROP 5–76, 5–119]



(1) An equipment grounding conductor is not run with the

supply to the building or structure.
(2) There are no continuous metallic paths bonded to the
grounding system in each building or structure involved.
(3) Ground-fault protection of equipment has not been installed
on the supply side of the feeder(s).
[ROP 5–119,
5–76]





Paul W. Abernathy
Reply With Quote
  #5  
Old 7/12/07, 9:31 PM
Peter Doane's Avatar
Peter Doane Peter Doane is offline
InterNACHI Member
 
Join Date: Dec 2005
Location: Olympia, WA
Posts: 2,055
Default Re: NEC 250.32B1 Isolate neutral from EGC

Code 792 of the 457, stipulates or requires, bonding of the 354.095.987 unlessssssss the moon is in the waxing phase of cycle,... Thennnnnnn the 457 should NOT be bonded to the 792..... You'll have to re pull all the wires you just ran, bring em back to the electrical supplier and tell them to shove it!

Any questions?

LOL I love electricians!!!!!!!!

Oh,.. thanks Paul for the info! He He!



Peter Doane
Realty Check Inspection Service
NACHI ID# 05120681
Reply With Quote
  #6  
Old 7/12/07, 9:49 PM
Gerald C. Wilcox's Avatar
Gerald C. Wilcox Gerald C. Wilcox is offline
InterNACHI Member
 
Join Date: Jan 2007
Location: Harvey, ND
Posts: 333
Default Re: NEC 250.32B1 Isolate neutral from EGC

I should have posted the pictures in the first place. Sorry about that.
Attached Thumbnails
national-electrical-code-250-32b1-isolate-neutral-equipment-grounding-conductor-pic-2.jpg   national-electrical-code-250-32b1-isolate-neutral-equipment-grounding-conductor-pic-1.jpg  
Reply With Quote
  #7  
Old 7/12/07, 9:52 PM
tdietrich1's Avatar
tdietrich1 tdietrich1 is offline
InterNACHI Member
 
Join Date: Oct 2006
Location: Northampton County - Pa
Posts: 1,954
Send a message via Yahoo to tdietrich1
Default Re: NEC 250.32B1 Isolate neutral from EGC

There doesn't look like there was even a ground ran to this panel.

tom
Reply With Quote
  #8  
Old 7/12/07, 9:54 PM
Peter Doane's Avatar
Peter Doane Peter Doane is offline
InterNACHI Member
 
Join Date: Dec 2005
Location: Olympia, WA
Posts: 2,055
Default Re: NEC 250.32B1 Isolate neutral from EGC

Quote:
Originally Posted by gwilcox
I should have posted the pictures in the first place. Sorry about that.
Gerald,
I call this out all the time on sub panels,.. never had an electricain (that I know about) say its ok. HEY, you did your job, its now on them.



Peter Doane
Realty Check Inspection Service
NACHI ID# 05120681
Reply With Quote
  #9  
Old 7/12/07, 10:06 PM
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,072
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: NEC 250.32B1 Isolate neutral from EGC

Ok Peter........Smart *****...lol.......I was just saying that thank goodness the NEC is addressing 250.32 issues finally in regards to new construction. That post was kinda for my fellow electrician ....

One important factor was missing here.......if the "Sub-Panel" was in an attached garage or somewhere in the dwelling itself it would have to be done with (4) conductors regardless of what 250.32(B)(2) might allow...

But I will assume you are talking about a detached garage....lol.....but I can think of many things that might stop the allowance of 250.32(B)(2)....running (4) conductors is just safer....simple as that and it is WHY the NEC is addressing it......enough of us complained over the years I guess.

If the "Sub-Panel" is indeed located in a detached garage, with no potential between the dwelling and the said garage or structure then currently a 3 wire setup is allowed by the NEC ( which is a minimum safety standard...always remember that...it is based on safety )

Now I think I see the GEC for that panel on the right...looks like a 6AWG or might be a 4AWG...can't really tell from the picture.....

Now I might question the conductors coming in...I can't tell and I think Mark Shunk is probably a better eye than me on that...but they do not look like conductors that are allowed to run into the building itself...but alas I can't tell on those very well.....

At the end of the day........defer it and let the electrician sort it out and if he is fine with it.....move on to a better fight.....if the panel is attached to the dwelling or in the dwelling....then I would make it an even bigger issue personally.



Paul W. Abernathy
Reply With Quote
  #10  
Old 7/12/07, 10:11 PM
Speedy Petey Speedy Petey is offline
Unmoderated Guest
 
Join Date: Jul 2006
Posts: 1,297
Please Note: Speedy Petey is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: NEC 250.32B1 Isolate neutral from EGC

Quote:
Originally Posted by pdoane
Gerald,
I call this out all the time on sub panels,.. never had an electricain (that I know about) say its ok. HEY, you did your job, its now on them.
Sometimes it IS perfectly legal and acceptable. As long as there are no other metallic paths, such as phone, CATV or water, then it is OK.

What I do see, or do not see, is no main disconnect.
A detached structure requires one. If the panel would accept six breakers or less, a separate, or main, disconnect would not be required. Six is the legal limit. That is an 8/16 panel.
Reply With Quote
  #11  
Old 7/12/07, 10:13 PM
Speedy Petey Speedy Petey is offline
Unmoderated Guest
 
Join Date: Jul 2006
Posts: 1,297
Please Note: Speedy Petey is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: NEC 250.32B1 Isolate neutral from EGC

Quote:
Originally Posted by pabernathy
Now I might question the conductors coming in...I can't tell and I think Mark Shunk is probably a better eye than me on that...but they do not look like conductors that are allowed to run into the building itself...but alas I can't tell on those very well.....
That is URD. I know Marc's area does not allow it but many/most others do. That is the standard wire/cable for this application in my area.
Reply With Quote
  #12  
Old 7/12/07, 10:20 PM
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,072
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: NEC 250.32B1 Isolate neutral from EGC

Yeah...I was not sure as it looks shinny and my area has issues with it also but I simply could not tell.

Do we know if this is a detached or attached garage....?

Anyway...Speedy did you notice the 2008 NEC change on 250.32(B)(1) ....sad to say we wont see the 2008 NEC in VA well....until like 2011..lol



Paul W. Abernathy
Reply With Quote
  #13  
Old 7/12/07, 11:02 PM
Gerald C. Wilcox's Avatar
Gerald C. Wilcox Gerald C. Wilcox is offline
InterNACHI Member
 
Join Date: Jan 2007
Location: Harvey, ND
Posts: 333
Default Re: NEC 250.32B1 Isolate neutral from EGC

Yes, it is a detached garage. Underground service from the house. No ground rod outside garage, believed to continue back to the main service panel and ground to copper water service pipe.
Reply With Quote
  #14  
Old 7/12/07, 11:03 PM
Peter Doane's Avatar
Peter Doane Peter Doane is offline
InterNACHI Member
 
Join Date: Dec 2005
Location: Olympia, WA
Posts: 2,055
Default Re: NEC 250.32B1 Isolate neutral from EGC

Quote:
Originally Posted by Speedy Petey
Sometimes it IS perfectly legal and acceptable. As long as there are no other metallic paths, such as phone, CATV or water, then it is OK.

What I do see, or do not see, is no main disconnect.
A detached structure requires one. If the panel would accept six breakers or less, a separate, or main, disconnect would not be required. Six is the legal limit. That is an 8/16 panel.
What are you saying is legal??? The grounds and neutrals on the same buss is ok??? or not having the extra (4th) ground wire???



Peter Doane
Realty Check Inspection Service
NACHI ID# 05120681
Reply With Quote
  #15  
Old 7/12/07, 11:04 PM
Peter Doane's Avatar
Peter Doane Peter Doane is offline
InterNACHI Member
 
Join Date: Dec 2005
Location: Olympia, WA
Posts: 2,055
Default Re: NEC 250.32B1 Isolate neutral from EGC

Quote:
Originally Posted by pabernathy
Ok Peter........Smart *****...lol.......I was just saying that thank goodness the NEC is addressing 250.32 issues finally
I know, just giving you crap! lol



Peter Doane
Realty Check Inspection Service
NACHI ID# 05120681
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
"UFER" Ground? see last paragraph. jtedesco1 Electrical Inspections 19 8/23/11 3:56 PM
Metal Rigid or PVC Rigid what is code bpotts Electrical Inspections 5 12/4/06 2:40 PM
Ground wire in neutral bar, neutral to breaker, hot to ground? rmc3inspection Electrical Inspections 4 8/1/06 9:44 AM
Proposed Definition of Neutral Conductor and Point jtedesco1 Electrical Inspections 1 4/22/06 10:19 AM


All times are GMT -4. The time now is 7:48 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts