Electrician says nothing wrong with sub panel. Wants to know from what code I am calling this out. Do I have the correct code? He said it is alright the way it is neutral and grounds using the same lug attached to the box. I said put it in writing and and make sure I get a copy.
"He is no fool who gives what he cannot keep to gain that which he cannot lose." Jim Elliot 1949 Gerald Wilcox Harvey, ND CMIA, RMT www.housecheckhomeinspections.com www.homeinspectorinnorthdakota.com 701.324.4075 Minot, ND Home Inspections Devil's Lake, ND Home Inspections Bismarck, ND Home Inspections Jamestown, ND Home Inspections Home Inspector in North Dakota North Dakota Home Inspection |
250.32(B)(1) supports you, BUT...250.32(B)(2) supports him. Who is correct, only you can tell.
(2) Grounded Conductor Where (1) an equipment grounding conductor is not run with the supply to the building or structure, (2) there are no continuous metallic paths bonded to the grounding system in each building or structure involved, and (3) ground-fault protection of equipment has not been installed on the supply side of the feeder(s), the grounded conductor run with the supply to the building or structure shall be connected to the building or structure disconnecting means and to the grounding electrode(s) and shall be used for grounding or bonding of equipment, structures, or frames required to be grounded or bonded. |
imho:
Photos, please. Besides, you recorded a concern, an electrician looked it over, you have filled your obligation. tom |
ewwww.......now SPEEDY knows that one is a catch 22 type of reply...lol
Let me just say this....lol....I am glad that the 2008 NEC will finally address this issue....thank GAWD... (B) Grounded Systems. For a grounded system at the separate building or structure, the connection to the grounding electrode, the grounding and bonding of equipment, structures, or frames required to be grounded and bonded shall comply with 250.32(B)(1). [ROP 5–77, 5–119, 5–121a] (1) Equipment Grounding Conductor. An equipment grounding conductor as described in 250.118 shall be run with the supply conductors and connected to the building or structure disconnecting means and to the grounding electrode( s). The equipment grounding conductor shall be used for grounding or bonding of equipment, structures, or frames required to be grounded or bonded. The equipment grounding conductor shall be sized in accordance with 250.122. Any installed grounded conductor shall not be connected to the equipment grounding conductor or to the grounding electrode(s). Exception: For existing premises wiring systems only, the grounded conductor run with the supply to the building or structure shall be permitted to be connected to the building or structure disconnecting means and to the grounding electrode(s) and shall be used for grounding and bonding of equipment, structures, or frames required to be grounded and bonded where all the following requirements of (1), (2), and (3) are met: [ROP 5–76, 5–119] (1) An equipment grounding conductor is not run with the supply to the building or structure. (2) There are no continuous metallic paths bonded to the grounding system in each building or structure involved. (3) Ground-fault protection of equipment has not been installed on the supply side of the feeder(s). [ROP 5–119, 5–76] Paul W. Abernathy |
Code 792 of the 457, stipulates or requires, bonding of the 354.095.987 unlessssssss the moon is in the waxing phase of cycle,... Thennnnnnn the 457 should NOT be bonded to the 792..... You'll have to re pull all the wires you just ran, bring em back to the electrical supplier and tell them to shove it!
Any questions? LOL I love electricians!!!!!!!! Oh,.. thanks Paul for the info! He He! Peter Doane Realty Check Inspection Service NACHI ID# 05120681
I should have posted the pictures in the first place. Sorry about that.
There doesn't look like there was even a ground ran to this panel.
tom |
I call this out all the time on sub panels,.. never had an electricain (that I know about) say its ok. HEY, you did your job, its now on them. Peter Doane Realty Check Inspection Service NACHI ID# 05120681
Ok Peter........Smart *****...lol.......I was just saying that thank goodness the NEC is addressing 250.32 issues finally in regards to new construction. That post was kinda for my fellow electrician ....
One important factor was missing here.......if the "Sub-Panel" was in an attached garage or somewhere in the dwelling itself it would have to be done with (4) conductors regardless of what 250.32(B)(2) might allow... But I will assume you are talking about a detached garage....lol.....but I can think of many things that might stop the allowance of 250.32(B)(2)....running (4) conductors is just safer....simple as that and it is WHY the NEC is addressing it......enough of us complained over the years I guess. If the "Sub-Panel" is indeed located in a detached garage, with no potential between the dwelling and the said garage or structure then currently a 3 wire setup is allowed by the NEC ( which is a minimum safety standard...always remember that...it is based on safety ) Now I think I see the GEC for that panel on the right...looks like a 6AWG or might be a 4AWG...can't really tell from the picture..... Now I might question the conductors coming in...I can't tell and I think Mark Shunk is probably a better eye than me on that...but they do not look like conductors that are allowed to run into the building itself...but alas I can't tell on those very well..... At the end of the day........defer it and let the electrician sort it out and if he is fine with it.....move on to a better fight.....if the panel is attached to the dwelling or in the dwelling....then I would make it an even bigger issue personally. Paul W. Abernathy |
What I do see, or do not see, is no main disconnect. A detached structure requires one. If the panel would accept six breakers or less, a separate, or main, disconnect would not be required. Six is the legal limit. That is an 8/16 panel. |
Yeah...I was not sure as it looks shinny and my area has issues with it also but I simply could not tell.
Do we know if this is a detached or attached garage....? Anyway...Speedy did you notice the 2008 NEC change on 250.32(B)(1) ....sad to say we wont see the 2008 NEC in VA well....until like 2011..lol Paul W. Abernathy |
Yes, it is a detached garage. Underground service from the house. No ground rod outside garage, believed to continue back to the main service panel and ground to copper water service pipe.