Default NFPA, OSHA and Power Strips

Can a coffee pot be plugged into a power strip? Power strips (also called relocatable power taps or RPTs) are not to be used to power appliances such as coffee pots, microwave ovens, toasters or refrigerators. Power strips also cannot be used with extension cords (constitutes a daisy chain extension cord).

As bob posted ( we live in a FREE country we can plug what ever we want into them...lol )


Discussion: Relocatable power taps (RPT) (also know as strip plugs, power strips, etc) and are for use with computers and their associated hardware components, low power usage components. Using an RPT with appliances or other high power loads is a violation of the OSHA requirement for proper usage ( OSHA IS NOT MY REASON FOR POSTING THIS..IGNORE OSHA..LOL ). NFPA 70 Article 110-3B also requires instructions to be followed. RPTs are not designed to handle high current loads. Small coffee pots (at 5-7 amps) are considered high current loads. UL pointed out that several 2 amp loads on the power strip would also represent hazard. The wire used in the strip to connect the outlets to the input is undersized for such usage, which may result in the wire overheating leading to insulation failure, arcing, and possible fire.

Reprint courtesy of :ES & H Safety Board



Paul W. Abernathy
Manager, Electrical Codes & Standards
Encore Wire Corporation

“Promise me you'll always remember: You're braver than you believe, and stronger than you seem, and smarter than you think.”

Disclaimer - All my posts on this forum are of my own personal opinion and in no way represent the opinions of Encore Wire, or other associations, organizations or affiliations.

Last edited by pabernathy; 1/2/06 at 10:09 AM..
Reply With Quote
  #2  
Old 1/2/06, 9:36 AM
Bob Badger Bob Badger is offline
New User
 
Join Date: Dec 2003
Posts: 77
Please Note: Bob Badger is a non-member guest and is in no way affiliated with InterNACHI or its members.
Post Re: NFPA, OSHA and Power Strips

Good morning Paul.

Quote:
Originally Posted by pabernathy
Can a coffee pot be plugged into a power strip?
Of course you can plug a coffee pot into a plug strip.

As a private citizen you can plug anything you want into a plug strip in your home.

OSHA is not a factor in a home, the UL White book is not a code.

Sure we can tell a homeowner that they have a 110.3(B) violation and then when they stop laughing at us they will go back to what they where doing.

Don't get me wrong I agree that these units can and do cause fires.

IMO, that has more to do with the poor quality of the majority of these units then the concept itself. I have two RPTs that have 20' 12/3 cords, a 20 amp male cord cap, 20 amp spec. grade duplexs, metal enclosure and a circuit breaker. I use these for many items temporarily.

IMO Something needs to be done far above the level of an electrician or a HI, either these units need to be banned (I am opposed to that) or these units need to be able to handle any load that can be plugged in.

JMO, Happy New Year Everyone, Bob
Reply With Quote
  #3  
Old 1/2/06, 9:40 AM
Paul W. Abernathy, CMI's Avatar
Paul W. Abernathy, CMI Paul W. Abernathy, CMI is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: McKinney, TX
Posts: 8,664
Send a message via Skype™ to pabernathy
Default Re: NFPA, OSHA and Power Strips

lol......I knew you would say that...lol.....

lol.....I happen to do commercial inspections as well so...but I was more interested in the effects of those RPT's as many just seem to load them up and on a residential front.....I see overloaded RPT's all the time and I do not consider all of them I see as temporary...lol

Teheheh...I do need to remove the OSHA line as it was not intended for that actually...just to show the possible dangers of overloading RPT's in general...



Paul W. Abernathy
Manager, Electrical Codes & Standards
Encore Wire Corporation

“Promise me you'll always remember: You're braver than you believe, and stronger than you seem, and smarter than you think.”

Disclaimer - All my posts on this forum are of my own personal opinion and in no way represent the opinions of Encore Wire, or other associations, organizations or affiliations.

Last edited by pabernathy; 1/2/06 at 9:51 AM..
Reply With Quote
  #4  
Old 1/2/06, 9:43 AM
jferry's Avatar
jferry jferry is offline
InterNACHI Member
 
Join Date: Apr 2005
Location: Erdenheim, PA
Posts: 1,615
Default Re: NFPA, OSHA and Power Strips

How safe is it to hook up the computer and peripherals to an RPT?



Joseph A. Ferry, Esquire
Two Penn Center Plaza
Suite 200
Philadelphia, PA 19102

215-854-6444 tel.
215-243-8202 fax
Reply With Quote
  #5  
Old 1/2/06, 9:49 AM
Paul W. Abernathy, CMI's Avatar
Paul W. Abernathy, CMI Paul W. Abernathy, CMI is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: McKinney, TX
Posts: 8,664
Send a message via Skype™ to pabernathy
Default Re: NFPA, OSHA and Power Strips

Joe,

It is done all the time....as bob said I also happen to have one for my computer system as well.

It really honestly depends on the manufacturer I believe as a good name will put efforts into building safety measures into them.

I get more concerned with the plugging in of larger draw items like large coffee pots, microwaves and larger items that work on the 20A spectrum per say.

I bought this up not because HI's should say anything about them but to leave it up to them to notice it....more or less as additional education on issues of safety and so on they may see.

Chances are in most home inspections the house is empty anyway or not in a state where you may see this alot....

I also just happen to have a good friend who has a RPT behind his large screen TV and it overheated and caught on fire and did severe damage to his TV, the wall in the house and of course his components in that area....BUT again the dude ( my friend ) had the strips overloaded beyond their listed capacity and even had them daisy chained to meet his need.....thats a WRONG move in itself.

I think they are fine for general use, temporary use and in well ventilated areas and ones made by reputable companies are fine.



Paul W. Abernathy
Manager, Electrical Codes & Standards
Encore Wire Corporation

“Promise me you'll always remember: You're braver than you believe, and stronger than you seem, and smarter than you think.”

Disclaimer - All my posts on this forum are of my own personal opinion and in no way represent the opinions of Encore Wire, or other associations, organizations or affiliations.
Reply With Quote
  #6  
Old 1/2/06, 9:50 AM
Bob Badger Bob Badger is offline
New User
 
Join Date: Dec 2003
Posts: 77
Please Note: Bob Badger is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: NFPA, OSHA and Power Strips

In commercial work enforcement can be more clear cut.

I have spent many 'overnights' in most of the major retailers installing permanent wiring on the shelves as the Fire Marshal had come through and said the dozens of daisychained plug strips running entire electronic depts. had to go.

Where it gets kind of cloudy is in computer rooms, all the major manufactures make what looks like (and is) an RPT except it has a different listing and is rack mountable.

The only difference is the listing and a set of mounting 'ears' these can be used forever like this.
Reply With Quote
  #7  
Old 1/2/06, 9:55 AM
Paul W. Abernathy, CMI's Avatar
Paul W. Abernathy, CMI Paul W. Abernathy, CMI is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: McKinney, TX
Posts: 8,664
Send a message via Skype™ to pabernathy
Default Re: NFPA, OSHA and Power Strips

Bob,

Many of the ones I have done are simply plug molding and designed to be used for display systems as you stated . I did one last year for Circuit City in which we had 3 banks of plug molding and set up for the purpose of display.

These were not temporary, however they did have their usage sized correctly and installed for the purpose. The bad thing about RPT's are like you said...they are a quick fix and many use them in non-temporary applications which is where they start to load them up and forget about the issues that can play on them.

The actual intent of the post was education on electrical safety and concerns of overloading things not intended for the proper applications is all....



Paul W. Abernathy
Manager, Electrical Codes & Standards
Encore Wire Corporation

“Promise me you'll always remember: You're braver than you believe, and stronger than you seem, and smarter than you think.”

Disclaimer - All my posts on this forum are of my own personal opinion and in no way represent the opinions of Encore Wire, or other associations, organizations or affiliations.
Reply With Quote
  #8  
Old 1/2/06, 9:59 AM
Bob Badger Bob Badger is offline
New User
 
Join Date: Dec 2003
Posts: 77
Please Note: Bob Badger is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: NFPA, OSHA and Power Strips

Quote:
Originally Posted by jferry
How safe is it to hook up the computer and peripherals to an RPT?
It could be perfectly safe or it could be a fire waiting for fuel.

IMO much depends on the quality of the plug strip and of course the amount of load connected to it.

In the end the 15 amp CB in the power strip should be able to open before an overload damages the power strip or the branch circuit it is connected to.

Admittedly this is not always the case.

Keeping that in mind if you where to keep the continuous load applied to the typical plug strip to less than 12 amps you should have no problems.

A typical PC with monitor and other peripherals (Laser Printers excluded) will not draw nearly 12 amp, most likely less than 5 amps, many less than 2 amps.
Reply With Quote
  #9  
Old 1/2/06, 10:16 AM
jtedesco1 jtedesco1 is offline
Account Suspended Due to Excessive Complaints
 
Join Date: Dec 2005
Posts: 1,890
Please Note: jtedesco1 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Smile Re: NFPA, OSHA and Power Strips

Quote:
Originally Posted by jferry
How safe is it to hook up the computer and peripherals to an RPT?

RELOCATABLE POWER TAPS

(XBYS)


USE AND INSTALLATION


This category covers relocatable power taps rated 250 V ac or less, 20 A
less, intended for indoor use as relocatable multiple outlet extensions of
branch circuit to supply laboratory equipment, home workshops, home
movie lighting controls, musical instrumentation, and to provide outlet
receptacles for computers, audio and video equipment, and other equipment.
They consist of an attachment plug and a length of flexible cord terminated
in an enclosure in which one or more receptacles are mounted.
They may, in addition, be provided with fuses or other supplementary
overcurrent protection, switches, suppression components and/or indicator
lights in any combination, or connections for cable, communications,
telephone and/or antenna.
Relocatable power taps are intended to be directly connected to a permanently
installed branch circuit receptacle. Relocatable power taps are
not intended to be series connected (daisy chained) to other relocatable
power taps or to extension cords.
Relocatable power taps are not intended for use at construction sites and
similar locations.
Relocatable power taps are not intended to be permanently secured to
building structures, tables, work benches or similar structures, nor are

Reply With Quote
  #10  
Old 1/2/06, 10:38 AM
Doug Edwards Doug Edwards is offline
InterNACHI Member
 
Join Date: Apr 2004
Posts: 5,118
Default Re: NFPA, OSHA and Power Strips

sample

Last edited by dedwards; 3/2/06 at 8:52 PM..
Reply With Quote
  #11  
Old 1/2/06, 10:50 AM
Paul W. Abernathy, CMI's Avatar
Paul W. Abernathy, CMI Paul W. Abernathy, CMI is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: McKinney, TX
Posts: 8,664
Send a message via Skype™ to pabernathy
Default Re: NFPA, OSHA and Power Strips

Ya.....the old Daisy Chain cost a freind of mine alot as I said before. Sad thing is I was in his house just 3 weeks before that and made a comment to him about it because I was their fixing something and told him to get rid of that RPT set up.

Now....imagine how I feel.....I may have told him but the FRIEND did not listen very well and paid for it...then gave me a guilt trip.



Paul W. Abernathy
Manager, Electrical Codes & Standards
Encore Wire Corporation

“Promise me you'll always remember: You're braver than you believe, and stronger than you seem, and smarter than you think.”

Disclaimer - All my posts on this forum are of my own personal opinion and in no way represent the opinions of Encore Wire, or other associations, organizations or affiliations.
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Download the videos here all about physics and electricity jtedesco1 Electrical Inspections 5 9/14/08 3:58 PM

All times are GMT -4. The time now is 6:26 AM.
no new posts