A contractor friend of mine performed the following experiment and asked for my explanation this evening.

A 5 gal plastic bucket is filled with water. electrical cord (with insulation stripped from the ends) is placed into the water in the bucket. The lamp cord plug is then placed into a GFCI receptacle. Circuit is in a house that is easily 60-70 years old. My friend tells me the GFCI did NOT trip and the breaker did NOT trip and he wants to know why not.

Soooo what is the explanation ??

Here is my response. The circuit could be ungrounded, 2 conductor wire based on the age of the house. The GFCI didn't trip because current is NOT unbalanced between the two lamp cord leads. The breaker didn't trip because even though the water is a good conductor the leads had to have been far enough apart (I have no idea how far apart) that the electrical current could not overcome the resistance of the water.


And now the million dollar question....If I place my hand in the bucket should the GFCI trip?
</IMG>



Scott Coslett
National Property Inspections
Berwick, PA
www.PennInspector.com
scoslett@pa.metrocast.net


"Life is Tough. Its even tougher if you're stupid" John Wayne
Reply With Quote
  #2  
Old 3/14/08, 10:09 PM
tdietrich1's Avatar
tdietrich1 tdietrich1 is offline
InterNACHI Member
 
Join Date: Oct 2006
Location: Northampton County - Pa
Posts: 1,954
Send a message via Yahoo to tdietrich1
Default Re: Neat GFCI Experiment

You pointed out something, there are so many factors, that is is possible it won't trip. I've handled energized wires, and touched energized junction boxes and no shock. However, I do where OSHA approved electrical safety shoes too.

Why mess around, the experiment sounds dumb.
Reply With Quote
  #3  
Old 3/14/08, 10:13 PM
Marc D. Shunk's Avatar
Marc D. Shunk Marc D. Shunk is offline
Banned
 
Join Date: Dec 2006
Location: Central PA
Posts: 1,980
Please Note: Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Neat GFCI Experiment

Water's not that good of a conductor until it gets some crap in it. An ICDI was developed to detect water immersion, because GFCI's suck at that.
Reply With Quote
  #4  
Old 3/14/08, 10:21 PM
Scott F. Coslett Scott F. Coslett is offline
InterNACHI Member
 
Join Date: Mar 2005
Location: Berwick, PA
Posts: 193
Default Re: Neat GFCI Experiment

Tom -

Dumb? Yes it is very dumb! (By the way, I certainly have no intention of duplicating the experiment or putting MY hand in the water!)

But it does make one think about grounding and how GFCI's work. Isn't this essentially why we test GFCI's with the test button on an ungrounded circuit as opposed to using a circuit tester?



Scott Coslett
National Property Inspections
Berwick, PA
www.PennInspector.com
scoslett@pa.metrocast.net


"Life is Tough. Its even tougher if you're stupid" John Wayne
Reply With Quote
  #5  
Old 3/14/08, 10:21 PM
Bob Elliott's Avatar
Bob Elliott Bob Elliott is offline
InterNACHI Member
 
Join Date: Aug 2006
Location: Chicago
Posts: 21,908
Default Re: Neat GFCI Experiment

Marc I have heard in a class room, that water is actually an insulater and you get shocked because you are the closest thing that does conduct.
Of course I have since learned this applies to pure water with out the crap.
Reply With Quote
  #6  
Old 3/14/08, 10:25 PM
Bob Elliott's Avatar
Bob Elliott Bob Elliott is offline
InterNACHI Member
 
Join Date: Aug 2006
Location: Chicago
Posts: 21,908
Default Re: Neat GFCI Experiment

In a real situation I would think you are touching the load side and creating an Unbalance.I suppose if you could grab both sides at the same time a GFCI would not trip. Seems right.
Reply With Quote
  #7  
Old 3/14/08, 10:26 PM
Marc D. Shunk's Avatar
Marc D. Shunk Marc D. Shunk is offline
Banned
 
Join Date: Dec 2006
Location: Central PA
Posts: 1,980
Please Note: Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Neat GFCI Experiment

Quote:
Originally Posted by relliott
Marc I have heard in a class room, that water is actually an insulater and you get shocked because you are the closest thing that does conduct.
There's an electrical instructor (maybe Mike Holt?) that plugs a cord into the wall and puts the other bare end in his glass of water and takes a drink out of it.
Reply With Quote
  #8  
Old 3/14/08, 10:31 PM
Bob Elliott's Avatar
Bob Elliott Bob Elliott is offline
InterNACHI Member
 
Join Date: Aug 2006
Location: Chicago
Posts: 21,908
Default Re: Neat GFCI Experiment

So I am guessing he uses pure water.
I wonder what happens if something like his skin oil or tooth particles mix in the water some day.
Reply With Quote
  #9  
Old 3/14/08, 10:34 PM
Marc D. Shunk's Avatar
Marc D. Shunk Marc D. Shunk is offline
Banned
 
Join Date: Dec 2006
Location: Central PA
Posts: 1,980
Please Note: Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Neat GFCI Experiment

Quote:
Originally Posted by relliott
I wonder what happens if something like his skin oil or tooth particles mix in the water some day.
My gut tells me it would take much more than that, like maybe a packet of salt. I'll expect a full report from you on Monday, Robert.
Reply With Quote
  #10  
Old 3/14/08, 10:35 PM
Bruce A. King's Avatar
Bruce A. King Bruce A. King is offline
InterNACHI Member
 
Join Date: Jan 2005
Location: York, SC
Posts: 3,206
Default Re: Neat GFCI Experiment

When they work on high voltage lines using a helicoter they clamp the hot wire to the frame of the helicopter to create a safer work environment.



B.A. King Home Inspections, LLC
www.BAKingHomeInspections.com
Serving Charlotte NC area and Rock Hill SC areas.
CMI Certified Master Inspector and Independent
License NC2449 and SC1597
704 301-3207



"Discovery consists in seeing what everyone else has seen and thinking what no one else has thought."
- Albert Szent-Gyvrgyi, Nobel Prize for Medicine 1937
Reply With Quote
  #11  
Old 3/14/08, 10:39 PM
Marc D. Shunk's Avatar
Marc D. Shunk Marc D. Shunk is offline
Banned
 
Join Date: Dec 2006
Location: Central PA
Posts: 1,980
Please Note: Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Neat GFCI Experiment

Quote:
Originally Posted by bking
When they work on high voltage lines using a helicoter they clamp the hot wire to the frame of the helicopter to create a safer work environment.
Yeah, the company from that thing you watched on TV is actually right down the road from me. Agrotors, Inc.

http://www.youtube.com/v/Z3q9WdjD5wc
Reply With Quote
  #12  
Old 3/14/08, 11:05 PM
Bob Elliott's Avatar
Bob Elliott Bob Elliott is offline
InterNACHI Member
 
Join Date: Aug 2006
Location: Chicago
Posts: 21,908
Default Re: Neat GFCI Experiment

That I do not understand at all.
Reply With Quote
  #13  
Old 3/14/08, 11:15 PM
Scott F. Coslett Scott F. Coslett is offline
InterNACHI Member
 
Join Date: Mar 2005
Location: Berwick, PA
Posts: 193
Default Re: Neat GFCI Experiment


I'd like to meet the 1st guy to ever do that....maybe he would stick his hand in the bucket.



Scott Coslett
National Property Inspections
Berwick, PA
www.PennInspector.com
scoslett@pa.metrocast.net


"Life is Tough. Its even tougher if you're stupid" John Wayne
Reply With Quote
  #14  
Old 3/14/08, 11:25 PM
cbuell's Avatar
cbuell cbuell is offline
Active Poster
 
Join Date: Feb 2004
Location: Shorline, WA
Posts: 380
Please Note: cbuell is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Neat GFCI Experiment

If you take an extension cord and strip the covering off both the hot and neutral a couple of inches apart (so they don't short each other) and immerse it in water it will not trip the gfci. Put a light bulb in the female end and start adding salt with a salt shaker and watch the bulb glow and the the water heat. Believe it or not, and try at your own peril
Reply With Quote
  #15  
Old 3/14/08, 11:33 PM
Richard L. Bennett Richard L. Bennett is offline
InterNACHI Member
 
Join Date: Mar 2005
Location: Frostproof, Fl
Posts: 2,304
Default Re: Neat GFCI Experiment

Electrical 101

Two wires in the bucket is not a ground fault - it is just another light bulb - no fault

Three wires in a bucket of water might be a fault

Three wires in a bucket of water with salt will be a fault

One hand in the bucket is not a problem

One hand in the bucket with salt is not a problem

One hand in the bucket with salt is a problem if your other hand or feet are on something that is in contact with ground

GFCI's trip when there is a current difference between ground and the neutral. GFCI give NO protection when a person is between the Hot and the Neutral. If that is you, your but is going to get warm

Draw it out on paper

rlb
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
AFCI Questions and Answers - Mike Holt pabernathy Electrical Inspections 7 4/16/12 9:51 PM
Inspection Pointers Here jtedesco1 Electrical Inspections 3 3/15/08 9:19 AM
More GFCI info from U/L Greg Fretwell Electrical Inspections 9 12/4/07 8:33 PM
GFCI Safety Notice rcooke Electrical Inspections 1 10/30/07 12:29 PM
The question asked on the new HI Study test here? jtedesco1 Electrical Inspections 28 10/4/06 9:31 AM


All times are GMT -4. The time now is 3:45 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts