#1
|
||||
|
||||
|
All the years I've been doing inspections, I've never ran into this situation.
Ok...Here's the situation. See the picture below. "Click To Enlarge" ![]() I have several 50 Amp metered panels wired into a 200 Amp service. There is only one (1) main disconnect (Long Handle) at the main SE panel. This will shut down the entire building. The other smaller metered panels do not contain main disconnects per panel and there are no other main disconnects anywhere for these individual smaller panels. Are these considered to be sub-panels/load side equipment, where all the grounds should be bonded? And aren't individual shut-offs required somewhere, for these smaller panels? |
|
#2
|
||||
|
||||
|
Please Note:
Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
You've got your main disconnect ahead of the meters, so your main is handled there. Each tennant panel does not require a main, but does need to be wired as a subpanel, since the main bonding jumper or screw will be in the main disco and the grounding electrode conductors will be there also.
What you picture there is called "cold sequence metering". |
|
#3
|
||||
|
||||
|
Quote:
That's what I thought and that's what I had told my client, but wanted a firm answer before I finalize my report. So this situation does indeed require bonded grounds and floating neutrals in every panel after the main SE. Thank you kindly, Sir. |
|
#4
|
||||
|
||||
|
Please Note:
Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Quote:
What screws people up here is that they look at a situation like this as 5 services, but what you really have there is one service, metered 5 times. What's interesting is that there is an exception that will permit the neutral to bond the meter cans internally if they're mounted directly adjacent to the main disco, as you have pictured. It's only 4-wire inside the panels. There's a heck of a lot of confusion out there related to exacltly how you do these apartment building setups, but it sounds like you pretty much had it straight to begin with and just wanted confirmation. |
|
#5
|
|||
|
|||
|
Please Note:
Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
There are AHJs that consider this whole cludge "service equipment" and don't expect to see the isolated ground until it leaves this assembly in a 4 wire feeder to the units. Certainly the panel in each unit should be treated as a sub.
I also believe each unit needs a disconnect. |
|
#6
|
||||
|
||||
|
Quote:
So now I have two different opinions. I'm going to add "Recommend disconnects at each sub-panel" to my report. Thank you Greg. |
|
#7
|
||||
|
||||
|
Please Note:
Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Quote:
|
|
#8
|
|||
|
|||
|
Please Note:
Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
Sad but true. Fortunately a HI only has the responsibility to warn the client about things they will hate later. If the guy in 101 is having his panel serviced it may be necessary to power down the whole building to do this work safely.
|
|
#9
|
||||
|
||||
|
Quote:
I knew there was something wrong here when I inspected it yesterday. Thanks guys. |
|
#10
|
|||
|
|||
|
David...in your picture you have posted.....what are the BOXES ( in your actual visual description ) below the meter housings.
Since you label the meters themselves and the 200A disconnect.....but not the boxes below the meters.......just for additional clarrification. Paul W. Abernathy |
|
#11
|
||||
|
||||
|
Quote:
Simply just breakers to individual circuits. Do you have something to add? |
![]() |
| Thread Tools | |
|
|
Similar Threads
|
||||
| Thread | Thread Starter | Forum | Replies | Last Post |
| Two Quick Questions On Receptacles | rtrain | Electrical Inspections | 7 | 11/27/07 11:24 PM |
| Does anyone know the answer to this???? | dcallahan | General Inspection Discussion | 5 | 7/2/07 5:33 PM |
| Thanks for the quick response | cpatzman | Miscellaneous Discussion for Inspectors | 6 | 6/11/06 10:54 PM |
| Quick Answer Needed - Reward | wdecker | Interior Inspections | 10 | 2/27/06 8:58 AM |
| Answer to a common question about GFCI's | jtedesco1 | Electrical Inspections | 4 | 1/12/06 9:29 PM |