Default I need an answer...Quick

All the years I've been doing inspections, I've never ran into this situation.

Ok...Here's the situation. See the picture below.

"Click To Enlarge"
need-answer-quick-elect.jpg

I have several 50 Amp metered panels wired into a 200 Amp service. There is only one (1) main disconnect (Long Handle) at the main SE panel. This will shut down the entire building. The other smaller metered panels do not contain main disconnects per panel and there are no other main disconnects anywhere for these individual smaller panels.

Are these considered to be sub-panels/load side equipment, where all the grounds should be bonded?

And aren't individual shut-offs required somewhere, for these smaller panels?
Reply With Quote
  #2  
Old 11/3/07, 6:39 PM
Marc D. Shunk's Avatar
Marc D. Shunk Marc D. Shunk is offline
Banned
 
Join Date: Dec 2006
Location: Central PA
Posts: 1,980
Please Note: Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: I need an answer...Quick

You've got your main disconnect ahead of the meters, so your main is handled there. Each tennant panel does not require a main, but does need to be wired as a subpanel, since the main bonding jumper or screw will be in the main disco and the grounding electrode conductors will be there also.

What you picture there is called "cold sequence metering".
Reply With Quote
  #3  
Old 11/3/07, 6:44 PM
David P. Valley's Avatar
David P. Valley David P. Valley is offline
InterNACHI Member
 
Join Date: Jun 2003
Location: METHUEN, MA
Posts: 8,681
Default Re: I need an answer...Quick

Quote:
Originally Posted by Marc D. Shunk
You've got your main disconnect ahead of the meters, so your main is handled there. Each tennant panel does not require a main, but does need to be wired as a subpanel, since the main bonding jumper or screw will be in the main disco and the grounding electrode conductors will be there also.

What you picture there is called "cold sequence metering".
Marc,

That's what I thought and that's what I had told my client, but wanted a firm answer before I finalize my report.

So this situation does indeed require bonded grounds and floating neutrals in every panel after the main SE.

Thank you kindly, Sir.
Reply With Quote
  #4  
Old 11/3/07, 6:59 PM
Marc D. Shunk's Avatar
Marc D. Shunk Marc D. Shunk is offline
Banned
 
Join Date: Dec 2006
Location: Central PA
Posts: 1,980
Please Note: Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: I need an answer...Quick

Quote:
Originally Posted by dvalley
So this situation does indeed require bonded grounds and floating neutrals in every panel after the main SE.
Yup. Your terminology is a little weird, but I get your meaning.

What screws people up here is that they look at a situation like this as 5 services, but what you really have there is one service, metered 5 times. What's interesting is that there is an exception that will permit the neutral to bond the meter cans internally if they're mounted directly adjacent to the main disco, as you have pictured. It's only 4-wire inside the panels. There's a heck of a lot of confusion out there related to exacltly how you do these apartment building setups, but it sounds like you pretty much had it straight to begin with and just wanted confirmation.
Reply With Quote
  #5  
Old 11/3/07, 11:54 PM
Greg Fretwell Greg Fretwell is offline
Active Poster
 
Join Date: Jul 2004
Location: Estero Florida
Posts: 1,798
Please Note: Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: I need an answer...Quick

There are AHJs that consider this whole cludge "service equipment" and don't expect to see the isolated ground until it leaves this assembly in a 4 wire feeder to the units. Certainly the panel in each unit should be treated as a sub.
I also believe each unit needs a disconnect.
Reply With Quote
  #6  
Old 11/4/07, 5:14 AM
David P. Valley's Avatar
David P. Valley David P. Valley is offline
InterNACHI Member
 
Join Date: Jun 2003
Location: METHUEN, MA
Posts: 8,681
Default Re: I need an answer...Quick

Quote:
Originally Posted by Greg Fretwell
There are AHJs that consider this whole cludge "service equipment" and don't expect to see the isolated ground until it leaves this assembly in a 4 wire feeder to the units. Certainly the panel in each unit should be treated as a sub.
I also believe each unit needs a disconnect.
That's what I had thought also, and that's the reason why this subject came up, as I wasn't 100% postive. I've always seen this type of electrical installation, but never with the individual disconnects missing.

So now I have two different opinions. I'm going to add "Recommend disconnects at each sub-panel" to my report.

Thank you Greg.
Reply With Quote
  #7  
Old 11/4/07, 10:54 AM
Marc D. Shunk's Avatar
Marc D. Shunk Marc D. Shunk is offline
Banned
 
Join Date: Dec 2006
Location: Central PA
Posts: 1,980
Please Note: Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: I need an answer...Quick

Quote:
Originally Posted by Greg Fretwell
There are AHJs that consider this whole cludge "service equipment" and don't expect to see the isolated ground until it leaves this assembly in a 4 wire feeder to the units.
They'd be entitled to that opinion, but this absolutely doesn't square with the NEC one bit. After you hit the disco, you have zero relief in the NEC from running 4-wire. It would be nice if each tennant panel had a disco, but there's no mandate for that either.
Reply With Quote
  #8  
Old 11/4/07, 12:50 PM
Greg Fretwell Greg Fretwell is offline
Active Poster
 
Join Date: Jul 2004
Location: Estero Florida
Posts: 1,798
Please Note: Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: I need an answer...Quick

Sad but true. Fortunately a HI only has the responsibility to warn the client about things they will hate later. If the guy in 101 is having his panel serviced it may be necessary to power down the whole building to do this work safely.
Reply With Quote
  #9  
Old 11/4/07, 3:04 PM
David P. Valley's Avatar
David P. Valley David P. Valley is offline
InterNACHI Member
 
Join Date: Jun 2003
Location: METHUEN, MA
Posts: 8,681
Default Re: I need an answer...Quick

Quote:
Originally Posted by Greg Fretwell
If the guy in 101 is having his panel serviced it may be necessary to power down the whole building to do this work safely.
Very good point Greg.

I knew there was something wrong here when I inspected it yesterday.

Thanks guys.
Reply With Quote
  #10  
Old 11/5/07, 8:51 AM
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,072
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: I need an answer...Quick

David...in your picture you have posted.....what are the BOXES ( in your actual visual description ) below the meter housings.

Since you label the meters themselves and the 200A disconnect.....but not the boxes below the meters.......just for additional clarrification.



Paul W. Abernathy
Reply With Quote
  #11  
Old 11/5/07, 10:54 AM
David P. Valley's Avatar
David P. Valley David P. Valley is offline
InterNACHI Member
 
Join Date: Jun 2003
Location: METHUEN, MA
Posts: 8,681
Default Re: I need an answer...Quick

Quote:
Originally Posted by pabernathy
David...in your picture you have posted.....what are the BOXES ( in your actual visual description ) below the meter housings.

Since you label the meters themselves and the 200A disconnect.....but not the boxes below the meters.......just for additional clarrification.
Those are the individual breaker panels for each tenant, with no main disconnects in them.

Simply just breakers to individual circuits.

Do you have something to add?
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Two Quick Questions On Receptacles rtrain Electrical Inspections 7 11/27/07 11:24 PM
Does anyone know the answer to this???? dcallahan General Inspection Discussion 5 7/2/07 5:33 PM
Thanks for the quick response cpatzman Miscellaneous Discussion for Inspectors 6 6/11/06 10:54 PM
Quick Answer Needed - Reward wdecker Interior Inspections 10 2/27/06 8:58 AM
Answer to a common question about GFCI's jtedesco1 Electrical Inspections 4 1/12/06 9:29 PM


All times are GMT -4. The time now is 7:48 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts