Default Need clarification

The data plate of this fairly new Exterior Trane A/C unit shows a minimum circuit ampacity of 17 Amps and is provided with a 12 AWG Cu (rated for 20 Amp) conductor connected to a 30 Amp breaker (unit disconnect also has 30 amp fuses).

I figure that this is so the breaker doesn't trip at start up each time. But the question I have is.....should the conductor be a 10 AWG Cu (for 30 amps) or is the 12 AWG CU considered okay since the start up surge is so short and unlikely to damage the 12 AWG Cu or create a fire hazard.

My feeling is that the conductor is too small.....but wanted to check it out before submitting my report (later tonight)
Attached Thumbnails
need-clarification-img_0045.jpg   need-clarification-img_0035.jpg  
Reply With Quote
  #2  
Old 1/21/08, 11:38 PM
Marc D. Shunk's Avatar
Marc D. Shunk Marc D. Shunk is offline
Active Poster
 
Join Date: Dec 2006
Location: Central PA
Posts: 1,967
Please Note: Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Need clarification

Quote:
Originally Posted by jweinberg
But the question I have is.....should the conductor be a 10 AWG Cu (for 30 amps) or is the 12 AWG CU considered okay since the start up surge is so short and unlikely to damage the 12 AWG Cu or create a fire hazard.)
Nope, there are special exceptions for things like motor loads and HVAC loads. The breaker in this sort of installation is providing the short circuit and ground fault protection, and the thermal overloads in the compressor unit are providing the overload protection.

It is quite common to see a great disparity between the breaker ampacity and the wire gauge for AC compressor feeds. This is completely permissible.

"Wire to the min, breaker to the max", are the limits of this rule when reading the dataplate.
Reply With Quote
  #3  
Old 1/21/08, 11:42 PM
Gerry Beaumont's Avatar
Gerry Beaumont Gerry Beaumont is offline
InterNACHI Member
 
Join Date: Jan 2003
Location: Clearwater, FL
Posts: 5,749
Send a message via AIM to gbeaumont Send a message via MSN to gbeaumont Send a message via Yahoo to gbeaumont
Default Re: Need clarification

Quote:
Originally Posted by Marc D. Shunk
"Wire to the min, breaker to the max", are the limits of this rule when reading the dataplate.
Nice quote Marc, I hope you don't mind considering it stolen

Very well put

Thanks

Gerry



Virtue is more to be feared than vice, because its excesses are not subject to the regulation of conscience.
Adam Smith (1723-1790)

Commercial property Inspection Tampa, Orlando, Sarasota, Jacksonville, Ft Launderdale, Miami, Florida.
NACHI cell 484-429-5466
NACHI02121106
Reply With Quote
  #4  
Old 1/21/08, 11:43 PM
Marc D. Shunk's Avatar
Marc D. Shunk Marc D. Shunk is offline
Active Poster
 
Join Date: Dec 2006
Location: Central PA
Posts: 1,967
Please Note: Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Need clarification

Quote:
Originally Posted by gbeaumont
Nice quote Marc, I hope you don't mind considering it stolen
Nope, not at all. That's my memory aid too.

I just noticed that this Trane dataplate also notes "min fuse or breaker size". That's something you seldom see noted on a dataplate. I suspect they do this to assure trouble-free future operation and not to mitigate any particular hazard. Usually it's just "min circuit ampacity", which relates to the wire gauge, and "max fuse or breaker size", which relates to the overcurrent protection size.

Last edited by Marc D. Shunk; 1/21/08 at 11:48 PM..
Reply With Quote
  #5  
Old 1/21/08, 11:55 PM
Gerry Beaumont's Avatar
Gerry Beaumont Gerry Beaumont is offline
InterNACHI Member
 
Join Date: Jan 2003
Location: Clearwater, FL
Posts: 5,749
Send a message via AIM to gbeaumont Send a message via MSN to gbeaumont Send a message via Yahoo to gbeaumont
Default Re: Need clarification

Quote:
Originally Posted by Marc D. Shunk
I just noticed that this Trane dataplate also notes "min fuse or breaker size". That's something you seldom see noted on a dataplate. I suspect they do this to assure trouble-free future operation and not to mitigate any particular hazard. Usually it's just "min circuit ampacity", which relates to the wire gauge, and "max fuse or breaker size", which relates to the overcurrent protection size.
Agreed, it would be nice if all manufacturers spelled it out interms of wire guage and breaker sizing, we would see many fewer potential issues.

BTW, down here duplicating it in Spanish would be a huge plus!!

Regards

Gerry



Virtue is more to be feared than vice, because its excesses are not subject to the regulation of conscience.
Adam Smith (1723-1790)

Commercial property Inspection Tampa, Orlando, Sarasota, Jacksonville, Ft Launderdale, Miami, Florida.
NACHI cell 484-429-5466
NACHI02121106

Last edited by gbeaumont; 1/21/08 at 11:59 PM..
Reply With Quote
  #6  
Old 1/22/08, 12:05 AM
jweinberg's Avatar
jweinberg jweinberg is offline
InterNACHI Member
 
Join Date: Feb 2005
Location: San Jose, CA
Posts: 420
Please Note: jweinberg is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Need clarification

Quote:
Originally Posted by Marc D. Shunk
I just noticed that this Trane dataplate also notes "min fuse or breaker size". That's something you seldom see noted on a dataplate.
Marc,

I've seen both min and max listed a lot but rarely have I seen them both listed at the same breaker size for both min and max. Figured this why there may be a need for 10 AWG.

Thanks for your answer....I liked the quote....easy to remember.

Gerry....are you claiming it as your quote originally?

Thanks again...

Jeff
Reply With Quote
  #7  
Old 1/22/08, 12:06 AM
jweinberg's Avatar
jweinberg jweinberg is offline
InterNACHI Member
 
Join Date: Feb 2005
Location: San Jose, CA
Posts: 420
Please Note: jweinberg is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Need clarification

Quote:
Originally Posted by gbeaumont

BTW, down here duplicating it in Spanish would be a huge plus!!

Regards

Gerry
Same on the vapor barrier of attic insulation. I constantly see it installed upside down.
Reply With Quote
  #8  
Old 1/22/08, 12:08 AM
Gerry Beaumont's Avatar
Gerry Beaumont Gerry Beaumont is offline
InterNACHI Member
 
Join Date: Jan 2003
Location: Clearwater, FL
Posts: 5,749
Send a message via AIM to gbeaumont Send a message via MSN to gbeaumont Send a message via Yahoo to gbeaumont
Default Re: Need clarification

Quote:
Originally Posted by jweinberg

Gerry....are you claiming it as your quote originally?

Jeff
Hi Jeff, heck no, credit where it's due, but I will use it, and I won't forget where I got it either, I love simple ways of remembering comlex issues.

Regards

Gerry



Virtue is more to be feared than vice, because its excesses are not subject to the regulation of conscience.
Adam Smith (1723-1790)

Commercial property Inspection Tampa, Orlando, Sarasota, Jacksonville, Ft Launderdale, Miami, Florida.
NACHI cell 484-429-5466
NACHI02121106
Reply With Quote
  #9  
Old 1/22/08, 1:21 AM
cbottger's Avatar
cbottger cbottger is offline
InterNACHI Member
 
Join Date: Apr 2004
Location: Marland, OK
Posts: 2,738
Default Re: Need clarification

Congradulations guys this is the way a message board is suppp0se to work ask a question get an answer. I used to have a good friend and tool buddy that drove me crazy in a good sort of way you could ask him the time of day and he would tell you how to build a watch. Keep up the good work



Freedom Express Inspections LLC
CMOR Thermography Certified Level 11 #2097
freedomexpressinspections.com
freedomexpress495@att.net
NACHI Member
Okla. State DEQ Environmental Phase One Certified
Master HVAC Mechanic (Retired)
Certified Universal Freon by 40CFR 82 Sub-part F
Professional Home Inspector State License # 130
Reporting system by Home Inspector Pro

Serving the State of Okla.
Reply With Quote
  #10  
Old 1/22/08, 1:37 AM
Marc D. Shunk's Avatar
Marc D. Shunk Marc D. Shunk is offline
Active Poster
 
Join Date: Dec 2006
Location: Central PA
Posts: 1,967
Please Note: Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Need clarification

Quote:
Originally Posted by cbottger
Congradulations guys this is the way a message board is suppp0se to work ask a question get an answer.
Sorry, I won't let it happen again.

Not every question has quite as straightforward of an answer as this one did.
Reply With Quote
  #11  
Old 1/22/08, 1:47 AM
Greg Fretwell Greg Fretwell is offline
Active Poster
 
Join Date: Jul 2004
Location: Estero Florida
Posts: 1,798
Please Note: Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Need clarification

Quote:
Originally Posted by jweinberg
Same on the vapor barrier of attic insulation. I constantly see it installed upside down.
Define "upside down" It is not the same in places where AC is your biggest season as it is where heating is the biggest season.

If you have the AC on more than the heat you probably want the vapor barrier on the top where the warm moist air usually is.
Reply With Quote
  #12  
Old 1/22/08, 1:51 AM
relliott's Avatar
relliott relliott is offline
Active Poster
 
Join Date: Aug 2006
Location: HARWOOD HTS, il
Posts: 8,570
Please Note: relliott is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Need clarification

I agree Marc as you do provide straight answers.
Reply With Quote
  #13  
Old 1/22/08, 9:56 AM
jweinberg's Avatar
jweinberg jweinberg is offline
InterNACHI Member
 
Join Date: Feb 2005
Location: San Jose, CA
Posts: 420
Please Note: jweinberg is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Need clarification

Quote:
Originally Posted by Greg Fretwell
Define "upside down" It is not the same in places where AC is your biggest season as it is where heating is the biggest season.

If you have the AC on more than the heat you probably want the vapor barrier on the top where the warm moist air usually is.
Upside down....as in the flammable vapor barrier exposed to the attic space.

Pretty dry in San Jose California. Definately more furnace days than Air Cond days. Need A/C about 5-10 days per year. Furnace for 60-90 days/year.
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Clarification of NACHI Conference in Toronto rwand1 Canadian Inspectors 2 7/17/07 11:31 AM
Need a little clarification rslocum Electrical 4 4/5/07 9:35 AM
Clarification on Safety Glass jweinberg General Inspection Discussion 4 12/25/06 2:35 AM
need clarification on "laundry circuit" for new const. bking Electrical 9 5/8/06 6:28 PM


All times are GMT -4. The time now is 2:09 PM.


Copyright © International Association of Certified Home Inspectors, Inc. 1 2 3 4 5 6 7 8 9 10 11 12 13 14 15 16 17 18 19 20 21 22 23 24 25 26 27 28 29 30 31 32 33 34 35 36 37 38 39 40 41 42 43 44 45 46 47 48 49 50 51 52 53 54 55 56 57 58 59 60 61 62 63 64 65 66 67 68 69 70 71 72 73 74 75 76 77 78 79 80 81 82 83 84 85 86 87 88 89 90 91 92 93 94 95 96 97 98 99 100 101 102 103 104 105 106 107 108 109 110 111 112 113 114 115 116 117 118 119 120 121 122 123 124 125 126 127 128 129 130 131 132 133 134 135 136 137 138 139 140 141 142 143 144 145 146 147

Popular Sections

:

All Sections

Popular

Membership

Inspection Standards

Education

Chapters & Members

Articles & Links

Other Organizations

 

 

 

NACHI.ORG Statistics

 

 

no new posts