Unhappy Need Code reference

I have been put on the spot to provide a code reference. 3ft clear for incoming service with 4:12 slope. Does anyone have the NEC ref. and year implimented?
Attached Thumbnails
need-code-reference-mvc-024s.jpg  
Reply With Quote
  #2  
Old 4/19/08, 6:54 PM
Bruce M. Graham, III's Avatar
Bruce M. Graham, III Bruce M. Graham, III is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Gainesville, FL
Posts: 1,605
Default Re: Need Code reference

That mast should be 18" off the roof deck. Don't have code handy, but then again I don't do code inspections. Have you asked the electricain to put on his letter head with his cert # and sign it that this is OK? I have yet to see one of these letters when I ask for them.
my bad it would be 36" 3504.2.1ex2



Bungalows to Mansions
Professional Inspection Services, LLC dba
1st Inspection Services
Bruce M. Graham III
Gainesville, FL 32608
352 871 8989
NACHI05091592
ICC 5268478
www.1stinspectionsfl.com
www.bungalowstomansions.com

Last edited by bgraham; 4/19/08 at 7:02 PM..
Reply With Quote
  #3  
Old 4/19/08, 6:55 PM
Michael Larson's Avatar
Michael Larson Michael Larson is offline
InterNACHI Member
 
Join Date: May 2006
Location: Hudson, WI including the Twin Cities of MN
Posts: 18,489
Default Re: Need Code reference

230.24 Clearances
Service-drop conductors must be located so that they are not readily accessible, and they must comply with the following clearance requirements:
(A) Above Roofs. Overhead service conductors must maintain a minimum clearance of 8 ft above the surface of a roof for a minimum distance of 3 ft in all directions from the edge of the roof.

Exception No. 2: Where the voltage does not exceed 300V between conductors, overhead conductor clearances from the roof can be reduced from 8 ft to 3 ft, if the slope of the roof exceeds 4 in. in 12 in.

Exception No. 3: If the voltage between conductors does not exceed 300V, the conductor clearance over the roof overhang can be reduced from 8 ft to 1.5 ft, if no more than 6 ft of overhead conductors pass over no more than 4 ft of roof overhang, and the conductors terminate at a through-the-roof raceway or approved support. Figure 230-10 230-24Ax3.cdr

Exception No. 4: The 3 ft vertical clearance that extends from the roof does not apply when the point of attachment is on the side of the building below the roof.



"Never underestimate the difficulty of changing false beliefs by facts."
Henry Rosovsky-Harvard

Michael Larson
Hudson, WI

Services provided in East MN and West WI
InspectraPro
or
Minnesota Home Inspector

Reply With Quote
  #4  
Old 4/19/08, 6:56 PM
Brian E. Kelly Brian E. Kelly is offline
InterNACHI Member
 
Join Date: Oct 2004
Location: Phoenix, AZ
Posts: 11,730
Default Re: Need Code reference

http://codecheck.com/images/CC5thEdSample.pdf



"Never ever threaten anyone in Camoflage"
Tim Wilson

"Not everyone follows the same path"
Governor Sanford, musings on the Appalachian Trail
Reply With Quote
  #5  
Old 4/19/08, 7:03 PM
Kevin Luce's Avatar
Kevin Luce Kevin Luce is offline
Active Poster
 
Join Date: Apr 2005
Location: Highland, Indiana
Posts: 190
Please Note: Kevin Luce is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Need Code reference

WHAT?

I wouldn't recommend even going in that direction. You called it out and now the sellers can get an electrician out there to confirm and correct this installation. It doesn't even meet the 18 inch clearance from the drip loop.

Since he thinks he knows what he is talking about, ask him exactly where he is getting his information from.

I know your are looking from when it was included (I don't have that information)but E3504.2.1 is where you can find it in the IRC book also.

Last edited by Kevin Luce; 4/19/08 at 7:07 PM..
Reply With Quote
  #6  
Old 4/19/08, 7:05 PM
Marc D. Shunk's Avatar
Marc D. Shunk Marc D. Shunk is offline
Active Poster
 
Join Date: Dec 2006
Location: Central PA
Posts: 1,967
Please Note: Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Need Code reference

That's also what appears to be a PVC weatherhead installed on RMC or IMC in a nonconforming manner.
Reply With Quote
  #7  
Old 4/19/08, 7:08 PM
Michael Larson's Avatar
Michael Larson Michael Larson is offline
InterNACHI Member
 
Join Date: May 2006
Location: Hudson, WI including the Twin Cities of MN
Posts: 18,489
Default Re: Need Code reference

Kevin's got it right I don't quote code but I like knowing where the requirements come from.

I guess it depends on who is challenging you.
Let the electrician take the liability.
You called it out as a concern/safety issue in your opinion.



"Never underestimate the difficulty of changing false beliefs by facts."
Henry Rosovsky-Harvard

Michael Larson
Hudson, WI

Services provided in East MN and West WI
InspectraPro
or
Minnesota Home Inspector

Reply With Quote
  #8  
Old 4/19/08, 7:09 PM
David P. Valley's Avatar
David P. Valley David P. Valley is offline
InterNACHI Member
 
Join Date: Jun 2003
Location: METHUEN, MA
Posts: 8,020
Default Re: Need Code reference

"CLICK to ENLARGE"
need-code-reference-se-clearances3.jpg
Reply With Quote
  #9  
Old 4/19/08, 7:11 PM
Kevin Luce's Avatar
Kevin Luce Kevin Luce is offline
Active Poster
 
Join Date: Apr 2005
Location: Highland, Indiana
Posts: 190
Please Note: Kevin Luce is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Need Code reference

Quote:
Originally Posted by kgerhauser
I have been put on the spot to provide a code reference. 3ft clear for incoming service with 4:12 slope. Does anyone have the NEC ref. and year implimented?
It looks newer, when do you think it was installed?
Reply With Quote
  #10  
Old 4/19/08, 7:15 PM
Karl E. Gerhauser's Avatar
Karl E. Gerhauser Karl E. Gerhauser is offline
InterNACHI Member
 
Join Date: Oct 2006
Location: Coos Bay, OR
Posts: 433
Default Re: Need Code reference

I am being called out by the listing agent who said I am maufacturing defects and have cause $500 damage to another home (blatent lie). He is denying my recomendation of further evaluation by an electrician. 1953 abortion remodel by the all structures licenced contractor who is the homeowner. I need the reference just to get it evaluated. Here is the rest of the service conduit and some other photos you will love. oops pushed wrong button.
Reply With Quote
  #11  
Old 4/19/08, 7:21 PM
Karl E. Gerhauser's Avatar
Karl E. Gerhauser Karl E. Gerhauser is offline
InterNACHI Member
 
Join Date: Oct 2006
Location: Coos Bay, OR
Posts: 433
Default Re: Need Code reference

Its raining, having sattelite problems. More to come.
Attached Thumbnails
need-code-reference-mvc-022s.jpg   need-code-reference-mvc-023s.jpg  
Reply With Quote
  #12  
Old 4/19/08, 7:22 PM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Harrisonburg, VA
Posts: 7,539
Send a message via AIM to pabernathy Send a message via MSN to pabernathy
Default Re: Need Code reference

Honestly Karl....I would simply state what you see, give your recommendations and CASH you check and move on......You simply can't comply with ignorance and you most certainly cant FIX stupid.



Paul W. Abernathy,CMI,CEI,CEPE
NECŪ Consultant/Columnist
www.twitter.com/ElectricalGuru

- ICC & IAEI Certified Electrical Inspector
- ICC & IAEI Certified Electrical Plans Examiner
- Look for my article in the Nov/Dec 2009 IAEI Magazine
- 2007 "Top Gun" Winner - Mike Holt Enterprises
" visit www.TheElectricalGuru.com Today !"

Reply With Quote
  #13  
Old 4/19/08, 7:27 PM
Karl E. Gerhauser's Avatar
Karl E. Gerhauser Karl E. Gerhauser is offline
InterNACHI Member
 
Join Date: Oct 2006
Location: Coos Bay, OR
Posts: 433
Default Re: Need Code reference

heres more
Attached Thumbnails
need-code-reference-mvc-001s.jpg   need-code-reference-mvc-017s.jpg   need-code-reference-mvc-016s.jpg   need-code-reference-mvc-018s.jpg   need-code-reference-mvc-020s.jpg  

Reply With Quote
  #14  
Old 4/19/08, 7:30 PM
Karl E. Gerhauser's Avatar
Karl E. Gerhauser Karl E. Gerhauser is offline
InterNACHI Member
 
Join Date: Oct 2006
Location: Coos Bay, OR
Posts: 433
Default Re: Need Code reference

Paul, how does that fix their refusal to allow furter evaluation nd the threats to sue me for manufactring defects? I don't know what happened the system won't let me upload any more pics.
Reply With Quote
  #15  
Old 4/19/08, 7:32 PM
Michael Larson's Avatar
Michael Larson Michael Larson is offline
InterNACHI Member
 
Join Date: May 2006
Location: Hudson, WI including the Twin Cities of MN
Posts: 18,489
Default Re: Need Code reference

Karl,

The service drop and weatherhead are the least of this homes problems.

Run away, run away.


P.S. I think it's limited to 5 pics per post.



"Never underestimate the difficulty of changing false beliefs by facts."
Henry Rosovsky-Harvard

Michael Larson
Hudson, WI

Services provided in East MN and West WI
InspectraPro
or
Minnesota Home Inspector

Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Garage/house fire door Steven C. Meyer General Inspection Discussion 15 2/5/08 8:06 AM
No "H" clips? jbreazeale Structural 7 5/17/07 3:28 PM


All times are GMT -4. The time now is 1:01 AM.


Copyright © International Association of Certified Home Inspectors, Inc. 1 2 3 4 5 6 7 8 9 10 11 12 13 14 15 16 17 18 19 20 21 22 23 24 25 26 27 28 29 30 31 32 33 34 35 36 37 38 39 40 41 42 43 44 45 46 47 48 49 50 51 52 53 54 55 56 57 58 59 60 61 62 63 64 65 66 67 68 69 70 71 72 73 74 75 76 77 78 79 80 81 82 83 84 85 86 87 88 89 90 91 92 93 94 95 96 97 98 99 100 101 102 103 104 105 106 107 108 109 110 111 112 113 114 115 116 117 118 119 120 121 122 123 124 125 126 127 128 129 130 131 132 133 134 135 136 137 138 139 140 141 142 143 144 145 146 147

Popular Sections

:

All Sections

Popular

Membership

Inspection Standards

Education

Chapters & Members

Articles & Links

Other Organizations

 

 

 

NACHI.ORG Statistics

 

 

no new posts