Little confused with coencentric knockouts and when your required to use a bonding bushing or grounding wedge. The service panel in this picture has non metallic conduit between panel and meter. The panel has concentric rings at the line side of the panel. Correct me if im wrong but since non metallic raceway was provided you dont have to use a bonding or grounding wedge, Correct? Any one have any good reference on this?

Thanks in advance
James
Attached Thumbnails
need-help-concentric-rings-and-bonding-nachi-2.jpg   need-help-concentric-rings-and-bonding-nachi-1.jpg  
Reply With Quote
  #2  
Old 6/6/07, 7:26 PM
jlybolt jlybolt is offline
Active Poster
 
Join Date: Feb 2005
Location: Conroe, TX
Posts: 305
Please Note: jlybolt is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Need help with Concentric rings and bonding

Non metallic raceway used between meter and service panel because the meter was grounded?
Reply With Quote
  #3  
Old 6/6/07, 8:41 PM
Speedy Petey Speedy Petey is offline
Active Poster
 
Join Date: Jul 2006
Posts: 1,294
Please Note: Speedy Petey is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Need help with Concentric rings and bonding

Quote:
Originally Posted by jlybolt
Non metallic raceway used between meter and service panel because the meter was grounded?
I have no ides what this means. Can you re-word the question?

Yes, since the raceway between the enclosures is NM there is no concentric KO issues. The raceway has nothing to do with grounding/bonding so the KO's are of no consequence.

In my area meter pans do NOT get "grounded" by anything but the service neutral. We used to have to hit the meter pan with a GEC but this was dropped years ago. Now all GECs go to the main panel/disconnect.
Reply With Quote
  #4  
Old 6/6/07, 8:47 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 5,033
Default Re: Need help with Concentric rings and bonding

Quote:
Originally Posted by jlybolt
Correct me if im wrong but since non metallic raceway was provided you dont have to use a bonding or grounding wedge, Correct? Any one have any good reference on this?
You cannot "bond" non-metallic parts, so there will be no reference to support this.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net
Reply With Quote
  #5  
Old 6/6/07, 8:51 PM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Harrisonburg, VA
Posts: 7,539
Send a message via AIM to pabernathy Send a message via MSN to pabernathy
Default Re: Need help with Concentric rings and bonding

James,

In this picture the connection between panels is PVC, the "Grounded" conductor would apply the connections required in this setup.

When assured bonding is required for example on Ess. and Cons. KO's it would be required to use the methods you have stated....either a bonding wedge or ring for example.....in other cases a bonding busing is used.

Here....this might help explain it better

(B) Method of Bonding at the Service.
Electrical continuity
at service equipment, service raceways, and service
conductor enclosures shall be ensured by one of the following
methods:

(1) Bonding equipment to the grounded service conductor
in a manner provided in 250.8
(2) Connections utilizing threaded couplings or threaded
bosses on enclosures where made up wrenchtight
(3) Threadless couplings and connectors where made up
tight for metal raceways and metal-clad cables
(4) Other approved devices, such as bonding-type locknuts
and bushings

Bonding jumpers meeting the other requirements of this
article shall be used around concentric or eccentric knockouts
that are punched or otherwise formed so as to impair
the electrical connection to ground. Standard locknuts or
bushings shall not be the sole means for the bonding required
by this section.


But without going into too much detail in the example you show here the panel to the left is backfed, it should have it's own support ( unless it is bolted type and I dont think it is ) holding it on......in addition to it's current support methods.

I am curious however...how come they did not simply terminate on the MLO terminals.......it is clear that if this is a service it is under the 6 throw allowance......

anyway....hope it's helpful



Paul W. Abernathy,CMI,CEI,CEPE
NECŪ Consultant/Columnist
www.twitter.com/ElectricalGuru

- ICC & IAEI Certified Electrical Inspector
- ICC & IAEI Certified Electrical Plans Examiner
- Look for my article in the Nov/Dec 2009 IAEI Magazine
- 2007 "Top Gun" Winner - Mike Holt Enterprises
" visit www.TheElectricalGuru.com Today !"

Reply With Quote
  #6  
Old 6/6/07, 9:55 PM
jlybolt jlybolt is offline
Active Poster
 
Join Date: Feb 2005
Location: Conroe, TX
Posts: 305
Please Note: jlybolt is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Need help with Concentric rings and bonding

Sorry Paul, Im not following?

Sorry Petey, I worded my question poorly.
Reply With Quote
  #7  
Old 6/6/07, 10:02 PM
Greg Fretwell Greg Fretwell is offline
Active Poster
 
Join Date: Jul 2004
Location: Estero Florida
Posts: 1,798
Please Note: Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Need help with Concentric rings and bonding

The neutral is usually bonded in the meter base, I assume that is what Ian is talking about. Depending on how your AHJ feels about parallel paths and how they read 250.142(A)(1) they may not want to see a parallel path from the meter can to the service disconnect can.
Some say it is no sweat but there are still some crusty old guys who say "parallel neutral" and don't want to see any path but the white wire. (plastic raceways or SE cable).
I tend to agree with those who say on the line side of the service disconnect/MBJ there is no problem with those parallel paths particularly if it is a massive total path. (like industrial switchgear with multiple 4" RMC risers, all using bonding bushings and jumpers the size of your finger)
Reply With Quote
  #8  
Old 6/6/07, 10:38 PM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Harrisonburg, VA
Posts: 7,539
Send a message via AIM to pabernathy Send a message via MSN to pabernathy
Default Re: Need help with Concentric rings and bonding

lol...I lost you did I James...lol...

Ok...Basically I don't see a requirement for a Bonding Wedge or Ring in your photo since the connection between the meter enclosure and the service panel is non-metalic in nature ( ie: PVC ).....using PVC like they did on this image is saving the issues Greg is refering to.....

The " Grounded " conductor is serving it's proper function in this example you have posted.

The example I was saying about the KO's was to explain that if assured bonding is required lets say at the service equipment as the NEC speaks about in 250.92(B)(4)

Note that method (4) in 250.92(B) requires other similar devices, such as listed bonding-type locknuts or bushings. Standard locknuts or sealing locknuts are not acceptable as the ``sole means'' for bonding on the line side of service equipment.
Grounding and bonding bushings for use with rigid or intermediate metal conduit are provided with means (usually one or more set screws that make positive contact with the conduit) for reliably bonding the bushing and the conduit on which it is threaded to the metal equipment enclosure or box.

Grounding bushings used with rigid or intermediate metal conduit or with tubing (EMT) fittings, such as those shown in Exhibits 250.35 and 250.36, have provisions for connecting a bonding jumper or have means provided by the manufacturer for use in mounting a wire connector. This type of bushing may also have means (usually one or more set screws) to reliably bond the bushing to the conduit.



Paul W. Abernathy,CMI,CEI,CEPE
NECŪ Consultant/Columnist
www.twitter.com/ElectricalGuru

- ICC & IAEI Certified Electrical Inspector
- ICC & IAEI Certified Electrical Plans Examiner
- Look for my article in the Nov/Dec 2009 IAEI Magazine
- 2007 "Top Gun" Winner - Mike Holt Enterprises
" visit www.TheElectricalGuru.com Today !"

Reply With Quote
  #9  
Old 6/6/07, 10:39 PM
jlybolt jlybolt is offline
Active Poster
 
Join Date: Feb 2005
Location: Conroe, TX
Posts: 305
Please Note: jlybolt is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Need help with Concentric rings and bonding

Light bulb just came on, its dim but does come on some time Paul. I see what you mean about back fed. No Idea why they would do that. Seams like more work to me.
Reply With Quote
  #10  
Old 6/6/07, 10:40 PM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Harrisonburg, VA
Posts: 7,539
Send a message via AIM to pabernathy Send a message via MSN to pabernathy
Default Re: Need help with Concentric rings and bonding

yeah..sorry......I kinda jumped onto another topic on ya......but it's all good because it is helping you learn and thats the only goal here.



Paul W. Abernathy,CMI,CEI,CEPE
NECŪ Consultant/Columnist
www.twitter.com/ElectricalGuru

- ICC & IAEI Certified Electrical Inspector
- ICC & IAEI Certified Electrical Plans Examiner
- Look for my article in the Nov/Dec 2009 IAEI Magazine
- 2007 "Top Gun" Winner - Mike Holt Enterprises
" visit www.TheElectricalGuru.com Today !"

Reply With Quote
  #11  
Old 6/6/07, 10:49 PM
jlybolt jlybolt is offline
Active Poster
 
Join Date: Feb 2005
Location: Conroe, TX
Posts: 305
Please Note: jlybolt is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Need help with Concentric rings and bonding

But without going into too much detail in the example you show here the panel to the left is backfed, it should have it's own support ( unless it is bolted type and I dont think it is ) holding it on......in addition to it's current support methods.

Paul was this meant with the set up that I show? What do you mean by holding it on.
Reply With Quote
  #12  
Old 6/6/07, 10:51 PM
jlybolt jlybolt is offline
Active Poster
 
Join Date: Feb 2005
Location: Conroe, TX
Posts: 305
Please Note: jlybolt is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Need help with Concentric rings and bonding

Man the more I learn about electrical the more I realize I dont know anything. Make it stop.
Reply With Quote
  #13  
Old 6/6/07, 11:04 PM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Harrisonburg, VA
Posts: 7,539
Send a message via AIM to pabernathy Send a message via MSN to pabernathy
Default Re: Need help with Concentric rings and bonding

lol...meaning it needs to be held on when backfed by something other than just clicking it in.....in other words if it is backfed it must meet this code requirement.

(F) Back-Fed Devices.
Plug-in-type overcurrent protection
devices or plug-in type-main lug assemblies that are
backfed and used to terminate
field-installed ungrounded
supply conductors shall be secured in place by an additional
fastener that requires other than a pull to release the
device from the mounting means on the panel.




Paul W. Abernathy,CMI,CEI,CEPE
NECŪ Consultant/Columnist
www.twitter.com/ElectricalGuru

- ICC & IAEI Certified Electrical Inspector
- ICC & IAEI Certified Electrical Plans Examiner
- Look for my article in the Nov/Dec 2009 IAEI Magazine
- 2007 "Top Gun" Winner - Mike Holt Enterprises
" visit www.TheElectricalGuru.com Today !"

Reply With Quote
  #14  
Old 6/7/07, 12:36 AM
jlybolt jlybolt is offline
Active Poster
 
Join Date: Feb 2005
Location: Conroe, TX
Posts: 305
Please Note: jlybolt is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Need help with Concentric rings and bonding

Paul, there is a white, possibly clip on that 125 amp breaker. It appears to be bolted to the enclosure and looks like it lays over the top of the breaker.
Reply With Quote
  #15  
Old 6/7/07, 7:47 AM
Speedy Petey Speedy Petey is offline
Active Poster
 
Join Date: Jul 2006
Posts: 1,294
Please Note: Speedy Petey is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Need help with Concentric rings and bonding

That white clip is the breaker retention device.
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On



All times are GMT -4. The time now is 12:33 AM.


Copyright © International Association of Certified Home Inspectors, Inc. 1 2 3 4 5 6 7 8 9 10 11 12 13 14 15 16 17 18 19 20 21 22 23 24 25 26 27 28 29 30 31 32 33 34 35 36 37 38 39 40 41 42 43 44 45 46 47 48 49 50 51 52 53 54 55 56 57 58 59 60 61 62 63 64 65 66 67 68 69 70 71 72 73 74 75 76 77 78 79 80 81 82 83 84 85 86 87 88 89 90 91 92 93 94 95 96 97 98 99 100 101 102 103 104 105 106 107 108 109 110 111 112 113 114 115 116 117 118 119 120 121 122 123 124 125 126 127 128 129 130 131 132 133 134 135 136 137 138 139 140 141 142 143 144 145 146 147

Popular Sections

:

All Sections

Popular

Membership

Inspection Standards

Education

Chapters & Members

Articles & Links

Other Organizations

 

 

 

NACHI.ORG Statistics

 

 

no new posts