still do not know why they went through all that trouble.....in regards to backfed of the breaker to begin with...but alas what is done is done. Paul W. Abernathy |
|
#17
|
||||
|
||||
|
Anyone want to comment on the ground bar with nothing on it, the grounds on the isolated neutral, and the neutral bar isolated(no green/bonding screw)?
Seems like the serious issue here(or I'm looking at the photo wrong). |
|
#18
|
|||
|
|||
|
Quote:
I think I see a "Z" bar strap in the back of this panel shown which is doing the bonding at the main service equipment, This is the first disconnection location and the "Grounded" and " Ground " terminations should share the same buss bar.......it is the panel INSIDE I worry about....because that one we can't see... Paul W. Abernathy |
|
#19
|
|||
|
|||
|
Now dont get me wrong thomas...maybe I am looking at the wrong picture or have not had ALL my coffee this morning...entirly possible...as I am going for my 3rd cup right now....( working on pricing a plan so I am bored )
Paul W. Abernathy |
|
#20
|
|||
|
|||
|
Please Note:
jlybolt is a non-member guest and is in no way affiliated with InterNACHI or its members.
Paul , your are correct. The panel shown is the service equipment panel not the distributiion panel. The distribution appeared to wired properly.
|
![]() |