My friend is currently upgrading his 100 Amp fuse box in our small house to a breaker box. There is, I believe, #4 copper or #2 Aluminum service from a 100 amp meter setting with a max 240 V meter. What is the highest amp breaker box he can go with? He needs 20 Spaces. Is an undersized service the hazard or oversized, or both? Any help on these questions would be wonderful.
|
|
#2
|
||||
|
||||
|
With the info from your post it is an undersized service that poses a hazard. The #4 copper would be too small for a 100 amp service. It should be at least a #3 copper. If it was a #2 aluminum, that would be ok for a 100 amp service. The panel itself is usually rated for 125 amps, but comes in many different sizes. They can hold 12, 16, 24, 32, 48, all the way up to 64 breakers depending on the brand you purchase. If the meter is only rated for 100 amps, that appears to be the smallest link in the chain, which would determine the maximum size of disconnect breaker it would allow. BUT...make sure its not a #4 copper supply as that would only be enough for a 70 amp system. It's always determined by the smallest rated link in the system, and does'nt matter if other components are rated higher than that.
I'm not the electrical wizard by any means, but this is how I understand it. I'm sure if I'm incorrect one of the specialized fellows will correct us. Darrell Hadler CMI Five Star Home Inspections Medicine Hat, AB. Canada NACHI# 04111082 Cell phone# (403)502-3593 Inspected once . . . inspected right! (website) http://inspectorpages.com/dhadler
|
|
#3
|
|||
|
|||
|
Please Note:
Speedy Petey is a non-member guest and is in no way affiliated with InterNACHI or its members.
Darrell, the info you provided may be correct for Canada, but the OP is in the US so not all of it is accurate.
#4cu (or #2al) is standard issue for a 100 amp service in the US. ALso, our panels are limimited to 42 circuits/spaces. Ryna, the largest panel you could install would be a 32 space Square D QO series. I don't know of anyone else who makes a 32 space or larger. Typical would be a 20 space, or 20/24, or 24 space. Depending on what is available in your area. |
|
#4
|
||||
|
||||
|
Petey,
Thanks for reminding us that CAN and US codes are similar but sometimes different in important areas for US inspectors. A Green box for you my friend. |
|
#5
|
||||
|
||||
|
Thank you for the information!! I will send this link to him!
So, Can he put a 125 amp breaker on the #2 al wire coming?? Thanks everyone. I love this NACHI family! |
|
#6
|
||||
|
||||
|
Quote:
Paul W. Abernathy,CMI,CPI,CME National Electrical Code Expert Electrical & Fire Protection Systems Code Supervisor- Alexandria,VA Weekly Live Radio Show :http://en.1000mikes.com/show/the_electrical_guru Weekly Chat on Wednesdays -7:30 PM E.S.T * Get my 13 hour commentary audio CD for the book "How to Perform Electrical Inspections" 2007 InterNACHI Member of the Year |
|
#7
|
|||
|
|||
|
Please Note:
Speedy Petey is a non-member guest and is in no way affiliated with InterNACHI or its members.
What Paul said.
The panel may very well be rated at 125 amps, but the main breaker must be 100 (or less). |
![]() |
| Thread Tools | |
|
|
Similar Threads
|
||||
| Thread | Thread Starter | Forum | Replies | Last Post |
| Download the videos here all about physics and electricity | jtedesco1 | Electrical Inspections | 5 | 9/14/08 4:58 PM |
| DOE Handbook Electrical Safety | pabernathy | Electrical Inspections | 2 | 1/1/07 6:33 PM |
| Handbook for Electrical Safety | pabernathy | Electrical Inspections | 1 | 1/1/07 2:14 PM |
| POLL- Paul Stay In The Electrical Forum | pabernathy | Miscellaneous Discussion for Inspectors | 40 | 12/19/06 12:05 PM |