Default Need help with lightning rods

Inspected a nice old victorian 3 story today. When I got on the 1-5 year old roof, I saw the lightning rods had been nicely cleaned up, but there was no grounding straps, cables, conductors, nothing. My question is: Would the owners be better off re grounding them, or would they be ok to just be a decorative bauble? I haven't seen that many lightning rod systems except in the country, and they have all been intact, all the way to an electrode in the ground. My gut feeling is that if the rods are up there, there should be a properly installed, complete system. Anyone know of any specs or references? Any first hand advise? Thanks in advance.
Stu
Reply With Quote
  #2  
Old 3/22/06, 11:37 PM
Jay Moge's Avatar
Jay Moge Jay Moge is offline
Active Poster
 
Join Date: Aug 2005
Location: Derry New Hampshire
Posts: 761
Please Note: Jay Moge is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Need help with lightning rods

i'm with you there. but i don't have a reverence either. if it's not grounded and is the highest point around, lightning hits it during a rain storm ( the rain giving it an electrical path to the earth.) are they helping or hurting?
Reply With Quote
  #3  
Old 3/22/06, 11:59 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 7,760
Default Re: Need help with lightning rods



This may help. . .


250.60 Use of Air Terminals. (Lightning Rods)

Air terminal conductors and driven pipes, rods, or plate electrodes used for grounding air terminals shall not be used in lieu of the grounding electrodes required by 250.50 for grounding wiring systems and equipment. This provision shall not prohibit the required bonding together of grounding electrodes of different systems.

FPN No. 1: See 250.106 for spacing from air terminals.
See 800.40(D), 810.21(J), and 820.40(D) for bonding of electrodes.

800.40(D) Bonding of Electrodes.

A bonding jumper not smaller than 6 AWG copper or equivalent shall be connected between the communications grounding electrode and power grounding electrode system at the building or structure served where separate electrodes are used. Bonding together of all separate electrodes shall be permitted.

















IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net



Last edited by jpope; 3/23/06 at 12:03 AM..
Reply With Quote
  #4  
Old 3/23/06, 12:17 AM
sspradling sspradling is offline
Active Poster
 
Join Date: Jan 2004
Location: Columbia, MO
Posts: 227
Please Note: sspradling is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Need help with lightning rods

Jeff, thanks for the reference, I didn't know the code name was air terminals. Do you think an incomplete system for these things is cause for calling it out? Who do I defer this to, an electrician? I'd really like to get it right the first time. Again thanks for any help.
Stu
Reply With Quote
  #5  
Old 3/23/06, 12:26 AM
gbeaumont's Avatar
gbeaumont gbeaumont is offline
InterNACHI Member
 
Join Date: Jan 2003
Location: Clearwater, FL
Posts: 6,261
Send a message via AIM to gbeaumont Send a message via MSN to gbeaumont Send a message via Yahoo to gbeaumont
Default Re: Need help with lightning rods

Stuart,

When many of these older Victorians were built they were the tallest things around, and they commonly had Air terminals installed, these days you only tend to see them on Highrises, commercial structures and comunications towers.

Whenever I have seen them I have defered them to a licensed electrician. I would certainly recommend that you note in your report that the Lightening rods were not connected at the time of inspection. Should they be re-connected frankly I don't know

Regards

Gerry



"To realize our true destiny, we must be guided not by a myth from our past, but by a vision of our future."
(Mark B Adams)

Commercial property Inspection Tampa, Orlando, Sarasota, Jacksonville, Ft Launderdale, Miami, Florida.
NACHI cell 484-429-5466
NACHI02121106

Reply With Quote
  #6  
Old 3/23/06, 12:34 AM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 7,760
Default Re: Need help with lightning rods

Quote:
Originally Posted by gbeaumont
Whenever I have seen them I have defered them to a licensed electrician. I would certainly recommend that you note in your report that the Lightening rods were not connected at the time of inspection. Should they be re-connected frankly I don't know
What he said. . .

I don't think I've ever seen a lightning rod, other than at the golf course



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #7  
Old 3/23/06, 1:23 AM
sspradling sspradling is offline
Active Poster
 
Join Date: Jan 2004
Location: Columbia, MO
Posts: 227
Please Note: sspradling is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Need help with lightning rods

If I could figure out the new photo upload for my (previously not too large) images, I would be sharing. Maybe I'll figure it out some day..
Thanks for your help on this topic.
Stu
Reply With Quote
  #8  
Old 3/23/06, 3:04 AM
jtedesco1 jtedesco1 is offline
Account Suspended Due to Excessive Complaints
 
Join Date: Dec 2005
Posts: 1,891
Please Note: jtedesco1 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Need help with lightning rods

NFPA 780 Standard for the Installation of Lightning Protection Systems 2004 Edition
Chapter 1 Administration
Chapter 2 Referenced Publications
Chapter 3 Definitions
Chapter 4 Protection for Ordinary Structures
Chapter 5 Protection for Miscellaneous Structures and Special Occupancies
Chapter 6 Protection for Heavy-Duty Stacks
Chapter 7 Protection for Structures Containing Flammable Vapors, Flammable Gases, or Liquids That Can Give Off Flammable Vapors
Chapter 8 Protection for Watercraft
Annex A Explanatory Material
Annex B Principles of Lightning Protection
Annex C Explanation of Bonding Principles
Annex D Inspection and Maintenance of Lightning Protection Systems
Annex E Ground Measurement Techniques
Annex F Protection for Trees
Annex G Protection for Picnic Grounds, Playgrounds, Ball Parks, and Other Open Places
Annex H Protection for Livestock in Fields
Annex I Protection for Parked Aircraft
Annex J(Reserved)
Annex KProtection of Structures Housing Explosive Materials
Annex L Lightning Risk Assessment
Annex M Guide for Personal Safety from Lightning
Annex N Informational References
Formal Interpretation
Index
Reply With Quote
  #9  
Old 3/23/06, 12:40 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 7,760
Default Re: Need help with lightning rods

Well that certainly made it clear Joe

I know nothing about lightning rods (and may never have the need). Can you give some insight as to some of the basics?



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #10  
Old 3/23/06, 1:43 PM
jtedesco1 jtedesco1 is offline
Account Suspended Due to Excessive Complaints
 
Join Date: Dec 2005
Posts: 1,891
Please Note: jtedesco1 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Need help with lightning rods

http://www.nfpa.org/aboutthecodes/Ab...asp?DocNum=780

Preview this document.

I posted this for review: Display the Table of Contents of this document.

My intention was to identify the standard that may have some information to be used for a reference only. See Chapter 3.

NFPA allows a review of all of their codes and that's where this is found, see www.nfpa.org codes and standards.

Last edited by jtedesco1; 3/23/06 at 1:57 PM..
Reply With Quote
  #11  
Old 3/23/06, 8:51 PM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,047
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Need help with lightning rods


The grounding electrode for a lightning protection system cannot be used for the building or structure grounding electrode system as required by 250.50. Figure 250–110

Author’s Comments:
• Where a lightning protection system is installed, it must be bonded to the building or structure grounding electrode (earthing) system [250.106].
• A lightning protection system installed in accordance with NFPA 780, Standard for the Installation of Lightning Protection Systems, is intended to protect the building structure from lightning damage. It isn’t intended to protect the electrical wiring or equipment within the structure from lightning damage. To protect from high-voltage transients, proper transient voltage surge-protection devices must be installed in accordance with Articles 280 and 285.

• GROUNDING ELECTRODE CONDUCTOR. Grounding metal parts of the electrical installation to earth is intended to reduce voltage on the metal parts from lightning so as to prevent fires from surface arcing (side-flashes) within the building or structure [250.4(A)(2)]. In addition, high-voltage distribution systems (typically electric utility wiring) are grounded to the earth to help limit high voltage on system windings from lightning, unintentional contact with higher-voltage lines, or line surges [250.4(A)(1)].



Paul W. Abernathy,CMI,CPI,CME
National Electrical Code Expert
Electrical & Fire Protection Systems Code Supervisor- Alexandria,VA
Weekly Live Radio Show :http://en.1000mikes.com/show/the_electrical_guru
Weekly Chat on Wednesdays -7:30 PM E.S.T
* Get my 13 hour commentary audio CD for the book "How to Perform Electrical Inspections"

2007 InterNACHI Member of the Year
Reply With Quote
  #12  
Old 3/23/06, 8:55 PM
bkelly1's Avatar
bkelly1 bkelly1 is offline
Active Poster
 
Join Date: Jan 2004
Location: Rives, TN
Posts: 1,738
Please Note: bkelly1 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Need help with lightning rods

In laymens terms. lol ... it should be bonded to something or lighting will find its own path. Ground or remove, that is my opionon. Have installed a dozen of these and they have to be grounded. We installed them on the many water and waste water plants I have wired, as well as all steeples on the churches I did. Back in the day.
Reply With Quote
  #13  
Old 3/23/06, 8:55 PM
rwand1 rwand1 is offline
Active Poster
 
Join Date: Sep 2005
Location: Caledon, ON
Posts: 7,861
Please Note: rwand1 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Need help with lightning rods

They are not functional. No ground does it still draw lightening?
I think lightening does not always hit the hightest point, it may go for transformer/pole, tree, ground.

Are you suppose to ground metal roofs?
Reply With Quote
  #14  
Old 3/23/06, 8:57 PM
bkelly1's Avatar
bkelly1 bkelly1 is offline
Active Poster
 
Join Date: Jan 2004
Location: Rives, TN
Posts: 1,738
Please Note: bkelly1 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Need help with lightning rods

That is just my thoughts. There are companys now that are making plastic rods for this reason. My sister looked into them while building her house. The state inspector sais if they were copper, they would be grouded. Period. But maybe that is just him ?
Reply With Quote
  #15  
Old 3/23/06, 8:58 PM
bkelly1's Avatar
bkelly1 bkelly1 is offline
Active Poster
 
Join Date: Jan 2004
Location: Rives, TN
Posts: 1,738
Please Note: bkelly1 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Need help with lightning rods

http://www.furse.com/elp/howtolp.htm
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
lightning rod question wsiegel Ancillary Inspection Services & Additional Topics 4 11/21/07 11:47 PM
2/12/2007- QOD - Electrical pabernathy Inspection Question of the Day 62 2/20/07 3:41 PM
Lightning Protection Systems- Do You Check It? pabernathy Electrical Inspections 20 12/29/06 10:38 PM
Electrical Inspection Training for Home Inspectors jtedesco1 Inspection Education & Training 6 4/27/06 11:43 PM


All times are GMT -4. The time now is 11:54 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts