Quote:
Originally Posted by Mike Whitt
If the panel that Joe posted was the service equipment the generalist could land three neutrals on the ground bar under one screw in the year that Joe's panel was installed and do it in compliance of the NEC.
Compliant with the NEC does not mean compliant with the manufacturer's instructions (as depicted by te panel label) The most stringent requirement is what should be followed is it not?



A2Z Inspection Services
Chris Duphily
RR 1 Box 1107
Dingmans Ferry, PA 18328
Office: 570-371-6696
NACHI06092689
Proudly serving: Stroudsburg PA,Dingmans Ferry PA, Scranton PA and all of: Monroe,Pike,Wayne,lackawanna counties
http://www.a2zpa.com
http://www.a2zpainspections.com
President - Pocono-Northeast PA Chapter of interNACHI
Reply With Quote
  #62  
Old 1/6/08, 2:38 PM
Chris D. Duphily's Avatar
Chris D. Duphily Chris D. Duphily is offline
InterNACHI Member
 
Join Date: Sep 2006
Location: Dingmans Ferry, PA
Posts: 2,465
Default Re: Need help with main panel board buss bar

I couldn't help but notice the author in your quote at JLC

"danny Saradon" a quick google seach showed some interesting websites.



A2Z Inspection Services
Chris Duphily
RR 1 Box 1107
Dingmans Ferry, PA 18328
Office: 570-371-6696
NACHI06092689
Proudly serving: Stroudsburg PA,Dingmans Ferry PA, Scranton PA and all of: Monroe,Pike,Wayne,lackawanna counties
http://www.a2zpa.com
http://www.a2zpainspections.com
President - Pocono-Northeast PA Chapter of interNACHI

Last edited by cduphily; 1/6/08 at 6:01 PM..
Reply With Quote
  #63  
Old 1/6/08, 3:44 PM
Mike Whitt's Avatar
Mike Whitt Mike Whitt is offline
Unmoderated Guest
 
Join Date: Sep 2005
Location: North Carolina
Posts: 476
Please Note: Mike Whitt is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Need help with main panel board buss bar

Quote:
Originally Posted by cduphily
Compliant with the NEC does not mean compliant with the manufacturer's instructions (as depicted by te panel label) The most stringent requirement is what should be followed is it not?


If a piece of equipment is not installed according with the instructions supplied with the equipment then it is not code compliant, see 110.3(B)

The NEC is a minimum safety standard and any instructions that are more stringent will prevail.

What is being discussed is the label installed in the panel and the wording concerning the word neutral. Where I see that word in Joe’s picture I see the torque requirements not the number of conductors allowed under a screw.

What is not being seen by some is just what is in service equipment where the doubling of neutrals and the combination of equipment grounds and neutrals under one screw occurs.

Let’s take a moment and look at a service panel as we discuss what Joe’s label says.
Here is a Cutler Hammer panel that has the two terminal bars tied together with a bus that travels from one side to the other behind the breaker panel assembly. This bonds the two bars together making them one and the same.

This panel has the same information on the label as the panel that Joe posted the label of, so we can use Joe’s label in the rest of this discussion.



What I now need for someone to do is tell me where the ground terminal bar is located in this panel.
Remember that when you point out the ground terminal bar then the bar you just pointed out will accept up to three conductors up to size #10.
The label that Joe posted says that if neutrals are installed they have to be torque to the ft. lbs. outlined for the neutral wire.
Which one of these bars requires the grounded neutral conductor to be attached?

Either and both bars are ground terminal bars and either and both are bars that must be torque if it holds a neutral or before the adoption of the 2002 NEC up to three neutrals.
Reply With Quote
  #64  
Old 1/8/08, 6:55 PM
jtedesco1 jtedesco1 is offline
Account Suspended Due to Excessive Complaints
 
Join Date: Dec 2005
Posts: 1,908
Please Note: jtedesco1 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Need help with main panel board buss bar

Quote:
Originally Posted by pabernathy
Let us not forget however that Panelboards must be installed by the manufacturers intent via 110.3(B) and I have first hand knowledge from Eaton and other manufactures that they never listed their panels for the intent to doubled up a "grounded" conductor.

While the 2002 NEC bought the issue to light, it has always been a bad practice in my mind and I have never done it. The issue with UL 67 actually dates back to the 70's and so does the installation intent of the manufacturer to not allow any double tapping of a "grounded" conductor.

Just figured I would chime in....
Good! Sing along again!

How's the inspection business? Where are you inspecting?

Here's another picture about this issue:

Last edited by jtedesco1; 1/22/08 at 8:12 AM..
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
GFCI below the main panel dmacy Electrical 14 9/21/07 7:14 PM
Disconnect and Main panel srowe Electrical 10 6/13/06 8:49 PM
New Hampshire Real Estate Agents Are Upset! fcarrio General Inspection Discussion 8 2/11/06 2:35 PM
No Ashi / Nachi Conflict!! fcarrio Legislation, Licensing & Legal Issues 5 2/11/06 2:32 PM
Bad electrical problem Pest Guy Electrical 4 1/20/06 10:26 PM


All times are GMT -4. The time now is 3:42 AM.


Popular Sections

:

All Sections

Popular

Membership

Inspection Standards

Education

Chapters & Members

Articles & Links

Other Organizations

 

 

 

NACHI.ORG Statistics

 

 

no new posts