Inpected a home where they updated receptacles with newer ones that had a grounding hole, they were installed on circuits that had no ground provided. Question. what would you put on the report, and the buyer wanted to know why this was wrong and is it a safety thing to be conscerned about?
Reply With Quote
  #17  
Old 6/11/06, 5:59 PM
brepanshek brepanshek is offline
Active Poster
 
Join Date: May 2006
Location: York, PA
Posts: 235
Please Note: brepanshek is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Need help: New service-old wiring

Paul, your pics are great, I am working under someone right now and when we came to the panel, 1 of your pics had that no more than 1 grounding neutrual should be under 1 screw. I inspected this panel and it had double tapping and like 3 neutrals under 1 screw, was told this was normal practices and you see it all the time, need your prof. opinion. thanks
Reply With Quote
  #18  
Old 6/11/06, 6:29 PM
Michael Larson's Avatar
Michael Larson Michael Larson is offline
InterNACHI Member
 
Join Date: May 2006
Location: Hudson, WI including the Twin Cities of MN
Posts: 30,557
Default Re: Need help: New service-old wiring

Quote:
Originally Posted by brepanshek
Inpected a home where they updated receptacles with newer ones that had a grounding hole, they were installed on circuits that had no ground provided. Question. what would you put on the report, and the buyer wanted to know why this was wrong and is it a safety thing to be conscerned about?
Brian,

It definately is a "safety concern". The NEC requires that the ground of the receptacle be bonded to Earth. Ther are some exceptions listed below. Read carefully.

I would write it up as "Receptacles at locations____ are not grounded and represent a potential safety hazard. This should be refered to a qualified electrical contractor for further evaluation"

Receptacle Replacement [210-7(d)] Where Grounding Means Exist. Where a grounding means exists in the receptacle enclosure, grounding-type receptacles shall replace nongrounding type receptacles and the receptacles grounding terminals must be grounded in accordance with Section 210-7(c).
GFCI Protection Required. When receptacles are replaced in locations where ground-fault circuit-interrupter protection is now required, the replacement receptacles must be GFCI protected. This includes the replacement of receptacles in bathrooms, garages, outdoors, crawl spaces, unfinished basements, kitchens, wet bar sinks and rooftops, etc.; see Section 210-8 for GFCI requirements.
Where No Ground Exists. Where no grounding means exist in the box, such as old NM cable without a ground, nongrounding-type receptacles can be replaced with:
· A nongrounding type receptacle.
· A GFCI-receptacle or a grounding type receptacle fed downstream from a GFCI-receptacle. These receptacles shall be marked “No Equipment Ground”.
· A grounding-type receptacle protected with a GFCI circuit breaker. These receptacles shall be marked “GFCI Protected” and “No Equipment Ground”.
Note. The GFCI protection will function properly on a 2-wire circuit without an equipment grounding conductor. The equipment grounding conductor serves no purpose in the operation of the GFCI protection device and has



He who knows nothing is closer to the truth than he whose mind is filled with falsehoods and errors - Thomas Jefferson - Founding Father

The democracy will cease to exist when you take away from those who are willing to work and give to those who would not. Thomas Jefferson

Never underestimate the difficulty of changing false beliefs by facts.
- Henry Rosovsky-Harvard

Michael Larson
Hudson, WI

Services provided in East MN and West WI
InspectraPro
and
Minnesota Home Inspector

Reply With Quote
  #19  
Old 6/11/06, 9:03 PM
brepanshek brepanshek is offline
Active Poster
 
Join Date: May 2006
Location: York, PA
Posts: 235
Please Note: brepanshek is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Need help: New service-old wiring

Thanks Micheal, so the only safety hazard here is that they replaced with wrong type of receptacle correct? If they were just standard 2 prong then nothing has to be said about a ground right? don't want to alarm buyer?
Reply With Quote
  #20  
Old 6/11/06, 9:17 PM
Larry D. Kage Larry D. Kage is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Lake Ann (Traverse City), MI
Posts: 8,482
Default Re: Need help: New service-old wiring

Quote:
Originally Posted by brepanshek
Thanks Micheal, so the only safety hazard here is that they replaced with wrong type of receptacle correct? If they were just standard 2 prong then nothing has to be said about a ground right?
...but you may want to check for reverse polarity.
Reply With Quote
  #21  
Old 6/11/06, 9:28 PM
Michael Larson's Avatar
Michael Larson Michael Larson is offline
InterNACHI Member
 
Join Date: May 2006
Location: Hudson, WI including the Twin Cities of MN
Posts: 30,557
Default Re: Need help: New service-old wiring

Quote:
Originally Posted by brepanshek
Thanks Micheal, so the only safety hazard here is that they replaced with wrong type of receptacle correct? If they were just standard 2 prong then nothing has to be said about a ground right? don't want to alarm buyer?
You should call lit out as a safety concern. GFCIs should be used in the bath etc. Better to call attention to it in you report. The work you describe is typical of an amateur retrofit. Did you check to see if the outlet screw was grounded? That would at least tell you if the wiring was in mc or conduit.

Easiest would be to suggest consultation with an electrical contractor. It is a safety hazard, especially in the bathroom or any outside outlets.



He who knows nothing is closer to the truth than he whose mind is filled with falsehoods and errors - Thomas Jefferson - Founding Father

The democracy will cease to exist when you take away from those who are willing to work and give to those who would not. Thomas Jefferson

Never underestimate the difficulty of changing false beliefs by facts.
- Henry Rosovsky-Harvard

Michael Larson
Hudson, WI

Services provided in East MN and West WI
InspectraPro
and
Minnesota Home Inspector

Reply With Quote
  #22  
Old 6/12/06, 3:12 PM
Greg Fretwell Greg Fretwell is offline
Active Poster
 
Join Date: Jul 2004
Location: Estero Florida
Posts: 1,798
Please Note: Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Need help: New service-old wiring

You really can't answer the question without seeing the plug at the dryer/range. It should have been changed to 4 wire if the branch circuit was run in 4 wire. Then you split out the neutral and ground to the appropriate bus in the panel.
I am not sure how the AHJ arrived at his answer since the old 3 wire rule prohibited connection to a sub panel. It had to originate from the main panel where neutral and ground were the same thing. There is no good answer for a sub panel connection. If you connect to the ground bus you are putting "objectionable <neutral> current on grounding conductors" and if you connect to the neutral bus you are putting circuit voltage on the can of the appliance (as much as the neutral drop on the range/dryer branch circuit PLUS the feeder).
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Top Ten Wiring Hazards Threaten Life and Property jtedesco1 Electrical Inspections 3 9/2/08 6:15 PM
Top Ten Wiring Hazards jtedesco1 Electrical Inspections 6 9/1/08 9:26 PM
Nice Report on AL Wire Terminations - Enjoy pabernathy Electrical Inspections 0 7/2/07 1:35 PM
K&T splice. egarcia1 Electrical Inspections 13 2/3/07 7:36 AM
PIC of State Rep and sponsor of new NACHI H.I. Bill in NH. gromicko Miscellaneous Discussion for Inspectors 53 8/30/06 6:58 PM


All times are GMT -4. The time now is 9:31 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts