Default Need a little clarification

200 amp main disconnect at the meter. Service(sub?) panel at the house with a 200 amp disconnect at the top of the panel. I called it a sub panel and called out the neutral bus was still bonded to the enclosure. Another sub panel in the basement, with most of the breakers for the house, was wire correctly. Was I correct here? Thanks for your input !



Rick Slocum
NACHI # 04072697
Elizabeth CO 80107
ABSOLUTE Home Inspection Service

Last edited by rslocum; 7/4/07 at 1:33 PM..
Reply With Quote
  #2  
Old 4/5/07, 12:17 AM
Joe Funderburk, CMI's Avatar
Joe Funderburk, CMI Joe Funderburk, CMI is offline
InterNACHI Member
 
Join Date: Dec 2005
Location: Hickory Grove, SC
Posts: 8,343
Send a message via Yahoo to jfunderburk
Default Re: Need a little clarification

Did you take the cover off the exterior panel? Was it feeding into the house from that breaker?

From the information I have, I'd call the panel at the meter the service entrance equipment (main) panel. The other panels are load side equipment (sub) panels.

I think you were correct, but can't be certain.



“The things that will destroy America are peace at any price,
prosperity at any cost, safety first instead of duty first,
the love of soft living, and the get-rich-quick theory of life.”
Theodore Roosevelt


Joe Funderburk, CMI
Alpha & Omega Home Inspections, LLC
Inspecting Upstate SC & Charlotte Metro, NC
NACHI ID: NACHI05120170
www.aohomeinspection.com


Reply With Quote
  #3  
Old 4/5/07, 12:24 AM
Richard D. Slocum's Avatar
Richard D. Slocum Richard D. Slocum is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Elizabeth, CO
Posts: 230
Default Re: Need a little clarification

Yes Joe, the feed from the this panel went inside to the other sub panel. The last 3 pics above are the exterior panel. Thanks for your input!



Rick Slocum
NACHI # 04072697
Elizabeth CO 80107
ABSOLUTE Home Inspection Service
Reply With Quote
  #4  
Old 4/5/07, 7:28 AM
wsiegel wsiegel is offline
Active Poster
 
Join Date: Oct 2006
Location: Hialeah, Fl
Posts: 2,649
Please Note: wsiegel is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Need a little clarification

The service equimpment is the first point of disconnect. It is only there that the nuetral and ground wires are bonded together.
Reply With Quote
  #5  
Old 4/5/07, 8:35 AM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,057
Default Re: Need a little clarification

Quote:
Originally Posted by wsiegel
The service equimpment is the first point of disconnect. It is only there that the nuetral and ground wires are bonded together.
Sometimes needs repeating. . .

You were correct in regarding the exterior panel. It is not the service equipment. The service disconnect is at the meter.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Need a clarification kmcmahon Electrical Inspections 15 8/12/07 1:56 PM
Clarification of NACHI Conference in Toronto rwand1 Canadian Inspectors 6 7/17/07 1:59 PM
Clarification on Safety Glass jweinberg General Inspection Discussion 4 12/25/06 1:35 AM
need clarification on "laundry circuit" for new const. bking Electrical Inspections 9 5/8/06 5:28 PM


All times are GMT -4. The time now is 7:49 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts