Default Need an opinion on older AL multistrand

This is all original installation from the previous owner. We have a water well wired with multi-strand Aluminum, plain covering, not weatherproof. It runs overhead from the barn 75-100 feet, and is spliced in one place. Splices are the bolt type, then taped. It's been like this for 15-20 years, now.

At the well house end there is a switchbox. With a light tester, not meter, the power is only about half on one leg, full on the other. The well puts out a reduced amount of water.

I figure the splice needs to be taken apart, cleaned, and secured again.

Do you think the conductor should be replaced, or just clean and rework?

Thanks for the feedback.
Reply With Quote
  #2  
Old 3/5/09, 4:34 PM
Michael R. Boyett's Avatar
Michael R. Boyett Michael R. Boyett is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Austin, TX
Posts: 4,749
Default Re: Need an opinion on older AL multistrand

I would say it likely needs to be completely replaced based on the improper type of wire but I would let a licensed electrician make the final call.



Excellence in Inspections
Mike Boyett, TREC #7290
mikeb@capcityinspections.com
Capital City Inspections
Austin, Texas
(512) 577-2579

Company blog is: www.capcityinspections.com/blog
Reply With Quote
  #3  
Old 3/5/09, 4:57 PM
lfoster's Avatar
lfoster lfoster is offline
Active Poster
 
Join Date: Apr 2006
Location: Utopia, TX
Posts: 489
Please Note: lfoster is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Need an opinion on older AL multistrand

Took the splices apart and cleaned / tightened. Still getting part power on one leg.

I think we have broken wires somewhere in that overhead line.

Going to get new conductor and run in conduit tomorrow.

Does anyone have a reference chart? The breaker is a 30 Amp, and the run is about 80 feet. Will 8 awg carry the load for that distance?
Reply With Quote
  #4  
Old 3/5/09, 6:01 PM
Brian E. Kelly's Avatar
Brian E. Kelly Brian E. Kelly is offline
InterNACHI Member
 
Join Date: Oct 2004
Location: Phoenix, AZ
Posts: 15,973
Default Re: Need an opinion on older AL multistrand

http://www.cerrowire.com/default.aspx?id=46


Last edited by bkelly2; 3/5/09 at 6:06 PM..
Reply With Quote
  #5  
Old 3/5/09, 6:44 PM
lfoster's Avatar
lfoster lfoster is offline
Active Poster
 
Join Date: Apr 2006
Location: Utopia, TX
Posts: 489
Please Note: lfoster is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Need an opinion on older AL multistrand

Thanks, 8 will do it.
Reply With Quote
  #6  
Old 3/5/09, 9:26 PM
brian winkle brian winkle is offline
Active Poster
 
Join Date: Sep 2005
Location: Arizona
Posts: 454
Please Note: brian winkle is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Need an opinion on older AL multistrand

Linda, you really should get some test equipment before you spend a lot of time and money replacing stuff. I am assuming the well pump is 240 volts from your OP. Did you verify 240V at the supply breaker? What do you mean by a light tester? Is it a neon voltage tester, or just a light bulb, or a non contact tester?

If you have one leg out but the motor is still connected, you will show voltage on the dead leg because it will come thru the motor windings from the good leg.
Reply With Quote
  #7  
Old 3/6/09, 9:36 PM
Mark Leonard Mark Leonard is offline
New User
 
Join Date: Feb 2005
Posts: 17
Please Note: Mark Leonard is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Need an opinion on older AL multistrand

Hello Linda

Did you make sure both legs were screwed down tight

Mark
Reply With Quote
  #8  
Old 3/8/09, 9:29 PM
Frank P. Newman Frank P. Newman is offline
InterNACHI Member
 
Join Date: Aug 2007
Location: Dublin, GA
Posts: 668
Default Re: Need an opinion on older AL multistrand

If all visible connections are tight and do not show signs of overheating, I would suspect a failing buried splice somewhere. No matter - replace the whole mess with properly rated Cu cable.



Frank P. Newman
Emerald City Inspections, LLC
Dublin, GA
Reply With Quote
  #9  
Old 3/9/09, 10:52 AM
lfoster's Avatar
lfoster lfoster is offline
Active Poster
 
Join Date: Apr 2006
Location: Utopia, TX
Posts: 489
Please Note: lfoster is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Need an opinion on older AL multistrand

We are back to having water again !!

On the AL, all electrical connections were tight, and we tried different things. Replaced the breaker, tried using different wire we had on hand. That showed equal current on both legs at the breaker, it just wasn't proper size for well pump.

We replaced the AL with 8 awg copper, buried in conduit, and it works great. Hooorayyyyy. Even found a ground rod connection in the barn near the panel - was pleasantly surprised. A lot of things around here were 'engineered' when we bought the place. Knew the wiring wasn't proper, just hadn't gotten in a hurry to fix it.

Pump problems made us worried because the well man had been at the neighbors. They added 3 joints of pipe into their well to get further into the water table. Afraid we might have to consider that, too. It's been dry around here for about 18 months now.

Thanks for all the help.
Linda
Reply With Quote
  #10  
Old 3/9/09, 8:13 PM
ecolclasure ecolclasure is offline
InterNACHI Member
 
Join Date: Dec 2008
Location: Hibbing Mn
Posts: 26
Default Re: Need an opinion on older AL multistrand

I am an electrician and the only thing i would suggest is that you install a new ground rod they tend to break down in fifteen to twenty years underground and become useless

just a thought
Ed
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
According to the latest opinion polls... jwilliams4 Miscellaneous Discussion for Inspectors 0 10/18/08 9:50 PM
older homes with Mario Kyriacou, rcooke Canadian Inspectors 45 5/9/08 5:30 PM
Texas Atty. General Renders Opinion about Liability Insurance bthompson1 Legislation, Licensing & Legal Issues for Inspectors 45 12/20/07 11:57 PM
Older wiring dmacy Electrical Inspections 1 5/11/07 2:40 PM


All times are GMT -4. The time now is 7:49 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts