Just ran into AWM wire for the first time. Does anybody know if it is safe to be hooked up with copper?
|
| Need a home inspection in South Carolina? Check out InterNACHI's listing of South Carolina certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine. |
|
#2
|
||||
|
||||
|
If you mean (Appliance Wiring Material), it usually is copper.
Christopher Currins Certified, Licensed Proudly serving the St.Louis Metro St. Charles, St. Peters, Maryland Heights, O'Fallon, Florrisant, MO Home Inspector BLESSED ARE THE CRACKED, FOR THEY ARE THE ONES WHO LET IN THE "LIGHT"!
|
|
#3
|
||||
|
||||
|
Please Note:
Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
What was the application and were these conductors dual rated? i.e.-also listed as THHN or another type of conductor?
|
|
#4
|
|||
|
|||
|
Ok. It looks like aluminum (shiny silver). I looked it up online and some different sources were saying that it is usually coated for moisture protection so I'm guessing that's where the color comes from. Thanks.
|
|
#5
|
|||
|
|||
|
Hey Robert,
There are some other codes on the wire. Namely CSA and FT1. Not sure what they mean so I'm gonna poke around online to see if I can find an answer. |
|
#6
|
||||
|
||||
|
Please Note:
Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
How are these conductors being used?
|
|
#7
|
|||
|
|||
|
They are in a ceiling fan/light.
|
|
#8
|
||||
|
||||
|
Please Note:
Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
So this is wiring in the fan/lt or branch circuit wiring feeding the unit?
|
|
#9
|
|||
|
|||
|
Roberts questions is VITAL to understanding the use of AWM conductors. Is it part of the assemblie or equipment or is it being run as circuit wiring.....Long and short...if the AWN is part of the equipment wiring...no worries....if it is being used as branch circuit wiring then it's a problem...AWM is not listed under 310.13 ( unless of course it is dual rated as AWM and then lets say THHN as well )
Paul W. Abernathy |
![]() |
| Thread Tools | |
|
|
Similar Threads
|
||||
| Thread | Thread Starter | Forum | Replies | Last Post |
| Need your advice!!! | bgrover | Miscellaneous Discussion for Inspectors | 28 | 6/12/08 6:16 PM |
| Home Inspection Business Part Time (Seeking Advice) | Shawn M. Nold | General Inspection Discussion | 32 | 9/16/07 11:58 AM |
| Video inspection system advice | thalpin | General Inspection Discussion | 0 | 3/14/07 11:13 PM |