Inspected a condo built in 1972. Inside the service panel it had aluminum wiring except for copper wiring for a new A.C. unit. When I took off an outlet cover it had both copper and aluminum wiring attached to it. How should I write this?
Thanks Gary Porter GLP's Home and Mold Inspections 321-239-0621 Certified Commercial Mold Inspector Serving Orlando, Kissimmee, Winter Park, Winter Springs, Oviedo, Titusville, Celebration, Harmony, Avalon, Windermere, Deltona, Debary, Sanford Orange County, Seminole County, Volusia County, Osceola County www.homeandmoldinspections.com |
|
#2
|
||||
|
||||
|
Gary,
Are you refering to AL and CU attached to the terminals inside the actual panel....or are you saying you removed a cover to a Receptacle and this took place. I will try to answer them both if you wish.....? Paul W. Abernathy,CMI,CEI,CEPE NECŪ Consultant/Columnist www.twitter.com/ElectricalGuru - ICC & IAEI Certified Electrical Inspector - ICC & IAEI Certified Electrical Plans Examiner - Look for my article in the Nov/Dec 2009 IAEI Magazine - 2007 "Top Gun" Winner - Mike Holt Enterprises " visit www.TheElectricalGuru.com Today !" |
|
#3
|
||||
|
||||
|
The service panel had all aluminum wiring accept for the A.C. The outlet had aluminum and copper attached to it. Copper was on the bottom. Does this wiring need to be replaced.
Gary Porter GLP's Home and Mold Inspections 321-239-0621 Certified Commercial Mold Inspector Serving Orlando, Kissimmee, Winter Park, Winter Springs, Oviedo, Titusville, Celebration, Harmony, Avalon, Windermere, Deltona, Debary, Sanford Orange County, Seminole County, Volusia County, Osceola County www.homeandmoldinspections.com |
|
#4
|
||||
|
||||
|
"The electrical system includes suspect, aluminum, wiring that, for several reasons, does not conduct current as efficiently as copper wiring and can create a fire-hazard many times at the termination point. Therefore, you should seek the counsel of a licensed electrician who is familiar with this issue or who performs copalum crimping."
Above is the PVS response. While the issue of the "receptacle" outlet is important and the receptacle would have to ALLOW both AL and CU conductors....the larger issue is the fact the dwelling has AL wiring itself and that is the MAIN thing I would write up for evaluation. While the largest problem with AL wiring tends to happen at the termination points.......it is important because many insurance companies will not insure a new buyer with AL wiring is present. The device MUST be rated for both.........and if AL and CU is spliced together it MUST be done by a listed and approved method....some wirenuts are rated for this...but the best method is Capalum Crimping.... If you have the entire system evaluated by an Electrical Contractor because of the AL.....they should remove you from any issues. Paul W. Abernathy,CMI,CEI,CEPE NECŪ Consultant/Columnist www.twitter.com/ElectricalGuru - ICC & IAEI Certified Electrical Inspector - ICC & IAEI Certified Electrical Plans Examiner - Look for my article in the Nov/Dec 2009 IAEI Magazine - 2007 "Top Gun" Winner - Mike Holt Enterprises " visit www.TheElectricalGuru.com Today !" |
|
#5
|
||||
|
||||
|
Not sure where I got this...so I can't give credit to it....I believe it was posted from faqs.org...if so......Theirs your CREDIT....
The main problem with aluminum wiring is a phenomenon known as "cold creep". When aluminum wiring warms up, it expands. When it cools down, it contracts. Unlike copper, when aluminum goes through a number of warm/cool cycles it loses a bit of tightness each time. To make the problem worse, aluminum oxidises, or corrodes when in contact with certain types of metal, so the resistance of the connection goes up. Which causes it to heat up and corrode/ oxidize still more. Eventually the wire may start getting very hot, melt the insulation or fixture it's attached to, and possibly even cause a fire. Since people usually encounter aluminum wiring when they move into a house built during the 70's, we will cover basic points of safe aluminum wiring. We suggest that, if you're considering purchasing a home with aluminum wiring, or have discovered it later, that you hire a licensed electrician or inspector to check over the wiring for the following things: 1) Fixtures (eg: outlets and switches) directly attached to aluminum wiring should be rated for it. The device will be stamped with "Al/Cu" or "CO/ALR". The latter supersedes the former, but both are safe. These fixtures are somewhat more expensive than the ordinary ones. 2) Wires should be properly connected (at least 3/4 way around the screw in a clockwise direction). Connections should be tight. While repeated tightening of the screws can make the problem worse, during the inspection it would pay off to snug up each connection. Note that aluminum wiring is still often used for the main service entrance cable. It should be inspected. 3) "push-in" terminals are an extreme hazard with aluminum wire. Any connections using push-in terminals should be redone with the proper screw connections immediately. 4) There should be no signs of overheating: darkened connections, melted insulation, or "baked" fixtures. Any such damage should be repaired. 5) Connections between aluminum and copper wire need to be handled specially. Current Canadian codes require that the connectors used must be specially marked for connecting aluminum to copper. The NEC requires that the wire be connected together using special crimp devices, with an anti-oxidant grease. The tools and materials for the latter are quite expensive - 6) Any non-rated receptacle can be connected to aluminum wiring by means of a short copper "pigtail". See (5) above. 7) Shows reasonable workmanship: neat wiring, properly stripped (not nicked) wire etc. Paul W. Abernathy,CMI,CEI,CEPE NECŪ Consultant/Columnist www.twitter.com/ElectricalGuru - ICC & IAEI Certified Electrical Inspector - ICC & IAEI Certified Electrical Plans Examiner - Look for my article in the Nov/Dec 2009 IAEI Magazine - 2007 "Top Gun" Winner - Mike Holt Enterprises " visit www.TheElectricalGuru.com Today !" |
|
#6
|
||||
|
||||
|
You better refer it out to be on the safe side. Any solid-core aluminum I see anywhere gets referred.
Joe Funderburk, CMI Alpha & Omega Home Inspections, LLC Inspecting Upstate SC & Charlotte Metro, NC NACHI ID: NACHI05120170 www.aohomeinspection.com |
![]() |