On one of my inspections today; there was an updated service panel. The 60 amp two pole GE breaker was 178 f. I didn't think to check the amps at the time (brain fart). It controlled the electric furnace that was running at the time. Oh, and the rest of the panel was between 80-85 f.
Any thoughts. Any comments would be very helpful. Bill Corbett C.H.I. Magic City Inspections LLC InspectingtheUnexpected.com
Last edited by wcorbett; 11/12/07 at 8:55 PM.. Reason: Forgot photo |
|
#2
|
||||
|
||||
|
Hi Bill,
A 90 degree Delta T is way too much, in my opinion I would even consider that high if the breaker was GFCI or AFCI, call it out for further evaluation. Regards Gerry "To realize our true destiny, we must be guided not by a myth from our past, but by a vision of our future." (Mark B Adams) Commercial property Inspection Tampa, Orlando, Sarasota, Jacksonville, Ft Launderdale, Miami, Florida. NACHI cell 484-429-5466 NACHI02121106 |
|
#3
|
|||
|
|||
|
10 degrees difference. Not so bad.
90? WAYY too much. Lot's of resistance in there somewhere. Like Gerry said, defer it to an electrician. Jeffrey Wortham ANS Inspections, Inc. www.ansinspections.com 630.276.8440 638 Langford Drive Bolingbrook, IL 60440 NACHI ID:04050181 |
|
#4
|
||||
|
||||
|
Quote:
Bill Corbett C.H.I. Magic City Inspections LLC InspectingtheUnexpected.com
|
|
#5
|
||||
|
||||
|
Hi Bill,
an amp load number would have been nice, but my "gut feel" is one of the following
Regards Gerry "To realize our true destiny, we must be guided not by a myth from our past, but by a vision of our future." (Mark B Adams) Commercial property Inspection Tampa, Orlando, Sarasota, Jacksonville, Ft Launderdale, Miami, Florida. NACHI cell 484-429-5466 NACHI02121106 |
|
#6
|
||||
|
||||
|
Inadequately sized conductors will contribute as well. . .
IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ® Jeff PopeJPI Home Inspection Service Santa Clarita CA (661) 212-0738 Santa Clarita Home Inspection http://www.MyInspector.net |
|
#7
|
||||
|
||||
|
Quote:
Thanks, but the conductors were #6 The panel had been recently updated (maybe 1 year old). I have sometimes seen discoloration to the contacts one side or both sides of a breaker (from a bad connection). I am thinking that it's a bad breaker. Thanks to all. Bill Corbett C.H.I. Magic City Inspections LLC InspectingtheUnexpected.com
|
|
#8
|
||||
|
||||
|
Quote:
Will Decker, CMI ILL License # 450.0002240 Board Certified Master Inspector Decker Home Services, LLC Chicago and Northern Suburban Home Inspections Office: (847) 676-8393 Cell: (847) 609-2345 Home: (847) 673-2702 wjd@DeckerHomeServices.com www.DeckerHomeServices.com Learn, Educate, Serve and have fun doing it! |
|
#9
|
|||
|
|||
|
Please Note:
Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
At a certain point point it really doesn't matter what the problem is, a qualified person should look at it.
|
|
#10
|
||||
|
||||
|
Just saw the pic and notice the red one is looking like the suspect.
|
|
#11
|
|||
|
|||
|
I don't think the amp load would be relevant.
I regularly used an IR thermometer to check up to 1500 amp breaker connections and rarely saw them more than 10-15 degrees over ambient. (Granted, I never saw them at full load!) Jeffrey Wortham ANS Inspections, Inc. www.ansinspections.com 630.276.8440 638 Langford Drive Bolingbrook, IL 60440 NACHI ID:04050181 |
![]() |