  #1  
Old 11/12/07, 7:56 PM
William M. Corbett's Avatar
William M. Corbett William M. Corbett is offline
InterNACHI Member
 
Join Date: Jun 2006
Location: Remlap, AL
Posts: 231
Default Need some help. Pleeeeeeze

On one of my inspections today; there was an updated service panel. The 60 amp two pole GE breaker was 178 f. I didn't think to check the amps at the time (brain fart). It controlled the electric furnace that was running at the time. Oh, and the rest of the panel was between 80-85 f.
Any thoughts. Any comments would be very helpful.
Attached Thumbnails
need-some-help-pleeeeeeze-042.jpg  



Bill Corbett C.H.I.
Magic City Inspections LLC
InspectingtheUnexpected.com

Last edited by wcorbett; 11/12/07 at 8:55 PM.. Reason: Forgot photo
Reply With Quote
  #2  
Old 11/12/07, 9:05 PM
gbeaumont's Avatar
gbeaumont gbeaumont is offline
InterNACHI Member
 
Join Date: Jan 2003
Location: Clearwater, FL
Posts: 6,261
Send a message via AIM to gbeaumont Send a message via MSN to gbeaumont Send a message via Yahoo to gbeaumont
Default Re: Need some help. Pleeeeeeze

Hi Bill,

A 90 degree Delta T is way too much, in my opinion I would even consider that high if the breaker was GFCI or AFCI, call it out for further evaluation.

Regards

Gerry



"To realize our true destiny, we must be guided not by a myth from our past, but by a vision of our future."
(Mark B Adams)

Commercial property Inspection Tampa, Orlando, Sarasota, Jacksonville, Ft Launderdale, Miami, Florida.
NACHI cell 484-429-5466
NACHI02121106

Reply With Quote
  #3  
Old 11/12/07, 9:26 PM
jwortham1 jwortham1 is offline
InterNACHI Member
 
Join Date: Jun 2006
Location: Bolingbrook, IL
Posts: 721
Default Re: Need some help. Pleeeeeeze

10 degrees difference. Not so bad.

90? WAYY too much. Lot's of resistance in there somewhere.

Like Gerry said, defer it to an electrician.



Jeffrey Wortham
ANS Inspections, Inc.
www.ansinspections.com
630.276.8440
638 Langford Drive
Bolingbrook, IL 60440
NACHI ID:04050181
Reply With Quote
  #4  
Old 11/12/07, 9:36 PM
William M. Corbett's Avatar
William M. Corbett William M. Corbett is offline
InterNACHI Member
 
Join Date: Jun 2006
Location: Remlap, AL
Posts: 231
Default Re: Need some help. Pleeeeeeze

Quote:
Originally Posted by jwortham1
10 degrees difference. Not so bad.

90? WAYY too much. Lot's of resistance in there somewhere.

Like Gerry said, defer it to an electrician.
I did call it out, however for educational purposes,does anyone have thoughts on possible causes? Do you think it could just be a defective breaker? I have never had this problem with GE breakers. Square D occasionally, FPE all the time; never GE. My second guess was a problem with the furnace (wish I checked the amps).



Bill Corbett C.H.I.
Magic City Inspections LLC
InspectingtheUnexpected.com
Reply With Quote
  #5  
Old 11/12/07, 9:50 PM
gbeaumont's Avatar
gbeaumont gbeaumont is offline
InterNACHI Member
 
Join Date: Jan 2003
Location: Clearwater, FL
Posts: 6,261
Send a message via AIM to gbeaumont Send a message via MSN to gbeaumont Send a message via Yahoo to gbeaumont
Default Re: Need some help. Pleeeeeeze

Hi Bill,

an amp load number would have been nice, but my "gut feel" is one of the following
  1. Defective breaker
  2. Poor connection between breaker and bus
  3. Loose conductor
MY best guess is #2

Regards

Gerry



"To realize our true destiny, we must be guided not by a myth from our past, but by a vision of our future."
(Mark B Adams)

Commercial property Inspection Tampa, Orlando, Sarasota, Jacksonville, Ft Launderdale, Miami, Florida.
NACHI cell 484-429-5466
NACHI02121106

Reply With Quote
  #6  
Old 11/12/07, 9:59 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,057
Default Re: Need some help. Pleeeeeeze

Inadequately sized conductors will contribute as well. . .



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #7  
Old 11/12/07, 10:06 PM
William M. Corbett's Avatar
William M. Corbett William M. Corbett is offline
InterNACHI Member
 
Join Date: Jun 2006
Location: Remlap, AL
Posts: 231
Default Re: Need some help. Pleeeeeeze

Quote:
Originally Posted by jpope
Inadequately sized conductors will contribute as well. . .
JP,
Thanks, but the conductors were #6
The panel had been recently updated (maybe 1 year old). I have sometimes seen discoloration to the contacts one side or both sides of a breaker (from a bad connection). I am thinking that it's a bad breaker.
Thanks to all.



Bill Corbett C.H.I.
Magic City Inspections LLC
InspectingtheUnexpected.com
Reply With Quote
  #8  
Old 11/12/07, 11:16 PM
William J. Decker's Avatar
William J. Decker William J. Decker is offline
InterNACHI Member
 
Join Date: Nov 2004
Location: Skokie, IL
Posts: 7,785
Default Re: Need some help. Pleeeeeeze

Quote:
Originally Posted by gbeaumont
Hi Bill,

an amp load number would have been nice, but my "gut feel" is one of the following
  1. Defective breaker
  2. Poor connection between breaker and bus
  3. Loose conductor
MY best guess is #2

Regards

Gerry
I agree with the funny looking man



Will Decker, CMI
ILL License # 450.0002240
Board Certified Master Inspector
Decker Home Services, LLC
Chicago and Northern Suburban Home Inspections
Office: (847) 676-8393
Cell: (847) 609-2345
Home: (847) 673-2702

wjd@DeckerHomeServices.com
www.DeckerHomeServices.com

Learn, Educate, Serve and have fun doing it!
Reply With Quote
  #9  
Old 11/12/07, 11:58 PM
Greg Fretwell Greg Fretwell is offline
Active Poster
 
Join Date: Jul 2004
Location: Estero Florida
Posts: 1,798
Please Note: Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Need some help. Pleeeeeeze

At a certain point point it really doesn't matter what the problem is, a qualified person should look at it.
Reply With Quote
  #10  
Old 11/13/07, 4:12 PM
Bob Elliott's Avatar
Bob Elliott Bob Elliott is offline
InterNACHI Member
 
Join Date: Aug 2006
Location: Chicago
Posts: 21,916
Default Re: Need some help. Pleeeeeeze

Just saw the pic and notice the red one is looking like the suspect.
Reply With Quote
  #11  
Old 11/13/07, 4:53 PM
jwortham1 jwortham1 is offline
InterNACHI Member
 
Join Date: Jun 2006
Location: Bolingbrook, IL
Posts: 721
Default Re: Need some help. Pleeeeeeze

I don't think the amp load would be relevant.

I regularly used an IR thermometer to check up to 1500 amp breaker connections and rarely saw them more than 10-15 degrees over ambient.
(Granted, I never saw them at full load!)



Jeffrey Wortham
ANS Inspections, Inc.
www.ansinspections.com
630.276.8440
638 Langford Drive
Bolingbrook, IL 60440
NACHI ID:04050181
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On



All times are GMT -4. The time now is 7:49 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts