Default I need a trained eye.

Can I get some imput?Two breakers on left bottom 3wires in line red is on a 30 amp breaker Black is on a 20 amp breaker yellow is running to netural bar. is this acceptable?It ran around house into attic then I lost it under insulation can't idenify what it is running. Rest of wiring is nightmare taped junctions in attic just laying in insulation no boxes or covers. The list is long.
Attached Thumbnails
need-trained-eye-533-grape-vine-place-lathrop-006.jpg  
Reply With Quote
  #2  
Old 2/10/09, 12:00 AM
relliott's Avatar
relliott relliott is offline
Active Poster
 
Join Date: Aug 2006
Location: HARWOOD HTS, il
Posts: 8,567
Please Note: relliott is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: I need a trained eye.

I see a green ground at bottom of the neutral bar.

Red has black tape around it ,so that's ok.

List panel as not labeled properly.

Were the wire gauges ok?

Yellow in neutral bar should be white or marked with white tape.
Not your job to trace them all though.

The bottom ground is stranded,was it secured?

I notice this is outside so did you trace to a ground rod?

Last edited by relliott; 2/10/09 at 12:03 AM..
Reply With Quote
  #3  
Old 2/10/09, 12:55 AM
William W. Van Damme William W. Van Damme is offline
InterNACHI Member
 
Join Date: Dec 2005
Location: Oakley, Ca
Posts: 30
Default Re: I need a trained eye.

Thanks Robert
Sometimes when I do these handyman specials I start second guessing myself. But not labeled properly was one of my comments on the panel.

Thanks again
Reply With Quote
  #4  
Old 2/10/09, 9:57 PM
Michael Thellend's Avatar
Michael Thellend Michael Thellend is offline
New User
 
Join Date: Feb 2009
Location: Cardinal, ON, Canada
Posts: 30
Please Note: Michael Thellend is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: I need a trained eye.

Hi there,

-If that's a one inch connector at the back bottom it needs a bushing.
-Two of your breakers need to be double poles, not singles. Bottom left where the three wire (red and black) is and top left (two larger blacks) I do believe is a two pole circuit as well. The three wire with red does appear to be a #12 0r #10 wire and should be on a double 20 or 30 Amp breaker respectively. The upper wires appear to be #10 as well.
-Stranded grounds do need a twisting and clipping.
-There is a hole at the bottom right hand corner; it should be filled with a K.O. filler. If there's a wire coming through it you should use a cover plate and fasten it to the panel. Knockout a 3/8 hole for a connector and use one on the wire.
-You will need a #6 ground if it's a 100 amp sub panel or a #8 ground if it's under 100 amps from your main distribution panel to this panel, I don't see one.
-I would get rid of those cob webs too.

Can you take a couple of more shots of your panel? Like above the main breaker and the left hand side of the panel?
Also can you list each breakers ampacity on both sides starting from the top down? I do believe you might have overrated breakers for conductor sizes in the panel.


Mike

Last edited by Michael Thellend; 2/11/09 at 8:16 AM..
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Repairs made by a LICENCED electrician cduphily Electrical Inspections 45 1/13/08 4:09 PM
Cross Trained Janitor bkelly2 Electrical Inspections 1 7/18/07 2:26 AM
IAC2 release 3 new and different logos for Mold, Radon, Radon & Mold trained members. gromicko IAC2 Indoor Air Forum 6 10/31/06 11:55 AM
We might have done the impossible. Mold E&O insurance for NACHI trained inspectors. gromicko Miscellaneous Discussion for Inspectors 4 8/24/06 4:56 AM


All times are GMT -4. The time now is 4:31 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts