During the evening the lights in the family room went out. I checked and reset the breaker but to no avail. Upon testing the outlets I found that suddenly the hot and ground were reversed. Am I correct in thinking the breaker has gone bad on me?
Reply With Quote
Need a home inspection in Georgia? Check out InterNACHI's listing of Georgia certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #2  
Old 11/22/11, 11:34 PM
KEVIN WOOD's Avatar
KEVIN WOOD KEVIN WOOD is online now
InterNACHI Member
 
Join Date: Mar 2006
Location: Sault Ste Marie ON
Posts: 3,107
Default Re: I need your help

I think you mean hot black and white neutral. I would think that it also is a bad light switch and this is a very common problem when they are old or have a loose connection.



THE RIGHT TRAK
CIAQP, IAC2
Certified Master Inspector
kwoodinspections@hotmail.com
www.kwood.inspectorpages.com www.homegauge.com/shgi/THERIGHTTRAKIAQ
www.linkedin.com/in/kevinwoodiaq
OOVOO account kwoodinspections
Cell: 705-971-2096
Ph : 705-946-2676
Reply With Quote
  #3  
Old 11/22/11, 11:56 PM
Aubrey J. Kahn Aubrey J. Kahn is offline
InterNACHI Member
 
Join Date: Dec 2009
Location: Kissimmee, Fl
Posts: 1,121
Default Re: I need your help

Sorry, maybe I should clarify further. The lights that went out in the family room are table lamps which are plugged into electrical outlets and controlled by wall mounted switches. When testing the electrical outlets I found that the hot and grounds were reversed. That is why I am thinking the breaker might have gone bad.
Reply With Quote
  #4  
Old 11/23/11, 4:55 AM
Robert Meier's Avatar
Robert Meier Robert Meier is online now
Active Poster
 
Join Date: Feb 2010
Location: New Jersey
Posts: 1,250
Please Note: Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: I need your help

Quote:
Originally Posted by akahn View Post
Sorry, maybe I should clarify further. The lights that went out in the family room are table lamps which are plugged into electrical outlets and controlled by wall mounted switches. When testing the electrical outlets I found that the hot and grounds were reversed. That is why I am thinking the breaker might have gone bad.
OK so how did you test these receptacles to determine that the hot and EG were suddenly reversed? If this just happened you might have a difficult problem to troubleshoot, not to mention the extreme danger that may be present when normally grounded objects are electrified.
Reply With Quote
  #5  
Old 11/23/11, 6:08 AM
KEVIN WOOD's Avatar
KEVIN WOOD KEVIN WOOD is online now
InterNACHI Member
 
Join Date: Mar 2006
Location: Sault Ste Marie ON
Posts: 3,107
Default Re: I need your help

Hot and ground reverse means you have a short circuit messed up between the ground and hot. I would think it is at the plug and you shoud call a electrician ASAP.



THE RIGHT TRAK
CIAQP, IAC2
Certified Master Inspector
kwoodinspections@hotmail.com
www.kwood.inspectorpages.com www.homegauge.com/shgi/THERIGHTTRAKIAQ
www.linkedin.com/in/kevinwoodiaq
OOVOO account kwoodinspections
Cell: 705-971-2096
Ph : 705-946-2676
Reply With Quote
  #6  
Old 11/23/11, 6:36 AM
Sean Fogarty's Avatar
Sean Fogarty Sean Fogarty is offline
InterNACHI Member
 
Join Date: Sep 2009
Location: Somewhere in Knoxville TN flipping breakers
Posts: 2,267
Default Re: I need your help

Sounds like you may have a loose wire possibly grounding out. I would start by checking your outlets in that circuit to see if any are bad or the connections were loose.

Just some thought as well. I have found many times when testing gfci outlets, if the outlet doesn't reset properly my tester will show all outlets on that circuit as having reverse polairty. Once reset, it corrects the issue. It obviously had something to do with the connection.

One can affect the rest. Dive on in Aubrey, you will find it.




Infraspection Institute Level 1 Certified Infrared Thermographer

Fogarty Inspection Services Group of Knoxville TN

Home inspections, Commercial Inspections, Thermal Imaging, Mold, Enviromental Testing and Radon Testing for Knoxville TN, Oak Ridge TN, Maryville, Clinton, Farragut, Lenoir City, Pigeon Forge, Sevierville and all the surrounding areas.

865-256-5397

www.homeinspectorknoxville.com

www.moldandradon.com

www.thermal-inspection.net

www.commercial-building-inspector.net
Reply With Quote
  #7  
Old 11/23/11, 6:39 AM
Sean Fogarty's Avatar
Sean Fogarty Sean Fogarty is offline
InterNACHI Member
 
Join Date: Sep 2009
Location: Somewhere in Knoxville TN flipping breakers
Posts: 2,267
Default Re: I need your help

Quote:
Originally Posted by kwood View Post
Hot and ground reverse means you have a short circuit messed up between the ground and hot. I would think it is at the plug and you shoud call a electrician ASAP.
I would hope the skills of any experienced home inspector would qualify you to evaluate your own plugs. If you can't check plugs in your own home for loose connections you may consider another line of work. Not directed at you Kevin, just in general. Its just 110, it doesn't hurt that bad.




Infraspection Institute Level 1 Certified Infrared Thermographer

Fogarty Inspection Services Group of Knoxville TN

Home inspections, Commercial Inspections, Thermal Imaging, Mold, Enviromental Testing and Radon Testing for Knoxville TN, Oak Ridge TN, Maryville, Clinton, Farragut, Lenoir City, Pigeon Forge, Sevierville and all the surrounding areas.

865-256-5397

www.homeinspectorknoxville.com

www.moldandradon.com

www.thermal-inspection.net

www.commercial-building-inspector.net
Reply With Quote
  #8  
Old 11/23/11, 6:56 AM
Wayne B. Wilson's Avatar
Wayne B. Wilson Wayne B. Wilson is offline
InterNACHI Member
 
Join Date: Aug 2008
Location: Powell, Tn
Posts: 8,234
Default Re: I need your help

Let us keep in mind that it not the voltage but amperage that kills you . 05 amps i believe, sounds like a short , remove the power , switch and outlets and use a ohm meter.



Wayne Wilson
East TN Home Inspections LLC
Knoxville, Oak Ridge, Maryville, Clinton, Farragut, Lenoir City, Pigeon Forge, Sevierville and all the surrounding areas.
865-256-1490

http://site.myhomeinspection.net


Last edited by wwilson3; 11/23/11 at 7:05 AM..
Reply With Quote
  #9  
Old 11/23/11, 7:38 AM
KEVIN WOOD's Avatar
KEVIN WOOD KEVIN WOOD is online now
InterNACHI Member
 
Join Date: Mar 2006
Location: Sault Ste Marie ON
Posts: 3,107
Default Re: I need your help

You may not de-energize this plug safely as Wayne is pointing out. Unless you can determine no power to the plug you should leave it to the electrician to analyze. If you start a fire or create a hazard you will not receive any insurance relief if someting goes wrong.
BTW some people react different to electrical shock and even at low amperage can not let go and in this instance you may become the path to ground.



THE RIGHT TRAK
CIAQP, IAC2
Certified Master Inspector
kwoodinspections@hotmail.com
www.kwood.inspectorpages.com www.homegauge.com/shgi/THERIGHTTRAKIAQ
www.linkedin.com/in/kevinwoodiaq
OOVOO account kwoodinspections
Cell: 705-971-2096
Ph : 705-946-2676

Last edited by kwood; 11/23/11 at 7:41 AM..
Reply With Quote
  #10  
Old 11/23/11, 9:18 AM
Joseph M. Whitt Joseph M. Whitt is offline
InterNACHI Member
 
Join Date: Oct 2008
Location: NC
Posts: 123
Default Re: I need your help

Quote:
Originally Posted by sfogarty View Post
Its just 110, it doesn't hurt that bad.

Sean
Please understand that I am not trying to jump on you in any way but this statement needs addressing even if you made it in pun.

A 120 volt circuit protected with a 15 amp breaker is capable of delivering 1800 watts of electrical energy continually.
To think that this is not enough to KILL is completely the wrong train of thought as it is more than enough to do damage or cause death



Mike Whitt
Contractor/Instructor
Reply With Quote
  #11  
Old 11/23/11, 9:36 AM
KEVIN WOOD's Avatar
KEVIN WOOD KEVIN WOOD is online now
InterNACHI Member
 
Join Date: Mar 2006
Location: Sault Ste Marie ON
Posts: 3,107
Default Re: I need your help

Correct and even here in SSM On the ESA says when posible all power is to be removed from outlet before removal by electrician to make proper repairs.



THE RIGHT TRAK
CIAQP, IAC2
Certified Master Inspector
kwoodinspections@hotmail.com
www.kwood.inspectorpages.com www.homegauge.com/shgi/THERIGHTTRAKIAQ
www.linkedin.com/in/kevinwoodiaq
OOVOO account kwoodinspections
Cell: 705-971-2096
Ph : 705-946-2676
Reply With Quote
  #12  
Old 11/23/11, 10:05 AM
Gary D. Rowden Gary D. Rowden is offline
InterNACHI Member
 
Join Date: Sep 2008
Location: Hemet, CA
Posts: 146
Default Re: I need your help

I have to agree, this doesn’t sound like a breaker issue. When troubleshooting this type of electrical issue I would personally start at the point of the problem which sounds like the switch. Then move downstream testing and making corrections as needed. Also if this is beyond your skill level then refer to someone that is qualified. Always remember safety first.
Reply With Quote
  #13  
Old 11/23/11, 10:18 AM
Jeffrey R. Jonas's Avatar
Jeffrey R. Jonas Jeffrey R. Jonas is offline
InterNACHI Member
 
Join Date: Feb 2007
Location: Owatonna, MN
Posts: 12,194
Default Re: I need your help

Quote:
Originally Posted by akahn View Post
Upon testing the outlets I found that suddenly the hot and ground were reversed.
One question: How do you know it "suddenly" reversed? Did you specifically test that outlet in the past? What makes you think it hasn't always been that way?

You weren't clear. Was the breaker tripped? You stated you 'reset' the breaker "but to no avail" and the polarity was reversed. How did you check polarity, if "no avail".

Perhaps the lamp socket went bad. Happens all the time.

Not trying to bust your nuts, but getting the exact facts is important. No wonder some of youse catch crap from electricians and other tradesmen.

Okay... that's more than one question, my bad.

Last edited by jjonas; 11/23/11 at 10:25 AM..
Reply With Quote
Need a home inspection in Georgia? Check out InterNACHI's listing of Georgia certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #14  
Old 11/23/11, 10:49 AM
Aubrey J. Kahn Aubrey J. Kahn is offline
InterNACHI Member
 
Join Date: Dec 2009
Location: Kissimmee, Fl
Posts: 1,121
Default Re: I need your help

Thanks for the input and guys. It was as I suspected, the CB had gone bad. A quick trip to Lowes and $4 later as is well with the world again.
Reply With Quote
  #15  
Old 11/23/11, 10:54 AM
Bob Elliott's Avatar
Bob Elliott Bob Elliott is offline
InterNACHI Member
 
Join Date: Aug 2006
Location: Chicago
Posts: 21,916
Default Re: I need your help

I am still trying to figure out how if the breaker did not reset you were able to get the juice for testing outlets as reversed.
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On



All times are GMT -4. The time now is 7:49 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts