  #1  
Old 4/25/07, 4:20 PM
Scott Schultz Scott Schultz is offline
Active Poster
 
Join Date: Sep 2006
Location: Surprise, AZ
Posts: 216
Please Note: Scott Schultz is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default netural not connected

I did an inspection today in which a 4 wire cable came into the box and 2 cables, the red and black were connected to a 2 pole breaker 50 amp breaker (A/C unit), the ground wire was connected to the bus bar and the white neutral was cut and bent back, not attached to a bus bar. Is this standard with 240v not to have the neutral connected?
Reply With Quote
  #2  
Old 4/25/07, 4:30 PM
cbellefontaine's Avatar
cbellefontaine cbellefontaine is offline
InterNACHI Member
 
Join Date: Dec 2006
Location: Bolingbrook, IL
Posts: 65
Send a message via MSN to cbellefontaine
Default Re: netural not connected

It all depends on the appliance. If the circuit goes to a central AC unit, then it is ok. If the appliance is a combination 240 and 120 unit (Example, electric stove burners are 240 but the lights and computer is 120, then a neutral is required.) My guess is that it goes to the AC unit.

Where is surprise?



Sincerely,
Charles M. Bellefontaine

Bellman Group, Inc.
877-316-0600 Extension #802
Click Here to Join our Email Newsletter

Get Illinois Home Inspector Pre-License Education and
Continuing Education at www.bellmangroup.com

Low cost professional report writing with a contact
management system. www.myreportwriter.com
Reply With Quote
  #3  
Old 4/25/07, 4:38 PM
Scott Schultz Scott Schultz is offline
Active Poster
 
Join Date: Sep 2006
Location: Surprise, AZ
Posts: 216
Please Note: Scott Schultz is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: netural not connected

thanks. surprise is in the northwest valley of metro phoenix.
Reply With Quote
  #4  
Old 4/25/07, 10:51 PM
brian winkle brian winkle is offline
Active Poster
 
Join Date: Sep 2005
Location: Arizona
Posts: 454
Please Note: brian winkle is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: netural not connected

I remember when Surprise was in the middle of nowhere on the way to Vegas. The only reason you stopped there was if you drove a gas guzzler like my 442 and you couldn't make it quite into Phx, so you stopped in Surprise for some of their gas which must have had gold in it.
Reply With Quote
  #5  
Old 4/25/07, 11:19 PM
David A. Andersen's Avatar
David A. Andersen David A. Andersen is offline
InterNACHI Member
 
Join Date: Jun 2005
Location: Woodlawn, TN
Posts: 5,686
Default Re: netural not connected

Three wire 240 VAC circuits do not require a neutral.
Reply With Quote
  #6  
Old 4/26/07, 7:12 AM
Roy D. Cooke, Sr's Avatar
Roy D. Cooke, Sr Roy D. Cooke, Sr is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Brighton, ON
Posts: 13,947
Default Re: netural not connected

Quote:
Originally Posted by dandersen
Three wire 240 VAC circuits do not require a neutral.
Examples ,welders ,some wood working equipment,most electric water heaters .

Roy Cooke



If I can answer any questions please send me email Roycooke@hotmail.com

On an inspection and need immediate help call my cell 613-827-2011
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Hot & neutral wires connected abolt Electrical Inspections 1 11/27/07 12:56 AM
4 x 200 amp breakers connected mbarnett Electrical Inspections 7 9/30/07 11:55 PM
Romex connected to male plug... OK? ghawley Electrical Inspections 20 3/4/07 7:05 PM
Question re combustion air connected to vent jhawes Canadian Inspectors 9 12/4/06 10:24 PM
Romex wire connected to standard male plug. ghawley Electrical Inspections 2 3/2/06 2:35 PM