I did an inspection today in which a 4 wire cable came into the box and 2 cables, the red and black were connected to a 2 pole breaker 50 amp breaker (A/C unit), the ground wire was connected to the bus bar and the white neutral was cut and bent back, not attached to a bus bar. Is this standard with 240v not to have the neutral connected?
|
|
#2
|
||||
|
||||
|
It all depends on the appliance. If the circuit goes to a central AC unit, then it is ok. If the appliance is a combination 240 and 120 unit (Example, electric stove burners are 240 but the lights and computer is 120, then a neutral is required.) My guess is that it goes to the AC unit.
Where is surprise? Sincerely, Charles M. Bellefontaine Bellman Group, Inc. 877-316-0600 Extension #802 Click Here to Join our Email Newsletter Get Illinois Home Inspector Pre-License Education and Continuing Education at www.bellmangroup.com |
|
#3
|
|||
|
|||
|
Please Note:
Scott Schultz is a non-member guest and is in no way affiliated with InterNACHI or its members.
thanks. surprise is in the northwest valley of metro phoenix.
|
|
#4
|
|||
|
|||
|
Please Note:
brian winkle is a non-member guest and is in no way affiliated with InterNACHI or its members.
I remember when Surprise was in the middle of nowhere on the way to Vegas. The only reason you stopped there was if you drove a gas guzzler like my 442 and you couldn't make it quite into Phx, so you stopped in Surprise for some of their gas which must have had gold in it.
|
|
#5
|
||||
|
||||
|
Three wire 240 VAC circuits do not require a neutral.
|
|
#6
|
||||
|
||||
|
Quote:
Roy Cooke If I can answer any questions please send me email Roycooke@hotmail.com On an inspection and need immediate help call my cell 613-827-2011 |
![]() |
| Thread Tools | |
|
|
Similar Threads
|
||||
| Thread | Thread Starter | Forum | Replies | Last Post |
| Hot & neutral wires connected | abolt | Electrical Inspections | 1 | 11/27/07 12:56 AM |
| 4 x 200 amp breakers connected | mbarnett | Electrical Inspections | 7 | 9/30/07 11:55 PM |
| Romex connected to male plug... OK? | ghawley | Electrical Inspections | 20 | 3/4/07 7:05 PM |
| Question re combustion air connected to vent | jhawes | Canadian Inspectors | 9 | 12/4/06 10:24 PM |
| Romex wire connected to standard male plug. | ghawley | Electrical Inspections | 2 | 3/2/06 2:35 PM |