Is it acceptable to have a neutral and gounding wire under the same lug and a neutral bus bar in a main panel?
|
|
#2
|
||||
|
||||
|
No it isn't Matt.....
Dale Duffy Inspect Arizona Companies, Inc. Phoenix Commercial Building Inspectors, Inc. Phoenix Thermal Imaging, Inc. Infraspection Certified Thermographer 602.402.5305 Home Hints eNews
InterNACHI 2007 U.S.A Member of the Year National Association of Commercial Building Inspectors, Inc. |
|
#3
|
|||
|
|||
|
Thats what I thought...Just wanted to make sure before I called it out!
|
|
#4
|
||||
|
||||
|
Dale,
Do you have a standard narrative that you use to report this defect? Thank you. |
|
#5
|
||||
|
||||
|
"One or more neutral wires are incorrectly connected under a single screw on the grounding or neutral bus bar at the (pick one: main panel/sub-panel), and should be serviced. (Unless the manufacturer states otherwise, bus bars are only designed for one current carrying conductor per terminating screw.)"
“The things that will destroy America are peace at any price, prosperity at any cost, safety first instead of duty first, the love of soft living, and the get-rich-quick theory of life.” Theodore Roosevelt Joe Funderburk, CMI Alpha & Omega Home Inspections, LLC Inspecting Upstate SC & Charlotte Metro, NC NACHI ID: NACHI05120170 www.aohomeinspection.com |
|
#6
|
||||
|
||||
|
Thanks! Joe.
Most SPARKY'S tell me there is nothing wrong with the neutral and ground under same lug. |
|
#7
|
||||
|
||||
|
Heres the wording that I use:
When neutrals and grounds are bonded (connected) together, the return neutral current will split (not necessarily equally) and run on parallel paths through the grounding and neutral system back to the main panel and up the neutral to the transformer. This parallel travel can cause unbalanced conditions in the system because the current remaining in the neutral will not counterbalance the current in the hot wire. In some cases, neutral current travel on the grounding system and other metal systems, such as piping or ductwork, can be a shock hazard. Mark Nahrgang www.DaytonSpringfieldHomeInspector.com www.HeyMark.info Home Inspections for Springfield, Dayton, and surrounding OH areas. |
|
#8
|
||||
|
||||
|
Quote:
Where did that come from? You could put the offending bonding wire on an empty terminal on the same bus and nothing would change except that it would be code compliant. You may want to reconsider your wording. You can argue with intelligent people but to argue with a mush head is like trying to grab fog-Thomas Sowell |
|
#9
|
||||
|
||||
|
|
|
#10
|
|||
|
|||
|
and a video
1st Inspection Services Bruce M. Graham III Gainesville, FL 32608 352 871 8989 Florida Licensed Home Inspector #HI10 Radon Measurment Technician # R2279 NACHI05091592 ICC 5268478 www.1stinspectionsfl.com www.bungalowstomansions.com |
|
#11
|
||||
|
||||
|
Matthew,
The biggest problem with two wires under one screw is that the neutral might be loose, potentially causing overheating of the wire and creating a potential fire hazard. A ground wire could be screwed right next to it. I am not sure where the "imbalance" would exist. I would choose a different narrative as well. Bill |
|
#12
|
||||
|
||||
|
Double Tapped On Neutral Bus Bar
more than one “grounded conductor” (neutral /white) wire per screw on the neutral bus bar (double tapped/lugged) Each “grounded conductor” is supposed to have it’s very own screw on the bus bar, no other “grounded conductor” or “ungrounded conductor” (bare copper wire) should be under the screw with the “grounded conductor”. Siemens Grounded Conductor Terminations Please note third paragraph on page 2 Christopher Currins Certified, Licensed Proudly serving the St.Louis Metro St. Charles, St. Peters, Maryland Heights, O'Fallon, Florrisant, MO Home Inspector BLESSED ARE THE CRACKED, FOR THEY ARE THE ONES WHO LET IN THE "LIGHT"!
|
|
#13
|
||||
|
||||
|
Quote:
You can argue with intelligent people but to argue with a mush head is like trying to grab fog-Thomas Sowell |
|
#14
|
|||
|
|||
|
Please Note:
Speedy Petey is a non-member guest and is in no way affiliated with InterNACHI or its members.
Quote:
I used to do this all the time (ground and neutral of the same circuit) and never once gave it a second thought. NEC 408.41 was even thought about. It never came up on a test, class or inspection. Ten or eleven years ago, with the advent of the internet, I realized this is an issue and stopped the practice. I even questioned an inspector on it and he said it is not in the NY Resi Code so it is fine. This changed in 2008 as this was added as Section E3606.4 in the 2007 NY Resi Code. |
![]() |