Default Neutral and Gound under same lug?

Is it acceptable to have a neutral and gounding wire under the same lug and a neutral bus bar in a main panel?
Attached Thumbnails
neutral-and-gound-under-same-lug-p2020078.jpg  
Reply With Quote
  #2  
Old 2/2/09, 9:27 PM
Dale Duffy's Avatar
Dale Duffy Dale Duffy is offline
InterNACHI Member
 
Join Date: Oct 2005
Location: Scottsdale, Arizona, Cuenca, Ecuador
Posts: 9,118
Default Re: Neutral and Gound under same lug?

No it isn't Matt.....
Reply With Quote
  #3  
Old 2/2/09, 10:01 PM
mmurphy4 mmurphy4 is offline
New User
 
Join Date: Oct 2007
Location: Springfield Illinois
Posts: 48
Please Note: mmurphy4 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Neutral and Gound under same lug?

Thats what I thought...Just wanted to make sure before I called it out!
Reply With Quote
  #4  
Old 2/3/09, 8:00 AM
Buck Hartley, CMI's Avatar
Buck Hartley, CMI Buck Hartley, CMI is offline
InterNACHI Member
 
Join Date: Nov 2005
Location: Shawnee, KS
Posts: 1,711
Default Re: Neutral and Gound under same lug?

Dale,

Do you have a standard narrative that you use to report this defect?

Thank you.
Reply With Quote
  #5  
Old 2/3/09, 9:50 AM
Joe Funderburk, CMI's Avatar
Joe Funderburk, CMI Joe Funderburk, CMI is offline
InterNACHI Member
 
Join Date: Dec 2005
Location: Hickory Grove, SC
Posts: 9,928
Send a message via Yahoo to jfunderburk
Default Re: Neutral and Gound under same lug?

"One or more neutral wires are incorrectly connected under a single screw on the grounding or neutral bus bar at the (pick one: main panel/sub-panel), and should be serviced. (Unless the manufacturer states otherwise, bus bars are only designed for one current carrying conductor per terminating screw.)"



“The things that will destroy America are peace at any price,
prosperity at any cost, safety first instead of duty first,
the love of soft living, and the get-rich-quick theory of life.”
Theodore Roosevelt


Joe Funderburk, CBO, CMI
Alpha & Omega Home Inspections, LLC
Inspecting Upstate SC & Charlotte Metro, NC
Angie's List Super Service Award Winner 2013, 2012, 2011, 2010.
Ph: 704-351-1776
NACHI ID: NACHI05120170
www.aohomeinspection.com

Reply With Quote
  #6  
Old 2/3/09, 11:11 AM
Buck Hartley, CMI's Avatar
Buck Hartley, CMI Buck Hartley, CMI is offline
InterNACHI Member
 
Join Date: Nov 2005
Location: Shawnee, KS
Posts: 1,711
Default Re: Neutral and Gound under same lug?

Thanks! Joe.

Most SPARKY'S tell me there is nothing wrong with the neutral and ground under same lug.
Reply With Quote
  #7  
Old 2/3/09, 11:24 AM
mnahrgang's Avatar
mnahrgang mnahrgang is offline
InterNACHI Member
 
Join Date: Apr 2007
Location: Springfield, OH
Posts: 5,763
Default Re: Neutral and Gound under same lug?

Heres the wording that I use:

When neutrals and grounds are bonded (connected) together, the return neutral current will split (not necessarily equally) and run on parallel paths through the grounding and neutral system back to the main panel and up the neutral to the transformer. This parallel travel can cause unbalanced conditions in the system because the current remaining in the neutral will not counterbalance the current in the hot wire. In some cases, neutral current travel on the grounding system and other metal systems, such as piping or ductwork, can be a shock hazard.



Mark Nahrgang
www.DaytonSpringfieldHomeInspector.com
www.HeyMark.info

Home Inspections for Springfield, Dayton, and surrounding OH areas.
Reply With Quote
  #8  
Old 2/3/09, 11:29 AM
Michael Larson's Avatar
Michael Larson Michael Larson is offline
InterNACHI Member
 
Join Date: May 2006
Location: Hudson, WI including the Twin Cities of MN
Posts: 49,837
Default Re: Neutral and Gound under same lug?

Quote:
Originally Posted by mnahrgang View Post
Heres the wording that I use:

When neutrals and grounds are bonded (connected) together, the return neutral current will split (not necessarily equally) and run on parallel paths through the grounding and neutral system back to the main panel and up the neutral to the transformer. This parallel travel can cause unbalanced conditions in the system because the current remaining in the neutral will not counterbalance the current in the hot wire. In some cases, neutral current travel on the grounding system and other metal systems, such as piping or ductwork, can be a shock hazard.
Mark,

Where did that come from?

You could put the offending bonding wire on an empty terminal on the same bus and nothing would change except that it would be code compliant.

You may want to reconsider your wording.



As a Professional Home Inspector, I support the privacy of my clients.

For more information click Trustyourinspector.ORG


www.InspectraPro.com
www.MinnesotaHomeInspector.biz

Michael Larson
Hudson, WI

Services provided in East MN and West WI

Reply With Quote
  #9  
Old 2/3/09, 11:47 AM
Bob Elliott's Avatar
Bob Elliott Bob Elliott is offline
InterNACHI Member
 
Join Date: Aug 2006
Location: Chicago
Posts: 31,999
Default Re: Neutral and Gound under same lug?

Here is an illustration from the Mike Holt site.



Reply With Quote
  #10  
Old 2/3/09, 12:44 PM
Bruce M. Graham Bruce M. Graham is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Gainesville, FL
Posts: 2,434
Default Re: Neutral and Gound under same lug?

and a video http://www.mikeholt.com/multimedia/N...LAN-smooth.ram as well as others http://www.mikeholt.com/videolist.php



http://www.nachi.org/forum/image.php?type=sigpic&userid=6376&dateline=1330979  258
Professional Inspection Services, LLC dba
1st Inspection Services
Bruce M. Graham III
Gainesville, FL 32608
352 871 8989
Florida Licensed Home Inspector #HI10
Certified Level II Infrared Thermographer
Radon Measurment Technician # R2279
NACHI05091592
ICC 5268478
www.1stinspectionsfl.com
www.bungalowstomansions.com
Reply With Quote
  #11  
Old 2/3/09, 2:19 PM
William Thacker's Avatar
William Thacker William Thacker is offline
InterNACHI Member
 
Join Date: Dec 2008
Location: Pennsylvania
Posts: 354
Default Re: Neutral and Gound under same lug?

Matthew,

The biggest problem with two wires under one screw is that the neutral might be loose, potentially causing overheating of the wire and creating a potential fire hazard.

A ground wire could be screwed right next to it. I am not sure where the "imbalance" would exist. I would choose a different narrative as well.

Bill
Reply With Quote
  #12  
Old 2/3/09, 2:35 PM
Christopher Currins's Avatar
Christopher Currins Christopher Currins is offline
InterNACHI Member
 
Join Date: Feb 2007
Location: Godfrey, IL
Posts: 12,198
Default Re: Neutral and Gound under same lug?

Double Tapped On Neutral Bus Bar


more than one “grounded conductor” (neutral /white) wire per screw on the neutral bus bar (double tapped/lugged) Each “grounded conductor” is supposed to have it’s very own screw on the bus bar, no other “grounded conductor” or “ungrounded conductor” (bare copper wire) should be under the screw with the “grounded conductor”.


Siemens Grounded Conductor Terminations Please note third paragraph on page 2






CBC HOME INSPECTIONS

Christopher Currins
Professional Home Inspector In Edwardsville, Glen Carbon, Godfrey, Maryville,
Fairview Heights, O'Fallon and surrounding areas of S
outhern Illinois

We Make It Safer
Reply With Quote
  #13  
Old 2/3/09, 2:55 PM
Michael Larson's Avatar
Michael Larson Michael Larson is offline
InterNACHI Member
 
Join Date: May 2006
Location: Hudson, WI including the Twin Cities of MN
Posts: 49,837
Default Re: Neutral and Gound under same lug?

Quote:
Originally Posted by ccurrins View Post
Double Tapped On Neutral Bus Bar


more than one “grounded conductor” (neutral /white) wire per screw on the neutral bus bar (double tapped/lugged) Each “grounded conductor” is supposed to have it’s very own screw on the bus bar, no other “grounded conductor” or “ungrounded conductor” (bare copper wire) should be under the screw with the “grounded conductor”.


Siemens Grounded Conductor Terminations Please note third paragraph on page 2
An "ungrounded conductor" is a (hot) and and NOT "a bare copper wire" which is a grounding conductor.



As a Professional Home Inspector, I support the privacy of my clients.

For more information click Trustyourinspector.ORG


www.InspectraPro.com
www.MinnesotaHomeInspector.biz

Michael Larson
Hudson, WI

Services provided in East MN and West WI

Reply With Quote
  #14  
Old 2/3/09, 5:26 PM
Speedy Petey Speedy Petey is offline
Unmoderated Guest
 
Join Date: Jul 2006
Posts: 1,295
Please Note: Speedy Petey is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Neutral and Gound under same lug?

Quote:
Originally Posted by bhartley View Post
Thanks! Joe.

Most SPARKY'S tell me there is nothing wrong with the neutral and ground under same lug.
Know that depending on your area you will come up against this quite often. This is a common practice that is done by electricians, AND accepted by inspectors in many areas. My part of NY it is very common.
I used to do this all the time (ground and neutral of the same circuit) and never once gave it a second thought. NEC 408.41 was even thought about. It never came up on a test, class or inspection.
Ten or eleven years ago, with the advent of the internet, I realized this is an issue and stopped the practice. I even questioned an inspector on it and he said it is not in the NY Resi Code so it is fine.
This changed in 2008 as this was added as Section E3606.4 in the 2007 NY Resi Code.
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


All times are GMT -4. The time now is 3:49 PM.
no new posts