  #1  
Old 7/13/11, 4:23 AM
Greg Strump Greg Strump is offline
InterNACHI Member
 
Join Date: Jul 2009
Location: St Augustine, FL
Posts: 55
Default Neutral and Ground Branch Wires

Could you please look at the attached photo and tell me if the wires on the right are a ground and nuetral sharing a single screw on the bus bar and should this be called out? Keep in mind this house was built in 1996 and 408.21 from the NEC did not go into effect until 2002.
Attached Thumbnails
neutral-and-ground-branch-wires-neutral-wires.jpg  

Last edited by gstrump; 7/13/11 at 6:37 AM..
Reply With Quote
Need a home inspection in Michigan? Check out InterNACHI's listing of Michigan certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #2  
Old 7/13/11, 7:04 AM
Robert Meier's Avatar
Robert Meier Robert Meier is online now
Active Poster
 
Join Date: Feb 2010
Location: New Jersey
Posts: 1,250
Please Note: Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Neutral and Ground Branch Wires

What does the label on the panel say about more than one conductor under a screw?
Reply With Quote
  #3  
Old 7/13/11, 7:42 AM
Greg Strump Greg Strump is offline
InterNACHI Member
 
Join Date: Jul 2009
Location: St Augustine, FL
Posts: 55
Default Re: Neutral and Ground Branch Wires

There was no label.
Reply With Quote
  #4  
Old 7/13/11, 7:58 AM
Robert Meier's Avatar
Robert Meier Robert Meier is online now
Active Poster
 
Join Date: Feb 2010
Location: New Jersey
Posts: 1,250
Please Note: Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Neutral and Ground Branch Wires

Although this was spelled out explicitly in the 2002 NEC the standard actually existed prior to 2002 in the form of 110.14(A) where terminals used for more than one conductor had to be listed as such. Usually this information can be found on the panel label. Chances are this was not permitted even prior to 2002.

Quote:
110.14 Electrical Connections.
Because of different characteristics of dissimilar metals, devices such as pressure terminal or pressure splicing connectors and soldering lugs shall be identified for the material of the conductor and shall be properly installed and used. Conductors of dissimilar metals shall not be intermixed in a terminal or splicing connector where physical contact occurs between dissimilar conductors (such as copper and aluminum, copper and copper-clad aluminum, or aluminum and copper-clad aluminum), unless the device is identified for the purpose and conditions of use. Materials such as solder, fluxes, inhibitors, and compounds, where employed, shall be suitable for the use and shall be of a type that will not adversely affect the conductors, installation, or equipment.
FPN: Many terminations and equipment are marked with a tightening torque.
(A) Terminals. Connection of conductors to terminal parts shall ensure a thoroughly good connection without damaging the conductors and shall be made by means of pressure connectors (including set-screw type), solder lugs, or splices to flexible leads. Connection by means of wire-binding screws or studs and nuts that have upturned lugs or the equivalent shall be permitted for 10 AWG or smaller conductors.
Terminals for more than one conductor and terminals used to connect aluminum shall be so identified.
Reply With Quote
  #5  
Old 7/13/11, 8:10 AM
Greg Strump Greg Strump is offline
InterNACHI Member
 
Join Date: Jul 2009
Location: St Augustine, FL
Posts: 55
Default Re: Neutral and Ground Branch Wires

Thanks for the info, very helpful.
Reply With Quote
  #6  
Old 7/13/11, 8:24 AM
Robert Meier's Avatar
Robert Meier Robert Meier is online now
Active Poster
 
Join Date: Feb 2010
Location: New Jersey
Posts: 1,250
Please Note: Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Neutral and Ground Branch Wires

As to whether or not you should call this out in your report I will leave that opinion to the HI's on this forum.
Reply With Quote
  #7  
Old 7/13/11, 1:18 PM
Robert J. OConnor's Avatar
Robert J. OConnor Robert J. OConnor is offline
InterNACHI Member
 
Join Date: Jul 2003
Location: Long Island, NY
Posts: 1,288
Default Re: Neutral and Ground Branch Wires

Quote:
Originally Posted by gstrump View Post
Keep in mind this house was built in 1996 and 408.21 from the NEC did not go into effect until 2002.
See this Mike Holt Video ... http://www.mikeholt.com/multimedia/NEC2002/408/408-21-Corp-LAN-smooth.ram

The requirement for one terminal per neutral wire has been around for a very long time. Prior to 2002 it was in UL 67 and should have been marked on the panel label.

It is a defect, but write this one up carefully (e.g. have an electrician check and separate the neutral wires as needed) as many electricians dont think it's a big deal for panels installed prior to 2002.



Robert O'Connor, PE
Consulting Engineer & Inspector
LIU CW Post Adjunct Professor
NACHI Education Committee
www.reporthost.com/-rjo

I am absolutely amazed sometimes by how much thought goes into doing things wrong ...
Reply With Quote
  #8  
Old 7/13/11, 1:38 PM
Sean Fogarty's Avatar
Sean Fogarty Sean Fogarty is offline
InterNACHI Member
 
Join Date: Sep 2009
Location: Somewhere in Knoxville TN flipping breakers
Posts: 2,267
Default Re: Neutral and Ground Branch Wires

In our area this was accepted practice until 2006 I believe, and I still see it in some counties for new construction. Double neutrals no, but one neutral and a ground yes. If the state electrical inspector said it was good then all I can would do was make note of it.




Infraspection Institute Level 1 Certified Infrared Thermographer

Fogarty Inspection Services Group of Knoxville TN

Home inspections, Commercial Inspections, Thermal Imaging, Mold, Enviromental Testing and Radon Testing for Knoxville TN, Oak Ridge TN, Maryville, Clinton, Farragut, Lenoir City, Pigeon Forge, Sevierville and all the surrounding areas.

865-256-5397

www.homeinspectorknoxville.com

www.moldandradon.com

www.thermal-inspection.net

www.commercial-building-inspector.net
Reply With Quote
  #9  
Old 7/13/11, 11:36 PM
ROBERT V. YOUNG's Avatar
ROBERT V. YOUNG ROBERT V. YOUNG is offline
InterNACHI Member
 
Join Date: Mar 2010
Location: Montreal.
Posts: 5,055
Default Re: Neutral and Ground Branch Wires

Quote:
Originally Posted by roconnor View Post
See this Mike Holt Video ... http://www.mikeholt.com/multimedia/NEC2002/408/408-21-Corp-LAN-smooth.ram

The requirement for one terminal per neutral wire has been around for a very long time. Prior to 2002 it was in UL 67 and should have been marked on the panel label.

It is a defect, but write this one up carefully (e.g. have an electrician check and separate the neutral wires as needed) as many electricians dont think it's a big deal for panels installed prior to 2002.
Thanks Robert.
Great PFD's



montrealbuildinginspectionservice.com
montreal-home-inspection-services.com
home-inspections-montreal.com
homeinspectionsservicesmontreal.com
ROBERT YOUNG'S MONTREAL HOME INSPECTION SERVICE INC.
Certified Inspecteur Professionnel Certifié en Bâtiment membre de InterNACHI ACHI , Chapters - OntarioAchi et du M.I.C.Q (CPI) - (CHI)
OFFICE (514) 489-1887 MOBILE (514) 441-3732 TOLL FREE 1- 855-819-1816
Reply With Quote
  #10  
Old 7/13/11, 11:39 PM
ROBERT V. YOUNG's Avatar
ROBERT V. YOUNG ROBERT V. YOUNG is offline
InterNACHI Member
 
Join Date: Mar 2010
Location: Montreal.
Posts: 5,055
Default Re: Neutral and Ground Branch Wires

Thanks Sean.
At Roy Cooke's in April he had a live double tapped neutrals hooked up to a free standing exterior light fixture to explain the reasoning behind double tapped nutrals.
Evidence is everything.



montrealbuildinginspectionservice.com
montreal-home-inspection-services.com
home-inspections-montreal.com
homeinspectionsservicesmontreal.com
ROBERT YOUNG'S MONTREAL HOME INSPECTION SERVICE INC.
Certified Inspecteur Professionnel Certifié en Bâtiment membre de InterNACHI ACHI , Chapters - OntarioAchi et du M.I.C.Q (CPI) - (CHI)
OFFICE (514) 489-1887 MOBILE (514) 441-3732 TOLL FREE 1- 855-819-1816
Reply With Quote
  #11  
Old 7/15/11, 9:45 PM
Greg Strump Greg Strump is offline
InterNACHI Member
 
Join Date: Jul 2009
Location: St Augustine, FL
Posts: 55
Default Re: Neutral and Ground Branch Wires

What was the outcome of the double tapped neutrals when you tested it?
Reply With Quote
  #12  
Old 7/16/11, 6:01 AM
ROBERT V. YOUNG's Avatar
ROBERT V. YOUNG ROBERT V. YOUNG is offline
InterNACHI Member
 
Join Date: Mar 2010
Location: Montreal.
Posts: 5,055
Default Re: Neutral and Ground Branch Wires

Quote:
Originally Posted by gstrump View Post
What was the outcome of the double tapped neutrals when you tested it?
What was the outcome of the double tapped neutrals when you tested.
Dimming light. Resistance.
Back-flow.



montrealbuildinginspectionservice.com
montreal-home-inspection-services.com
home-inspections-montreal.com
homeinspectionsservicesmontreal.com
ROBERT YOUNG'S MONTREAL HOME INSPECTION SERVICE INC.
Certified Inspecteur Professionnel Certifié en Bâtiment membre de InterNACHI ACHI , Chapters - OntarioAchi et du M.I.C.Q (CPI) - (CHI)
OFFICE (514) 489-1887 MOBILE (514) 441-3732 TOLL FREE 1- 855-819-1816
Reply With Quote
  #13  
Old 7/16/11, 6:17 AM
ROBERT V. YOUNG's Avatar
ROBERT V. YOUNG ROBERT V. YOUNG is offline
InterNACHI Member
 
Join Date: Mar 2010
Location: Montreal.
Posts: 5,055
Default Re: Neutral and Ground Branch Wires

Sorry Greg called away for a moment.
#1: Safety hazard'
#2: No double lugging of white wire ( neutral ) conductor.
#3: Following the white wires to the breaker or its entry point.
Recommend a licensed electrician.



montrealbuildinginspectionservice.com
montreal-home-inspection-services.com
home-inspections-montreal.com
homeinspectionsservicesmontreal.com
ROBERT YOUNG'S MONTREAL HOME INSPECTION SERVICE INC.
Certified Inspecteur Professionnel Certifié en Bâtiment membre de InterNACHI ACHI , Chapters - OntarioAchi et du M.I.C.Q (CPI) - (CHI)
OFFICE (514) 489-1887 MOBILE (514) 441-3732 TOLL FREE 1- 855-819-1816
Reply With Quote
Need a home inspection in Michigan? Check out InterNACHI's listing of Michigan certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #14  
Old 7/19/11, 6:01 PM
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,072
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Neutral and Ground Branch Wires

It seems to me that I have explained this one before....many times. Remember guys, we have a great search feature on this site as most (if not all) of these topics have been talked about before. Just some good info for research..



Paul W. Abernathy
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
"UFER" Ground? see last paragraph. jtedesco1 Electrical Inspections 19 8/23/11 3:56 PM
What's this video worth? jtedesco1 Inspection Education & Training 5 4/18/08 9:24 AM
Ground Wires Inside a Panel mveitenhans Electrical Inspections 13 10/29/06 11:39 AM


All times are GMT -4. The time now is 7:52 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts