  #1  
Old 5/18/07, 4:49 PM
lprinzi lprinzi is offline
InterNACHI Member
 
Join Date: Sep 2004
Location: Jacksonville, Fl
Posts: 43
Default Neutral & ground photo

Sorry, here's the photo
Lou
Attached Thumbnails
neutral-and-ground-photo-308213-0004.jpg  



Lou Prinzi
First Choice Building Inspections, Inc.
www.FCBIJax.com
(904) 223-0068
Reply With Quote
  #2  
Old 5/18/07, 4:59 PM
Scott Schultz Scott Schultz is offline
Active Poster
 
Join Date: Sep 2006
Location: Surprise, AZ
Posts: 216
Please Note: Scott Schultz is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Neutral & ground photo

I always report when there are two or more neutrals sharing the same lug. It's probably ok to have multiple ground wires in the same lug but each neutral wire should have its own connection.
Reply With Quote
  #3  
Old 5/18/07, 5:00 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,057
Default Re: Neutral & ground photo

Neutrals and grounds should not share the same lug. . .



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #4  
Old 5/18/07, 6:07 PM
lprinzi lprinzi is offline
InterNACHI Member
 
Join Date: Sep 2004
Location: Jacksonville, Fl
Posts: 43
Default Re: Neutral & ground photo

What's the reasoning behind not sharing the same bar. Is there a specific reference. When I report it I'll need some backup since the answer I get will be that the city passed the inspection on it.



Lou Prinzi
First Choice Building Inspections, Inc.
www.FCBIJax.com
(904) 223-0068
Reply With Quote
  #5  
Old 5/18/07, 6:10 PM
Marc D. Shunk's Avatar
Marc D. Shunk Marc D. Shunk is offline
Banned
 
Join Date: Dec 2006
Location: Central PA
Posts: 1,980
Please Note: Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Neutral & ground photo

Quote:
Originally Posted by lprinzi
What's the reasoning behind not sharing the same bar. Is there a specific reference. When I report it I'll need some backup since the answer I get will be that the city passed the inspection on it.
You're a third party code inspector?
Reply With Quote
  #6  
Old 5/18/07, 6:12 PM
lprinzi lprinzi is offline
InterNACHI Member
 
Join Date: Sep 2004
Location: Jacksonville, Fl
Posts: 43
Default Re: Neutral & ground photo

No, not a code inspector... but still need to know the reason why it's not allowed so I can pass it on and any code reference if it exists.



Lou Prinzi
First Choice Building Inspections, Inc.
www.FCBIJax.com
(904) 223-0068
Reply With Quote
  #7  
Old 5/18/07, 6:14 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,057
Default Re: Neutral & ground photo

408.21 Grounded Conductor Terminations.
Each grounded conductor shall terminate within the panelboard in an individual terminal that is not also used for another conductor.




IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #8  
Old 5/18/07, 6:21 PM
lprinzi lprinzi is offline
InterNACHI Member
 
Join Date: Sep 2004
Location: Jacksonville, Fl
Posts: 43
Default Re: Neutral & ground photo

thanks a bunch...



Lou Prinzi
First Choice Building Inspections, Inc.
www.FCBIJax.com
(904) 223-0068
Reply With Quote
  #9  
Old 5/18/07, 9:57 PM
Greg Fretwell Greg Fretwell is offline
Active Poster
 
Join Date: Jul 2004
Location: Estero Florida
Posts: 1,798
Please Note: Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Neutral & ground photo

They can be in the same busbar, just not the same hole. You also should not connect neutrals to the busbar(s) that are bolted to the cabinet. That is for grounding only. You are using the main bonding jumper to conduct circuit current (250.6)
Reply With Quote
  #10  
Old 5/23/07, 3:38 PM
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,072
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Neutral & ground photo

I notice that atleast one of the cases where the "Grounded" and "Grounding" conductors are sharing the same termination point....and it appears one is larger than the other within the termination...which is exactly one of the reasons it is something you should call out.....no possible way for a termination to be solid with two different size conductors going into the same termination point......which leads to other issues.



Paul W. Abernathy
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
"UFER" Ground? see last paragraph. jtedesco1 Electrical Inspections 19 8/23/11 3:56 PM
THE "GROUNDING "TRUTH- Article To Read pabernathy Electrical Inspections 1 1/1/07 1:14 PM
Bare wire on old dryer or stove circuit: neutral or ground? fbartlo Electrical Inspections 9 8/28/06 1:08 AM
Ground wire in neutral bar, neutral to breaker, hot to ground? rmc3inspection Electrical Inspections 4 8/1/06 9:44 AM