Sorry, here's the photo
Lou |
|
#2
|
|||
|
|||
|
Please Note:
Scott Schultz is a non-member guest and is in no way affiliated with InterNACHI or its members.
I always report when there are two or more neutrals sharing the same lug. It's probably ok to have multiple ground wires in the same lug but each neutral wire should have its own connection.
|
|
#3
|
||||
|
||||
|
Neutrals and grounds should not share the same lug. . .
IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ® Jeff PopeJPI Home Inspection Service Santa Clarita CA (661) 212-0738 Santa Clarita Home Inspection http://www.MyInspector.net |
|
#4
|
|||
|
|||
|
What's the reasoning behind not sharing the same bar. Is there a specific reference. When I report it I'll need some backup since the answer I get will be that the city passed the inspection on it.
|
|
#5
|
||||
|
||||
|
Please Note:
Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Quote:
|
|
#6
|
|||
|
|||
|
No, not a code inspector... but still need to know the reason why it's not allowed so I can pass it on and any code reference if it exists.
|
|
#7
|
||||
|
||||
|
408.21 Grounded Conductor Terminations. Each grounded conductor shall terminate within the panelboard in an individual terminal that is not also used for another conductor. IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ® Jeff PopeJPI Home Inspection Service Santa Clarita CA (661) 212-0738 Santa Clarita Home Inspection http://www.MyInspector.net |
|
#8
|
|||
|
|||
|
thanks a bunch...
|
|
#9
|
|||
|
|||
|
Please Note:
Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
They can be in the same busbar, just not the same hole. You also should not connect neutrals to the busbar(s) that are bolted to the cabinet. That is for grounding only. You are using the main bonding jumper to conduct circuit current (250.6)
|
|
#10
|
|||
|
|||
|
I notice that atleast one of the cases where the "Grounded" and "Grounding" conductors are sharing the same termination point....and it appears one is larger than the other within the termination...which is exactly one of the reasons it is something you should call out.....no possible way for a termination to be solid with two different size conductors going into the same termination point......which leads to other issues.
Paul W. Abernathy |
![]() |
| Thread Tools | |
|
|
Similar Threads
|
||||
| Thread | Thread Starter | Forum | Replies | Last Post |
| "UFER" Ground? see last paragraph. | jtedesco1 | Electrical Inspections | 19 | 8/23/11 3:56 PM |
| THE "GROUNDING "TRUTH- Article To Read | pabernathy | Electrical Inspections | 1 | 1/1/07 1:14 PM |
| Bare wire on old dryer or stove circuit: neutral or ground? | fbartlo | Electrical Inspections | 9 | 8/28/06 1:08 AM |
| Ground wire in neutral bar, neutral to breaker, hot to ground? | rmc3inspection | Electrical Inspections | 4 | 8/1/06 9:44 AM |