Default neutral & ground same buss bar lug

I saw this today. Most times I see neutral and ground on the same bar but different lugs. This panel has about 9 on the same lug. Is it acceptable?

Lou P.
Reply With Quote
  #2  
Old 5/18/07, 7:21 PM
Shawn Rowe's Avatar
Shawn Rowe Shawn Rowe is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: St. Augustine, FL
Posts: 274
Default Re: neutral & ground same buss bar lug

this may help you (I believe someone posted this a while back)
Attached Thumbnails
neutral-and-ground-same-buss-bar-lug-double-tapped-neutrals.gif  



**************************************
Shawn Rowe, CMI
HomeFirst Inspection Services, LLC
- InfraRed Specialist (Level 1 & Building Science certified)
- Code Certified Residential Building Inspector
- Certified Master Inspector
-- Serving NE Florida, St. Johns, Duval, Flagler, Putnam counties --
Reply With Quote
  #3  
Old 5/18/07, 7:28 PM
lfoster's Avatar
lfoster lfoster is offline
Active Poster
 
Join Date: Apr 2006
Location: Utopia, TX
Posts: 489
Please Note: lfoster is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: neutral & ground same buss bar lug

Is it the entrance panel, or a distribution panel? Distribution panel must be separate bus bars; one neutral grounded conductor to one terminal screw; grounding can be doubled.
Reply With Quote
  #4  
Old 5/20/07, 11:51 AM
tdietrich1's Avatar
tdietrich1 tdietrich1 is offline
InterNACHI Member
 
Join Date: Oct 2006
Location: Northampton County - Pa
Posts: 1,954
Send a message via Yahoo to tdietrich1
Default Re: neutral & ground same buss bar lug

Lugs, Bugs, Bars, Oh My.

I'm getting the sense there is a miss communication going on here since there is a terminology mix up.

I believe the OP is asking if Equipment Grounding Conductors "Grounds" and Grounded Conductors "Neutrals" can be on the same bar? Even though they are under different terminal screws (what I think the OP is calling lugs). Under certain conditions this is ok. However, you compound two questions into one paragraph, and mention you see one with 9 'somethings' under a 'lug'. huh?


Rather than explain what you meant, a photo would be nice.

tom
Reply With Quote
  #5  
Old 5/20/07, 11:57 AM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,057
Default Re: neutral & ground same buss bar lug

It was clarified here. . .

http://www.nachi.org/forum/f19/neutral-and-ground-photo-17109/



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #6  
Old 5/20/07, 5:11 PM
tdietrich1's Avatar
tdietrich1 tdietrich1 is offline
InterNACHI Member
 
Join Date: Oct 2006
Location: Northampton County - Pa
Posts: 1,954
Send a message via Yahoo to tdietrich1
Default Re: neutral & ground same buss bar lug

Ah, there is the photo I was looking for...

tom
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
"UFER" Ground? see last paragraph. jtedesco1 Electrical Inspections 19 8/23/11 3:56 PM
Bare wire on old dryer or stove circuit: neutral or ground? fbartlo Electrical Inspections 9 8/28/06 1:08 AM
Ground wire in neutral bar, neutral to breaker, hot to ground? rmc3inspection Electrical Inspections 4 8/1/06 9:44 AM


All times are GMT -4. The time now is 7:52 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts