Default NEUTRAL and ground together in sub panel

When is it ok to put ground and neutrel on same bus bar.
Reply With Quote
Need a home inspection in Delaware? Check out InterNACHI's listing of Delaware certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #2  
Old 1/10/12, 12:32 PM
Robert Meier's Avatar
Robert Meier Robert Meier is online now
Active Poster
 
Join Date: Feb 2010
Location: New Jersey
Posts: 1,250
Please Note: Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: NEUTRAL and ground together in sub panel

If the panel was located at a separate structure and they were under the 2005 (I believe) or earlier versions of the NEC.
Reply With Quote
  #3  
Old 1/10/12, 12:37 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,057
Default Re: NEUTRAL and ground together in sub panel

Quote:
Originally Posted by Robert Meier View Post
If the panel was located at a separate structure and they were under the 2005 (I believe) or earlier versions of the NEC.
... and there are no other metallic paths (connections) between the structures, i.e. metal conduit, metal piping, cables/low voltage wiring, fencing, etc.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #4  
Old 1/10/12, 12:46 PM
Robert Meier's Avatar
Robert Meier Robert Meier is online now
Active Poster
 
Join Date: Feb 2010
Location: New Jersey
Posts: 1,250
Please Note: Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: NEUTRAL and ground together in sub panel

Quote:
Originally Posted by jpope View Post
... and there are no other metallic paths (connections) between the structures, i.e. metal conduit, metal piping, cables/low voltage wiring, fencing, etc.
Yes that's true. I was focusing on the requirement applying to separate structures. If the structures are not separate then I don't think that it was ever permitted.
Reply With Quote
  #5  
Old 1/10/12, 1:12 PM
Joe Funderburk, CMI's Avatar
Joe Funderburk, CMI Joe Funderburk, CMI is offline
InterNACHI Member
 
Join Date: Dec 2005
Location: Hickory Grove, SC
Posts: 8,343
Send a message via Yahoo to jfunderburk
Default Re: NEUTRAL and ground together in sub panel

Quote:
Originally Posted by jpope View Post
... and there are no other metallic paths (connections) between the structures, i.e. metal conduit, metal piping, cables/low voltage wiring, fencing, etc.
A difficult thing to determine during a home inspection, so refer it to a sparky.



“The things that will destroy America are peace at any price,
prosperity at any cost, safety first instead of duty first,
the love of soft living, and the get-rich-quick theory of life.”
Theodore Roosevelt


Joe Funderburk, CMI
Alpha & Omega Home Inspections, LLC
Inspecting Upstate SC & Charlotte Metro, NC
NACHI ID: NACHI05120170
www.aohomeinspection.com


Reply With Quote
  #6  
Old 1/10/12, 1:17 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,057
Default Re: NEUTRAL and ground together in sub panel

Quote:
Originally Posted by jfunderburk View Post
A difficult thing to determine during a home inspection, so refer it to a sparky.
That has always been my position as an inspector.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #7  
Old 1/10/12, 4:42 PM
Joseph M. Whitt Joseph M. Whitt is offline
InterNACHI Member
 
Join Date: Oct 2008
Location: NC
Posts: 123
Default Re: NEUTRAL and ground together in sub panel

Quote:
Originally Posted by JAMES DAVIS View Post
When is it ok to put ground and neutrel on same bus bar.

In any enclosure that contains the service disconnect is the only place where this is permitted except in earlier editions of the NEC where a remote building is supplied by a three wire feeder and another grounding electrode system is established.



Mike Whitt
Contractor/Instructor
Reply With Quote
  #8  
Old 1/15/12, 12:22 PM
JAMES DAVIS JAMES DAVIS is offline
New User
 
Join Date: Jan 2012
Posts: 4
Please Note: JAMES DAVIS is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: NEUTRAL and ground together in sub panel

Thank you , Mr Whitt. I have one more question, this remote well I am hooking up is a 3 wire connection and I was wondering if I could use a single pole 120/230 breaker.
Reply With Quote
  #9  
Old 1/15/12, 12:42 PM
Robert Meier's Avatar
Robert Meier Robert Meier is online now
Active Poster
 
Join Date: Feb 2010
Location: New Jersey
Posts: 1,250
Please Note: Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: NEUTRAL and ground together in sub panel

Quote:
Originally Posted by JAMES DAVIS View Post
Thank you , Mr Whitt. I have one more question, this remote well I am hooking up is a 3 wire connection and I was wondering if I could use a single pole 120/230 breaker.
Is this a home project or is it related to an inspection?
Reply With Quote
  #10  
Old 1/15/12, 1:04 PM
JAMES DAVIS JAMES DAVIS is offline
New User
 
Join Date: Jan 2012
Posts: 4
Please Note: JAMES DAVIS is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: NEUTRAL and ground together in sub panel

It is an inspection,thank you.
Reply With Quote
  #11  
Old 1/15/12, 6:06 PM
Jim Port Jim Port is offline
Unmoderated Guest
 
Join Date: Jul 2007
Location: Maryland
Posts: 805
Please Note: Jim Port is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: NEUTRAL and ground together in sub panel

A single pole breaker will only supply 120, not 240.

A tandem will allow two circuits of 120.
Reply With Quote
  #12  
Old 1/15/12, 6:16 PM
ROBERT V. YOUNG's Avatar
ROBERT V. YOUNG ROBERT V. YOUNG is offline
InterNACHI Member
 
Join Date: Mar 2010
Location: Montreal.
Posts: 5,055
Default Re: NEUTRAL and ground together in sub panel

Quote:
Originally Posted by jpope View Post
That has always been my position as an inspector.
Good to know and note taken.
My weakest subject for now.



montrealbuildinginspectionservice.com
montreal-home-inspection-services.com
home-inspections-montreal.com
homeinspectionsservicesmontreal.com
ROBERT YOUNG'S MONTREAL HOME INSPECTION SERVICE INC.
Certified Inspecteur Professionnel Certifié en Bâtiment membre de InterNACHI ACHI , Chapters - OntarioAchi et du M.I.C.Q (CPI) - (CHI)
OFFICE (514) 489-1887 MOBILE (514) 441-3732 TOLL FREE 1- 855-819-1816
Reply With Quote
  #13  
Old 1/16/12, 12:10 PM
JAMES DAVIS JAMES DAVIS is offline
New User
 
Join Date: Jan 2012
Posts: 4
Please Note: JAMES DAVIS is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: NEUTRAL and ground together in sub panel

Quote:
Originally Posted by Robert Meier View Post
Is this a home project or is it related to an inspection?
Why do they sell a single pole 120/230 breaker if it cant do what it says:
Reply With Quote
Need a home inspection in Delaware? Check out InterNACHI's listing of Delaware certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #14  
Old 1/16/12, 2:49 PM
Robert Meier's Avatar
Robert Meier Robert Meier is online now
Active Poster
 
Join Date: Feb 2010
Location: New Jersey
Posts: 1,250
Please Note: Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: NEUTRAL and ground together in sub panel

Quote:
Originally Posted by JAMES DAVIS View Post
Why do they sell a single pole 120/230 breaker if it cant do what it says:
Not sure I understand, where are you finding a 120/230 volt circuit breaker? If anything a slash rated breaker would be 120/240 not 230.
Reply With Quote
  #15  
Old 1/16/12, 2:52 PM
Christopher Currins's Avatar
Christopher Currins Christopher Currins is offline
InterNACHI Member
 
Join Date: Feb 2007
Location: Godfrey, IL
Posts: 7,626
Default Re: NEUTRAL and ground together in sub panel

Quote:
Originally Posted by JAMES DAVIS View Post
Why do they sell a single pole 120/230 breaker if it cant do what it says:
James you said this
Quote:
What I am hooking up is a 3 wire connection and I was wondering if I could use a single pole 120/230 breaker.
Ask your self, where would I connect 3 wires at a panel with a single pole breaker?

http://electrical.about.com/od/panel...fanduseage.htm



Christopher Currins
Certified, Licensed

Proudly serving the St.Louis Metro

St. Charles, St. Peters, Maryland Heights,
O'Fallon, Florrisant, MO Home Inspector




BLESSED ARE THE CRACKED, FOR THEY ARE THE ONES WHO LET IN THE "LIGHT"!
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
"UFER" Ground? see last paragraph. jtedesco1 Electrical Inspections 19 8/23/11 3:56 PM
Electric Panel dmozzillo Electrical Inspections 26 1/26/09 1:18 PM
What's this video worth? jtedesco1 Inspection Education & Training 5 4/18/08 9:24 AM


All times are GMT -4. The time now is 7:52 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts