Default Re: Neutral bus bar

Quote:
Originally Posted by ccurrins View Post
Not giving you a hard time, but you might want to read the bold phrase a few times.

It was sufficent for the time it was installed, and complied with the AHJ. Its not a repair. Its only a recommendation to update it. Are you going to request they rewire a 2 strand romex because it doesn't meet todays standards?




Infraspection Institute Level 1 Certified Infrared Thermographer

Fogarty Inspection Services Group of Knoxville TN

Home inspections, Commercial Inspections, Thermal Imaging, Mold, Enviromental Testing and Radon Testing for Knoxville TN, Oak Ridge TN, Maryville, Clinton, Farragut, Lenoir City, Pigeon Forge, Sevierville and all the surrounding areas.

865-256-5397

www.homeinspectorknoxville.com

www.moldandradon.com

www.thermal-inspection.net

www.commercial-building-inspector.net
Reply With Quote
Need a home inspection in Pennsylvania? Check out InterNACHI's listing of Pennsylvania certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #17  
Old 5/12/11, 9:42 PM
Sean Fogarty's Avatar
Sean Fogarty Sean Fogarty is offline
InterNACHI Member
 
Join Date: Sep 2009
Location: Somewhere in Knoxville TN flipping breakers
Posts: 2,267
Default Re: Neutral bus bar

Quote:
Originally Posted by lkage View Post
You may want to clarify the above bolded sentence.

I would hope that since the topic was about neutral wires, then most should comprehend this. But hey I will make the correction. Thanks.




Infraspection Institute Level 1 Certified Infrared Thermographer

Fogarty Inspection Services Group of Knoxville TN

Home inspections, Commercial Inspections, Thermal Imaging, Mold, Enviromental Testing and Radon Testing for Knoxville TN, Oak Ridge TN, Maryville, Clinton, Farragut, Lenoir City, Pigeon Forge, Sevierville and all the surrounding areas.

865-256-5397

www.homeinspectorknoxville.com

www.moldandradon.com

www.thermal-inspection.net

www.commercial-building-inspector.net
Reply With Quote
  #18  
Old 5/12/11, 9:57 PM
Christopher Currins's Avatar
Christopher Currins Christopher Currins is offline
InterNACHI Member
 
Join Date: Feb 2007
Location: Godfrey, IL
Posts: 7,626
Default Re: Neutral bus bar

Quote:
Originally Posted by sfogarty View Post
It was sufficent for the time it was installed, and complied with the AHJ. Its not a repair. Its only a recommendation to update it. Are you going to request they rewire a 2 strand romex because it doesn't meet todays standards?
Not at all. you missed my point.

This ( and should be repaired if you choose to.) doesn't make sense to me.



Christopher Currins
Certified, Licensed

Proudly serving the St.Louis Metro

St. Charles, St. Peters, Maryland Heights,
O'Fallon, Florrisant, MO Home Inspector




BLESSED ARE THE CRACKED, FOR THEY ARE THE ONES WHO LET IN THE "LIGHT"!

Last edited by ccurrins; 5/12/11 at 11:01 PM..
Reply With Quote
  #19  
Old 5/12/11, 10:09 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,057
Default Re: Neutral bus bar

Quote:
Originally Posted by ccurrins View Post
This ( and should be repaired if you choose to.) doesn't make since to me.
Doesn't make since to me either , but I'd be happy to make cents (sense) of it for you



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #20  
Old 5/12/11, 10:57 PM
Christopher Currins's Avatar
Christopher Currins Christopher Currins is offline
InterNACHI Member
 
Join Date: Feb 2007
Location: Godfrey, IL
Posts: 7,626
Default Re: Neutral bus bar

Quote:
Originally Posted by jpope View Post
Doesn't make since to me either , but I'd be happy to make cents (sense) of it for you
Ha...ha I have a bad habit of doing that since I can't remember when.



Christopher Currins
Certified, Licensed

Proudly serving the St.Louis Metro

St. Charles, St. Peters, Maryland Heights,
O'Fallon, Florrisant, MO Home Inspector




BLESSED ARE THE CRACKED, FOR THEY ARE THE ONES WHO LET IN THE "LIGHT"!
Reply With Quote
  #21  
Old 5/13/11, 6:39 AM
Bruce M. Graham Bruce M. Graham is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Gainesville, FL
Posts: 2,099
Default Re: Neutral bus bar

I like Mike.
check this out
http://www.mikeholt.com/multimedia/N...LAN-smooth.ram



http://www.nachi.org/forum/image.php?type=sigpic&userid=6376&dateline=1330979  258
Professional Inspection Services, LLC dba
1st Inspection Services
Bruce M. Graham III
Gainesville, FL 32608
352 871 8989
Florida Licensed Home Inspector #HI10
Radon Measurment Technician # R2279
NACHI05091592
ICC 5268478
www.1stinspectionsfl.com
www.bungalowstomansions.com
Reply With Quote
  #22  
Old 5/13/11, 8:23 AM
George P. Wells, CMI's Avatar
George P. Wells, CMI George P. Wells, CMI is offline
InterNACHI Member
 
Join Date: Oct 2004
Location: Michigan
Posts: 554
Send a message via Skype™ to gwells
Default Re: Neutral bus bar

Quote:
Originally Posted by rrudomanski View Post
Ok,
I sited this on an inspection, the owner called an electrician, was charged $70 for the visit, and the electrician stated there was no violations in the main panel and left. Does the Florida code specifically state one neutral to a lug? I've seen this a lot on houses less than five years old.

Rick
The owner should ask for his $70 back! Maybe the electrician was really Joe the Plumber?

Personally, I'm very uncomfortable using words like "violation" in my inspection reports or, for that matter, in casual conversation when doing home inspections. As a licensed electrician, however, I can tell you that this practice has been prohibited by the NEC for a long time. Any first-year apprentice should know that it is a problem and why.

As a fire investigator specializing in electrical fires, I can tell you that Loss-of-neutral is a major cause of electrical fires. Anyone who doesn't think this is a problem is dead wrong! Loss-of-neutral fires do not start at the panels. The fires start at the loads. Consequently, the real cause is often not recognized by C&O investigators. That's why C&O investigators call in an electrical investigator for assistance. As an example, a C&O investigator will determine that a fire was started at a kitchen toaster. He may not, however, be able to determine whether it was from the Poptart in the toaster (Poptarts are also a major cause of house fires) or it was an electrical fire. I can look at toaster and know immediately whether it was electrical or not and what the nature of the electrical malfunction was.



BestInspectors.Net
& Real Estate Training Academy

Inspection Report Software for
Windows - iOS - Mac - Android

Continuing Education
Home and Commercial Building Inspection - Skilled Trades – Real Estate – Appraisal – NFPA 921

http://www.bestinspectors.net

est. 1992

Last edited by gwells; 5/13/11 at 6:53 PM..
Reply With Quote
  #23  
Old 5/15/11, 10:13 AM
Rollie Meyers Rollie Meyers is offline
New User
 
Join Date: Jul 2007
Location: People's Republic of Chico,CA
Posts: 40
Please Note: Rollie Meyers is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Neutral bus bar

408.21 was new in the 2002 NEC, it is 408.41 in the '05, '08, & '11 editions. Art. 408 was Art. 384 in the 1996 NEC.

Here is the text from the 2011 NEC

408.41 Grounded Conductor Terminations. Each grounded
conductor shall terminate within the panelboard in an individual
terminal that is not also used for another conductor.

Exception: Grounded conductors of circuits with parallel
conductors shall be permitted to terminate in a single terminal
if the terminal is identified for connection of more
than one conductor.

The exception does not apply in this case, but included it anyway.
Reply With Quote
  #24  
Old 5/16/11, 9:10 PM
William Warner's Avatar
William Warner William Warner is offline
InterNACHI Member
 
Join Date: May 2003
Location: Dayton, OH
Posts: 3,293
Default Re: Neutral bus bar

http://static.schneider-electric.us/...0100DB0705.pdf




Submit your AWARDS NOMINATIONS here

Visit the InterNACHI Awards web portal here

Blessed are the blissfully ignorant... for they shall be easily led...
Reply With Quote
  #25  
Old 5/16/11, 9:13 PM
Robert Meier's Avatar
Robert Meier Robert Meier is online now
Active Poster
 
Join Date: Feb 2010
Location: New Jersey
Posts: 1,250
Please Note: Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Neutral bus bar

Quote:
Originally Posted by wwarner View Post
That document reiterates the fact that this requirement was in existence prior to it being added to the NEC code language in 2002. I'm guessing that it was installation practice was common place because no one was really enforcing it prior to them adding the words directly in the NEC.
Reply With Quote
  #26  
Old 5/16/11, 9:21 PM
Russell J. Hensel's Avatar
Russell J. Hensel Russell J. Hensel is offline
InterNACHI Member
 
Join Date: Jul 2008
Location: Fort Myers, FL
Posts: 5,576
Default Re: Neutral bus bar

I had a client, call me an want her $120 for an electrician who came out and said nothing was wrong with her panel and wanted her money for the useless call out of the electrician.

Now she is a seller and has used me about 5 times on properties she has bought. So, I went back to the house and looked at the panel and sure as hell, it was tandem breakers in the wrong places and the panel was too full for expansion. So, I told her that I was positive I was right and she then called the electrician back again and ONCE again, told he I was wrong. Needless to say she was fuming mad.

I then returned to the house, took a picture of the legend, called the manufacture and got the name and phone number of the technical representative and typed up a mini report and sent it to the client and the electrician.

$2200 she has a new panel installed. Not real happy about it when its on a house she was selling. But now, she knows that I do not call stuff out for the heck of it and guess what she tells people now? This guy knows more than _____ the electrical contractor.

Stick to your guns, find the appropriate documentation to back up your findings and then present them in a professional manner. It's actually great marketing.



Comprehensive Building Consultants
Naples Home Inspection, Naples Mold Inspection, Naples Radon Inspection, Bonita Springs Home Inspection, Bonita Springs Mold Inspection, Bonita Springs Radon Inspection.



Donate here:

or send checks to the
Fl Home and Insurance Inspector Chapter
1103 W Hibiscus Blvd Ste 311
Melbourne, Fl 32901
Reply With Quote
  #27  
Old 5/16/11, 9:21 PM
John Gromkoski's Avatar
John Gromkoski John Gromkoski is online now
InterNACHI Member
 
Join Date: Apr 2007
Location: Staten Island, NY
Posts: 608
Default Re: Neutral bus bar

Quote:
Originally Posted by wwarner View Post
Thanks. I like that the explanation of the potential issue is included.




774 Manor Road
Staten Island, NY 10314
718-514-3393
Reply With Quote
  #28  
Old 5/17/11, 12:31 PM
George P. Wells, CMI's Avatar
George P. Wells, CMI George P. Wells, CMI is offline
InterNACHI Member
 
Join Date: Oct 2004
Location: Michigan
Posts: 554
Send a message via Skype™ to gwells
Default Re: Neutral bus bar

Quote:
Originally Posted by Robert Meier View Post
That document reiterates the fact that this requirement was in existence prior to it being added to the NEC code language in 2002. I'm guessing that it was installation practice was common place because no one was really enforcing it prior to them adding the words directly in the NEC.
I did my apprenticeship under the 1971 and 1975 editions of the NEC. We were not trained to do things to code minimums (for that matter, my instructors put considerable effort into shifting the emphasis away from codes in favor of understanding how electrical systems work). It was already well known in the early 1970s that loss-of-neutral was a problem in the electrical construction industry. In the areas where I worked (mostly Ohio, Michigan, Indiana, Illinois, Kansas and Missouri), the practice was discouraged, if not outright prohibited.

It did many loss-of-neutral service calls in my electrician days but never really thought all that much about the magnitude of the problem. I have developed some strong opinions on some things in the electrical industry since I started doing electrical fire investigations 11 years ago. It wasn't until then that I realized how many fires are caused by a loss-of-neutral. I know I sound like I am on a continuous rant about loss-of-neutral but when you go into a home and see that a family has lost everything over a loose screw, it has an effect.



BestInspectors.Net
& Real Estate Training Academy

Inspection Report Software for
Windows - iOS - Mac - Android

Continuing Education
Home and Commercial Building Inspection - Skilled Trades – Real Estate – Appraisal – NFPA 921

http://www.bestinspectors.net

est. 1992

Last edited by gwells; 5/17/11 at 12:36 PM..
Reply With Quote
Need a home inspection in Pennsylvania? Check out InterNACHI's listing of Pennsylvania certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #29  
Old 5/18/11, 8:46 PM
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,072
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Neutral bus bar

FYI - As a consultant to a leading manufacturer of panelboards, enclosures and what have you. I spoke with one of their leading engineers many times on this issue. They (as I have always agreed) stated that UL 67 standards and their specifications have always stated that EGC's (Equipment Grounding Conductors) can have multiple conductors (of the same size) under a single terminal on the buss in accordance with the listing posted in the panelboard enclosure. They never intended for grounded (neutral conductors for most all of your typical home inspector situations) conductors to be doubled up since they never specifically gave permission for that...only the EGC's as identified.

So low and behold the confusion began because how many electricians have a UL White Book Handy ( I do....they sent me 20 of them for my inspectors to have....ask they will send you one also...has some GREAT INFO in them ) so finally in the 2002 National Electrical Code it emerged and people thought it came out of left field but in reality it was there all along under little ole' 110.3(B) and the UL White Book.

Ok....brief stay...I am OFF to other things....Nite Nite folks!



Paul W. Abernathy
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
"UFER" Ground? see last paragraph. jtedesco1 Electrical Inspections 19 8/23/11 3:56 PM
What's this video worth? jtedesco1 Inspection Education & Training 5 4/18/08 9:24 AM
Metal Rigid or PVC Rigid what is code bpotts Electrical Inspections 5 12/4/06 2:40 PM
Ground wire in neutral bar, neutral to breaker, hot to ground? rmc3inspection Electrical Inspections 4 8/1/06 9:44 AM
Proposed Definition of Neutral Conductor and Point jtedesco1 Electrical Inspections 1 4/22/06 10:19 AM


All times are GMT -4. The time now is 7:52 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts