Default Neutral wires at main service disconnect

Newer SD 200 amp main service panel. Most of the grounded & grounding conductors were installed appropriately on the bus bars. However there were two isolated (bonded to panel) bus bars on both sides, with a few grounded & grounding conductors installed there. Now, I know the grounds are o.k. here, but what about the neutral wires and/or grounded conductors? Do the neutral wires need to be installed at the main neutral bus bar(s)?

Thanks in advance.
Attached Thumbnails
neutral-wires-main-service-disconnect-img_0054.jpg  
Reply With Quote
Need a home inspection in Maryland? Check out InterNACHI's listing of Maryland certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #2  
Old 9/10/11, 8:59 AM
Larry D. Kage Larry D. Kage is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Lake Ann (Traverse City), MI
Posts: 8,848
Default Re: Neutral wires at main service disconnect

Quote:
Originally Posted by jfrederick View Post
Newer SD 200 amp main service panel. Most of the grounded & grounding conductors were installed appropriately on the bus bars. However there were two isolated (bonded to panel) bus bars on both sides, with a few grounded & grounding conductors installed there. Now, I know the grounds are o.k. here, but what about the neutral wires and/or grounded conductors? Do the neutral wires need to be installed at the main neutral bus bar(s)?

Thanks in advance.
The grounded and grounding wires should be bonded at the service disconnect anyway...



InterNachi Awards Portal: http://co.nachi.org/inachiawards/

____________________________________________
"An Education, not just an Inspection"

Larry Kage, CMI
Lake Ann (Traverse City), Michigan 49650
231 929 3525


Professional Inspector serving the Traverse City, Michigan area and beyond.
Reply With Quote
  #3  
Old 9/10/11, 9:06 AM
Robert Meier's Avatar
Robert Meier Robert Meier is online now
Active Poster
 
Join Date: Feb 2010
Location: New Jersey
Posts: 1,250
Please Note: Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Neutral wires at main service disconnect

Those neutrals conductors are not permitted on the EGC bus even in a service panel as shown in that photo. I see a main breaker, is this the service disconnect?

Quote:
200.2 General.
(B) Continuity. The continuity of a grounded conductor shall not depend on a connection to a metallic enclosure, raceway, or cable armor.
Reply With Quote
  #4  
Old 9/10/11, 9:07 AM
Joshua L. Frederick Joshua L. Frederick is offline
InterNACHI Member
 
Join Date: Jan 2007
Location: Defiance, OH
Posts: 832
Send a message via AIM to jfrederick
Default Re: Neutral wires at main service disconnect

Thanks Robert, just wanted to confirm.
Reply With Quote
  #5  
Old 9/10/11, 9:09 AM
Jim Port Jim Port is offline
Unmoderated Guest
 
Join Date: Jul 2007
Location: Maryland
Posts: 805
Please Note: Jim Port is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Neutral wires at main service disconnect

Quote:
Originally Posted by lkage View Post
The grounded and grounding wires should be bonded at the service disconnect anyway...
The problem is that you now have return current on the metallic enclosure where you should not. RM has posted the code prohibition below.
Reply With Quote
  #6  
Old 9/10/11, 9:19 AM
Larry D. Kage Larry D. Kage is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Lake Ann (Traverse City), MI
Posts: 8,848
Default Re: Neutral wires at main service disconnect

Quote:
Originally Posted by Jim Port View Post
The problem is that you now have return current on the metallic enclosure where you should not. RM has posted the code prohibition below.
Please help me out. Isn't that a bonding screw at the bottom of the grounded conductor bus bar?



InterNachi Awards Portal: http://co.nachi.org/inachiawards/

____________________________________________
"An Education, not just an Inspection"

Larry Kage, CMI
Lake Ann (Traverse City), Michigan 49650
231 929 3525


Professional Inspector serving the Traverse City, Michigan area and beyond.
Reply With Quote
  #7  
Old 9/10/11, 9:32 AM
Jim Port Jim Port is offline
Unmoderated Guest
 
Join Date: Jul 2007
Location: Maryland
Posts: 805
Please Note: Jim Port is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Neutral wires at main service disconnect

That is a lug for a larger conductor. The bond screw on that Square D panel is out of the pic. It is a green domed head screw near the main breaker.

As it is now the neutral current will flow across the enclosure to the bond screw and then through the neutral buss and then out to the transformer.
Reply With Quote
  #8  
Old 9/10/11, 9:36 AM
Larry D. Kage Larry D. Kage is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Lake Ann (Traverse City), MI
Posts: 8,848
Default Re: Neutral wires at main service disconnect

Quote:
Originally Posted by Jim Port View Post
As it is now the neutral current will flow across the enclosure to the bond screw and then through the neutral buss and then out to the transformer.
Thanks for the help.



InterNachi Awards Portal: http://co.nachi.org/inachiawards/

____________________________________________
"An Education, not just an Inspection"

Larry Kage, CMI
Lake Ann (Traverse City), Michigan 49650
231 929 3525


Professional Inspector serving the Traverse City, Michigan area and beyond.
Reply With Quote
  #9  
Old 9/15/11, 9:40 PM
ROBERT V. YOUNG's Avatar
ROBERT V. YOUNG ROBERT V. YOUNG is offline
InterNACHI Member
 
Join Date: Mar 2010
Location: Montreal.
Posts: 5,055
Default Re: Neutral wires at main service disconnect

Quote:
Originally Posted by Jim Port View Post
That is a lug for a larger conductor. The bond screw on that Square D panel is out of the pic. It is a green domed head screw near the main breaker.

As it is now the neutral current will flow across the enclosure to the bond screw and then through the neutral buss and then out to the transformer.
Alwaysa green doomed or green screw that is sized to fit only that thread on the panel. Will not fit any other entry.
Am I correct in my statement Jim.



montrealbuildinginspectionservice.com
montreal-home-inspection-services.com
home-inspections-montreal.com
homeinspectionsservicesmontreal.com
ROBERT YOUNG'S MONTREAL HOME INSPECTION SERVICE INC.
Certified Inspecteur Professionnel Certifié en Bâtiment membre de InterNACHI ACHI , Chapters - OntarioAchi et du M.I.C.Q (CPI) - (CHI)
OFFICE (514) 489-1887 MOBILE (514) 441-3732 TOLL FREE 1- 855-819-1816
Reply With Quote
  #10  
Old 9/15/11, 10:26 PM
Jim Port Jim Port is offline
Unmoderated Guest
 
Join Date: Jul 2007
Location: Maryland
Posts: 805
Please Note: Jim Port is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Neutral wires at main service disconnect

The domed screw is just for the Square D. The correct location is shown on the panel label.

IIRC Cutler-Hammer Classic uses a bond strap into the buss.
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
"UFER" Ground? see last paragraph. jtedesco1 Electrical Inspections 19 8/23/11 3:56 PM
Main Disconnect missing verbage & cut main wire rwashington Electrical Inspections 19 1/16/11 2:07 PM
Main panel without...Main Disconnect, need help dnasser Electrical Inspections 8 10/4/10 11:34 PM
Main Panel vs Sub-Panel and main disconnect? rbassett Electrical Inspections 11 10/24/09 6:16 PM


All times are GMT -4. The time now is 7:53 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts