Can having two or more neutrals on the same lug feed the other circuits that are on the same buss? I know the hazards of a multi circuit installation but what about a single circuit sharing the same lug for the their neutrals?
"I have not failed, I have just found a 1000's way's that didn't work" Thomas Edison www.newbeginningshomeinspection.com |
|
#2
|
||||
|
||||
|
If I understand your question(s) Mike Holt 408.21 grounded conductor termination commentary and video discussion
gone for the day, I'll see if I passed later badair ADAIR INSPECTION 972-487-5634 Residential-Commercial-Construction-EIFS-Infrared Thermography TREC # 4563 EDI: EIFS-MA TX # 39 2008 US Member of the Year life is the random lottery of events followed by numerous narrow escapes...accept the good |
|
#3
|
|||
|
|||
|
Please Note:
Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
As long as all of the screws are tight there really isn't a problem. The hazard arises when you want to work on one of those circuits and the other one remains energized. When you loosen that connection you can find yourself holding a white conductor with 120v on it.
|
|
#4
|
||||
|
||||
|
Greg
What makes the difference then that all the neutrals are by themselves, own lug, but on the same buss? Wouldn't that be the samething as sharing the same lug? "I have not failed, I have just found a 1000's way's that didn't work" Thomas Edison www.newbeginningshomeinspection.com |
|
#5
|
||||
|
||||
|
Quote:
|
|
#6
|
|||
|
|||
|
Please Note:
Jim Port is a non-member guest and is in no way affiliated with InterNACHI or its members.
The buss is rated for the current. The current carried by the neutrals is trying to get back to the source. It is not going back out of the panel on other branch circuit wires.
|
|
#7
|
|||
|
|||
|
Please Note:
Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
The problem is only when you are working on the circuits. If I am working on circuit "A" I would trip the "A" breaker and feel pretty safe but if it was double lugged with "B" and I open up that lug I could see full circuit current on the "B" neutral. If everyone was "qualified" and understood white wires are not always ground it wouldn't really be a problem. Alas the NEC has started assuming unqualified people are going to be working on the wiring.
|
|
#8
|
|||
|
|||
|
Please Note:
jkogel is a non-member guest and is in no way affiliated with InterNACHI or its members.
Isn't the intent of the rule simply to get the best possible connection, one wire, one lug?
Besides, if they allowed two, Sparky would jam three in there. John Kogel www.allsafehome.ca |
|
#9
|
|||
|
|||
|
Please Note:
Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
Most ground buses are listed for 3 EGC wires. The don't seem to have a problem with those connections. If you look at the geometry 3 is probably as good as one. They would all wedge themselves into a tight configuration
|
![]() |
| Thread Tools | |
|
|
Similar Threads
|
||||
| Thread | Thread Starter | Forum | Replies | Last Post |
| Shared neutrals | Ian Gills | Electrical | 17 | 1/8/08 1:22 AM |
| Electrician signs off 'ganged neutrals'...now what? | mgault | Electrical | 16 | 6/3/07 12:09 AM |
| Double lugged neutrals | lschmid | Electrical | 14 | 8/11/06 10:11 AM |
| grounds and neutrals | nbhi | Electrical | 4 | 4/5/06 12:14 AM |
| Double lugging neutrals? | JohnH515 | Electrical | 17 | 3/3/06 11:05 AM |