Default Neutrals and Grounds

I understand that the ground bar may be part of the neutral bar, but when are they required to be seperate?

Thanks

Erol Kartal
Reply With Quote
  #2  
Old 9/30/07, 12:48 PM
Greg Fretwell Greg Fretwell is offline
Active Poster
 
Join Date: Jul 2004
Location: Estero Florida
Posts: 1,798
Please Note: Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Neutrals and Grounds

They must be separated anywhere down stream of the cabinet with the service disconnect (and connection to the ground electrode).
Reply With Quote
  #3  
Old 10/1/07, 5:10 PM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,047
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Neutrals and Grounds

visit www.theelectricalguru.com/GandB.pps



Paul W. Abernathy,CMI,CPI,CME
National Electrical Code Expert
Electrical & Fire Protection Systems Code Supervisor- Alexandria,VA
Weekly Live Radio Show :http://en.1000mikes.com/show/the_electrical_guru
Weekly Chat on Wednesdays -7:30 PM E.S.T
* Get my 13 hour commentary audio CD for the book "How to Perform Electrical Inspections"

2007 InterNACHI Member of the Year
Reply With Quote
  #4  
Old 10/1/07, 5:12 PM
ekartal6 ekartal6 is offline
Active Poster
 
Join Date: Oct 2006
Location: Schaumburg, IL
Posts: 1,094
Please Note: ekartal6 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Neutrals and Grounds

Thank you Greg and Paul.
Reply With Quote
  #5  
Old 10/2/07, 11:46 AM
Frank P. Newman Frank P. Newman is offline
InterNACHI Member
 
Join Date: Aug 2007
Location: Dublin, GA
Posts: 668
Default Re: Neutrals and Grounds

Paul: Here is a question that has come to mind. If the connection to the sub panel is not in conduit, and if the sub panel is itself non-metallic, do the same (or other) hazards exist if the sub panel neutral and grounding terminals are connected?



Frank P. Newman
Emerald City Inspections, LLC
Dublin, GA
Reply With Quote
  #6  
Old 10/2/07, 1:43 PM
Greg Fretwell Greg Fretwell is offline
Active Poster
 
Join Date: Jul 2004
Location: Estero Florida
Posts: 1,798
Please Note: Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Neutrals and Grounds

You are still carrying circuit current over the grounding conductor and voltage will be applied to that conductor at the load end. That can result in a "tingle" voltage if you are sitting on a conductive floor or dirt, using a metal cased tool. That also will not trip the GFCI since the fault path is via the grounding conductor.
Reply With Quote
  #7  
Old 10/4/07, 11:32 AM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,047
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Neutrals and Grounds

Thanks Greg for taking that one.....I did not come online yesterday as I am in more pain than I expected at this point in my recovery....thanks again.



Paul W. Abernathy,CMI,CPI,CME
National Electrical Code Expert
Electrical & Fire Protection Systems Code Supervisor- Alexandria,VA
Weekly Live Radio Show :http://en.1000mikes.com/show/the_electrical_guru
Weekly Chat on Wednesdays -7:30 PM E.S.T
* Get my 13 hour commentary audio CD for the book "How to Perform Electrical Inspections"

2007 InterNACHI Member of the Year
Reply With Quote
  #8  
Old 10/4/07, 3:52 PM
Frank P. Newman Frank P. Newman is offline
InterNACHI Member
 
Join Date: Aug 2007
Location: Dublin, GA
Posts: 668
Default Re: Neutrals and Grounds

Interesting - since I know where such a subpanel exists (100A on a second floor). I think I will go see if I can measure any voltage between the neutral/ground and a nearby copper water pipe.

Second question - which revision of the NEC provided that subpanel neutral and ground busses be separate? In other words, would you expect to see 3-wire feeders in homes older than a certain age?



Frank P. Newman
Emerald City Inspections, LLC
Dublin, GA
Reply With Quote
  #9  
Old 10/8/07, 10:06 AM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,047
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Neutrals and Grounds

Frank,
Remember they are connected back at the main panel, the intent of the seperation at the " remote distribution panel " to remove parallel paths and potential objectional currents in the system.

If you remember back in 1996 I believe the 3 wire installation to Ranges and Dryers was nixed.....and so on...the only exception that allows the use of 3 wires for this installation ( ie: sub-panel ) is 250.32(B)(2) which for your FYI is finally removed and not allowed on new installations when the 2008 NEC is adopted in your area....until then if the electrician can meet the requirements of 250.32(B)(2) then to detached buildings the 3 wire allowance will be allowed.....

Now....I dont now any dates because I am not a NEC Historian...I only stay up to date on cycles I teach....1999-2008 NEC....but you will see it in older and newer installs simply because of ignorance....nothing more.



Paul W. Abernathy,CMI,CPI,CME
National Electrical Code Expert
Electrical & Fire Protection Systems Code Supervisor- Alexandria,VA
Weekly Live Radio Show :http://en.1000mikes.com/show/the_electrical_guru
Weekly Chat on Wednesdays -7:30 PM E.S.T
* Get my 13 hour commentary audio CD for the book "How to Perform Electrical Inspections"

2007 InterNACHI Member of the Year
Reply With Quote
  #10  
Old 10/8/07, 12:42 PM
Greg Fretwell Greg Fretwell is offline
Active Poster
 
Join Date: Jul 2004
Location: Estero Florida
Posts: 1,798
Please Note: Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Neutrals and Grounds

I think the idea of not regrounding the neutral is as old as the NEC but the exception for the ranges came during WWII.
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
"UFER" Ground? see last paragraph. jtedesco1 Electrical Inspections 19 8/23/11 4:56 PM
Stray Voltage can kill rcooke Electrical Inspections 24 10/26/07 12:40 PM
Electrician signs off 'ganged neutrals'...now what? mgault Electrical Inspections 16 6/3/07 12:09 AM
Multiple grounds gmathias Electrical Inspections 11 4/30/07 2:49 PM
grounds and neutrals nbhi Electrical Inspections 4 4/5/06 12:14 AM


All times are GMT -4. The time now is 9:58 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts