Default What New (2002 NEC) and existing rules are being violated here?



I have been failing jobs for this under 110-3. The job has to be installed as per the manufactures instructions. Most manufactures only allow 1 neutral wire per terminal. I am glad that it is finally written under another code section that can be written up for. I once looked inside an old service panel and wondered who left a small red light on inside this panel. Imagine my surprise when I found out that the red light was really a neutral conductor glowing red hot. It was doubled up under a screw terminal and they were both very loose.

The UL product standard for panelboards has not permitted more than one neutral under a single screw for a long time. It does still permit in some cases more than one EGC under the same screw, but not neutrals. The rule has been enforceable under 110-3(B) but was added in Article 408 to make it very clear and to make sure that more installers are aware of the requirement.

Panels that are in compliance with the UL product standard for Panelboards are required to have one neutral termination space for each breaker space. They are not required to have an EGC terminal bar and most of the time, in a new panel, where neutrals are doubled up, it is because the contractor used the neutral bar for EGCs. This in itself is not a violation at the service panel, but it becomes a violation when you double up a neutral.

Last edited by jtedesco1; 1/8/08 at 7:37 AM.. Reason: Increase size of picture
Reply With Quote
  #2  
Old 1/8/08, 4:33 AM
Larry D. Kage Larry D. Kage is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Lake Ann (Traverse City), MI
Posts: 5,730
Default Re: What New (2002 NEC) and existing rules are being violated here?

[quote= I once looked inside an old service panel and wondered who left a small red light on inside this panel. Imagine my surprise when I found out that the red light was really a neutral conductor glowing red hot. It was doubled up under a screw terminal and they were both very loose.[/quote]

You done good, Joe...



____________________________________________
"An Education, not just an Inspection"

Larry Kage
Lake Ann (Traverse City), Michigan 49650
231 929 3525


Professional Inspector and Infrared Thermographer serving the Traverse City, Michigan area and beyond.


ITC/FLIR CERTIFIED BUILDING SCIENCES THERMOGRAPHER

ITC/FLIR CERTIFIED LEVEL 1 THERMOGRAPHER
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On



All times are GMT -4. The time now is 10:13 AM.


Copyright © International Association of Certified Home Inspectors, Inc. 1 2 3 4 5 6 7 8 9 10 11 12 13 14 15 16 17 18 19 20 21 22 23 24 25 26 27 28 29 30 31 32 33 34 35 36 37 38 39 40 41 42 43 44 45 46 47 48 49 50 51 52 53 54 55 56 57 58 59 60 61 62 63 64 65 66 67 68 69 70 71 72 73 74 75 76 77 78 79 80 81 82 83 84 85 86 87 88 89 90 91 92 93 94 95 96 97 98 99 100 101 102 103 104 105 106 107 108 109 110 111 112 113 114 115 116 117 118 119 120 121 122 123 124 125 126 127 128 129 130 131 132 133 134 135 136 137 138 139 140 141 142 143 144 145 146 147

Popular Sections

:

All Sections

Popular

Membership

Inspection Standards

Education

Chapters & Members

Articles & Links

Other Organizations

 

 

 

NACHI.ORG Statistics

 

 

no new posts