Default New Build/Gas line ground

Is it required in new builds to ground the gas line? There was no CSST piping and I always thought you bonded the gas line but this was connected to a rod in the floor.

Not the best pic in the world but you can see the connection at the gas line, the one on the floor I missed in my pic, maybe I should hire a professional photographer.
Attached Thumbnails
new-build-gas-line-ground-198011-017-small-.jpg.JPG
Views:	135
Size:	23.8 KB
ID:	49696  



Performing Home Inspections in Cleveland, Strongsville, Brecksville, Broadview Heights, North Royalton, Parma and surrounding areas.
Reply With Quote
Need a home inspection in Utah? Check out InterNACHI's listing of Utah certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #2  
Old 11/12/11, 7:53 AM
Joseph M. Whitt Joseph M. Whitt is offline
InterNACHI Member
 
Join Date: Oct 2008
Location: NC
Posts: 123
Default Re: New Build/Gas line ground

In 250.104(B) we are told that gas piping is to be bonded but it allows this bonding to be done as follows:
The equipment grounding conductor for the circuit that is likely to energize the piping shall be permitted to serve as the bonding means. The points of attachment of the bonding jumper(s) shall be accessible.

Should there be some sort of flexible connection of the gas line to an appliance then the installation instructions of the flexible pipe could mandate the bonding of the gas pipe with a bonding jumper of #6 or larger.



Mike Whitt
Contractor/Instructor
Reply With Quote
  #3  
Old 11/12/11, 10:48 AM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,057
Default Re: New Build/Gas line ground

Quote:
Originally Posted by dmacy View Post
Is it required in new builds to ground the gas line? There was no CSST piping and I always thought you bonded the gas line but this was connected to a rod in the floor.
Bonding is required in most jurisdictions, you are correct. The bonding connects the piping to the grounding electrode, which essentially means that the piping is "grounded."

It is a prohibited practice to use the gas piping as the grounding electrode and/or the grounding electrode conductor for the electrical system.

In other words, the gas piping cannot be used as the primary connection from the electrical panel to the ground-rod, and the gas piping cannot be used as the system ground.

So, as long as the rod you spoke of is connected to the electrical panel with a separate conductor, your picture is of the required bonding for the gas piping.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #4  
Old 11/12/11, 11:43 AM
Robert Meier's Avatar
Robert Meier Robert Meier is online now
Active Poster
 
Join Date: Feb 2010
Location: New Jersey
Posts: 1,250
Please Note: Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: New Build/Gas line ground

I agree with Mike. The gas pipe is permitted to be bonded by the EGC in the gas appliance circuit. The bond in the photo is permitted but not required.
Reply With Quote
  #5  
Old 11/12/11, 2:09 PM
David C. Macy's Avatar
David C. Macy David C. Macy is online now
InterNACHI Member
 
Join Date: Jan 2004
Location: NE. OH
Posts: 2,658
Default Re: New Build/Gas line ground

Thanks for the professional responses and information.



Performing Home Inspections in Cleveland, Strongsville, Brecksville, Broadview Heights, North Royalton, Parma and surrounding areas.
Reply With Quote
  #6  
Old 11/15/11, 9:43 PM
Robert J. OConnor's Avatar
Robert J. OConnor Robert J. OConnor is offline
InterNACHI Member
 
Join Date: Jul 2003
Location: Long Island, NY
Posts: 1,288
Default Re: New Build/Gas line ground

Quote:
Originally Posted by dmacy View Post
Is it required in new builds to ground the gas line? There was no CSST piping and I always thought you bonded the gas line but this was connected to a rod in the floor.
I agree with Jeff. There should not just be a wire from the gas piping to the ground rod. Are you sure there weren't separate wires from the gas piping and the ground rod to the panel?



Robert O'Connor, PE
Consulting Engineer & Inspector
LIU CW Post Adjunct Professor
NACHI Education Committee
www.reporthost.com/-rjo

I am absolutely amazed sometimes by how much thought goes into doing things wrong ...
Reply With Quote
  #7  
Old 11/16/11, 7:14 AM
Jim Port Jim Port is offline
Unmoderated Guest
 
Join Date: Jul 2007
Location: Maryland
Posts: 805
Please Note: Jim Port is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: New Build/Gas line ground

Quote:
Originally Posted by roconnor View Post
I agree with Jeff. There should not just be a wire from the gas piping to the ground rod. Are you sure there weren't separate wires from the gas piping and the ground rod to the panel?
What if the conductor was coming from a Ufer or rod and happened to bond the gas line on the way to the panel?
Reply With Quote
  #8  
Old 11/16/11, 7:47 AM
Mike Whitt's Avatar
Mike Whitt Mike Whitt is offline
Unmoderated Guest
 
Join Date: Sep 2005
Location: North Carolina
Posts: 477
Please Note: Mike Whitt is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: New Build/Gas line ground

The NEC says;

shall be bonded to the service equipment enclosure, the grounded conductor at the service, the grounding electrode conductor where of sufficient size,
or the one or more grounding electrodes used.

It would be fine to bond the gas pipe to one of the grounding electrodes
Reply With Quote
  #9  
Old 11/16/11, 10:22 AM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,057
Default Re: New Build/Gas line ground

Quote:
Originally Posted by Jim Port View Post
What if the conductor was coming from a Ufer or rod and happened to bond the gas line on the way to the panel?
A continuous conductor from the GE to the panel, also attached to the gas line?

Sounds acceptable to me...



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #10  
Old 11/16/11, 3:39 PM
Robert Meier's Avatar
Robert Meier Robert Meier is online now
Active Poster
 
Join Date: Feb 2010
Location: New Jersey
Posts: 1,250
Please Note: Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: New Build/Gas line ground

I'm somewhat surprised that this new building doesn't have a concrete encased electrode. It's also rather odd that the ground rod is sticking up through the slab. Unless it was 10' rod it would would not have 8' in contact with the earth as required. Is the GEC connection definitely to a ground rod? I was thinking that maybe it was a turned up piece of rebar from the CEE.

Since the gas piping is not an electrode then the connection to it woild need to be unbroken if the GEC continues onto the actual electrode.
Reply With Quote
  #11  
Old 11/21/11, 3:49 PM
Mike Parks's Avatar
Mike Parks Mike Parks is offline
Active Poster
 
Join Date: Oct 2003
Location: Columbus Ohio
Posts: 152
Please Note: Mike Parks is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: New Build/Gas line ground

Dave if you are inspecting the electrical connections on a new build you are in violation of Ohio law. May I please see your certificate as per 3783 ORC. I am formally asking you for this.
Reply With Quote
  #12  
Old 11/22/11, 2:36 PM
David C. Macy's Avatar
David C. Macy David C. Macy is online now
InterNACHI Member
 
Join Date: Jan 2004
Location: NE. OH
Posts: 2,658
Default Re: New Build/Gas line ground

Mike I take it you are looking for a sticker like this but with a 2009 date on it?
I can not provide one as I am not licensed or State certified.

I was hired to perform a general inspection for my client, not a code inspection. No license requirements in state of Ohio for performing a general inspection. The picture for this post was inquiring on proper electrical practices for a gas line connection.
Attached Thumbnails
new-build-gas-line-ground-198811-021-small-.jpg.JPG
Views:	23
Size:	33.1 KB
ID:	50002  



Performing Home Inspections in Cleveland, Strongsville, Brecksville, Broadview Heights, North Royalton, Parma and surrounding areas.
Reply With Quote
  #13  
Old 11/22/11, 6:31 PM
Sean Fogarty's Avatar
Sean Fogarty Sean Fogarty is offline
InterNACHI Member
 
Join Date: Sep 2009
Location: Somewhere in Knoxville TN flipping breakers
Posts: 2,267
Default Re: New Build/Gas line ground

Quote:
Originally Posted by Mike Parks View Post
Dave if you are inspecting the electrical connections on a new build you are in violation of Ohio law. May I please see your certificate as per 3783 ORC. I am formally asking you for this.
Mike are you a douche to everyone or just Ohio inspectors?

Can I see your license?

This is a place to ask questions and learn. If you are not going to contribute then you may consider going somewhere else.




Infraspection Institute Level 1 Certified Infrared Thermographer

Fogarty Inspection Services Group of Knoxville TN

Home inspections, Commercial Inspections, Thermal Imaging, Mold, Enviromental Testing and Radon Testing for Knoxville TN, Oak Ridge TN, Maryville, Clinton, Farragut, Lenoir City, Pigeon Forge, Sevierville and all the surrounding areas.

865-256-5397

www.homeinspectorknoxville.com

www.moldandradon.com

www.thermal-inspection.net

www.commercial-building-inspector.net
Reply With Quote
Need a home inspection in Utah? Check out InterNACHI's listing of Utah certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #14  
Old 11/22/11, 7:13 PM
Robert Meier's Avatar
Robert Meier Robert Meier is online now
Active Poster
 
Join Date: Feb 2010
Location: New Jersey
Posts: 1,250
Please Note: Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: New Build/Gas line ground

Quote:
Originally Posted by sfogarty View Post
Mike are you a douche to everyone or just Ohio inspectors?

Can I see your license?

This is a place to ask questions and learn. If you are not going to contribute then you may consider going somewhere else.
Touche'.
Reply With Quote
  #15  
Old 11/24/11, 9:37 AM
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,072
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: New Build/Gas line ground

Quote:
Originally Posted by sfogarty View Post
Mike are you a douche to everyone or just Ohio inspectors?

Can I see your license?

This is a place to ask questions and learn. If you are not going to contribute then you may consider going somewhere else.
Agreed...I am not licensed in OHIO.....but I bet the OHIO board can't stop me from looking at them and commenting on them........Mr. Parks....Please turn me in to the OHIO board for helping people understand how to inspect them....I will laugh at the board.



Paul W. Abernathy
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
new ground bar kit Mike Kasper Electrical Inspections 12 12/1/08 10:12 PM
980 Questions/Answers to the NHIE....Free! jbushart Legislation, Licensing & Legal Issues for Inspectors 50 4/20/08 1:26 AM
Ground Wires Inside a Panel mveitenhans Electrical Inspections 13 10/29/06 11:39 AM
Ground at a Gas Line jpope Electrical Inspections 4 1/17/06 5:45 AM