Default New construction

Inspected a house yesterday - the kitchen has 2 GFCI outlets - one of the won't reset without resetting the other outlet - can they be tied together?
Reply With Quote
Need a home inspection in New Jersey? Check out InterNACHI's listing of New Jersey certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #2  
Old 1/30/11, 9:56 AM
Jim Port Jim Port is offline
Unmoderated Guest
 
Join Date: Jul 2007
Location: Maryland
Posts: 805
Please Note: Jim Port is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: New construction

You can install multiple GFIs on the same circuit, but if wired properly there is no need. Downstream receptacles can be regual duplexes if wired from the LOAD terminals on the upstream GFI. You could also just use the LINE terminals and make each receptacle a GFI. That way if it trips it is near the point of use and you do not need to look elsewhere.

Did the kitchen have another 20 amp small appliance branch circuit?
Reply With Quote
  #3  
Old 1/30/11, 10:08 AM
Jack Tanner Jack Tanner is offline
InterNACHI Member
 
Join Date: Aug 2009
Posts: 11
Default Re: New construction

The other strange thing is when I tested the upstairs bathrooms - they tripped but I couldn't find a reset anywhere in the house or panel - thoughts?
Reply With Quote
  #4  
Old 1/30/11, 10:10 AM
Greg Bell's Avatar
Greg Bell Greg Bell is offline
InterNACHI Member
 
Join Date: Oct 2002
Location: Titusville, FL
Posts: 4,155
Default Re: New construction

Quote:
Originally Posted by jtanner View Post
The other strange thing is when I tested the upstairs bathrooms - they tripped but I couldn't find a reset anywhere in the house or panel - thoughts?
I have often found them to be connected to an exterior outlet.



Greg Bell
Titusville, Fl
02111507

Serving Central Florida
Reply With Quote
  #5  
Old 1/30/11, 10:12 AM
Jack Tanner Jack Tanner is offline
InterNACHI Member
 
Join Date: Aug 2009
Posts: 11
Default Re: New construction

Really - So if you trip one , you have to go outside to reset - that shouldn't be in code - saftey issues.
Reply With Quote
  #6  
Old 1/30/11, 10:14 AM
Jack Tanner Jack Tanner is offline
InterNACHI Member
 
Join Date: Aug 2009
Posts: 11
Default Re: New construction

Greg - the same house has a hipped roof and the truss run parallel to the wall - the sheathing is not flush with the truss - thoughts?
Reply With Quote
  #7  
Old 1/30/11, 10:24 AM
Curtis M. Vilt's Avatar
Curtis M. Vilt Curtis M. Vilt is offline
InterNACHI Member
 
Join Date: Mar 2010
Location: Palmetto Florida
Posts: 890
Default Re: New construction

Some GFCIs are in the garage for the bathroom outlets etc.. Just so they are present
Reply With Quote
  #8  
Old 1/30/11, 10:35 AM
Jim Port Jim Port is offline
Unmoderated Guest
 
Join Date: Jul 2007
Location: Maryland
Posts: 805
Please Note: Jim Port is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: New construction

Quote:
Some GFCIs are in the garage for the bathroom outlets etc.. Just so they are present
The OP stated new construction. Bathroom receptacle circuits have not been allowed to be shared outside of bathrooms for quite a few code cycles. Without looking back this probably changed back in the 90's.
Reply With Quote
  #9  
Old 1/30/11, 10:43 AM
Curtis M. Vilt's Avatar
Curtis M. Vilt Curtis M. Vilt is offline
InterNACHI Member
 
Join Date: Mar 2010
Location: Palmetto Florida
Posts: 890
Default Re: New construction

Jim my house is 1997 and when I built in the early 2000s they were shared. Down here I belive it was enforced mid 2000s ?
Reply With Quote
  #10  
Old 1/30/11, 11:40 AM
Brian A. MacNeish Brian A. MacNeish is offline
Banned
 
Join Date: Apr 2007
Location: CANADA
Posts: 4,638
Please Note: Brian A. MacNeish is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: New construction

Quote:
Originally Posted by Jim Port View Post
The OP stated new construction. Bathroom receptacle circuits have not been allowed to be shared outside of bathrooms for quite a few code cycles. Without looking back this probably changed back in the 90's.
In the 1987 Canadian Electrical Code (CEC- our model document), the receptacles for bathrooms/washrooms were split from other GFCI protected circuits. Prior to that point, the only requirements for CFCI protection were for exterior/bath/washroom receptacles and all (up to could be on the same GFCI protected circuit). The problem was that folks would wake up in the morning after heavy rains, wind or fog to find the circuit tripped by moisture at an exterior receptacle and no power at bath receptacles .
Reply With Quote
  #11  
Old 1/30/11, 11:43 AM
Curtis M. Vilt's Avatar
Curtis M. Vilt Curtis M. Vilt is offline
InterNACHI Member
 
Join Date: Mar 2010
Location: Palmetto Florida
Posts: 890
Default Re: New construction

problem was that folks would wake up in the morning after heavy rains, wind or fog to find the circuit tripped by moisture at an exterior receptacle and no power at bath receptacles .

That just happened at my house the GFCI is in the garage
Reply With Quote
  #12  
Old 1/30/11, 11:47 AM
Brian A. MacNeish Brian A. MacNeish is offline
Banned
 
Join Date: Apr 2007
Location: CANADA
Posts: 4,638
Please Note: Brian A. MacNeish is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: New construction

Quote:
Originally Posted by cvilt View Post
problem was that folks would wake up in the morning after heavy rains, wind or fog to find the circuit tripped by moisture at an exterior receptacle and no power at bath receptacles .

That just happened at my house the GFCI is in the garage
Where was the moisture from......... or some other type of nuisance trip?
Reply With Quote
  #13  
Old 1/30/11, 11:51 AM
Curtis M. Vilt's Avatar
Curtis M. Vilt Curtis M. Vilt is offline
InterNACHI Member
 
Join Date: Mar 2010
Location: Palmetto Florida
Posts: 890
Default Re: New construction

My wife has some lights on the Lanai with a timer. We had a blowing rain hit the outlet 4' under the OVH.
Reply With Quote
Need a home inspection in New Jersey? Check out InterNACHI's listing of New Jersey certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #14  
Old 1/30/11, 4:41 PM
Michael Larson's Avatar
Michael Larson Michael Larson is offline
InterNACHI Member
 
Join Date: May 2006
Location: Hudson, WI including the Twin Cities of MN
Posts: 32,090
Default Re: New construction

Quote:
Originally Posted by cvilt View Post
Some GFCIs are in the garage for the bathroom outlets etc.. Just so they are present
Yep.



You can argue with intelligent people but to argue with a mush head is like trying to grab fog-Thomas Sowell

Never underestimate the difficulty of changing false beliefs by facts. - Henry Rosovsky-Harvard

Michael Larson
Hudson, WI

Services provided in East MN and West WI

Reply With Quote
  #15  
Old 2/8/11, 10:44 PM
Andrew Nazir Andrew Nazir is offline
New User
 
Join Date: Feb 2011
Posts: 1
Please Note: Andrew Nazir is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: New construction

quite right, as its safer too to put all the connectors outside of home.
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Options in selecting materials for basement construction wdevries Canadian Inspectors 2 8/4/08 1:30 PM
Selected Electrical Incidents and Occurrences - First Quarter pabernathy Electrical Inspections 0 12/2/07 1:43 PM
IAC2 In new residential construction mcyr IAC2 Indoor Air Forum 0 10/9/07 6:45 PM