Default New construction questions

In a 2005/2006 new build do the nuetrals & ground need to be isolated?

Also is this a UFER gound by the meter. Is this a new requirement?
Attached Thumbnails
new-construction-questions-86706-garfield-017-small-.jpg.jpg
Views:	57
Size:	29.4 KB
ID:	7519   new-construction-questions-86706-garfield-014-small-.jpg.jpg
Views:	58
Size:	64.0 KB
ID:	7520   new-construction-questions-86706-garfield-015-small-.jpg.jpg
Views:	48
Size:	73.3 KB
ID:	7521  
Reply With Quote
  #2  
Old 12/5/06, 1:44 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 5,038
Default Re: New construction questions

This looks like the service equipment David. The grounds and neutrals are required to be bonded at the service equipment.

Generally speaking, grounding conductors are never "isolated." They are always bonded to their enclosures and/or equipment.

Neutrals are "isolated" at all points past the service equipment.

The rebar can be used for a Ufer, but there is no conductor attached. It looks like the water pipe is being used as the GE.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net

Last edited by jpope; 12/5/06 at 1:47 PM..
Reply With Quote
  #3  
Old 12/5/06, 1:49 PM
David C. Macy's Avatar
David C. Macy David C. Macy is offline
InterNACHI Member
 
Join Date: Jan 2004
Location: Broadview Hts., OH
Posts: 1,466
Default Re: New construction questions

Jeff

The home had an exterior ground rod & water line ground. I spoke with the builder & he stated that it was required for grounding purposes. It wasnt being utilized but there was no water meter installed and he stated it was for an option for the water company.

I didnt see the need for it as it had the other sources. I just questioned & he explained to me. This builder was very knowledgeable and was a pleasure to work with.

I thought I read about new construction that The ground & nuetrals should be seperated at the main as well. What you say makes sense.

Thanks
Reply With Quote
  #4  
Old 12/5/06, 1:57 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 5,038
Default Re: New construction questions

This is a "supplemental" grounding electrode. The ground rod is typically the primary, and the water pipe is the secondary. This is common in new construction where a ufer is not used.

The neutral is the grounded conductor (a current carrying conductor), which can only be (and must be) grounded at the service equipment. If it is grounded or bonded anywhere else, it can energize the component it is attached to. That is why it must remain "isolated."



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net
Reply With Quote
  #5  
Old 12/5/06, 4:37 PM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Harrisonburg, VA
Posts: 7,539
Send a message via AIM to pabernathy Send a message via MSN to pabernathy
Default Re: New construction questions

If they are under the 2005 NEC in your area and the UFER is their in plain sight then it would have to be used in this case because it is present....in new construction.....




Part III. Grounding Electrode System and Grounding Electrode Conductor


The words “if available” have been replaced with “are present.” The effect is that a concrete-encased electrode (Ufer) is always required for new construction, because it is present. However, a new exception adds clarity that a concrete-encased electrode [250.52(A)(3)] isn’t required for existing buildings or structures.
All grounding electrodes as described in 250.52(A)(1) through (A)(6) that are present at each building or structure must be bonded together to form the grounding electrode system. Figure 250-15

Ex: Concrete-encased electrodes are not required for existing buildings or structures where the conductive steel reinforcing bars aren’t accessible without disturbing the concrete.




Paul W. Abernathy,CMI,CEI,CEPE
NEC® Consultant/Columnist
www.twitter.com/ElectricalGuru

- ICC & IAEI Certified Electrical Inspector
- ICC & IAEI Certified Electrical Plans Examiner
- Look for my article in the Nov/Dec 2009 IAEI Magazine
- 2007 "Top Gun" Winner - Mike Holt Enterprises
" visit www.TheElectricalGuru.com Today !"

Reply With Quote
  #6  
Old 12/5/06, 5:08 PM
Speedy Petey Speedy Petey is offline
Active Poster
 
Join Date: Jul 2006
Posts: 1,294
Please Note: Speedy Petey is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: New construction questions

A metallic water pipe is regarded as the primary electrode. It must then be supplemented by a rod or other electrode.

Under NEC 2005, if there is ANY rebar a Ufer MUST be used, in sight or not. There is no distinction to it being burried in conctrete. This was the change from the word "available" and "present" Paul mentioned.
With a Ufer, there is NO requirement to "add" any other electrodes if they are not "present" at the installation.

For instance, at a home fed by a well with plastic pipe the ONLY electrode required is the Ufer (provided rebar is present). NO supplemental rod is required. This is good part about Ufers being mandatory.

For a home fed by a metallic water pipe, the water pipe IS the primary electrode, and the Ufer is the supplemental.
Reply With Quote
  #7  
Old 12/5/06, 5:17 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 5,038
Default Re: New construction questions

Well, it's almost 2007, in which case, CA will likely adopt the 2005 NEC. So, I guess it's time that I start getting familiar with this "new" code



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net
Reply With Quote
  #8  
Old 12/5/06, 5:18 PM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Harrisonburg, VA
Posts: 7,539
Send a message via AIM to pabernathy Send a message via MSN to pabernathy
Default Re: New construction questions

Me just LOVES a UFER ground........I sent out a letter to all the builders in my area to start installing them if available....I like EM...



Paul W. Abernathy,CMI,CEI,CEPE
NEC® Consultant/Columnist
www.twitter.com/ElectricalGuru

- ICC & IAEI Certified Electrical Inspector
- ICC & IAEI Certified Electrical Plans Examiner
- Look for my article in the Nov/Dec 2009 IAEI Magazine
- 2007 "Top Gun" Winner - Mike Holt Enterprises
" visit www.TheElectricalGuru.com Today !"

Reply With Quote
  #9  
Old 12/5/06, 5:19 PM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Harrisonburg, VA
Posts: 7,539
Send a message via AIM to pabernathy Send a message via MSN to pabernathy
Default Re: New construction questions

lol...Jeff....think about me here in VA....I do classes on 1999, 2002, 2005 and starting to get ready for 2008......sometimes I worry about my brain and when it will start to smoke.......

Heck...in VA...we just adopted 2002.....and it is now 2006.....so i figure will adopt 2005 at around 2009 and then 2008 in the year 2011.



Paul W. Abernathy,CMI,CEI,CEPE
NEC® Consultant/Columnist
www.twitter.com/ElectricalGuru

- ICC & IAEI Certified Electrical Inspector
- ICC & IAEI Certified Electrical Plans Examiner
- Look for my article in the Nov/Dec 2009 IAEI Magazine
- 2007 "Top Gun" Winner - Mike Holt Enterprises
" visit www.TheElectricalGuru.com Today !"

Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
IAC2 In new residential construction mcyr IAC2 Forum 0 10/9/07 7:45 PM
Extractd from the archives, Thanks Paul for this list! jtedesco1 Electrical 4 1/2/07 8:51 PM


All times are GMT -4. The time now is 3:11 AM.


Copyright © International Association of Certified Home Inspectors, Inc. 1 2 3 4 5 6 7 8 9 10 11 12 13 14 15 16 17 18 19 20 21 22 23 24 25 26 27 28 29 30 31 32 33 34 35 36 37 38 39 40 41 42 43 44 45 46 47 48 49 50 51 52 53 54 55 56 57 58 59 60 61 62 63 64 65 66 67 68 69 70 71 72 73 74 75 76 77 78 79 80 81 82 83 84 85 86 87 88 89 90 91 92 93 94 95 96 97 98 99 100 101 102 103 104 105 106 107 108 109 110 111 112 113 114 115 116 117 118 119 120 121 122 123 124 125 126 127 128 129 130 131 132 133 134 135 136 137 138 139 140 141 142 143 144 145 146 147

Popular Sections

:

All Sections

Popular

Membership

Inspection Standards

Education

Chapters & Members

Articles & Links

Other Organizations

 

 

 

NACHI.ORG Statistics

 

 

no new posts