This 103 year old home that was/is in the middle of an electrical upgrade. The home has been vacant for 18 months.

I wanted to ask the inspectors/electricians as if they were the ones that would be actually doing this job.

Now the home had 100 amp SEC. There is no A/C, stove or dryer electrical. It is all set up for gas so the load is somewhat minumal.

Why would they install an AFCI for the refrigerator? The orange wire is the one for the refrigerator as the walls are open. By the way they opened the walls between each stud to run the wiring. Not small holes I mean like large sections!

Why would they use armored cable when the application would of been easier to use romex? The application is at the attic floor that is being finished & the notched the sub floor but ran Armored cable?

They installed a 200 amp main but only have 100 amp SEC. Now since we dont do a load calc. If you were installing this system I would think 125 or 150 would be sufficient. What size SEC and main breaker would you install?

The kitchen only had 1 GFCI. 1-2 prong receptacle at the opposite wall and the AFCI for the designated receptacle for the refrigerator. Isnt it required that 2 20 amp circuits be installed for the kitchen?

Now at the main panel they installed what looks like a temporary panel but it was totally in the way and not supported properly. Why would the electrician install this extra panel.

I defferred the whole house to be reviewed for repairs and to have an itemized list by a licensed electrician. There was a lot of work that was done but a lot still needs to be done.

Another question. When doing a total update are the receptacles(outlets required to be at least 18 inches above the floor or can they still be installed at the baseboards?
Attached Thumbnails
new-old-94607-056-small-.jpg.jpg
Views:	59
Size:	52.5 KB
ID:	10446   new-old-94607-052-small-.jpg.jpg
Views:	53
Size:	70.9 KB
ID:	10447   new-old-94607-059-small-.jpg.jpg
Views:	52
Size:	59.2 KB
ID:	10448   new-old-94607-053-small-.jpg.jpg
Views:	56
Size:	60.6 KB
ID:	10449  

Last edited by dmacy; 4/1/07 at 12:39 PM..
Reply With Quote
  #2  
Old 4/1/07, 1:13 PM
Speedy Petey Speedy Petey is offline
Unmoderated Guest
 
Join Date: Jul 2006
Posts: 1,297
Please Note: Speedy Petey is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: New for old.

Where is the 200 amp main? I see a 100.

#10 for the refer? No idea. Waste of money and MUCH harder to work with.
AFCI? Again, a waste of $$ and the risk of nuisance tripping.

NO, there is NO code as to receptacle height. To meet the requirements for "required" receptacles they can be anywhere from in the floor near the wall all the way up to 5'6" high.
Reply With Quote
  #3  
Old 4/1/07, 2:43 PM
Marc D. Shunk's Avatar
Marc D. Shunk Marc D. Shunk is offline
Banned
 
Join Date: Dec 2006
Location: Central PA
Posts: 1,980
Please Note: Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: New for old.

A couple quick comments...
  • The main does appear to be a 100 amp main. I'm not that familiar with GE equipment, but it is possible that the panel and its associated buss are rated at up to 200 amp, and they installed a 100 amp main breaker. No problem. Some people do this to get a generously sized panel, with lots of "slots"
  • The new wiring that is completed so far seems a bit messy, and was probably DIY work. It should be scrutinized more closely than normal by somebody.
  • That second (sub)panel is partially behind the structure that supports the service rated panel. That's a working space violation that will present a hazard to people working on that panel, and also may not permit 90° opening of the panel door.
  • I have no idea why an AFCI breaker for the refrigerator. That is odd, but no safety issue exists. That does put them at greater risk for loss of refrigerated food items in the future.
  • #10 to the refrigerator is weird, too. Is this the type of home that you envision could be completed as a 'high end' dwelling? Some of the Sub-Zero brand/style refrigerators may require a more stout branch circuit.
  • The blue insulated butt splices that are extending the existing K&T into the new panel should be checked by somebody to assure that the crimping procedure was properly completed by appropriate tooling. It is difficult to get a good crimp on solid conductors, and even more difficult to get a quality crimp with improper crimping tooling.
  • The black electrical tape on the end of the jacket of the 6-3 cable that feeds the sub panel is suspicious. This is often a sign that a DIY skinned the cable jacket, and nicked the conductor insulation off as well.
  • The feed to the subpanel appears to be improperly wired. It appears to be fed with 4-wire, but setup as 3-wire. The grounds and neutrals do not appear to be seperated.
DIY To The Rescue, for sure.

Last edited by Marc D. Shunk; 4/1/07 at 2:49 PM..
Reply With Quote
  #4  
Old 4/1/07, 2:52 PM
mthomas2 mthomas2 is offline
Active Poster
 
Join Date: Oct 2005
Location: Evanston, IL
Posts: 703
Please Note: mthomas2 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: New for old.

"Why would they use armored cable when the application would of been easier to use romex? The application is at the attic floor that is being finished & the notched the sub floor but ran Armored cable?"

Neither would be correct for installation below a finished floor if installed by "notching" subflooring if by "notching" you mean, for example, routing a channel in the subflooring or installing the cable in the space between two sheets of subflooring material.
Reply With Quote
  #5  
Old 4/1/07, 4:35 PM
David C. Macy's Avatar
David C. Macy David C. Macy is offline
InterNACHI Member
 
Join Date: Jan 2004
Location: NE. OH
Posts: 2,657
Default Re: New for old.

Quote:
Originally Posted by mthomas2
"Why would they use armored cable when the application would of been easier to use romex? The application is at the attic floor that is being finished & the notched the sub floor but ran Armored cable?"

Neither would be correct for installation below a finished floor if installed by "notching" subflooring if by "notching" you mean, for example, routing a channel in the subflooring or installing the cable in the space between two sheets of subflooring material.
Actually they drilled the holes thru the floor joist & I made a mistake by saying notched. It just seemed odd that they were using armored cable.
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Making a six-figure salary using the Five P's rray Miscellaneous Discussion for Inspectors 270 6/8/07 6:20 AM
FREE fold up chairs with beer holder. gromicko Special Discounts for InterNACHI Inspectors 2 5/9/07 9:42 PM
FREE fold up chairs with beer holder. gromicko Canadian Inspectors 6 5/8/07 11:43 PM
Great Lakes - East Chapter of NACHI developing their own Seller Inspection brochure. gromicko Miscellaneous Discussion for Inspectors 1 3/3/07 12:03 PM


All times are GMT -4. The time now is 3:50 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts