Default New one on me

new-one-me-elec2.jpg

I am kinda lost on this one guys and I am not sure if you can figure it out from such a poor photo but here it goes. It appears to me the fused panel on the left is the main. It has incoming #3 Awg Copper conductors. But it also appears the load center is rated at 60 AMP (It says A. 60 240V on the front). The sub-panel is a GE load center 125 AMP max Breaker set up. I have reported it as 60 AMP and now I am not sure since I rarely see a set up like this let known fused as oppose to breakers. I hope you can somehow blow up the photo to get a closer look. There is also double tapping and such and all was written up. Okay fellas beat this one up and let me know if I am correct to say 60 AMP. Realtors get funny when it comes to reporting 60 AMP service.
Thanks in advance and Happy Easter!
Reply With Quote
  #2  
Old 3/22/08, 9:03 PM
Michael Larson's Avatar
Michael Larson Michael Larson is offline
InterNACHI Member
 
Join Date: May 2006
Location: Hudson, WI including the Twin Cities of MN
Posts: 18,489
Default Re: New one on me

Randy, what feeds the newer distrubution panel?

Any better pics?



"Never underestimate the difficulty of changing false beliefs by facts."
Henry Rosovsky-Harvard

Michael Larson
Hudson, WI

Services provided in East MN and West WI
InspectraPro
or
Minnesota Home Inspector

Reply With Quote
  #3  
Old 3/22/08, 9:05 PM
Randy D. Stufflebeem's Avatar
Randy D. Stufflebeem Randy D. Stufflebeem is offline
InterNACHI Member
 
Join Date: Nov 2006
Location: Galesburg, IL
Posts: 2,889
Default Re: New one on me

Quote:
Originally Posted by mlarson
Randy, what feeds the newer distrubution panel?

Any better pics?
Michael,

I apologize I have no better pics but the incoming to the newer panel is #6 AWG Copper. Hope this helps!
Reply With Quote
  #4  
Old 3/22/08, 9:09 PM
Michael Larson's Avatar
Michael Larson Michael Larson is offline
InterNACHI Member
 
Join Date: May 2006
Location: Hudson, WI including the Twin Cities of MN
Posts: 18,489
Default Re: New one on me

Quote:
Originally Posted by rstufflebeem
Michael,

I apologize I have no better pics but the incoming to the newer panel is #6 AWG Copper. Hope this helps!
Was it fed by the range "pullout" or doubled up with the incoming #3?



"Never underestimate the difficulty of changing false beliefs by facts."
Henry Rosovsky-Harvard

Michael Larson
Hudson, WI

Services provided in East MN and West WI
InspectraPro
or
Minnesota Home Inspector

Reply With Quote
  #5  
Old 3/22/08, 9:13 PM
Randy D. Stufflebeem's Avatar
Randy D. Stufflebeem Randy D. Stufflebeem is offline
InterNACHI Member
 
Join Date: Nov 2006
Location: Galesburg, IL
Posts: 2,889
Default Re: New one on me

Quote:
Originally Posted by mlarson
Was it fed by the range "pullout" or doubled up with the incoming #3?
I will look up the report and get back to you. Off to Easter Mass! Thanks for your help so far.
Randy
PS: Been a brutal Electrical week for me!
Reply With Quote
  #6  
Old 3/22/08, 9:13 PM
rcooke rcooke is offline
Banned for Violating COE
 
Join Date: Aug 2003
Location: Brighton, ON
Posts: 9,381
Please Note: rcooke is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: New one on me

Weakest link in the chain It says 60 amp then thats what it is.
...Cookie
Reply With Quote
  #7  
Old 3/22/08, 9:25 PM
Randy D. Stufflebeem's Avatar
Randy D. Stufflebeem Randy D. Stufflebeem is offline
InterNACHI Member
 
Join Date: Nov 2006
Location: Galesburg, IL
Posts: 2,889
Default Re: New one on me

Quote:
Originally Posted by mlarson
Was it fed by the range "pullout" or doubled up with the incoming #3?
Kids are not quite ready to go! It is fed by the "pull out" on the right side. I am weak with fused anything so the more you can give me the less I have to bug you all with it later Gotta go Catholic Easter mass lasts like a million years. I will check back later!
Thanks

PS: Cookie, agreed!
Reply With Quote
  #8  
Old 3/22/08, 9:27 PM
Greg Fretwell Greg Fretwell is offline
Active Poster
 
Join Date: Jul 2004
Location: Estero Florida
Posts: 1,798
Please Note: Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: New one on me

I am betting this is 100a service with a split bus panel using the right pullout to feed the GE breaker panel at 60a.
Reply With Quote
  #9  
Old 3/22/08, 9:27 PM
Speedy Petey Speedy Petey is offline
Active Poster
 
Join Date: Jul 2006
Posts: 1,294
Please Note: Speedy Petey is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: New one on me

That's a 100A service. The "sub" is off the 50 or 60 amp "range" fuses.
One pullout kills the fuses, the other kills the new breaker panel.
Reply With Quote
  #10  
Old 3/22/08, 9:32 PM
Greg Fretwell Greg Fretwell is offline
Active Poster
 
Join Date: Jul 2004
Location: Estero Florida
Posts: 1,798
Please Note: Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: New one on me

Mike I didn't see any double lugging on the 60a pullout or the main lugs (zooming the picture)
My guess is the range got moved to the lower left 2 pole breaker.
Reply With Quote
  #11  
Old 3/22/08, 9:41 PM
Ralph Brady's Avatar
Ralph Brady Ralph Brady is offline
InterNACHI Member
 
Join Date: Feb 2007
Location: Eureka, CA
Posts: 613
Default Re: New one on me

From my experience, those types of panels typically have 60 - 100 amp cartridge fuses for the main fuse. I never know for sure because I'm not about to pull them out to check. You can get a good idea by looking for the label on the panel. The second panel is fed through the second set of cartridge fuses which would be rated at 40 - 60 amps.

BTW - to enlarge the photo view try CTRL+. (hold the ctrl key while pressing =/+ key) It works on my Windows XP with explorer 7.



"An expert is a person who has made all the mistakes that can be made in a very narrow field"
Niels Bohr

"Learn all you can from the mistakes of others. You won't have time to make them all yourself"
Alfred Sheinwold


Eureka, Fortuna & Arcata, CA
Reply With Quote
  #12  
Old 3/22/08, 9:49 PM
Michael Larson's Avatar
Michael Larson Michael Larson is offline
InterNACHI Member
 
Join Date: May 2006
Location: Hudson, WI including the Twin Cities of MN
Posts: 18,489
Default Re: New one on me

Quote:
Originally Posted by Greg Fretwell
Mike I didn't see any double lugging on the 60a pullout or the main lugs (zooming the picture)
My guess is the range got moved to the lower left 2 pole breaker.
That's the way I saw it too. Tough to tell from the small pics.

Should be a 60 Amp Service then agree?



"Never underestimate the difficulty of changing false beliefs by facts."
Henry Rosovsky-Harvard

Michael Larson
Hudson, WI

Services provided in East MN and West WI
InspectraPro
or
Minnesota Home Inspector

Reply With Quote
  #13  
Old 3/22/08, 10:08 PM
rromoser's Avatar
rromoser rromoser is offline
InterNACHI Member
 
Join Date: Oct 2006
Location: Fishers, IN
Posts: 187
Default Re: New one on me

This panel appears to be a 60 amp service. Cartridge fuses rated for 100 amps typically have 1/2 inch copper blades at each end. This makes them longer than 60 amp cartridge fuses. Usually a 100 amp panel with a single main pull-out is located at the top of the panel all by itself. Not side by side with another pull-out.
BTW The main is the left pull-out.
Reply With Quote
  #14  
Old 3/22/08, 10:17 PM
Greg Fretwell Greg Fretwell is offline
Active Poster
 
Join Date: Jul 2004
Location: Estero Florida
Posts: 1,798
Please Note: Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: New one on me

No this looks like 100amp. There is no "main" hence no 100a fuses. It is a split bus panel. One pullout goes to the plug fuse array in the bottom and the other is now feeding the breaker panel. The rails behind the pullouts are hot all the time.
Reply With Quote
  #15  
Old 3/22/08, 10:21 PM
Speedy Petey Speedy Petey is offline
Active Poster
 
Join Date: Jul 2006
Posts: 1,294
Please Note: Speedy Petey is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: New one on me

Quote:
Originally Posted by rromoser
BTW The main is the left pull-out.
And the "Range" main is on the right.
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On



All times are GMT -4. The time now is 8:30 AM.


Copyright © International Association of Certified Home Inspectors, Inc. 1 2 3 4 5 6 7 8 9 10 11 12 13 14 15 16 17 18 19 20 21 22 23 24 25 26 27 28 29 30 31 32 33 34 35 36 37 38 39 40 41 42 43 44 45 46 47 48 49 50 51 52 53 54 55 56 57 58 59 60 61 62 63 64 65 66 67 68 69 70 71 72 73 74 75 76 77 78 79 80 81 82 83 84 85 86 87 88 89 90 91 92 93 94 95 96 97 98 99 100 101 102 103 104 105 106 107 108 109 110 111 112 113 114 115 116 117 118 119 120 121 122 123 124 125 126 127 128 129 130 131 132 133 134 135 136 137 138 139 140 141 142 143 144 145 146 147

Popular Sections

:

All Sections

Popular

Membership

Inspection Standards

Education

Chapters & Members

Articles & Links

Other Organizations

 

 

 

NACHI.ORG Statistics

 

 

no new posts