#1
|
||||
|
||||
![]() I am kinda lost on this one guys and I am not sure if you can figure it out from such a poor photo but here it goes. It appears to me the fused panel on the left is the main. It has incoming #3 Awg Copper conductors. But it also appears the load center is rated at 60 AMP (It says A. 60 240V on the front). The sub-panel is a GE load center 125 AMP max Breaker set up. I have reported it as 60 AMP and now I am not sure since I rarely see a set up like this let known fused as oppose to breakers. I hope you can somehow blow up the photo to get a closer look. There is also double tapping and such and all was written up. Okay fellas beat this one up and let me know if I am correct to say 60 AMP. Realtors get funny when it comes to reporting 60 AMP service. Thanks in advance and Happy Easter! |
|
#2
|
||||
|
||||
|
Randy, what feeds the newer distrubution panel?
Any better pics? "Never underestimate the difficulty of changing false beliefs by facts." |
|
#3
|
||||
|
||||
|
Quote:
I apologize I have no better pics but the incoming to the newer panel is #6 AWG Copper. Hope this helps! |
|
#4
|
||||
|
||||
|
Quote:
"Never underestimate the difficulty of changing false beliefs by facts." |
|
#5
|
||||
|
||||
|
Quote:
Randy PS: Been a brutal Electrical week for me! |
|
#6
|
|||
|
|||
|
Please Note:
rcooke is a non-member guest and is in no way affiliated with InterNACHI or its members.
Weakest link in the chain It says 60 amp then thats what it is.
...Cookie |
|
#7
|
||||
|
||||
|
Quote:
Thanks PS: Cookie, agreed! |
|
#8
|
|||
|
|||
|
Please Note:
Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
I am betting this is 100a service with a split bus panel using the right pullout to feed the GE breaker panel at 60a.
|
|
#9
|
|||
|
|||
|
Please Note:
Speedy Petey is a non-member guest and is in no way affiliated with InterNACHI or its members.
That's a 100A service. The "sub" is off the 50 or 60 amp "range" fuses.
One pullout kills the fuses, the other kills the new breaker panel. |
|
#10
|
|||
|
|||
|
Please Note:
Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
Mike I didn't see any double lugging on the 60a pullout or the main lugs (zooming the picture)
My guess is the range got moved to the lower left 2 pole breaker. |
|
#11
|
||||
|
||||
|
From my experience, those types of panels typically have 60 - 100 amp cartridge fuses for the main fuse. I never know for sure because I'm not about to pull them out to check. You can get a good idea by looking for the label on the panel. The second panel is fed through the second set of cartridge fuses which would be rated at 40 - 60 amps.
BTW - to enlarge the photo view try CTRL+. (hold the ctrl key while pressing =/+ key) It works on my Windows XP with explorer 7. "An expert is a person who has made all the mistakes that can be made in a very narrow field" Niels Bohr "Learn all you can from the mistakes of others. You won't have time to make them all yourself" Alfred Sheinwold Eureka, Fortuna & Arcata, CA
|
|
#12
|
||||
|
||||
|
Quote:
Should be a 60 Amp Service then agree? "Never underestimate the difficulty of changing false beliefs by facts." |
|
#13
|
||||
|
||||
|
This panel appears to be a 60 amp service. Cartridge fuses rated for 100 amps typically have 1/2 inch copper blades at each end. This makes them longer than 60 amp cartridge fuses. Usually a 100 amp panel with a single main pull-out is located at the top of the panel all by itself. Not side by side with another pull-out.
BTW The main is the left pull-out. |
|
#14
|
|||
|
|||
|
Please Note:
Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
No this looks like 100amp. There is no "main" hence no 100a fuses. It is a split bus panel. One pullout goes to the plug fuse array in the bottom and the other is now feeding the breaker panel. The rails behind the pullouts are hot all the time.
|
|
#15
|
|||
|
|||
|
Please Note:
Speedy Petey is a non-member guest and is in no way affiliated with InterNACHI or its members.
Quote:
|
![]() |