Default Re: New one on me

I think calling either of the pullouts a "main" is going to be misleading. The one on the left is simply a disconnect for the plug fuses and the one on the right used to be for the range (or some other large appliance), now it disconnects the breaker panel. Pulling either one does not disconnect the other side.
This is a classic case of the < 6 disconnect rule. There are 2. Some of these panels could have more pullouts. I have seen 4 and I suppose 6 would be possible. Marc is our expert on antique hardware.
Reply With Quote
  #17  
Old 3/23/08, 1:46 AM
Randy D. Stufflebeem's Avatar
Randy D. Stufflebeem Randy D. Stufflebeem is offline
InterNACHI Member
 
Join Date: Nov 2006
Location: Galesburg, IL
Posts: 3,278
Default Re: New one on me

new-one-me-100_0014-medium-.jpg.jpg
Views:	48
Size:	51.2 KB
ID:	19783
new-one-me-100_0015-medium-.jpg.jpg
Views:	44
Size:	81.3 KB
ID:	19784

I think this may help fellas! Enlarged and another photo thrown. The front cover said A. 60 and 240V which was my first indication of 60 AMP fused. The left "pull out" is the incoming service connection #3 Copper. The right "pull out" has #6 Copper to the sub-panel (newer).
Reply With Quote
  #18  
Old 3/23/08, 2:29 AM
Marc D. Shunk's Avatar
Marc D. Shunk Marc D. Shunk is offline
Banned
 
Join Date: Dec 2006
Location: Central PA
Posts: 1,980
Please Note: Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: New one on me

Quote:
Originally Posted by Greg Fretwell
I think calling either of the pullouts a "main" is going to be misleading.
Not really.

I'd rather see this subpanel under the range pullout than the subfeed lugs.

This install looks like good work, to me, save for the fact that they didn't feed it with 4-wire.
Reply With Quote
  #19  
Old 3/23/08, 2:53 AM
Greg Fretwell Greg Fretwell is offline
Active Poster
 
Join Date: Jul 2004
Location: Estero Florida
Posts: 1,798
Please Note: Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: New one on me

Marc I was just referring to the fact that pulling either one will not drop power to the whole panel like most people think of when they say "main" AKA Service Disconnect"
Reply With Quote
  #20  
Old 3/23/08, 2:59 AM
Marc D. Shunk's Avatar
Marc D. Shunk Marc D. Shunk is offline
Banned
 
Join Date: Dec 2006
Location: Central PA
Posts: 1,980
Please Note: Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: New one on me

Quote:
Originally Posted by Greg Fretwell
Marc I was just referring to the fact that pulling either one will not drop power to the whole panel like most people think of when they say "main" AKA Service Disconnect"
The "mains" of a split buss panel don't dump the whole panel either. A main is still a main, without regard to how much of the connected load it disconnects. Feel free to make some arbitrary distinction if it gets you hard. You might note that a new panel will come with stickers for this use. It will have one sticker that says "service disconnect" and many stickers that say "main". There is, indeed, a difference. Just because a certain portion of the population might not be aware of this difference is no reason to pretend the distinction does not exist.

Last edited by Marc D. Shunk; 3/23/08 at 3:05 AM..
Reply With Quote
  #21  
Old 3/23/08, 3:18 AM
Greg Fretwell Greg Fretwell is offline
Active Poster
 
Join Date: Jul 2004
Location: Estero Florida
Posts: 1,798
Please Note: Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: New one on me

I guess we are saying the same thing I am just pointing out "main" in this case is not "service disconnect" and that might confuse people who think "I pulled the MAIN, why didn't everything go off". The other thing is they are using the size of the "main" to determine the service size.
Reply With Quote
  #22  
Old 3/23/08, 6:54 AM
David P. Valley's Avatar
David P. Valley David P. Valley is offline
InterNACHI Member
 
Join Date: Jun 2003
Location: METHUEN, MA
Posts: 8,684
Default Re: New one on me

I guess what's most important right now, is what size are the cartridges inside the left pull-out?
Reply With Quote
  #23  
Old 3/23/08, 8:14 AM
jtedesco1 jtedesco1 is offline
Account Suspended Due to Excessive Complaints
 
Join Date: Dec 2005
Posts: 1,891
Please Note: jtedesco1 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: New one on me

Wrong thread deleted and relocated message

Last edited by jtedesco1; 3/23/08 at 12:11 PM..
Reply With Quote
  #24  
Old 3/23/08, 8:34 AM
Speedy Petey Speedy Petey is offline
Unmoderated Guest
 
Join Date: Jul 2006
Posts: 1,297
Please Note: Speedy Petey is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: New one on me

Quote:
Originally Posted by dvalley
I guess what's most important right now, is what size are the cartridges inside the left pull-out?
They can be no larger than 60A, same as the right side.

Two "mains", with a maximum of 60A each.
100A service.

I don't know why this is so confusing. Most of you are clear on what a split-buss breaker panel is. This is no different.
Reply With Quote
  #25  
Old 3/23/08, 8:41 AM
David P. Valley's Avatar
David P. Valley David P. Valley is offline
InterNACHI Member
 
Join Date: Jun 2003
Location: METHUEN, MA
Posts: 8,684
Default Re: New one on me

Quote:
Originally Posted by Speedy Petey
They can be no larger than 60A, same as the right side.

Two "mains", with a maximum of 60A each.
100A service.

I don't know why this is so confusing. Most of you are clear on what a split-buss breaker panel is. This is no different.
I don't see split buss panels in my area.

Tell me something, what is the purpose of using a split buss panel (2 60 amp pulls) verses a simple 100 amp panel?
Reply With Quote
  #26  
Old 3/23/08, 8:46 AM
Speedy Petey Speedy Petey is offline
Unmoderated Guest
 
Join Date: Jul 2006
Posts: 1,297
Please Note: Speedy Petey is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: New one on me

I'm very suprised you don't see them in Ma. We see them ALL the time here in eastern NY.

I'm not sure what the answer is though.
Possibly that one big main was not required, and if one of the several smaller mains tripped it would not take out the whole house? I'm really not sure of the original intent of that design.

The fuse panels were designed that way and used for a LONG time, and breaker panels were very popular in the 50's & 60's.
Reply With Quote
  #27  
Old 3/23/08, 8:50 AM
David P. Valley's Avatar
David P. Valley David P. Valley is offline
InterNACHI Member
 
Join Date: Jun 2003
Location: METHUEN, MA
Posts: 8,684
Default Re: New one on me

Quote:
Originally Posted by Speedy Petey
I'm very suprised you don't see them in Ma. We see them ALL the time here in eastern NY.

I'm not sure what the answer is though.
Possibly that one big main was not required, and if one of the several smaller mains tripped it would not take out the whole house? I'm really not sure of the original intent of that design.

The fuse panels were designed that way and used for a LONG time, and breaker panels were very popular in the 50's & 60's.
Hmmm, I can't recall ever seeing them here. If I did inspect one, I wasn't aware of it being a spilt buss.
Reply With Quote
  #28  
Old 3/23/08, 1:13 PM
Greg Fretwell Greg Fretwell is offline
Active Poster
 
Join Date: Jul 2004
Location: Estero Florida
Posts: 1,798
Please Note: Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: New one on me

I think it was simply the cost of 100a fuses. You could put in a pair of 60s to run the 120v and then use other pullouts for the range and any other 240v loads. My next door neighbor has a 4 pullout split bus panel, installed in the 60s. One P/U controls 8 (or 10?) plug fuses, one goes to the water heater, one for the range and one for the wall heaters. I really try to stay away from this thing. I did take out all the 30a fuses and replace them with 20s but since they have fuse stat adapters and I don't have the tool I couldn't get them to the 15s that belong in there.
I have told this lady a bunch of times she needs a panel upgrade and I won't work on it.
Reply With Quote
  #29  
Old 3/23/08, 1:18 PM
jtedesco1 jtedesco1 is offline
Account Suspended Due to Excessive Complaints
 
Join Date: Dec 2005
Posts: 1,891
Please Note: jtedesco1 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: New one on me

Here's a diagram of this equipment along with an explanation:

Reply With Quote
  #30  
Old 3/23/08, 1:24 PM
Peter Hughes Peter Hughes is offline
InterNACHI Member
 
Join Date: Feb 2003
Location: Garland, TX
Posts: 126
Default Re: New one on me

Good picture Joe



"Arrogance and Ignorance are not mutually exclusive"
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On



All times are GMT -4. The time now is 4:56 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts