Default New Panel, Old Meter

Fellow Inspectors,

50 year old home. New Panel. See if you can identify the issue.

Anatol
Attached Thumbnails
new-panel-old-meter-panel.jpg  
Reply With Quote
  #2  
Old 2/3/07, 6:17 PM
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,072
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: New Panel, Old Meter

lol.....a bit blurry but I see a few obvious violations.........should we post them or let YOU do it



Paul W. Abernathy
Reply With Quote
  #3  
Old 2/3/07, 6:29 PM
apolillo's Avatar
apolillo apolillo is offline
Active Poster
 
Join Date: Nov 2004
Location: Baltimore, Md
Posts: 191
Please Note: apolillo is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: New Panel, Old Meter

Let's see what comes in..............
Hint... The main breaker is 100 amps
Reply With Quote
  #4  
Old 2/3/07, 6:31 PM
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,072
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: New Panel, Old Meter

OK....lets all post one and see how long it takes to get a bunch....

1.) I doubt that MOUNTING hole was designed for the GEC to enter into it...

Edit: Yep I was right...thats the GEC in that mounting hole...shame..shame...

Who's Next.....



Paul W. Abernathy

Last edited by pabernathy; 2/3/07 at 6:48 PM..
Reply With Quote
  #5  
Old 2/3/07, 6:35 PM
gbeaumont's Avatar
gbeaumont gbeaumont is offline
InterNACHI Member
 
Join Date: Jan 2003
Location: Clearwater, FL
Posts: 6,261
Send a message via AIM to gbeaumont Send a message via MSN to gbeaumont Send a message via Yahoo to gbeaumont
Default Re: New Panel, Old Meter

Hi Anatol,

what size are those conductors?

Regards

Gerry



"To realize our true destiny, we must be guided not by a myth from our past, but by a vision of our future."
(Mark B Adams)

Commercial property Inspection Tampa, Orlando, Sarasota, Jacksonville, Ft Launderdale, Miami, Florida.
NACHI cell 484-429-5466
NACHI02121106

Reply With Quote
  #6  
Old 2/3/07, 6:39 PM
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,072
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: New Panel, Old Meter

Not fair GB.....you gotta GUESS mate...



Paul W. Abernathy
Reply With Quote
  #7  
Old 2/3/07, 6:40 PM
gbeaumont's Avatar
gbeaumont gbeaumont is offline
InterNACHI Member
 
Join Date: Jan 2003
Location: Clearwater, FL
Posts: 6,261
Send a message via AIM to gbeaumont Send a message via MSN to gbeaumont Send a message via Yahoo to gbeaumont
Default Re: New Panel, Old Meter

Quote:
Originally Posted by pabernathy
Not fair GB.....you gotta GUESS mate...
Well my guess is that they are far from big enough

Regards

Gerry



"To realize our true destiny, we must be guided not by a myth from our past, but by a vision of our future."
(Mark B Adams)

Commercial property Inspection Tampa, Orlando, Sarasota, Jacksonville, Ft Launderdale, Miami, Florida.
NACHI cell 484-429-5466
NACHI02121106

Reply With Quote
  #8  
Old 2/3/07, 6:46 PM
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,072
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: New Panel, Old Meter

Thats a BRITISH way of saying Mr. B thinks those ungrounded conductors are a bit undersized for that main OCPD.......



Paul W. Abernathy
Reply With Quote
  #9  
Old 2/3/07, 6:47 PM
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,072
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: New Panel, Old Meter

DANG...now that picture is REAL clear.......Bravo ..Bravo

Ok...someone elses turn...( please dont say that easy one on the lower right...)

Also for clarrification...Anatol...where exactly is that GEC conductor going to..does not seem to be going to the terminal bar that are in VIEW...



Paul W. Abernathy

Last edited by pabernathy; 2/3/07 at 6:56 PM..
Reply With Quote
  #10  
Old 2/3/07, 6:56 PM
gbeaumont's Avatar
gbeaumont gbeaumont is offline
InterNACHI Member
 
Join Date: Jan 2003
Location: Clearwater, FL
Posts: 6,261
Send a message via AIM to gbeaumont Send a message via MSN to gbeaumont Send a message via Yahoo to gbeaumont
Default Re: New Panel, Old Meter

Quote:
Originally Posted by pabernathy
DANG...now that picture is REAL clear.......Bravo ..Bravo

Ok...someone elses turn...( please dont say that easy one on the lower right...)
OK Paul I won't mention the bushing issue,but what I want to know is when did Anatol start inspecting in Australia??

Regards

Gerry



"To realize our true destiny, we must be guided not by a myth from our past, but by a vision of our future."
(Mark B Adams)

Commercial property Inspection Tampa, Orlando, Sarasota, Jacksonville, Ft Launderdale, Miami, Florida.
NACHI cell 484-429-5466
NACHI02121106

Reply With Quote
  #11  
Old 2/3/07, 6:57 PM
apolillo's Avatar
apolillo apolillo is offline
Active Poster
 
Join Date: Nov 2004
Location: Baltimore, Md
Posts: 191
Please Note: apolillo is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: New Panel, Old Meter

Gerry,
Bingo... The are the original copper 60 amp feed.
The only thing I inspected in Australia was the outback.........
Reply With Quote
  #12  
Old 2/3/07, 7:01 PM
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,072
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: New Panel, Old Meter

BUT thats not all thats wrong with that panel...lol....we have found quite a few...lol
Attached Thumbnails
new-panel-old-meter-panel.jpg  



Paul W. Abernathy

Last edited by pabernathy; 2/3/07 at 7:06 PM..
Reply With Quote
  #13  
Old 2/3/07, 7:19 PM
apolillo's Avatar
apolillo apolillo is offline
Active Poster
 
Join Date: Nov 2004
Location: Baltimore, Md
Posts: 191
Please Note: apolillo is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: New Panel, Old Meter

Thanks Paul, I did write all of those up, just wanted to have some fun with the SEC question.
Anatol
Reply With Quote
  #14  
Old 2/3/07, 7:27 PM
Marc D. Shunk's Avatar
Marc D. Shunk Marc D. Shunk is offline
Banned
 
Join Date: Dec 2006
Location: Central PA
Posts: 1,980
Please Note: Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: New Panel, Old Meter

Paul, I agree with your picture commentary that the concentric conductor not being twisted is "lazy".

I marvel at times at the workmanship of dead and gone electricians, who's names I'll never know. It's a treat when you come across many of these old SE cable installs where the original electrician actually took the time to braid the concentric conductor's strands. I should learn how to braid, because that sure makes for a sweet looking install.
Reply With Quote
  #15  
Old 2/4/07, 2:55 AM
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,072
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: New Panel, Old Meter

Braid hell.........how about thety just TWIST the damn thing like a freakin normal electrician would. Also newly installed SO CALLED upgrade so that electrician is STILL livin.....You can admire him freely...I dont.



Paul W. Abernathy
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
National Electrical Code Information and Discussion jtedesco1 Electrical Inspections 50 6/15/10 7:28 PM
City electrical inspector says move the meter and panel cbottger Electrical Inspections 9 4/4/07 8:59 PM
Panel Inspection Safety roconnor Electrical Inspections 10 9/24/06 9:02 PM
Bad electrical problem Pest Guy Electrical Inspections 4 1/20/06 9:26 PM