Default New Standards for GFCI's

02/01/2006

New Standards Set for Ground Fault Circuit Interrupters

An extensive evaluation ground fault circuit interrupters (GFCI), one of the major innovations in electrical safety, recently yielded new safety requirements from the Underwriters Laboratories, Inc. (UL), and the Canadian Standards Association (CSA).


Since the early 1970s, GFCIs have reduced household electrocutions by protecting residents from lethal currents. A GFCI is a wiring device that de-energizes a circuit when a current to ground could result in electric shock. The GFCI "interrupts" power before it reaches a level that would cause injury. The National Electrical Code(r) requires GFCIs to be used in bathrooms, kitchens, garages, basements, crawlspaces, and outdoors. Similarly, the Canadian Electrical Code (CEC) requires GFCI´s to be used in many locations such as bathrooms, outdoors, basic care areas of hospitals, pools, spas, and hot tubs.


Before the introduction of GFCIs, more than 700 people died from household electrocutions each year. As of 2001, that number had been reduced to 400 cases annually. However, a 2001 field study from UL and the National Electrical Manufacturers Association determined that a small but significant percent of GFCIs, particularly older ones, did not work after several years. These findings created a demand for more stringent safety features that can alert users when a GFCI malfunctions.


The new requirements are being set by the CSA and UL and apply to the harmonized standard, UL 943, Safety Standard for Ground Fault Circuit Interrupters (GFCIs) and CSA C22.2 No. 144.1 (Ground Fault Circuit Interrupters). New UL and CSA requirements include:
  • End of Life Provision: when a GFCI receptacle is incapable of passing its internal test function (it can no longer provide ground fault protection) it will either a) render itself incapable of delivering power, or b) indicate by visual or audible means that the device must be replaced.
  • Reverse Line-Load Miswire: a GFCI will deny power to the receptacle face if it is miswired.
In the U.S., manufacturers must stop producing old versions of GFCIs on July 28, 2006, and must introduce new, redesigned GFCIs after that date. Distributors can sell and contractors can install old GFCIs until their supplies run out. The UL revisions will not affect the NEC, which regulates installations, not products.


In Canada, the selection of the effective date involves a process that has not yet been completed. Once this occurs, the effective date will be included in the Certification Notice announcing the 2006 edition of CSA Standard C22.2 No. 144.1. The CSA revisions will not affect the CEC, which regulates installations, not products.


For more information about GFCIs or the new UL and CSA requirements, contact the Electrical Safety Foundation International at (703)841-3229 or visit http://www.esfi.org.



http://hisearch.org has over 1,000 hits per month and climbing. Currently ranked #1 in many search engines for determing the age of HVAC equipment. Check it out at http://hisearch.org/hvac.aspx Feel free to bookmark and use our site at any time.

List your business in our Home Inspector Registry with a link exchange. Check out your state now at http://hisearch.org/homeinspectorregistry.aspx Are you listed???
Reply With Quote
  #2  
Old 2/18/06, 10:43 AM
Jay Schwartz's Avatar
Jay Schwartz Jay Schwartz is offline
InterNACHI Member
 
Join Date: Apr 2004
Location: Pembroke Pines, FL
Posts: 663
Default Re: New Standards for GFCI's

John:

Thanks for the Great News. Don't want to have thread drift, but I use a Sperry GFCI tester and whenever I have a GFCI with two white buttons (Cheap Contractor Bulk) receptacles, more than half of the time the test button will work on the device but not when I test it with my device. The traditional red/black buttons I have no problems with at all.

Any thoughts?



Jay Schwartz

Coast To Coast Home Services, Inc
Your Florida Home Inspection Company TM
Corporate Office: 954-673-3479
Naples Office: 239-298-4396
1-877-79-Windstorm

www.CoastToCoastHomeServices.com
www.SaveOnWindStorm.com

South Florida Home Inspectors Association

Southeast Florida NACHI Chapter - VP
Reply With Quote
  #3  
Old 2/18/06, 10:46 AM
Leonard E. Ungar's Avatar
Leonard E. Ungar Leonard E. Ungar is offline
InterNACHI Member
 
Join Date: Oct 2003
Location: Bayport, NY
Posts: 348
Smile Re: New Standards for GFCI's

Hi! John;
I just copied your post on the GFCI's and I am going to show it to all of my students in my module five class today.
It's so much better to help one another instead of nitpicking correct !!!!!!!!!!

Regards Len Ungar [L I Nachi chapter Pres.]
Reply With Quote
  #4  
Old 2/18/06, 10:48 AM
Jay Schwartz's Avatar
Jay Schwartz Jay Schwartz is offline
InterNACHI Member
 
Join Date: Apr 2004
Location: Pembroke Pines, FL
Posts: 663
Default Re: New Standards for GFCI's

Quote:
Originally Posted by lungar
Hi! John;
I just copied your post on the GFCI's and I am going to show it to all of my students in my module five class today.
It's so much better to help one another instead of nitpicking correct !!!!!!!!!!

Regards Len Ungar [L I Nachi chapter Pres.]
Nitpicking?? or speaking the truth??



Jay Schwartz

Coast To Coast Home Services, Inc
Your Florida Home Inspection Company TM
Corporate Office: 954-673-3479
Naples Office: 239-298-4396
1-877-79-Windstorm

www.CoastToCoastHomeServices.com
www.SaveOnWindStorm.com

South Florida Home Inspectors Association

Southeast Florida NACHI Chapter - VP
Reply With Quote
  #5  
Old 2/18/06, 11:25 AM
brian winkle brian winkle is offline
Active Poster
 
Join Date: Sep 2005
Location: Arizona
Posts: 454
Please Note: brian winkle is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: New Standards for GFCI's

Quote:
Originally Posted by jschwartz1
John:

Thanks for the Great News. Don't want to have thread drift, but I use a Sperry GFCI tester and whenever I have a GFCI with two white buttons (Cheap Contractor Bulk) receptacles, more than half of the time the test button will work on the device but not when I test it with my device. The traditional red/black buttons I have no problems with at all.

Any thoughts?
I have never seen cheap GFCI's, we pay $10.00 each for Pass & Seymour. They have two white buttons which look a lot nicer than the black/white ones (Leviton) that Home depot sells in the 3 pack for $27.00.
If they won't trip with your tester perhaps there is no equipment ground, or perhaps there is a problem with your tester. Next time try going from the hot to a nearby grounded water pipe with a Wiggy, that will trip an ungrounded GFCI.

Incidentally, the UL approved test for a GFCI IS the test button, not a piece of test equipment.
Reply With Quote
  #6  
Old 2/18/06, 11:53 AM
Leonard E. Ungar's Avatar
Leonard E. Ungar Leonard E. Ungar is offline
InterNACHI Member
 
Join Date: Oct 2003
Location: Bayport, NY
Posts: 348
Smile Re: New Standards for GFCI's

Hi! Jay;
There you go trying to create havoc, nobody mentioned anything about truth or nontruth. That's one of the biggest problems with this board two many stick there noses in where they don't belong. Have a nice day !!!!!!!!!!!

Regards Len
Reply With Quote
  #7  
Old 2/20/06, 8:10 AM
jbowman's Avatar
jbowman jbowman is offline
Active Poster
 
Join Date: Dec 2003
Location: ROME, PA
Posts: 2,270
Please Note: jbowman is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: New Standards for GFCI's

Quote:
Originally Posted by lungar
Hi! John;
I just copied your post on the GFCI's and I am going to show it to all of my students in my module five class today.
It's so much better to help one another instead of nitpicking correct !!!!!!!!!!

Regards Len Ungar [L I Nachi chapter Pres.]
Exactly.
Reply With Quote
  #8  
Old 2/20/06, 8:43 AM
Robert T. Brown Robert T. Brown is offline
InterNACHI Member
 
Join Date: Sep 2004
Location: Bowmanville, ON
Posts: 140
Default Re: New Standards for GFCI's

Thanks John,

It is great to see members share. Like Len, I too will copy your entire post to hand out to our students.

More of this needs to be done!

Thanks again,

Bob
Reply With Quote
  #9  
Old 2/20/06, 10:48 AM
jbowman's Avatar
jbowman jbowman is offline
Active Poster
 
Join Date: Dec 2003
Location: ROME, PA
Posts: 2,270
Please Note: jbowman is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: New Standards for GFCI's

Quote:
Originally Posted by rbrown1
Thanks John,

It is great to see members share. Like Len, I too will copy your entire post to hand out to our students.

More of this needs to be done!

Thanks again,

Bob
You're welcome.
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Texas Warranty Inspection Standards badair General Inspection Discussion 5 9/30/06 6:12 PM
PIC of State Rep and sponsor of new NACHI H.I. Bill in NH. gromicko Misc. Discussion 53 8/30/06 6:58 PM
AZ Home inspector rules and standards committee tallen Legislation, Licensing & Legal Issues 51 6/7/06 2:14 PM
ILLINOIS Section 1410.200 Standards of Practice jtedesco1 Legislation, Licensing & Legal Issues 11 3/9/06 12:22 PM


All times are GMT -4. The time now is 8:25 AM.


Copyright © International Association of Certified Home Inspectors, Inc. 1 2 3 4 5 6 7 8 9 10 11 12 13 14 15 16 17 18 19 20 21 22 23 24 25 26 27 28 29 30 31 32 33 34 35 36 37 38 39 40 41 42 43 44 45 46 47 48 49 50 51 52 53 54 55 56 57 58 59 60 61 62 63 64 65 66 67 68 69 70 71 72 73 74 75 76 77 78 79 80 81 82 83 84 85 86 87 88 89 90 91 92 93 94 95 96 97 98 99 100 101 102 103 104 105 106 107 108 109 110 111 112 113 114 115 116 117 118 119 120 121 122 123 124 125 126 127 128 129 130 131 132 133 134 135 136 137 138 139 140 141 142 143 144 145 146

Popular Sections

:

All Sections

Popular

Membership

Inspection Standards

Education

Chapters & Members

Articles & Links

Other Organizations

 

 

 

NACHI.ORG Statistics

 

 

no new posts